chop saws are often an issue.
Hope this helps,
Chris
On Wed, Oct 11, 2023 at 10:19 AM Jay via RE-wrenches
wrote:
I’d look at a 3 phase pump with vfd/soft start control and
eliminate the start surge.
Jay
> On Oct 11, 2023, at 8:12 AM, frenergy via RE-wrench
I'm looking for opinions and/or real world experience on recommendation
for the largest 240V submersible well pump the Sol-Ark 12KW inverter can
start/run. Assume 500 watt load prior to starting the pump, static
level of water in well is 75 feet, system psi when it starts is 40.
Thanks,
Bi
hinking about doing a job I have in mind with
buss bars and plexi dead front vs 4/0 cable.
Jay
On Sep 21, 2023, at 9:25 PM, frenergy via RE-wrenches
wrote:
Jay,
I sent a diagram of my proposed arrangement and bus sizes
to SimpliPhi prior to installation, which they approved. The bu
Wrenchers,
We haven't done any hybrid systems with the Outback Mojave
with ESS yet. Comments up or down accepted.
Thanks, Bill
Feather River Solar Electric
Bill Battagin, Owner
4291 Nelson St.(shipping)
5575 Genesee Rd. (USPS, UPS)
Taylorsville, CA 95983
530.284.1925 Office/ 530.
David,
I don't have your part and it doesn't look like Zonna has it
either, though a phone call might be good to confirm:
https://www.zonnaenergy.com/solar/replacement-parts/outback/gs-series/outback-power-gs8048-parts/?8060_device=tablet
They claim they can fix components also, thoug
Adam,
Have you registered and been working through their new and
"improved" Online Service Center? I just needed a replacement inverter
for a 1001 code and it was pretty clunky going through the OSC:
https://my.sma-service.com/s/?language=en_US
I'm hoping it gets better but it t
Not sure where this install is located but here in the Sierra, we had a
near record snowfall and we saw a few failures, very few, but...
Bill
Feather River Solar Electric
Bill Battagin, Owner
4291 Nelson St.(shipping)
5575 Genesee Rd. (USPS, UPS)
Taylorsville, CA 95983
530.284.1925 Office/ 530.
Wrenches,
I've got a call from a customer that said their (my
install) 17 year old GT system went dead. Basic stats: 23, Mitsubishi
PVMF120EC3, label says V mpp= 17.6V and Voc = 22 V; top-of-pole; SMA
SB3800U. Its one string of 23 PVs. Full sun, 75 degrees ambient during
testing.
l double your parasitic load, I have not done this
so beware. This is not the answer for V2H; other inverters can
work in this combination but
On Wed, May 10, 2023 at 10:04 AM frenergy via RE-wrenches
wrote:
The wrench list has some very creative thinkers that
The wrench list has some very creative thinkers that may have a
go around to be able to master/slave an old Radian's output with a new
one. Outback says this is not do-able. We're completely off-grid out
here and have been charging EVs (one at a time) with an eleven year old
Radian
Kris,
Seems there was discussion about scanners before and I
don't remember anyone saying they found one that was reliable especially
with varying roofing materials. Our current method is fist-thumping to
get in the area of the rafter, drill exploratory hole then use the
Chiptool
Howie,
SimpliPhi also has the benefit of adding smaller KWhr
batteries (3.8). They have a ten year warranty but also say:" AmpliPHI
and PHI batteries’ /expected/ cycle life rating is 10,000 cycles when a
maximum of 80% DOD is maintained"
Bill
Feather River Solar Electric
Bill B
Wrenches,
I feel compelled to chime in here. Ten years ago, we
installed 24, Rolls 2-KS-33P, 2 volt batteries for the shop. Though they
were in a climate-controlled environment and maybe went to 50% SOC a
dozen times over 10 years, usually ranged 75-100% SOC, we had the first
fai
Matt,
I guess my questions are 1/2" plywood or 5/8" and how thick
is the foam? Oh and I assume its nominal 2X6 T&G? Do you know how the
plywood is attached?.through the foam into the T&G?... to stringers,
nailers or whatever they're called?
Bill
Feather River Solar Electri
Greg,
My Fronius manual goes up to a code 517 but no "higher". I
assume you're talking about an "IG". The last Ph # I used for them was
810-220-4414.
Bill
Feather River Solar Electric
Bill Battagin, Owner
4291 Nelson St.(shipping)
5575 Genesee Rd. (USPS, UPS)
Taylorsville, CA 9
Carl,
In my area (PG&E, N. California) I've installed solar on
four of my rentals. Rather than trying to figure out monthly billing,
renters come, renters go, true-up, some occasionally don't pay their
bills, etc. I decided to just bump up the rent to cover the average cost
of po
Hi Wayne,
We've done about a dozen Outback systems with SimpliPhi
batteries. SimpliPhi has integration guides with well thought out and
complete settings to program OB Inverters and CC's the play properly
with SimpliPhi batteries (24 and 48 volt). Straight-forward stuff.
Bill
Michael,
Are you using kerosene as a cutting fluid? We've had
better luck with that in softer than steel metals.
Bill
Feather River Solar Electric
Bill Battagin, Owner
4291 Nelson St.
Taylorsville, CA 95983
530.284.7849
CA Lic 874049
On 9/11/2022 7:00 PM, Michael Morningstar via
Doesn't the EVO have that capability?
Bill
Feather River Solar Electric
Bill Battagin, Owner
4291 Nelson St.
Taylorsville, CA 95983
530.284.7849
CA Lic 874049
Solar Powered since 1982
On 9/2/2022 7:51 PM, Jeremy Rodriguez via RE-wrenches wrote:
Can anyone recommend a reliable AGS module that w
Its kinda fuzzy in my head now but about a year and a half ago we
delivered a pallet of old PVs to some warehouse in Reno (Sparks) on Greg
St. It was supposed to be the beginning of recycling here on the west
coast and was headed up by Sam Vanderhoof and a fellow named Lamar.
Hopefully this i
Jay,
With the SimpliPhi's we've been installing we require a
shed on slab, walls R-21, roof, R-38 and then the smallest propane wall
heater (they use zero power to operate) we can find and set it at 55
degrees. No need for the insulated box or fretting about toasting $20K+
in bat
Just stack 8 SimpliPhi 3.8's for your 30 Kwhrs.
Bill
Feather River Solar Electric
Bill Battagin, Owner
4291 Nelson St.
Taylorsville, CA 95983
530.284.7849
CA Lic 874049
On 7/13/2022 4:14 AM, Jeremy Rodriguez via RE-wrenches wrote:
I’d look at the Simpliphi brand
We’ve had good luck, however th
As an aside, maybe I've been living under a rock but I have not heard of
1800 RPM gensets running on propane, but exclusive to diesel. It sounds
like that's a thing. I'm small time off-grid here but I could easily
see 3-4 units/year. I'm assuming if this come to fruition, the
manufacturer wo
Chalk it up as another reason Rapid Shutdown is a bummer.
Bill
Feather River Solar Electric
Bill Battagin, Owner
4291 Nelson St.
Taylorsville, CA 95983
530.284.7849
CA Lic 874049
On 4/28/2022 9:11 AM, Harry Mahon via RE-wrenches wrote:
Dave – Unfortunately the SPS feature is not “back” fully.
You can easily "clean-up" a Simplify install by using bus bars. If you
spend a little time with steel wool, that copper looks pretty cool.
Bill
Feather River Solar Electric
Bill Battagin, Owner
4291 Nelson St.
Taylorsville, CA 95983
530.284.7849
CA Lic C-10 874049
On 4/6/2022 8:46 AM, Jerry Sh
Wrenchers,
In searching the list I saw ferrite cores discussed for EMP
and Enphase but a tech at SMA just told me I can put the DC conductors
through ferrite cores to prevent false AFCI events in their SB-40 and
-41 inverters. Is this a thing? are folks doing this with success? An
Jay,
I have an Outback Flexpower2 installed in my shop for a
year now and they are as quite a church mouse at lower power. Once the
fans come on though its fan noise, usually for awhile as loads pick-up
for the day. If the power drops below about 5-600 watts? or so for
awhile, th
If an AP Smart fails does it sometimes or always take out the string.
And how is it found in the string? Any melted or near fire type
failures out there?
Bill
Feather River Solar Electric
Bill Battagin, Owner
4291 Nelson St.
Taylorsville, CA 95983
530.284.7849
CA Lic 874049
www.frenergy.net
I think that's the same trick I've used on OB MX and FM CCs ??
On 2/6/2022 12:06 AM, Foxfire Energy wrote:
Not sure we're talking about the same thing, but I seem to recall if
you hold down the far left and 3^rd soft key (1&3 from the Left),
while you power up, it resets the Mate 2.
---
, frenergy wrote:
This is good, I'm not yet willing to accept egg-defeat. In my
previously described scenario, the atmospheric pressure does not play
a role because I'm not evacuating the air-filled pipe with the
suction side of a pump which /would/ rely on atmospheric pressure to
fil
idelines
Jay
On Jan 27, 2022, at 5:34 PM, frenergy wrote:
OK, I'll gamble some egg on my face. In this case though, you would
not be "pulling a vacuum" with air (a gas) involved. If you can fill
the entire pipe with a liquid (water), the water that's down slope of
t
OK, I'll gamble some egg on my face. In this case though, you would not
be "pulling a vacuum" with air (a gas) involved. If you can fill the
entire pipe with a liquid (water), the water that's down slope of the
water in the well on the other side of the ridge it would pull the water
out of th
Grid Depot
www.offgridnow.com <http://www.offgridnow.com>
970-596-3744
On Wed, Jan 26, 2022, 7:59 PM frenergy wrote:
Aaron,
It would be helpful to know how many amps are required
to power the 24 volt loads and should we assume the batteries are
toast or nearly
Aaron,
It would be helpful to know how many amps are required to
power the 24 volt loads and should we assume the batteries are toast or
nearly so? The brand of inverter?
As Jeff said there are 24V L-ion choices.
Bill
Feather River Solar Electric
Bill Battagin, Owne
Jay,
You caught me at a "good" time as I have 2, 2 volt 1788 Ahr
batteries failing. This is the third and fourth (EXPENSIVE) cell I may
have to replace in this 48 volt pack in just 9 years, I was expecting
twice the life.
Anyway, there is a variety of ways to discove
We've sacrificed a small-medium ice chest to be the battery box for our
tool batteries. affixed to the side of the ice chest is a small 7
watt reptile heat pad with the cord sneaking out the lid and plugged in
overnight. You don't want the pad on the bottom it'll actually get the
battery se
Mac,
Though the FW is up to date, have you tried unplugging the CAT5 at the
back of the Mate, waiting a minute and plugging it back in (the correct
port!)?
Bill
Feather River Solar Electric
Bill Battagin, Owner
4291 Nelson St.
Taylorsville, CA 95983
530.284.7849
CA Lic 874049
On 1/13/2022 4
Mike,
If I understand SMA's AFCI detection system right, it
detects arc on the AC and DC side of the inverter. If correct, and from
my "AFCI reset" experiences, it seems to also trip with some area
lighting strikes. It would certainly be helpful in finding the issue to
know at le
Yikes, that's a tough one. Was it an old one on a dusty shelf? was it
given to you or pulled off an old system, or Ebay? I have no idea what
they originally cost. Christmas is coming.
Bill
Feather River Solar Electric
Bill Battagin, Owner
4291 Nelson St.
Taylorsville, CA 95983
530.284.78
many of
those.
Cheers,
Dave
On Mon, Dec 6, 2021 at 11:42 PM frenergy wrote:
Wrenches,
Not sure if AC panels are being installed yet, am I
living
under a rock? We've been really happy with LG NeON 370 watt
panels and
wondering if anybody has installed an
Wrenches,
Not sure if AC panels are being installed yet, am I living
under a rock? We've been really happy with LG NeON 370 watt panels and
wondering if anybody has installed any of their AC panels yet:
https://www.lg.com/us/business/neon-2/lg-lg380m1c-a6
or any other AC PVs. T
ese days I would probably just set it for min of
some 2 or 3 hours and then a max could be the same
time or longer for FLA batteries.
boB
On 11/30/2021 7:16 PM, frenergy wrote:
Yes, the old one, not the FM. This oldie had an interesting way to
set the absorption time. You would set the
Yes, the old one, not the FM. This oldie had an interesting way to set
the absorption time. You would set the "min" time (in minutes) and you
would set the "max" time (in hours, you have to set it to 1,2,3 or 4 hours).
I need to know if I set the "min" to 10 minutes and the
"max"
Hey Folks,
From the SimpliPHI/Outback integration guide download,
using an Outback (I assume any brand of) charge controller (EG: FM80,
FM60, FM100), their chart shows absorbtion voltage at 56.4 for 51.2 nom
PHI batteries with time set at 6 minutes, page 18. If using the
inverter
We 're looking into pairing a smaller 6-8KW diesel generator back -up to
an off-grid Outback system to take advantage of the surplus of
bio-diesel here. We're aware of the need to keep it a warmish winter
location Suggestions? Experiences? No China knock-offs thank you.
Bill
Feather River Sol
I've got another off-gridder that is telling me the propane frig they
want to get pulls 350 watts. Is this correct?... Never heard of a glow
bar for a frig.
Bill
Feather River Solar Electric
Bill Battagin, Owner
4291 Nelson St.
Taylorsville, CA 95983
530.284.7849
CA Lic 874049
solar powered
/2021 7:14 AM, Jerry Shafer wrote:
Look at the batteries, use a meter right at the bolts going in to the
inverter, sounds like low voltage cut out.
On Sun, Oct 17, 2021, 9:07 PM frenergy wrote:
Hey Folks,
I haven't seen this one until yesterday. Customer with a
20
Hey Folks,
I haven't seen this one until yesterday. Customer with a
20 year old Trace SW4024 called. I've been servicing this reliable
system for the last 8 years. He said after a delay the power shuts off
when a moderate load comes on after 5-15 seconds, then back on, then
off
Mac,
How many amps?
Bill
Feather River Solar Electric
Bill Battagin, Owner
4291 Nelson St.
Taylorsville, CA 95983
530.284.7849
CA Lic 874049
www.frenergy.net
On 7/22/2021 6:01 PM, Mac Lewis wrote:
Hi Wrenches,
What's the most cost effective way to disconnect 4 poles of 600Vdc?
Jeremy,
My response is welcome to the world of FLA batteries. I
see variations like this all the time. Are you using a refractometer or
hydrometer, are all the cells same manufacture date, are some cells
warmer than others, terminal connections all clean? I've tried
"correcting
tion in our plan notes, based on our interpretation of
250.52(A)(7). AHJs have never questioned it, and we also tie the pole to any
rebar, so its all one big happy grounding electrode.
Ray Walters
Remote Solar
303 505-8760
On 6/24/21 6:49 PM, frenergy wrote:
Ray,
I couldn't
Ray,
I couldn't agree more, its been my experience over the
years that using 20 feet of #4 rebar in a building's footing was kosher
and accepted NEC 250.52(3). There's a heck of a lot more surface area
in 8" pipe 5-6 feet into the earth than rebar in a foundation footing.
The gr
Very few details...What does it mean "he opened it up" I would even
know how to do that with the L-ions I've been around, seems like its
something a manufacturer should be doing. Temperature? charge rate?
recent usage history? Age? Was it disconnected? Did contacts touch a
conductor?
I need some actual off-grid experience some of you wrenches may have had
with with a (or 2) Radian(s) starting and running a 3HP, 230Volt, single
phase, 3-wire submersible well pump. It would be starting against a
50-100 foot static level in the well and a pressure in the pressure tank
of 35ps
Jerry,
That's the easy answer but this all gets really deep into
weeds as unless you're a PG&E smart meter (and we /really/ trust them),
you don't know when that E-6 baseline is crossed to know when you're
getting or paying the higher rate. There's 2 things going on, baseline
and
Eric,
I like your idea of drilling the weepage holes as long as
they are not big enough to allow critters like wasps to make a home
inside the J-box. We will use aluminum tape on unused mounting holes in
the back of the box for the same reason. Lurkers welcome.
Bill
Feather Riv
We're setting up charge points for a new pack of SimpliPhi 3.8
batteries. Needed to use the voltage "offset" function in the FM80's a
bit to jive with the 2, Fluke 87 meters we got testing the actual
voltage at the battery bus bars. However. the Mate3s is reading .6
volts high and can't find
Blake,
Its great to get definitive clarification on this MC4/THHN
issue, we've been using 4-14 Polaris connectors with good results.
Being inside a Nema3 can and having silicone grease in the Polaris makes
for a solid, durable connection. Inspecting some of these that are now
17
It would be interesting to know if there is some collaboration between
the rack manufacturers offering these new EPDM or peel and stick legs/
cones/attachment points and roof shingle manufacturers, and what that
conversation is like.
Bill
Feather River Solar Electric
Bill Battagin, Owner
4291
OK, I'll stick my neck out. We've done very few flashings on comp for
the last 18 years or so, using (first) the highest quality polyurethane
caulk we could find. However, for the last 10 years we've been using
Geocell 4500 which states on the tube that it is compatible with
asphalt/comp shin
Off-gridders,
I'm looking for anyone who has experience powering a 2 HP
(or even a 1 1/2 HP) submersible 3-wire well pump with a OB FlexPower2
(30 KWhrs of L-ion battery at 48 volt). I'm mostly interested in just
starting the pump as I'm sure it would run it. The lift out of the w
On the other hand, utilities /have/ accepted inverters to shut-off power
production into the grid if the grid fails via, I assume, software
and/or electro-mechanical means.
Bill
Feather River Solar Electric
Bill Battagin, Owner
4291 Nelson St.
Taylorsville, CA 95983
530.284.7849
CA Lic 874049
Hey Folks,
Why am I having such a difficult time finding a Grundfos
distributor that can help me with a pump design for a new well? Their
website seems clunky for getting info Static at 25 feet, drilled to 340
feet to hit 30+ GPM. We would like to have 25 GPM at 40 psi, pump set
tp://members.sti.net/offgridsolar/> e-mail offgridso...@sti.net
<mailto:offgridso...@sti.net> text 209 813 0060*
On Sun, 21 Mar 2021 21:00:05 -0700, frenergy wrote:
Dave,
I just went through a thorough installation/programming
regime for an Outback FlexPower2 married to 8
Dave,
I just went through a thorough installation/programming
regime for an Outback FlexPower2 married to 8, SimpliPhi 3.8's. Outback
and SimpliPhi have spent a great deal of time developing setpoints for
several of OB's products in a 23 detailed page integration guide.
Bill
Fe
John,
If you can make up the cables in your shop, I've been
putting one of the handles of the BA hand crimper in the vice. You can
then put your all on the 'free' handle, much better for 4/0 magnalugs.
Out in the field it is a grunt for sure. Sorry no idea about electric.
Bill
Considering slot/board alignment, ribbon cable, sensor and poor
visibility when attempting either a board change or fan swap on a VFX
Flex Power 3 or 4, if you're doing it on one of the FX's in the middle,
leaving on the wall may not work out so well. Might be time to pull it off.
Andrew,
If these are the only two examples of justification of MLSD
and not knowing the details of the examples you've cited, I suggest
there is a more effective, equal in labor to apply, less expensive,
durable solution. For the squirrel problem, an alternate solution is
one of
The only thing I would add to William's list of things to do to solve
this issue is that there is a proper sequence in shutting down and
rebooting the inverter, found in Outback docs. There is also firmware
for the HUB but not sure if that would help or is necessary in this
situation.
Bill
This is a very timely discussion for us also as we have
many Midnight MNPV6 discos in the sun. Though we're careful about
tightening wire landings, using contact cleaner for the fuses and fuse
holders, some installs seem to get hotter than others. We just started
making a very sim
Happens all the time, pulling the string between those cans too tight.
It may not help in this instance but I've been communicating with Zena
at AEE the last few days ala email without problems.
Bill
On 11/6/2020 3:11 PM, Dana Orzel wrote:
I just spoke with Leslie Cannon at AEE. Their phone
I think I'm going to have to side with Jason. Many times my distributor
has eaten crow for stuff like this and of course there has been times
months after a delivery where I've found damage that I've had to eat.
Its the cost of doing business but if these were a fairly recent
delivery, the di
We have a drawer full of labels and placards from PV-Labels. If we need
smaller "fine-tuned" labels quickly, occasionally we'll use the Brady
BMP21 Plus (3/4" vinyl cartridge) if its not going to see much sun. The
label makers you may be referring to cost $700 to $4K! so we've opted to
stock
-
From: RE-wrenches On Behalf Of
frenergy
Sent: Tuesday, September 22, 2020 1:12 PM
To: re-wrenches@lists.re-wrenches.org
Subject: [RE-wrenches] Pump power
Wrenchers,
We're upgrading an off-grid water system. Dynamic head while
pumping at 20 GPM is 150 ft from water level to
Wrenchers,
We're upgrading an off-grid water system. Dynamic head
while pumping at 20 GPM is 150 ft from water level to wellhead and then
its 85 ft vertical to storage tank so 235 ft total head to open
discharge. We would like to get most of that 20 GPM, we need to know if
there
I will second that, Todd. I've had a Hartell MD-10-HEH mag drive pump
pumping glycol in my SHW closed loop for 23 years direct powered by a 20
watt PV. It does make a little noise when your close to it...so be it.
Bill
Feather River Solar Electric
Bill Battagin, Owner
4291 Nelson St.
Taylor
Dearest off-gridders,
OK, many of you micro-hydro fanatics on the west coast are
stuck inside with all the smoke, time to put on your tin foil thinking
caps
I brought this up some time back but got little (zero
maybe) feedback. I'm hoping there are some other mic
August,
Quite frankly and with due respect about the comment about
more PV and battery to forego the need for a generator, I disagree.
Those folks living off-grid in the sticks (um,er, myself included), it
would be a very bad thing not to have Gen input. The current situation
here
OK, I'll bite. I use SMA and Outback almost exclusively. SMA for
grid-tie so I can't vouch for SI for Off-grid and I don't seem to have
the same wait problem with SMA, its usually 10-20 minutes.
And Outback well they're not perfect but I've been
using there stuff since day 1
Jason,
Is it the actual display behind the window of the cover or
is it the window in the cover? It might be worth a try to contact a
place that repairs SMA (and other inverters) like the Solar Cowboys
(530) 273-4895. If its just the window, we've replaced them.
And
Hey Folks,
Here in the Boonies of NE California one of my customers just had a fire
(the Hog Fire) go through his property. It spared his house but roasted
the power shed. I'll try to summarize: 2003 Outback FP2 (AC enclosure,
2 FXs,DC enclosure with related equipment), Classic 150 and 24V H
Hey Corey,
We almost always use the labels and placards from PV-Labels
and have had about the same result as it appears you did in your test.
Of course they last much longer when out of the sun. There are a
variety of "label-maker" tapes (Brady brand), we mostly use vinyl the
fe
We've charged both a 2012 RAV4EV (many times) and a 2018 Tesla Model 3
(couple dozen times) on OB VFX3524s. I wouldn't think the sign wave was
much cleaner than the older SWs?, if that was what you were referring to.
Bill
On 6/5/2020 3:57 PM, Ray wrote:
I don't know about a Bolt, but we've su
Hey Folks,
I need some clarification, I'm getting conflicting views.
When running DC in metal conduit from the roof array to the exterior
wall mounted string Inverter and the attic is the way to go (for various
reasons, usually snow), how far below the roof does that conduit have
Awhile back there was some discussion about walking the talk regarding
recycling old, damaged, 'golf-balled",heritage PVs. I just wanted to
share my recent experience with Recycle PV solar.
We had quite a variety of damaged, out of spec,
freight-forked PVs that needed to be gone t
Wrenchers,
I seem to continue to have my foot stuck in the past
regarding off-grid. Off -grid seems to have more of an element of a
need for reliability, redundancy, klugability. Believe me L-ion
batteries and especially the "total units" like the:
https://simpliphipower.com/pr
Of course then there is the "bottom line", final say approval determined
by the AHJ which might be hard for this inspector to refuse your
clearances when he/she is asked to operate that switch and see that
there is zero issue with its safe and easy operation. AHJ's are allowed
to use common se
Mark,
OR, you change-out your inverter to an SMA with Secure
Power Supply and during grid power outage, while there is some sun on
the panels, you would have up to 2KW of 120VAC power on the SPS circuit
by just flipping a switch. We usually install a 4X outdoor box with a
120 VAC
...and we were told at Intersolar 2.5 years ago that the B17 was
comingstill waiting.
Bill
On 2/22/2020 6:56 PM, Allan Sindelar wrote:
Jeff, according to Midnite’s website, their B-17 inverter can be up to
40 kW in 2 kW increments.
Allan
On Feb 22, 2020, at 8:05 PM, Jeff Clearwater
Hey Folks,
I'm coming into a least a couple small load 200 Amp/240 Vac
single phase commercial jobs that need a Meter/main panel change-out
that I can backfeed ~96 amps of solar onto. Been using a Sq. D 'Solar
Ready' panel for residential jobs but can't find equivalent for this
t
There was a period of time when we were installing Mitsubishi PVs. Now
we are seeing issues with installs where we were using Mitsubishi
MF170EB3 panels, bubbling backsheets, occasional bad solder joints, many
with half the label's VOC voltage. We actually just discovered one
panel that was p
Wrenchers,
This particular install requires 6 Gauge for the AC output
from a few SB7.7..-41 inverters (for voltage drop). Pretty tight for
the 3/4" knock-outs in that inverter. Any harm in using a step-drill to
open it up to a 1" KO? Any experiences with this? I'm trying to
Probably is not the cause but hard not to notice the big ding in the
cardboard at about the right spot to cause your "deflection" from just
the right whack with the fork lift. Did it affect all the mods?
Bill
Feather River Solar Electric
Bill Battagin, Owner
4291 Nelson St.
Taylorsville, CA 9
nt dancing that evening.
Allan
> On Nov 4, 2019, at 9:46 PM, frenergy mailto:frene...@psln.com>> wrote:
>
> I'm going to have to remove the cells from 4 HUP Solar1
battery cases to change-out the pack (no option, bad access).
Anyone ever had problems
I'm going to have to remove the cells from 4 HUP Solar1 battery cases to
change-out the pack (no option, bad access). Anyone ever had problems
come-a-longing from above the first cell and if so, what's the
solution?...and what are you doing tomorrow?
Thx,
Bill
Feather River Solar Electric
B
Drake,
After having 2 Stabers in the last 25 years, we were having
too many problems with the second one (mechanically was OK but the
brains were not working correctly and board replacements are pretty
spendy. So we ended up with an LG model # WM3500CW as of 3 months ago.
Made
I've only had the "tapping" method work on SB-22 inverters, not on -40
inverters. You gotta log on to the machine which I think you can only
do onsite. Has anyone ever done a reset of the 8206 from the portal?
Bill
Feather River Solar Electric
Bill Battagin, Owner
4291 Nelson St.
Taylorsvill
Interestingly, the problems I've had with the SMA -40 AFCI faults have
been on Comp roofs. When I've gone "inside" a -40 with my laptop, I'm
pretty sure I've seen where you can disable it?
Bill
On 9/2/2019 7:12 AM, drake.chamber...@redwoodalliance.org wrote:
At least with the TL-22s, the AFCI
Hey Marco,
I hear you, we have installed many SMA-40's and we're not
at the same point as you may be but we've definitely had a fair number
of arc fault shut-downs which take a site visit to rectify. One
location had been experiencing lightening over a year and a half which
seeme
Wrenches,
Is the only a way to back feed 128 amps (240v, split PH)
onto a 200 amp panel is to tap the conductors between the meter and the
main CB, assuming I can pull it off in the "customer section" of the
panel. Of course with the requisite AC disco within 10 feet. Or, has
an
1 - 100 of 314 matches