chop saws are often an issue. Hope this helps, Chris On Wed, Oct 11, 2023 at 10:19 AM Jay via RE-wrenches wrote: I’d look at a 3 phase pump with vfd/soft start control and eliminate the start surge. Jay > On Oct 11, 2023, at 8:12 AM, frenergy via RE-wrench

[RE-wrenches] Well pump with Sol-Ark

2023-10-11 Thread frenergy via RE-wrenches
I'm looking for opinions and/or real world experience on recommendation for the largest 240V submersible well pump the Sol-Ark 12KW inverter can start/run.  Assume 500 watt load prior to starting the pump, static level of water in well is 75 feet, system psi when it starts is 40. Thanks, Bi

Re: [RE-wrenches] GT with BB

2023-09-25 Thread frenergy via RE-wrenches
hinking about doing a job I have in mind with buss bars and plexi dead front vs 4/0 cable. Jay On Sep 21, 2023, at 9:25 PM, frenergy via RE-wrenches wrote: Jay,    I sent a diagram of my proposed arrangement and bus sizes to SimpliPhi prior to installation, which they approved. The bu

[RE-wrenches] Mojave/ESS

2023-09-01 Thread frenergy via RE-wrenches
Wrenchers,             We haven't done any hybrid systems with the Outback Mojave with ESS yet.  Comments up or down accepted. Thanks, Bill Feather River Solar Electric Bill Battagin, Owner 4291 Nelson St.(shipping) 5575 Genesee Rd. (USPS, UPS) Taylorsville, CA 95983 530.284.1925 Office/ 530.

Re: [RE-wrenches] Radian power supply

2023-08-22 Thread frenergy via RE-wrenches
David,         I don't have your part and it doesn't look like Zonna has it either, though a phone call might be good to confirm: https://www.zonnaenergy.com/solar/replacement-parts/outback/gs-series/outback-power-gs8048-parts/?8060_device=tablet They claim they can fix components also, thoug

Re: [RE-wrenches] SMA Tech Support

2023-07-24 Thread frenergy via RE-wrenches
Adam,             Have you registered and been working through their new and "improved" Online Service Center?  I just needed a replacement inverter for a 1001 code and it was pretty clunky going through the OSC: https://my.sma-service.com/s/?language=en_US I'm hoping it gets better but it t

Re: [RE-wrenches] Damaged PV module cells

2023-07-17 Thread frenergy via RE-wrenches
Not sure where this install is located but here in the Sierra, we had a near record snowfall and we saw a few failures, very few, but... Bill Feather River Solar Electric Bill Battagin, Owner 4291 Nelson St.(shipping) 5575 Genesee Rd. (USPS, UPS) Taylorsville, CA 95983 530.284.1925 Office/ 530.

[RE-wrenches] Just getting old?

2023-05-17 Thread frenergy via RE-wrenches
Wrenches,             I've got a call from a customer that said their (my install) 17 year old GT system went dead. Basic stats: 23, Mitsubishi PVMF120EC3, label says V mpp= 17.6V and Voc = 22 V; top-of-pole; SMA SB3800U. Its one string of 23 PVs.  Full sun, 75 degrees ambient during testing.

Re: [RE-wrenches] Old and new Radian

2023-05-11 Thread frenergy via RE-wrenches
l double your parasitic load, I have not done this so beware.  This is not the answer for V2H; other inverters can work in this combination but On Wed, May 10, 2023 at 10:04 AM frenergy via RE-wrenches wrote:     The wrench list has some very creative thinkers that

[RE-wrenches] Old and new Radian

2023-05-10 Thread frenergy via RE-wrenches
        The wrench list has some very creative thinkers that may have a go around to be able to master/slave an old Radian's output with a new one.   Outback says this is not do-able.   We're completely off-grid out here and have been charging EVs (one at a time) with an eleven year old Radian

Re: [RE-wrenches] Truss finder

2023-04-16 Thread frenergy via RE-wrenches
Kris,             Seems there was discussion about scanners before and I don't remember anyone saying they found one that was reliable especially with varying roofing materials.  Our current method is fist-thumping to get in the area of the rafter, drill exploratory hole then use the Chiptool

Re: [RE-wrenches] HomeGrid Battery Experience

2023-04-15 Thread frenergy via RE-wrenches
Howie,             SimpliPhi also has the benefit of adding smaller KWhr batteries (3.8).  They have a ten year warranty but also say:" AmpliPHI and PHI batteries’ /expected/ cycle life rating is 10,000 cycles when a maximum of 80% DOD is maintained" Bill Feather River Solar Electric Bill B

Re: [RE-wrenches] replace part of rolls battery bank

2023-04-05 Thread frenergy via RE-wrenches
Wrenches,             I feel compelled to chime in here.  Ten years ago, we installed 24, Rolls 2-KS-33P, 2 volt batteries for the shop. Though they were in a climate-controlled environment and maybe went to 50% SOC a dozen times over 10 years, usually ranged 75-100% SOC, we had the first fai

Re: [RE-wrenches] Attaching Array To or Through Ply

2023-03-29 Thread frenergy via RE-wrenches
Matt,             I guess my questions are 1/2" plywood or 5/8" and how thick is the foam?  Oh and I assume its nominal 2X6 T&G?  Do you know how the plywood is attached?.through the foam into the T&G?... to stringers, nailers or whatever they're called? Bill Feather River Solar Electri

Re: [RE-wrenches] Fronius Primo 3.8 with State 573 error code

2023-03-14 Thread frenergy via RE-wrenches
Greg,             My Fronius manual goes up to a code 517 but no "higher".  I assume you're talking about an "IG".  The last Ph # I used for them was 810-220-4414. Bill Feather River Solar Electric Bill Battagin, Owner 4291 Nelson St.(shipping) 5575 Genesee Rd. (USPS, UPS) Taylorsville, CA 9

Re: [RE-wrenches] Solar and tenant billing

2023-01-30 Thread frenergy via RE-wrenches
Carl,             In my area (PG&E, N. California) I've installed solar on four of my rentals.  Rather than trying to figure out monthly billing, renters come, renters go, true-up, some occasionally don't pay their bills, etc. I decided to just bump up the rent to cover the average cost of po

Re: [RE-wrenches] Outback with a 48V Lithium battery

2022-10-18 Thread frenergy via RE-wrenches
Hi Wayne,             We've done about a dozen Outback systems with SimpliPhi  batteries.  SimpliPhi has integration guides with well thought out  and complete settings to program OB Inverters and CC's the play properly with SimpliPhi batteries (24 and 48 volt). Straight-forward stuff. Bill

Re: [RE-wrenches] Large current battery combiners, UL Listing

2022-09-12 Thread frenergy via RE-wrenches
Michael,             Are you using kerosene as a cutting fluid?  We've had better luck with that in softer than steel metals. Bill Feather River Solar Electric Bill Battagin, Owner 4291 Nelson St. Taylorsville, CA 95983 530.284.7849 CA Lic 874049 On 9/11/2022 7:00 PM, Michael Morningstar via

Re: [RE-wrenches] Samlex EVO series and AGS

2022-09-02 Thread frenergy via RE-wrenches
Doesn't the EVO have that capability? Bill Feather River Solar Electric Bill Battagin, Owner 4291 Nelson St. Taylorsville, CA 95983 530.284.7849 CA Lic 874049 Solar Powered since 1982 On 9/2/2022 7:51 PM, Jeremy Rodriguez via RE-wrenches wrote: Can anyone recommend a reliable AGS module that w

Re: [RE-wrenches] solar panel recycling

2022-08-18 Thread frenergy via RE-wrenches
Its kinda fuzzy in my head now but about a year and a half ago we delivered a pallet of old PVs to some warehouse in Reno (Sparks) on Greg St.  It was supposed to be the beginning of recycling here on the west coast and was headed up by Sam Vanderhoof and a fellow named Lamar.  Hopefully this i

Re: [RE-wrenches] lithium in cold weather/heating

2022-07-21 Thread frenergy via RE-wrenches
Jay,             With the SimpliPhi's we've been installing we require a shed on slab, walls R-21, roof, R-38 and then the smallest propane wall heater (they use zero power to operate) we can find and set it at 55 degrees.  No need for the insulated box or fretting about toasting $20K+ in bat

Re: [RE-wrenches] LiPO with Trace SW5548

2022-07-13 Thread frenergy via RE-wrenches
Just stack 8 SimpliPhi 3.8's for your 30 Kwhrs. Bill Feather River Solar Electric Bill Battagin, Owner 4291 Nelson St. Taylorsville, CA 95983 530.284.7849 CA Lic 874049 On 7/13/2022 4:14 AM, Jeremy Rodriguez via RE-wrenches wrote: I’d look at the Simpliphi brand We’ve had good luck, however th

Re: [RE-wrenches] WATER COOLED - 1800 RPM - 13KW GENERATORS INQUIRY

2022-07-02 Thread frenergy via RE-wrenches
As an aside, maybe I've been living under a rock but I have not heard of 1800 RPM gensets running on propane, but exclusive to diesel.  It sounds like that's a thing.  I'm small time off-grid here but I could easily see 3-4 units/year.  I'm assuming if this come to fruition, the manufacturer wo

Re: [RE-wrenches] SMA Rapid Shutdown and Secure Power Supply

2022-04-28 Thread frenergy via RE-wrenches
Chalk it up as another reason Rapid Shutdown is a bummer. Bill Feather River Solar Electric Bill Battagin, Owner 4291 Nelson St. Taylorsville, CA 95983 530.284.7849 CA Lic 874049 On 4/28/2022 9:11 AM, Harry Mahon via RE-wrenches wrote: Dave – Unfortunately the SPS feature is not “back” fully.

Re: [RE-wrenches] Outdoor LiPO batteries

2022-04-06 Thread frenergy via RE-wrenches
You can easily "clean-up" a Simplify install by using bus bars. If you spend a little time with steel wool, that copper looks pretty cool. Bill Feather River Solar Electric Bill Battagin, Owner 4291 Nelson St. Taylorsville, CA 95983 530.284.7849 CA Lic C-10 874049 On 4/6/2022 8:46 AM, Jerry Sh

[RE-wrenches] SMA AFCI events and ferrite cores

2022-03-31 Thread frenergy via RE-wrenches
Wrenchers,             In searching the list I saw ferrite cores discussed for EMP and Enphase but a tech at SMA just told me I can put the DC conductors through ferrite cores to prevent false AFCI events in their SB-40 and -41 inverters.  Is this a thing? are folks doing this with success? An

Re: [RE-wrenches] 3000 watt quiet inverter

2022-03-07 Thread frenergy
Jay,             I have an Outback Flexpower2 installed in my shop for a year now and they are as quite a church mouse at lower power. Once the fans come on though its fan noise, usually for awhile as loads pick-up for the day.  If the power drops below about 5-600 watts? or so for awhile, th

[RE-wrenches] AP Smart failure

2022-02-08 Thread frenergy
If an AP Smart fails does it sometimes or always take out the string.  And how is it found in the string?  Any melted or near fire type failures out there? Bill Feather River Solar Electric Bill Battagin, Owner 4291 Nelson St. Taylorsville, CA 95983 530.284.7849 CA Lic 874049 www.frenergy.net

Re: [RE-wrenches] Bricked Mate2

2022-02-06 Thread frenergy
I think that's the same trick I've used on OB MX and FM CCs  ?? On 2/6/2022 12:06 AM, Foxfire Energy wrote: Not sure we're talking about the same thing, but I seem to recall if you hold down the far left and 3^rd  soft key (1&3 from the Left), while you power up, it resets the Mate 2. ---

Re: [RE-wrenches] Well siphon?

2022-01-29 Thread frenergy
, frenergy wrote:  This is good, I'm not yet willing to accept egg-defeat.  In my previously described scenario, the atmospheric pressure does not play a role because I'm not evacuating the air-filled pipe with the suction side of a pump which /would/ rely on atmospheric pressure to fil

Re: [RE-wrenches] Well siphon?

2022-01-27 Thread frenergy
idelines Jay On Jan 27, 2022, at 5:34 PM, frenergy wrote:  OK, I'll gamble some egg on my face.  In this case though, you would not be "pulling a vacuum" with air (a gas) involved.  If you can fill the entire pipe with a liquid (water), the water that's down slope of t

Re: [RE-wrenches] Well siphon?

2022-01-27 Thread frenergy
OK, I'll gamble some egg on my face.  In this case though, you would not be "pulling a vacuum" with air (a gas) involved.  If you can fill the entire pipe with a liquid (water), the water that's down slope of the water in the well on the other side of the ridge it would pull the water out of th

Re: [RE-wrenches] 24v to 48v upgrade help

2022-01-27 Thread frenergy
Grid Depot www.offgridnow.com <http://www.offgridnow.com> 970-596-3744 On Wed, Jan 26, 2022, 7:59 PM frenergy wrote: Aaron,             It would be helpful to know how many amps are required to power the 24 volt loads and should we assume the batteries are toast or nearly

Re: [RE-wrenches] 24v to 48v upgrade help

2022-01-26 Thread frenergy
Aaron,             It would be helpful to know how many amps are required to power the 24 volt loads and should we assume the batteries are toast or nearly so?  The brand of inverter?             As Jeff said there are 24V L-ion choices. Bill Feather River Solar Electric Bill Battagin, Owne

Re: [RE-wrenches] 2v battery charger

2022-01-20 Thread frenergy
Jay,             You caught me at a "good" time as I have 2, 2 volt 1788 Ahr batteries failing.  This is the third and fourth (EXPENSIVE) cell I may have to replace in this 48 volt pack in just 9 years, I was expecting twice the life.             Anyway, there is a variety of ways to discove

Re: [RE-wrenches] Lithium Ion tool batteries

2022-01-19 Thread frenergy
We've sacrificed a small-medium ice chest to be the battery box for our tool batteries.  affixed to the side  of the ice chest is a small 7 watt  reptile heat pad with the cord sneaking out the lid and plugged in overnight.  You don't want the pad on the bottom it'll actually get the battery se

Re: [RE-wrenches] Radian Glitch

2022-01-13 Thread frenergy
Mac, Though the FW is up to date, have you tried unplugging the CAT5 at the back of the Mate, waiting a minute and plugging it back in (the correct port!)? Bill Feather River Solar Electric Bill Battagin, Owner 4291 Nelson St. Taylorsville, CA 95983 530.284.7849 CA Lic 874049 On 1/13/2022 4

Re: [RE-wrenches] SMA arc faults

2021-12-23 Thread frenergy
Mike,             If I understand SMA's AFCI detection system right, it detects arc on the AC and DC side of the inverter. If correct, and from my "AFCI reset" experiences, it seems to also trip with some area lighting strikes.  It would certainly be helpful in finding the issue to know at le

Re: [RE-wrenches] Fair price for an obsolete component

2021-12-10 Thread frenergy
Yikes, that's a tough one. Was it an old one on a dusty shelf? was it given to you or pulled off an old system, or Ebay?  I have no idea what they originally cost.  Christmas is coming. Bill Feather River Solar Electric Bill Battagin, Owner 4291 Nelson St. Taylorsville, CA 95983 530.284.78

Re: [RE-wrenches] AC-PVs

2021-12-07 Thread frenergy
many of those. Cheers, Dave On Mon, Dec 6, 2021 at 11:42 PM frenergy wrote: Wrenches,         Not sure if AC panels are being installed yet, am I living under a rock?  We've been really happy with LG NeON 370 watt panels and wondering if anybody has installed an

[RE-wrenches] AC-PVs

2021-12-06 Thread frenergy
Wrenches,             Not sure if AC panels are being installed yet, am I living under a rock?  We've been really happy with LG NeON 370 watt panels and wondering if anybody has installed any of their AC panels yet: https://www.lg.com/us/business/neon-2/lg-lg380m1c-a6 or any other AC PVs.  T

Re: [RE-wrenches] Outback MX-60

2021-12-01 Thread frenergy
ese days I would probably just set it for min of some 2 or 3 hours and then a max could be the same time or longer for FLA batteries. boB On 11/30/2021 7:16 PM, frenergy wrote: Yes, the old one, not the FM.  This oldie had an interesting way to set the absorption time. You would set the

[RE-wrenches] Outback MX-60

2021-11-30 Thread frenergy
Yes, the old one, not the FM.  This oldie had an interesting way to set the absorption time. You would set the "min" time (in minutes) and you would set the "max" time (in hours, you have to set it to 1,2,3 or 4 hours).             I need to know if I set the "min" to 10 minutes and the "max"

Re: [RE-wrenches] Max charge for lithium batteries

2021-11-01 Thread frenergy
Hey Folks,             From the SimpliPHI/Outback integration guide download, using an Outback (I assume any brand of) charge controller (EG: FM80, FM60, FM100), their chart shows absorbtion voltage at 56.4 for 51.2 nom PHI batteries with time set at 6 minutes, page 18.  If using the inverter

[RE-wrenches] Small diesel generator

2021-10-20 Thread frenergy
We 're looking into pairing a smaller 6-8KW diesel generator back -up to an off-grid Outback system to take advantage of the surplus of bio-diesel here. We're aware of the need to keep it a warmish winter location Suggestions? Experiences? No China knock-offs thank you. Bill Feather River Sol

[RE-wrenches] Propane frig

2021-10-18 Thread frenergy
I've got another off-gridder that is telling me the propane frig they want to get pulls 350 watts.  Is this correct?...  Never heard of a glow bar for a frig. Bill Feather River Solar Electric Bill Battagin, Owner 4291 Nelson St. Taylorsville, CA 95983 530.284.7849 CA Lic 874049 solar powered

Re: [RE-wrenches] Trace 4024 cutting out

2021-10-18 Thread frenergy
/2021 7:14 AM, Jerry Shafer wrote: Look at the batteries, use a meter right at the bolts going in to the inverter, sounds like low voltage cut out. On Sun, Oct 17, 2021, 9:07 PM frenergy wrote: Hey Folks,         I haven't seen this one until yesterday. Customer with a 20

[RE-wrenches] Trace 4024 cutting out

2021-10-17 Thread frenergy
Hey Folks,             I haven't seen this one until yesterday.  Customer with a 20 year old Trace SW4024 called.  I've been servicing this reliable system for the last 8 years.  He said after a delay the power shuts off when a moderate load comes on after 5-15 seconds, then back on, then off

Re: [RE-wrenches] Cost effective 4 pole HV disconnect

2021-07-24 Thread frenergy
Mac,             How many amps? Bill Feather River Solar Electric Bill Battagin, Owner 4291 Nelson St. Taylorsville, CA 95983 530.284.7849 CA Lic 874049 www.frenergy.net On 7/22/2021 6:01 PM, Mac Lewis wrote: Hi Wrenches, What's the most cost effective way to disconnect 4 poles of 600Vdc? 

Re: [RE-wrenches] High to normal SG

2021-07-21 Thread frenergy
Jeremy,             My response is welcome to the world of FLA batteries.  I see variations like this all the time.  Are you using a refractometer or hydrometer, are all the cells same manufacture date, are some cells warmer than others, terminal connections all clean?  I've tried "correcting

Re: [RE-wrenches] Grounding Top of Pole Mount Array with a Ufer

2021-06-25 Thread frenergy
tion in our plan notes, based on our interpretation of 250.52(A)(7). AHJs have never questioned it, and we also tie the pole to any rebar, so its all one big happy grounding electrode. Ray Walters Remote Solar 303 505-8760 On 6/24/21 6:49 PM, frenergy wrote: Ray, I couldn't

Re: [RE-wrenches] Grounding Top of Pole Mount Array with a Ufer

2021-06-24 Thread frenergy
Ray,             I couldn't agree more, its been my experience over the years that using 20 feet of #4 rebar in a building's footing was kosher and accepted NEC 250.52(3).  There's a heck of a lot more surface area in 8" pipe 5-6 feet into the earth than rebar in a foundation footing.  The gr

Re: [RE-wrenches] Exploding LFP battery

2021-06-15 Thread frenergy
Very few details...What does it mean "he opened it up"  I would even know how to do that with the L-ions I've been around, seems like its something a manufacturer should be doing.  Temperature? charge rate? recent usage history? Age? Was it disconnected? Did contacts touch a conductor?

[RE-wrenches] Wellpump VS Radian

2021-05-25 Thread frenergy
I need some actual off-grid experience some of you wrenches may have had with with a (or 2) Radian(s) starting and running a 3HP, 230Volt, single phase, 3-wire submersible well pump.  It would be starting against a 50-100 foot static level in the well and a pressure in the pressure tank of 35ps

Re: [RE-wrenches] Utitlity Rate question

2021-05-02 Thread frenergy
Jerry,             That's the easy answer but this all gets really deep into weeds as unless you're a PG&E smart meter (and we /really/ trust them), you don't know when that E-6 baseline is crossed to know when you're getting or paying the higher rate.  There's 2 things going on, baseline and

Re: [RE-wrenches] MC4s are listed for THWN, right?

2021-04-29 Thread frenergy
Eric,             I like your idea of drilling the weepage holes as long as they are not big enough to allow critters like wasps to make a home inside the J-box.  We will use aluminum tape on unused mounting holes in the back of the box for the same reason. Lurkers welcome. Bill Feather Riv

[RE-wrenches] Mate 3s voltage off

2021-04-27 Thread frenergy
We're setting up charge points for a new pack of SimpliPhi 3.8 batteries.  Needed to use the voltage  "offset" function in the FM80's a bit to jive with the 2, Fluke 87 meters we got testing the actual voltage at the battery bus bars.  However. the Mate3s is reading .6 volts high and can't find

Re: [RE-wrenches] MC4s are listed for THWN, right?

2021-04-26 Thread frenergy
Blake,             Its great to get definitive clarification on this MC4/THHN issue, we've been using 4-14 Polaris connectors with good results.  Being inside a Nema3 can and having silicone grease in the Polaris makes for a solid, durable connection.  Inspecting some of these that are now 17

Re: [RE-wrenches] Trend away from roof flashings???

2021-04-22 Thread frenergy
It would be interesting to know if there is some collaboration between the rack manufacturers offering these new EPDM or peel and stick legs/ cones/attachment points and roof shingle manufacturers, and what that conversation is like. Bill Feather River Solar Electric Bill Battagin, Owner 4291

Re: [RE-wrenches] Trend away from roof flashings???

2021-04-21 Thread frenergy
OK, I'll stick my neck out.  We've done very few flashings on comp for the last 18 years or so, using (first) the highest quality polyurethane caulk we could find.  However, for the last 10 years we've been using Geocell 4500 which states on the tube that it is compatible with asphalt/comp shin

[RE-wrenches] 2HP submersible ala OB Flexpower2

2021-04-05 Thread frenergy
Off-gridders,             I'm looking for anyone who has experience powering a 2 HP (or even a 1 1/2 HP) submersible 3-wire well pump with a OB FlexPower2 (30 KWhrs of L-ion battery at 48 volt).  I'm mostly interested in just starting the pump as I'm sure it would run it. The lift out of the w

Re: [RE-wrenches] how to prevent selling to grid with grid tie inverter

2021-03-31 Thread frenergy
On the other hand, utilities /have/ accepted inverters to shut-off power production into the grid if the grid fails via, I assume, software and/or electro-mechanical means. Bill Feather River Solar Electric Bill Battagin, Owner 4291 Nelson St. Taylorsville, CA 95983 530.284.7849 CA Lic 874049

[RE-wrenches] Deep well pumping

2021-03-26 Thread frenergy
Hey Folks,             Why am I having such a difficult time finding a Grundfos distributor that can help me with a pump design for a new well?  Their website seems clunky for getting info  Static at 25 feet, drilled to 340 feet to hit 30+ GPM.  We would like to have 25 GPM at 40 psi, pump set

Re: [RE-wrenches] Outback settings adjustment so batteries consume less of PV output

2021-03-22 Thread frenergy
tp://members.sti.net/offgridsolar/> e-mail offgridso...@sti.net <mailto:offgridso...@sti.net> text 209 813 0060* On Sun, 21 Mar 2021 21:00:05 -0700, frenergy wrote: Dave,             I just went through a thorough installation/programming regime for an Outback FlexPower2 married to 8

Re: [RE-wrenches] Outback settings adjustment so batteries consume less of PV output

2021-03-21 Thread frenergy
Dave,             I just went through a thorough installation/programming regime for an Outback FlexPower2 married to 8, SimpliPhi 3.8's.  Outback and SimpliPhi have spent a great deal of time developing setpoints for several of OB's products in a 23 detailed page integration guide. Bill Fe

Re: [RE-wrenches] Electric Crimper Recommendations

2021-02-21 Thread frenergy
John,             If you can make up the cables in your shop, I've been putting one of the handles of the BA hand crimper in the vice. You can then put your all on the 'free' handle, much better for 4/0 magnalugs.  Out in the field it is a grunt for sure.  Sorry no idea about electric. Bill

Re: [RE-wrenches] GVFX3524 fan replacement

2021-02-15 Thread frenergy
Considering slot/board alignment, ribbon cable, sensor and poor visibility when attempting either a board change or fan swap on a VFX Flex Power 3 or 4, if you're doing it on one of the FX's in the middle, leaving on the wall may not work out so well.  Might be time to pull it off.            

Re: [RE-wrenches] MLSD module level shutdown

2021-01-29 Thread frenergy
Andrew,             If these are the only two examples of justification of MLSD and not knowing the details of the examples you've cited, I suggest there is a more effective, equal in labor to apply, less expensive, durable solution.  For the squirrel problem, an alternate solution is one of

Re: [RE-wrenches] Radian Charges 1 hour per calendar day

2021-01-08 Thread frenergy
The only thing I would add to William's list of things to do to solve this issue is that there is a proper sequence in shutting down and rebooting the inverter, found in Outback  docs.  There is also firmware for the HUB but not sure if that would help or is necessary in this situation. Bill

Re: [RE-wrenches] Enphase intermittent breaker trippjng

2020-11-19 Thread frenergy
            This is a very timely discussion for us also as we have many Midnight MNPV6 discos in the sun.  Though we're careful about tightening wire landings, using contact cleaner for the fuses and fuse holders, some installs seem to get hotter than others.  We just started making a very sim

Re: [RE-wrenches] AEE Phones on fritz

2020-11-06 Thread frenergy
Happens all the time, pulling the string between those cans too tight.  It may not help in this instance but I've been communicating with Zena at AEE the last few days ala email without problems. Bill On 11/6/2020 3:11 PM, Dana Orzel wrote: I just spoke with Leslie Cannon at AEE. Their phone

Re: [RE-wrenches] factory module damage, has anyone seen this?

2020-11-05 Thread frenergy
I think I'm going to have to side with Jason.  Many times my distributor has eaten crow for stuff like this and of course there has been times months after a delivery where I've found damage that I've had to eat.  Its the cost of doing business but if these were a fairly recent delivery, the di

Re: [RE-wrenches] Label Maker

2020-10-10 Thread frenergy
We have a drawer full of labels and placards from PV-Labels.  If we need smaller "fine-tuned" labels quickly, occasionally we'll use the Brady BMP21 Plus (3/4" vinyl cartridge) if its not going to see much sun.  The label makers you may be referring to cost $700 to $4K! so we've opted to stock

Re: [RE-wrenches] Pentair Pump power

2020-09-22 Thread frenergy
- From: RE-wrenches On Behalf Of frenergy Sent: Tuesday, September 22, 2020 1:12 PM To: re-wrenches@lists.re-wrenches.org Subject: [RE-wrenches] Pump power Wrenchers, We're upgrading an off-grid water system. Dynamic head while pumping at 20 GPM is 150 ft from water level to

[RE-wrenches] Pump power

2020-09-22 Thread frenergy
Wrenchers,             We're upgrading an off-grid water system.  Dynamic head while pumping at 20 GPM is 150 ft from water level to wellhead and then its 85 ft vertical to storage tank so 235 ft total head to open discharge.  We would like to get most of that 20 GPM, we need to know if there

Re: [RE-wrenches] Another pump quesiton

2020-09-17 Thread frenergy
I will second that, Todd.  I've had a Hartell  MD-10-HEH mag drive pump pumping glycol in my SHW closed loop for 23 years direct powered by a 20 watt PV.  It does make a little noise when your close to it...so be it. Bill Feather River Solar Electric Bill Battagin, Owner 4291 Nelson St. Taylor

[RE-wrenches] Micro-hydro with L-ion

2020-09-12 Thread frenergy
Dearest off-gridders,              OK, many of you micro-hydro fanatics on the west coast are stuck inside with all the smoke, time to put on your tin foil thinking caps             I brought this up some time back but got little (zero maybe) feedback.  I'm hoping there are some other mic

Re: [RE-wrenches] Pika Support by chance?

2020-09-11 Thread frenergy
August,             Quite frankly and with due respect about the comment about more PV and battery to forego the need for a generator, I disagree. Those folks living off-grid in the sticks (um,er, myself included), it would be a very bad thing not to have Gen input. The current situation here

Re: [RE-wrenches] Microgrid... Outback or SMA or other?

2020-09-09 Thread frenergy
OK, I'll bite.  I use SMA and Outback almost exclusively.  SMA for grid-tie so I can't vouch for SI for Off-grid and I don't seem to have the same wait problem with SMA, its usually 10-20 minutes.             And Outback well they're not perfect but I've been using there stuff since day 1

Re: [RE-wrenches] SMA SB#000US LCD Displays

2020-08-18 Thread frenergy
Jason,             Is it the actual display behind the window of the cover or is it the window in the cover?  It might be worth a try to contact a place that repairs SMA (and other inverters) like the Solar Cowboys (530) 273-4895.  If its just the window, we've replaced them.             And

[RE-wrenches] Off-grid French fried

2020-07-28 Thread frenergy
Hey Folks, Here in the Boonies of NE California one of my customers just had a fire (the Hog Fire) go through his property.  It spared his house but roasted the power shed.  I'll try to summarize: 2003 Outback FP2 (AC enclosure, 2 FXs,DC enclosure with related equipment), Classic 150 and 24V H

Re: [RE-wrenches] ADV: Re: Label Durability

2020-06-28 Thread frenergy
Hey Corey,             We almost always use the labels and placards from PV-Labels and have had about the same result as it appears you did in your test.  Of course they last much longer when out of the sun.  There are a variety of "label-maker" tapes (Brady brand), we mostly use vinyl the fe

Re: [RE-wrenches] ADV: Re: SW4024

2020-06-05 Thread frenergy
We've charged both a 2012 RAV4EV (many times) and a 2018 Tesla Model 3 (couple dozen times) on OB VFX3524s.  I wouldn't think the sign wave was much cleaner than the older SWs?, if that was what you were referring to. Bill On 6/5/2020 3:57 PM, Ray wrote: I don't know about a Bolt, but we've su

[RE-wrenches] DC run

2020-06-05 Thread frenergy
Hey Folks,             I need some clarification, I'm getting conflicting views.  When running DC in metal conduit from the roof array to the exterior wall mounted string Inverter and the attic is the way to go (for various reasons, usually snow), how far below the roof does that conduit have

[RE-wrenches] Finally, we recycle

2020-05-21 Thread frenergy
Awhile back there was some discussion about walking the talk regarding recycling old, damaged, 'golf-balled",heritage PVs.  I just wanted to share my recent experience with Recycle PV solar.             We had quite a variety of damaged, out of spec, freight-forked PVs that needed to be gone t

Re: [RE-wrenches] Lithium Ion Batteries

2020-03-23 Thread frenergy
Wrenchers,             I seem to continue to have my foot stuck in the past regarding off-grid.  Off -grid seems to have more of an element of a need for reliability, redundancy, klugability.  Believe me L-ion batteries and especially the "total units" like the: https://simpliphipower.com/pr

Re: [RE-wrenches] Disconnect spacing

2020-03-12 Thread frenergy
Of course then there is the "bottom line", final say approval determined by the AHJ which might be hard for this inspector to refuse your clearances when he/she is asked to operate that switch and see that there is zero issue with its safe and easy operation.  AHJ's are allowed to use common se

Re: [RE-wrenches] OK, so what iwould happen if I do this...

2020-03-01 Thread frenergy
Mark,             OR, you change-out your inverter to an SMA with Secure Power Supply and during grid power outage, while there is some sun on the panels, you would have up to 2KW of 120VAC power on the SPS circuit by just flipping a switch. We usually install a 4X outdoor box with a 120 VAC

Re: [RE-wrenches] High Power Split phase inverter/chargers

2020-02-22 Thread frenergy
...and we were told at Intersolar 2.5 years ago that the B17 was comingstill waiting. Bill On 2/22/2020 6:56 PM, Allan Sindelar wrote:  Jeff, according to Midnite’s website, their B-17 inverter can be up to 40 kW in 2 kW increments.  Allan On Feb 22, 2020, at 8:05 PM, Jeff Clearwater

[RE-wrenches] 240 commercial single phase

2020-02-10 Thread frenergy
Hey Folks,             I'm coming into a least a couple small load 200 Amp/240 Vac single phase commercial jobs that need a Meter/main panel change-out that I can backfeed ~96 amps of solar onto.  Been using a Sq. D 'Solar Ready' panel for residential jobs but can't find equivalent for this t

[RE-wrenches] Issues with another Out of Production Panel

2020-01-31 Thread frenergy
There was a period of time when we were installing Mitsubishi PVs.  Now we are seeing issues with installs where we were using Mitsubishi MF170EB3 panels, bubbling backsheets, occasional bad solder joints, many with half the label's VOC voltage.  We actually just discovered one panel that was p

[RE-wrenches] SMA connection box access

2019-12-03 Thread frenergy
Wrenchers,             This particular install requires 6 Gauge for the AC output from a few SB7.7..-41 inverters (for voltage drop). Pretty tight for the 3/4" knock-outs in that inverter.  Any harm in using a step-drill to open it up to a 1" KO?  Any experiences with this?  I'm trying to

Re: [RE-wrenches] Convex modules

2019-11-16 Thread frenergy
Probably is not the cause but hard not to notice the big ding in the cardboard at about the right spot to cause your "deflection" from just the right whack with the fork lift.  Did it affect all the mods? Bill Feather River Solar Electric Bill Battagin, Owner 4291 Nelson St. Taylorsville, CA 9

Re: [RE-wrenches] HUP cell removal

2019-11-07 Thread frenergy
nt dancing that evening. Allan > On Nov 4, 2019, at 9:46 PM, frenergy mailto:frene...@psln.com>> wrote: > > I'm going to have to remove the cells from 4 HUP Solar1 battery cases to change-out the pack (no option, bad access).  Anyone ever had problems

[RE-wrenches] HUP cell removal

2019-11-04 Thread frenergy
I'm going to have to remove the cells from 4 HUP Solar1 battery cases to change-out the pack (no option, bad access).  Anyone ever had problems come-a-longing from above the first cell and if so, what's the solution?...and what are you doing tomorrow? Thx, Bill Feather River Solar Electric B

[RE-wrenches] Fwd: Re: Off Grid Washing Machine

2019-09-18 Thread frenergy
Drake,             After having 2 Stabers in the last 25 years, we were having too many problems with the second one (mechanically was OK but the brains were not working correctly and board replacements are pretty spendy.  So we ended up with an LG model # WM3500CW as of 3 months ago.  Made

Re: [RE-wrenches] SMA phantom arc faults

2019-09-15 Thread frenergy
I've only had the "tapping" method work on SB-22 inverters, not on -40 inverters.  You gotta log on to the machine which I think you can only do onsite.  Has anyone ever done a reset of the 8206 from the portal? Bill Feather River Solar Electric Bill Battagin, Owner 4291 Nelson St. Taylorsvill

Re: [RE-wrenches] SMA phantom arc faults

2019-09-02 Thread frenergy
Interestingly, the problems I've had with the SMA -40 AFCI faults have been on Comp roofs.  When I've gone "inside" a -40 with my laptop, I'm pretty sure I've seen where you can disable it? Bill On 9/2/2019 7:12 AM, drake.chamber...@redwoodalliance.org wrote: At least with the TL-22s, the AFCI

Re: [RE-wrenches] SMA phantom arc faults

2019-09-01 Thread frenergy
Hey Marco,             I hear you, we have installed many SMA-40's and we're not at the same point as you may be but we've definitely had a fair number of arc fault shut-downs which take a site visit to rectify.  One location had been experiencing lightening over a year and a half which seeme

[RE-wrenches] Backfeed in PG&E territory

2019-08-27 Thread frenergy
Wrenches,             Is the only a way to back feed 128 amps (240v, split PH) onto a 200 amp panel is to tap the conductors between the meter and the main CB, assuming I can pull it off in the "customer section" of the panel.  Of course with the requisite AC disco within 10 feet.  Or, has an