Hey Folks,
From the SimpliPHI/Outback integration guide download,
using an Outback (I assume any brand of) charge controller (EG: FM80,
FM60, FM100), their chart shows absorbtion voltage at 56.4 for 51.2 nom
PHI batteries with time set at 6 minutes, page 18. If using the
inverter, they show 54.0 volts for 2 hrs, page 13.
I found this at their website:
https://simpliphipower.com/product-documentation/
then scroll down. There may be a longevity advantage to not fully
charging L-ion batteries but if you're only charging to 80% and not
really supposed to go below 20% SOC then L-ion batteries aren't looking
much better than FLA batteries in terms of capacity.
Bill
Feather River Solar Electric
On 11/1/2021 10:03 AM, Chris Mason wrote:
There's no benefit to charging to 100%. If the charging parameters are
set up correctly, you'll never really get to 100%.
If you look at most prismatic cells, the absolutely maximum voltage is
3.65V. My systems are set up to charge to 3.4V or 54.4V. I take that
as 100%.
On Sun, Oct 31, 2021 at 12:19 PM
<drake.chamber...@redwoodalliance.org> wrote:
I have a client that insists it is better not to charge lithium
batteries to 100%. Is there any truth to this?
Thanks,
Drake
Drake Chamberlin
Athens Electric LLC
Ohio Electrical Contractor’s License 44810
CO Master Electrician’s License 4526
NABCEP Certified PV Installation Professional
--
_______________________________________________
List sponsored by Redwood Alliance
Pay optional member dues here: http://re-wrenches.org
List Address: RE-wrenches@lists.re-wrenches.org
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
There are two list archives for searching. When one doesn't work,
try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
http://www.members.re-wrenches.org
--
Chris Mason
Solar systems designer
Generac Generators Industrial technician
Comet Systems Ltd DBA Comet Solar
Anguilla Cell 264.235.5670
WhatsApp 264.235.5670
Skype: netconcepts
www.cometsolar.com <http://www.cometenergysystems.com/>
_______________________________________________
List sponsored by Redwood Alliance
Pay optional member dues here:http://re-wrenches.org
List Address:RE-wrenches@lists.re-wrenches.org
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
http://www.members.re-wrenches.org
--
Feather River Solar Electric
Bill Battagin, Owner
4291 Nelson St.
Taylorsville, CA 95983
530.284.7849
CA Lic 874049
www.frenergy.net
--
This email has been checked for viruses by Avast antivirus software.
https://www.avast.com/antivirus
_______________________________________________
List sponsored by Redwood Alliance
Pay optional member dues here: http://re-wrenches.org
List Address: RE-wrenches@lists.re-wrenches.org
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
http://www.members.re-wrenches.org