I understand and agree Todd, before I shot my mouth of to the layout
tech I wanted to make sure I was headed in the right direction.
Thank you!
*Ken Wagoner, SET*
*Parsley Consulting
500 West Mechanic Street
Harrisonville, Missouri 64701-2235*
*Phone: (760) 745-6181 *
*Visit the website
<https://linkprotect.cudasvc.com/url?a=http%3a%2f%2fwww.parsleyconsulting.com%2f&c=E,1,Y5zKJKPEh1mBEBqSR-VE9cUKl5y-eyP8BpvmE_5j9ZqW2eJbNphYzrCMBZ-2YuX6d-RRkHI4gQ1FV-cvOeCfRC58uZS9NiToZv2mx7909oCqLvCW_n5hDHeK&typo=1>*
On 10/9/2023 11:27 AM, Fpdcdesign wrote:
Ken, I think you would have to with the check valve. I would push back
a little in that by adding a normally open valve and a flow switch or
manifold would not change the physics of the system enough to warrant
the additional vents. If you had a 2 story building without zone
valves, you would only need one vent. However, if you add normally
open valves and flow switches, you would now need 2 (or 3?). From the
standpoint of physics, why?
Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860-535-2080 <tel:860-535-2080> (ofc)
860-554-7054 <tel:860-554-7054> (fax)
860-608-4559 <tel:860-608-4559> (cell)
On Oct 9, 2023 at 12:06 PM, <Ken Wagoner
<mailto:[email protected]>> wrote:
Yes, Todd, on each floor, as they're using a Victaulic UMC manifold
which includes a check valve.
thanks for the information,
*Ken Wagoner, SET*
*Parsley Consulting
500 West Mechanic Street
Harrisonville, Missouri 64701-2235*
*Phone: (760) 745-6181 *
*Visit the website
<https://linkprotect.cudasvc.com/url?a=http%3a%2f%2fwww.parsleyconsulting.com%2f&c=E,1,Y5zKJKPEh1mBEBqSR-VE9cUKl5y-eyP8BpvmE_5j9ZqW2eJbNphYzrCMBZ-2YuX6d-RRkHI4gQ1FV-cvOeCfRC58uZS9NiToZv2mx7909oCqLvCW_n5hDHeK&typo=1>*
On 10/9/2023 10:49 AM, Fpdcdesign wrote:
Is there a check valve on the floor control assembly?
Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860-535-2080 <tel:860-535-2080> (ofc)
860-554-7054 <tel:860-554-7054> (fax)
860-608-4559 <tel:860-608-4559> (cell)
On Oct 9, 2023 at 11:44 AM, <Ken Wagoner
<mailto:[email protected]>> wrote:
Forumites,
I'm working on a multi-story building protected per NFPA 13. As
each floor has a separate control valve, is a means to vent trapped
air required on each floor? Or is it only required at the highest
level of the building?
My thinking is that each floor has a separate fire sprinklers system.
Any thoughts?
*Ken Wagoner, SET*
*Parsley Consulting
500 West Mechanic Street
Harrisonville, Missouri 64701-2235*
*Phone: (760) 745-6181 *
*Visit the website
<https://linkprotect.cudasvc.com/url?a=http%3a%2f%2fwww.parsleyconsulting.com%2f&c=E,1,Y5zKJKPEh1mBEBqSR-VE9cUKl5y-eyP8BpvmE_5j9ZqW2eJbNphYzrCMBZ-2YuX6d-RRkHI4gQ1FV-cvOeCfRC58uZS9NiToZv2mx7909oCqLvCW_n5hDHeK&typo=1>*
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to
[email protected]
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email [email protected]
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to
[email protected]
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email [email protected]
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]