Ken, I think you would have to with the check valve. I would push back a 
little in that by adding a normally open valve and a flow switch or manifold 
would not change the physics of the system enough to warrant the additional 
vents. If you had a 2 story building without zone valves, you would only need 
one vent. However, if you add normally open valves and flow switches, you would 
now need 2 (or 3?). From the standpoint of physics, why?
 
 
 
Todd G Williams, PE 
Fire Protection Design/Consulting
 
Stonington, CT
 
860-535-2080 (tel:860-535-2080)  (ofc)
 
860-554-7054 (tel:860-554-7054)     (fax)
 
860-608-4559 (tel:860-608-4559)  (cell)
 
 
 
 

 
 
>  
> On Oct 9, 2023 at 12:06 PM,  <Ken Wagoner 
> (mailto:[email protected])>  wrote:
>  
>  
>   Yes, Todd, on each floor, as they're using a Victaulic UMC manifold which 
> includes a check valve.
>  
>  thanks for the information,
>  
> Ken Wagoner, SET
>   Parsley Consulting
>  500 West Mechanic Street
>  Harrisonville, Missouri 64701-2235
>   Phone: (760) 745-6181
>    Visit the website 
> (https://linkprotect.cudasvc.com/url?a=http%3a%2f%2fwww.parsleyconsulting.com%2f&c=E,1,Y5zKJKPEh1mBEBqSR-VE9cUKl5y-eyP8BpvmE_5j9ZqW2eJbNphYzrCMBZ-2YuX6d-RRkHI4gQ1FV-cvOeCfRC58uZS9NiToZv2mx7909oCqLvCW_n5hDHeK&typo=1)
>   
> On 10/9/2023 10:49 AM, Fpdcdesign wrote:
>  
> >    
> > Is there a check valve on the floor control assembly?
> >  
> >  
> >  
> > Todd G Williams, PE 
> > Fire Protection Design/Consulting
> >  
> > Stonington, CT
> >  
> > 860-535-2080 (tel:860-535-2080)  (ofc)
> >  
> > 860-554-7054 (tel:860-554-7054)     (fax)
> >  
> > 860-608-4559 (tel:860-608-4559)  (cell)
> >  
> >  
> >  
> >  
> >
> >  
> >  
> > >  
> > > On Oct 9, 2023 at 11:44 AM,  <Ken Wagoner 
> > > (mailto:[email protected])>  wrote:
> > >  
> > >  
> > >   Forumites,
> > >  
> > >  I'm working on a multi-story building protected per NFPA 13.    As each 
> > > floor has a separate control valve, is a means to vent trapped air 
> > > required on each floor?    Or is it only required at the highest level of 
> > > the building?
> > >  
> > >  My thinking is that each floor has a separate fire sprinklers system.  
> > >  
> > >  Any thoughts?
> > >  
> > > Ken Wagoner, SET
> > >   Parsley Consulting
> > >  500 West Mechanic Street
> > >  Harrisonville, Missouri 64701-2235
> > >   Phone: (760) 745-6181
> > >   Visit the website 
> > > (https://linkprotect.cudasvc.com/url?a=http%3a%2f%2fwww.parsleyconsulting.com%2f&c=E,1,Y5zKJKPEh1mBEBqSR-VE9cUKl5y-eyP8BpvmE_5j9ZqW2eJbNphYzrCMBZ-2YuX6d-RRkHI4gQ1FV-cvOeCfRC58uZS9NiToZv2mx7909oCqLvCW_n5hDHeK&typo=1)
> > >   
> > >
> > >  _________________________________________________________ SprinklerForum 
> > > mailing list:   
> > > https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
> > >   To unsubscribe send an email to  
> > > [email protected] 
> > > (mailto:[email protected])        
> >    
> >  _________________________________________________________ SprinklerForum 
> > mailing list:  
> > https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org 
> >  To unsubscribe send an email to  
> > [email protected] 
> > (mailto:[email protected])  
>
>  
>  _________________________________________________________ SprinklerForum 
> mailing list: 
> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org 
> To unsubscribe send an email to [email protected]  
>           
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to