I would say that you are correct that each floor is a separate sprinkler system 
and will require it’s own means of venting.

Regards,

Dale F. Wingard, SET
Designer Commercial/Marine Division
NICET IV #76284
Water-based Systems

3751 Joy Springs Drive, Mobile, Alabama 36693
o: 251.661.1275 | c: 251.509.7108 | HillerFire.com
[Logo  Description automatically generated with low confidence][A close-up of a 
certificate  Description automatically generated with low confidence]

From: Ken Wagoner <[email protected]>
Sent: Monday, October 9, 2023 10:43 AM
To: [email protected]
Subject: [Sprinklerforum] Air venting

Forumites,

I'm working on a multi-story building protected per NFPA 13.  As each floor has 
a separate control valve, is a means to vent trapped air required on each 
floor?  Or is it only required at the highest level of the building?

My thinking is that each floor has a separate fire sprinklers system.

Any thoughts?