Ken The Appendix states that it is necessary to choose a location where the greatest volume of trapped air is vented during the first fill and each subsequent drain and fill event. Being that you must have a control valve, water flow alarm and drain for each floor then that is the definition of a system. I agree that you would need an air vent for each floor.
Anthony Carrizosa Project Manager | Fire Protection 7855 S 206th St Kent, WA 98032 Cell: 206-679-5283 | Office Dir: 253-341-4593 [cid:[email protected]] https://archerconstruction.com<https://linkprotect.cudasvc.com/url?a=https%3a%2f%2farcherconstruction.com%2f&c=E,1,Wdb65AWzMgSBzW3HDw91SfcRQCtxDUQKoJf-UowQ-WnB_WMosgG-8W7eLePJ42PwWQvLiQx16Pls052VqwHO7tKm-_u5AnWly0ewkNiMkxn-AjQb1JI,&typo=1> From: Ken Wagoner <[email protected]> Sent: Monday, October 9, 2023 8:43 AM To: [email protected] Subject: [Sprinklerforum] Air venting Forumites, I'm working on a multi-story building protected per NFPA 13. As each floor has a separate control valve, is a means to vent trapped air required on each floor? Or is it only required at the highest level of the building? My thinking is that each floor has a separate fire sprinklers system. Any thoughts? Ken Wagoner, SET Parsley Consulting 500 West Mechanic Street Harrisonville, Missouri 64701-2235 Phone: (760) 745-6181 Visit the website<https://linkprotect.cudasvc.com/url?a=http%3a%2f%2fwww.parsleyconsulting.com%2f&c=E,1,Y5zKJKPEh1mBEBqSR-VE9cUKl5y-eyP8BpvmE_5j9ZqW2eJbNphYzrCMBZ-2YuX6d-RRkHI4gQ1FV-cvOeCfRC58uZS9NiToZv2mx7909oCqLvCW_n5hDHeK&typo=1>