8.1.5 Air Venting.
A single air vent with a connection conforming to Section 
16.7<https://link.nfpa.org/publications/13/2022/chapters/16#ID000130006575> 
shall be provided on each wet pipe system utilizing metallic pipe. (See 
A.‍16.7<https://link.nfpa.org/publications/13/2022/annexes/A/groups/16#ID000130005726>.)


3.3.216*<https://link.nfpa.org/publications/13/2022/annexes/A/groups/3#ID000130005318>
 Sprinkler System.
A system, commonly activated by heat from a fire and discharges water over the 
fire area, that consists of an integrated network of piping designed in 
accordance with fire protection engineering standards that includes a water 
supply source, a control valve, a waterflow alarm, and a drain. The portion of 
the sprinkler system above ground is a network of specifically sized or 
hydraulically designed piping installed in a building, structure, or area, 
generally overhead, and to which sprinklers are attached in a systematic 
pattern. (AUT-SSI)


Please rate our customer 
service<https://survey.medallia.com/?emailsignature&fc=3539&bg=Fire%20and%20Fabrication>

Matthew J. Willis, CWBSP, CET
Engineering Manager – Southwest Region
FERGUSON FIRE DESIGN, LLC
A Wholly Owned Subsidiary of Ferguson Fire & Fabrication, LLC
3508 Hwy. 557
West Monroe, LA. 71292
C: 307-236-8249
[email protected]<mailto:[email protected]>
www.FergusonFire.com<http://www.fergusonfire.com/>


From: Travis Mack <[email protected]>
Sent: Monday, October 9, 2023 11:51 AM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]>
Subject: [Sprinklerforum] Re: Air venting

My understanding is that it is per system.


Travis Mack, SET
M.E.P.CAD | Instructor / Support
181 N. Arroyo Grande Blvd. #105 I Henderson, NV 89074
www.mepcad.com<http://www.mepcad.com/> | m: 480.547.9348| Whatspp: +14805479348
Email: [email protected]<mailto:[email protected]>

AutoSPRINK  |  AutoSPRINK FAB  |  AutoSPRINK RVT  |  AlarmCAD

From: Ken Wagoner 
<[email protected]<mailto:[email protected]>>
Sent: Monday, October 9, 2023 8:43 AM
To: 
[email protected]<mailto:[email protected]>
Subject: [Sprinklerforum] Air venting

Forumites,

I'm working on a multi-story building protected per NFPA 13.  As each floor has 
a separate control valve, is a means to vent trapped air required on each 
floor?  Or is it only required at the highest level of the building?

My thinking is that each floor has a separate fire sprinklers system.

Any thoughts?
Ken Wagoner, SET
Parsley Consulting
500 West Mechanic Street
Harrisonville, Missouri 64701-2235
Phone: (760) 745-6181
Visit the 
website<https://linkprotect.cudasvc.com/url?a=http%3a%2f%2fwww.parsleyconsulting.com%2f&c=E,1,Y5zKJKPEh1mBEBqSR-VE9cUKl5y-eyP8BpvmE_5j9ZqW2eJbNphYzrCMBZ-2YuX6d-RRkHI4gQ1FV-cvOeCfRC58uZS9NiToZv2mx7909oCqLvCW_n5hDHeK&typo=1>

_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to