If you shut off and drain one system you can’t use a high point air vent when 
you refill unless you drained the whole building which pretty much defeats the 
purpose of having floor controls.

Mike Morey
CFPS 3229 • NICET S.E.T. 123677
Project Manager • Fire Protection Group
Shambaugh & Son, LP an EMCOR Company
7614 Opportunity Drive • Fort Wayne, IN • 46825
direct 260.487.7824 /  cell 260.417.0625 /  fax 260.487.7991
email [email protected]
[cid:[email protected]]

From: Fpdcdesign <[email protected]>
Sent: Monday, October 9, 2023 12:28 PM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]>
Subject: [Sprinklerforum] Re: Air venting

Ken, I think you would have to with the check valve. I would push back a little 
in that by adding a normally open valve and a flow switch or manifold would not 
change the physics of the system enough to warrant the additional vents. If you
ZjQcmQRYFpfptBannerStart
This Message Is From an External Sender
This message originated outside your organization.
ZjQcmQRYFpfptBannerEnd
Ken, I think you would have to with the check valve. I would push back a little 
in that by adding a normally open valve and a flow switch or manifold would not 
change the physics of the system enough to warrant the additional vents. If you 
had a 2 story building without zone valves, you would only need one vent. 
However, if you add normally open valves and flow switches, you would now need 
2 (or 3?). From the standpoint of physics, why?

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860-535-2080<tel:860-535-2080> (ofc)
860-554-7054<tel:860-554-7054>  (fax)
860-608-4559<tel:860-608-4559> (cell)



On Oct 9, 2023 at 12:06 PM, <Ken Wagoner<mailto:[email protected]>> 
wrote:
Yes, Todd, on each floor, as they're using a Victaulic UMC manifold which 
includes a check valve.

thanks for the information,
Ken Wagoner, SET
Parsley Consulting
500 West Mechanic Street
Harrisonville, Missouri 64701-2235
Phone: (760) 745-6181
Visit the 
website<https://urldefense.com/v3/__https:/linkprotect.cudasvc.com/url?a=http*3a*2f*2fwww.parsleyconsulting.com*2f&c=E,1,Y5zKJKPEh1mBEBqSR-VE9cUKl5y-eyP8BpvmE_5j9ZqW2eJbNphYzrCMBZ-2YuX6d-RRkHI4gQ1FV-cvOeCfRC58uZS9NiToZv2mx7909oCqLvCW_n5hDHeK&typo=1__;JSUlJQ!!FaxH778!fTxBK8PE-7xZT7FmscAmw7LvK4RYA1YsXdEr7WgwWkllUjSeHbzEYKqj_5tk8E7wasqqFVvy7MQVkBlJo50$>
On 10/9/2023 10:49 AM, Fpdcdesign wrote:
Is there a check valve on the floor control assembly?

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860-535-2080<tel:860-535-2080> (ofc)
860-554-7054<tel:860-554-7054>  (fax)
860-608-4559<tel:860-608-4559> (cell)



On Oct 9, 2023 at 11:44 AM, <Ken Wagoner<mailto:[email protected]>> 
wrote:
Forumites,

I'm working on a multi-story building protected per NFPA 13.  As each floor has 
a separate control valve, is a means to vent trapped air required on each 
floor?  Or is it only required at the highest level of the building?

My thinking is that each floor has a separate fire sprinklers system.

Any thoughts?
Ken Wagoner, SET
Parsley Consulting
500 West Mechanic Street
Harrisonville, Missouri 64701-2235
Phone: (760) 745-6181
Visit the 
website<https://urldefense.com/v3/__https:/linkprotect.cudasvc.com/url?a=http*3a*2f*2fwww.parsleyconsulting.com*2f&c=E,1,Y5zKJKPEh1mBEBqSR-VE9cUKl5y-eyP8BpvmE_5j9ZqW2eJbNphYzrCMBZ-2YuX6d-RRkHI4gQ1FV-cvOeCfRC58uZS9NiToZv2mx7909oCqLvCW_n5hDHeK&typo=1__;JSUlJQ!!FaxH778!fTxBK8PE-7xZT7FmscAmw7LvK4RYA1YsXdEr7WgwWkllUjSeHbzEYKqj_5tk8E7wasqqFVvy7MQVkBlJo50$>

_________________________________________________________ SprinklerForum 
mailing list: 
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org<https://urldefense.com/v3/__https:/lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org__;!!FaxH778!fTxBK8PE-7xZT7FmscAmw7LvK4RYA1YsXdEr7WgwWkllUjSeHbzEYKqj_5tk8E7wasqqFVvy7MQVAr48BC8$>
 To unsubscribe send an email to 
[email protected]<mailto:[email protected]>



_________________________________________________________

SprinklerForum mailing list:

https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org<https://urldefense.com/v3/__https:/lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org__;!!FaxH778!fTxBK8PE-7xZT7FmscAmw7LvK4RYA1YsXdEr7WgwWkllUjSeHbzEYKqj_5tk8E7wasqqFVvy7MQVAr48BC8$>

To unsubscribe send an email to 
[email protected]<mailto:[email protected]>

_________________________________________________________ SprinklerForum 
mailing list: 
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org<https://urldefense.com/v3/__https:/lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org__;!!FaxH778!fTxBK8PE-7xZT7FmscAmw7LvK4RYA1YsXdEr7WgwWkllUjSeHbzEYKqj_5tk8E7wasqqFVvy7MQVAr48BC8$>
 To unsubscribe send an email to 
[email protected]<mailto:[email protected]>

This message is for the named person's use only.  It may contain confidential, 
proprietary or legally privileged information. No confidentiality or privilege 
is waived or lost by any mistransmission.  If you receive this message in 
error, please  immediately delete it and all copies of it from your system, 
destroy any hard copies of it and notify the sender.  You must not, directly or 
indirectly, use, disclose, distribute, print, or copy any part of this message 
if you are not the intended recipient.
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to