Hey Ken,
As has already been stated by others, I believe the intent is to remove as much 
air from 'each wet system' as possible.  'System', in this case, is any piping 
network isolated from the rest of the upstream system by isolation valving be 
it a check valve or a shutoff valve.

Support for this may be found on page three of the 'Origin and Development' at 
the beginning of NFPA 13 (2022).  While multiple floor control valve 
configurations may be on a single wet-pipe system, it is unlikely that air 
trapped in piping in lower floors will migrate through these valve 
configurations =, and the common low points in the piping configuration, to the 
single high-point connection in the top floor piping.  Also, when work is done 
on a single level (not at the highest level), piping is likely drained on that 
floor only.  Air will be reintroduced into this piping at high points upon 
refilling which, without having a single high-point vent on that floor 
(downstream of the floor control valve) would have to migrate back through 
multiple open floor control system valving configurations and up to the top 
floor...which I think is unlikely.

Annex A16.7 provides further rationale for removal of as much air from 
wet-piping networks as possible from a single location on metal systems to 
reduce corrosion and is currently up to the discretion of the designer.  I 
would contend that this is on any system segment that can be isolated while 
leaving the remainder of the system in service.  Furthermore, the annex section 
also recommends each wet pipe sprinkler system to be vented every time the 
system is filled.  On a multi-floor controlled wet pipe system without venting 
on each floor, I would contend that is will result in multiple problems for 
contractors trying to do their due diligence and purge these systems.

Even though not outright required, I believe at least one air vent should be 
downstream of each isolatable wet-pipe system section.  It is definitely a 
'good practice' as you have suggested.

Hope this helps,

Ryan L. Hinson, PE*, SET**  \  Burns & McDonnell
Associate Fire Protection Engineer
O 612-900-3755 \  M 763-688-4045 \  F 952-229-2923
[email protected]<mailto:[email protected]>  \  
burnsmcd.com<http://www.burnsmcd.com/>
8201 Norman Center Drive, Suite 500  \  Minneapolis-St. Paul, MN 55437
*Registered in: AK, LA, MD, MN, PA, TX, & UT
**NICET IV - Water-Based Systems Layout

From: Ken Wagoner <[email protected]>
Sent: Monday, October 9, 2023 10:43 AM
To: [email protected]
Subject: [Sprinklerforum] Air venting

Forumites,

I'm working on a multi-story building protected per NFPA 13.  As each floor has 
a separate control valve, is a means to vent trapped air required on each 
floor?  Or is it only required at the highest level of the building?

My thinking is that each floor has a separate fire sprinklers system.

Any thoughts?
Ken Wagoner, SET
Parsley Consulting
500 West Mechanic Street
Harrisonville, Missouri 64701-2235
Phone: (760) 745-6181
Visit the 
website<https://linkprotect.cudasvc.com/url?a=http%3a%2f%2fwww.parsleyconsulting.com%2f&c=E,1,Y5zKJKPEh1mBEBqSR-VE9cUKl5y-eyP8BpvmE_5j9ZqW2eJbNphYzrCMBZ-2YuX6d-RRkHI4gQ1FV-cvOeCfRC58uZS9NiToZv2mx7909oCqLvCW_n5hDHeK&typo=1>

_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to