by someone, somewhere. Find out what others have done.
Once you educate yourself you will then have the tools to modify your
approach, if needed, or to argue your case if you are convinced your
approach is correct.
I hope this helps.
William Miller
Miller Solar
17395 Oak Road, Atascad
there has been regularly service pump efficiency should have been logged.
William Miller
Miller Solar.com
805-438-5600
www.millersolar.com
On Thu, Jan 23, 2025 at 7:44 PM John Blittersdorf via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:
> The only thing I could find in
Ear plugs?
William Miller
Miller Solar.com
805-438-5600
www.millersolar.com
On Thu, Jan 23, 2025 at 7:44 PM John Blittersdorf via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:
> The only thing I could find in the whole system that was not up to snuff
> was incomplete s
Alameda Electric
1200 Holm Road
Petaluma, CA 94954
*(707) 778-8881* <707771>
The local office gives me good pricing and treats me well.
William Miller
Miller Solar.com
805-438-5600
www.millersolar.com
On Thu, Jan 23, 2025 at 10:57 AM david quattro via RE-wrenches <
re-wrenches
.
William
Miller Solar
17395 Oak Road, Atascadero, CA 93422
805-438-5600
www.millersolar.com
CA Lic. 773985
___
List sponsored by Redwood Alliance
Pay optional member dues here: http://re-wrenches.org
List Address: RE-wrenches@lists.re-wrenches.org
Could be a nuisance trip. Check and replace the fuse. Cross fingers.
William Miller
Miller Solar.com
805-438-5600
www.millersolar.com
On Sat, Jan 18, 2025 at 2:41 PM Dana Orzel via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:
> Hey, all you wise ones,
> 37 years in the
Friends:
I have a Sunny Island system that is intermittently experiencing a stuck
transfer relay. Has anyone tried to clean these relay contacts or replace
the relay? If so, what can you tell me about your experience?
Thanks in advance.
William Miller
Miller Solar
17395 Oak Road
? That information is not in the manual
that I can find.
Thanks in advance.
William Miller
Miller Solar
17395 Oak Road, Atascadero, CA 93422
805-438-5600
www.millersolar.com
CA Lic. 773985
*From:* RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] *On
Behalf Of *Stuart
I would measure the water pumped with a simple water meter. You get the
important data about water pumping rates and total volume. You can
extrapolate energy consumption. Simple installation.
William Miller
Miller Solar.com
805-438-5600
www.millersolar.com
On Thu, Jan 16, 2025 at 1:54 PM jay
They may be able to
request a meter that does not connect wirelessly to the utility for meter
reading purposes. This is pure speculation on my part.
William
Miller Solar
17395 Oak Road, Atascadero, CA 93422
805-438-5600
www.millersolar.com
CA Lic. 773985
-Original Message-
this? If it is
not required, the manufacturers should certainly correct these problems.
This may be a case against All-in-on inverters. If there is a PV arc fault
on systems with separate charge controllers the inverter will not curtail
operation and it’s pass-through capabilities.
William
electrical systems are both
rebuilt. Field repairs are typically less reliable than a new unit.
William
Miller Solar
17395 Oak Road, Atascadero, CA 93422
805-438-5600
www.millersolar.com
CA Lic. 773985
*From:* RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] *On
Behalf Of
I will post a synopsis of the situation a little later today.
William Miller
Miller Solar.com
805-438-5600
www.millersolar.com
On Tue, Jan 14, 2025 at 4:30 AM Mac Lewis via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:
> We are out of Colorado and I would encourage you to
that keeps this industry going will decrease significantly.
I think anyone on this list should be interested in this trend.
William Miller
Miller Solar
17395 Oak Road, Atascadero, CA 93422
805-438-5600
www.millersolar.com
CA Lic. 773985
*From:* Jay [mailto:jay.pe...@gmail.com]
*
his
list-serve?
William Miller
Miller Solar
17395 Oak Road, Atascadero, CA 93422
805-438-5600
www.millersolar.com
CA Lic. 773985
___
List sponsored by Redwood Alliance
Pay optional member dues here: http://re-wrenches.org
List Address: RE-
the Full River DC-400-2. You might be able to do a one string
installation.
Unigy II is a great system. Very robust. Hard to deliver but I can offer
tips. Lots of AH size options.
William
Miller Solar
17395 Oak Road, Atascadero, CA 93422
805-438-5600
www.millersolar.com
CA Lic. 773985
Jay:
I saw this exact behavior recently with an older MX80. Replacing it
resolved the problem.
William
Miller Solar
17395 Oak Road, Atascadero, CA 93422
805-438-5600
www.millersolar.com
CA Lic. 773985
-Original Message-
From: RE-wrenches [mailto:re-wrenches-boun...@lists.re
ips in use, please?
Thanks in advance for contributing to this study.
William Miller
Miller Solar
17395 Oak Road, Atascadero, CA 93422
805-438-5600
www.millersolar.com
CA Lic. 773985
___
List sponsored by Redwood Alliance
Pay optional member du
.
William Miller
Miller Solar
17395 Oak Road, Atascadero, CA 93422
805-438-5600
www.millersolar.com
CA Lic. 773985
*From:* RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] *On
Behalf Of *Jay via RE-wrenches
*Sent:* Wednesday, December 18, 2024 12:19 PM
*To:* RE-wrenches
*Cc
charging.
Once the SOC came up to acceptable levels we reset the system for a BMS
battery and we were back running.
Maybe this procedure might work for someone else. I have a step-by-step for
doing this with a Sunny Island system if anyone wants to look it over.
William Miller
Miller Solar.com
805
Pieter:
Interesting. One would think the Coast Guard would have access to the
space lasers. These should easily melt off any snow accumulation.
William Miller
Miller Solar
17395 Oak Road, Atascadero, CA 93422
805-438-5600
www.millersolar.com
CA Lic. 773985
*From:* RE-wrenches
and I have
not heard a thing.
Anyone else having problems with Sunny Portal? What is this world of ours
coming to? It seems tech support is falling apart in every product line.
William Miller
Miller Solar
17395 Oak Road, Atascadero, CA 93422
805-438-5600
www.millersolar.com
CA Lic
string of one RSD on the bench? I would input into PV input 1
from a bench power supply and test for voltage at the string output
connectors.
Has anyone tried this?
Thanks in advance.
William Miller
Miller Solar
17395 Oak Road, Atascadero, CA 93422
805-438-5600
www.millersolar.com
CA
The one and only TOP rack manufacturer I will work with:
https://solarrackworks.com/tablet/index.html
j...@solarrackworks.com
William Miller
Miller Solar.com
805-438-5600
www.millersolar.com
On Wed, Nov 13, 2024 at 2:55 PM Sam Haraldson via RE-wrenches <
re-wrenches@lists.re-wrenches.
without risking damage to the PVG units.
As always, the devil is in the details. Success is achieved in
understanding and dealing with the details.
William Miller
Miller Solar
17395 Oak Road, Atascadero, CA 93422
805-438-5600
www.millersolar.com
CA Lic. 773985
*From:* Lloyd
and then connect the PV. Can I interconnect the PVG units
prior to connecting the PV modules? This sure would make the process
easier.
Thanks in advance for in any input on working with these units.
William Miller
Miller Solar
17395 Oak Road, Atascadero, CA 93422
805-438-5600
Jay:
I just configured a new XW Pro with an old SCP.
William Miller
Miller Solar.com
805-438-5600
www.millersolar.com
On Mon, Nov 11, 2024 at 2:23 PM jay via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:
>
> I know this has been discussed before but I couldn’t find what
that versed on the
equipment. Do any of you know what might be causing this problem?
Thanks in advance.
William
Miller Solar
17395 Oak Road, Atascadero, CA 93422
805-438-5600
www.millersolar.com
CA Lic. 773985
___
List sponsored by Redwood
Jeremy:
Question: Did you install the ATS as a work-around to the problem
described?
William Miller
Miller Solar
17395 Oak Road, Atascadero, CA 93422
805-438-5600
www.millersolar.com
CA Lic. 773985
*From:* RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] *On
Behalf
Am:
Check with PV Cables to see if they have a recommendation.
William
Miller Solar
17395 Oak Road, Atascadero, CA 93422
805-438-5600
www.millersolar.com
CA Lic. 773985
*From:* RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] *On
Behalf Of *Sam Haraldson via RE
Friends:
Like many of you I have a big investment in the use of Outback inverters
and associated equipment. I have been unable to talk with tech support for
months.
When I call 360-435-6030 I am immediately shunted to voicemail and my
messages go un-replied.
I discovered another tech supp
inverter to sleep. Does the FXR
inverter support that stacking and that use of the X240 transformer? I
have a vague recollection that the R series does not offer that stacking
option.
Thanks in advance.
William Miller
Miller Solar
17395 Oak Road, Atascadero, CA 93422
805-438-5600
Kevin:
Your experience sounds a lot like a similar one we had with a Radian
system. It is documented here
<https://millersolar.com/MillerSolar/case_studies/25_GFI%20Tripping/GFI_Tripping.html>
along with the solution we found. I hope you find some value in our case
study.
William
Rick:
You’re OK leaving this random high voltage DC on the AC output?
William Miller
Miller Solar.com
805-438-5600
www.millersolar.com
On Wed, Oct 16, 2024 at 6:09 PM r...@solshineenergy.com <
r...@solshineenergy.com> wrote:
> Confirmed! Reading the same points on a different inverte
inputs.
While you are at it, check DC voltages between the Sunny Boy DC inputs to
ground and between the Sunny Boy Chassis and ground.
Check your GEC, GEC bonding conductor and all of the system EGCs.
I would also check the GFDI fuse on the Sunny Boy.
William Miller
Miller Solar
17395
say?
If the DC Fault is not eternal then it must be internal to the inverter.
This could be a dangerous situation. I would proceed with caution.
Try completely isolating the PV from the inverter as a start.
Good luck.
William Miller
Miller Solar
17395 Oak Road, Atascadero, CA 93422
the inverter system for normal operation, but if the inverter system
errors out, the ATS can start the generator and activate the bypass-- all
unattended.
William
Miller Solar
17395 Oak Road, Atascadero, CA 93422
805-438-5600
www.millersolar.com
CA Lic. 773985
*From:* RE-wrenches
I mis-wrote: it’s a VFX3648 existing and a FXR3048 I’m am adding.
It does not work. There is a warning on the screen forbidding the marriage.
William Miller
Miller Solar.com
805-438-5600
www.millersolar.com
On Tue, Oct 8, 2024 at 12:19 PM jay wrote:
> I have done in the past VFX and
I’m in the field with a dead VXR3048. Will the FXR play nice with the
VFXR? Which should be Master?
Tech support did not answer of course.
William Miller
Miller Solar.com
805-438-5600
www.millersolar.com
___
List sponsored by Redwood Alliance
Pay
level or plumb was not that easy when I
tried it and that seems necessary, so I am looking for hints on your
process.
William
Miller Solar
17395 Oak Road, Atascadero, CA 93422
805-438-5600
www.millersolar.com
CA Lic. 773985
*From:* RE-wrenches [mailto:re-wrenches-boun...@lists.re
. You can check this by setting an extra stick of rail
across the tops of your installed rail and looking for gaps.
The process is tedious but if you check as you go and don’t let the error
get too big the error can be corrected.
Jim, I hope this answers your qestion.
William Miller
Howie:
The SB2500 is a 240 VAC inverter. So is the rare SB2100. The SB1800 is 120
VAC.
I have a 2500 I could spare. I am in need of an 1800.
William Miller
Miller Solar.com
805-438-5600
www.millersolar.com
On Wed, Oct 2, 2024 at 7:29 AM Howie Michaelson via RE-wrenches <
re-wrenches@lists
I’ve got lots of those. Contact me off list.
William Miller
Miller Solar.com
805-438-5600
www.millersolar.com
On Fri, Sep 27, 2024 at 5:41 AM Jeremy Rodriguez via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:
> If anyone knows of a source for the DC negative and positive bus
batteries can be tedious to install because they are heavy and you
have to stack them. I can provide some tips on handling them. I’ve been
meaning to make a web-page on the subject.
William
Miller Solar
17395 Oak Road, Atascadero, CA 93422
805-438-5600
www.millersolar.com
CA Lic. 773985
Jay:
I like the Control-by-web <https://controlbyweb.com/> product line. It is
a Swiss Army Knife type system with many building blocks. Here
<https://millersolar.com/MillerSolar/Portfolio/Commercial/Cal_Trans/Remote/Remote_Control.html>
is a project using the system.
Wi
error light is a generator problem, if I recall correctly.
I doubt you have an inverter problem but if it turns out to be so I
probably have a working, used 24 VDC VFX I could donate, if you can
convert.
William Miller
Miller Solar.com
805-438-5600
www.millersolar.com
On Wed, Aug 14, 2024 at 3
They called me today to sell me more batteries but they can’t fix my SMA
system.
William Miller
Miller Solar.com
805-438-5600
www.millersolar.com
On Tue, Aug 6, 2024 at 5:35 PM Kirpal Khalsa via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:
> Hi Folks
> Anyone
practice.
Based on the code and this logic, I am very clear that one must connect
neutrals within the load-center that holds the overcurrent protection
feeding that circuit.
William Miller
*300.3(B) Conductors of the Same Circuit. All conductors of the*
*same circuit and, where used, the
button for 7-10 seconds. I will try that.
William
Miller Solar
17395 Oak Road, Atascadero, CA 93422
805-438-5600
www.millersolar.com
CA Lic. 773985
*From:* MDElectricSolar [mailto:mdelectricso...@gmail.com]
*Sent:* Monday, July 29, 2024 10:21 PM
*To:* will...@millersolar.com; RE
versus the 2P?
Thank you for your time.
William Miller
Miller Solar
17395 Oak Road, Atascadero, CA 93422
805-438-5600
www.millersolar.com
CA Lic. 773985
*From:* MD Electric & Solar [mailto:mdelectricso...@gmail.com]
*Sent:* Monday, July 29, 2024 9:14 PM
*To:* will...@millersolar
the circuit. I have looked through the NEC to
find a passage that spells this out but I can seem to find one.
Is this a code requirement? Is this recommended practice?
Thanks in advance.
William Miller
Miller Solar
17395 Oak Road, Atascadero, CA 93422
805-438-5600
www.millersolar.com
Friends:
I have been through the manual and I can’t find anywhere where you can see
on the inverter front panel the PV volts or amps for each of the MPPT
inputs. Am I missing something?
Thanks,
William Miller
Miller Solar
17395 Oak Road, Atascadero, CA 93422
805-438-5600
I can’t get through to tech support and they don’t return my calls.
William Miller
Miller Solar.com
805-438-5600
www.millersolar.com
On Sat, Jul 20, 2024 at 1:48 PM Dana Orzel via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:
> What’s up with Outback as a biz?
> A
No, although I have tried. I have left messages for weeks but no response.
William Miller
Miller Solar.com
805-438-5600
www.millersolar.com
On Thu, Jul 18, 2024 at 2:56 PM Bruce Erickson
wrote:
> Speaking of OB tech support, I was on hold for two hours yesterday, then
> gave up. Has
Jim:
You may be logged in as a limited access user. Try logging in as installer.
William Miller
Miller Solar.com
805-438-5600
www.millersolar.com
On Thu, Jul 18, 2024 at 2:12 PM Jim Gowdy via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:
> I'm having issues trying to s
Friends:
I have a low voltage PV array that is begging for a Sunny Boy 1800U. If
anyone has one they are willing to part with, please contact me directly.
Thanks,
William
Miller Solar
17395 Oak Road, Atascadero, CA 93422
805-438-5600
www.millersolar.com
CA Lic. 773985
.
William Miller
Miller Solar
17395 Oak Road, Atascadero, CA 93422
805-438-5600
www.millersolar.com
CA Lic. 773985
___
List sponsored by Redwood Alliance
Pay optional member dues here: http://re-wrenches.org
List Address: RE-wrenches@lists.re
problem in itself. Add the BOS. The PV charge needs to
have either two battery breakers or be wired on the inverter side of the
battery breaker, an arrangement that I do not recommend.
Did I mention I think this is a bad idea?
William Miller
Miller Solar
17395 Oak Road, Atascadero, CA 93422
805
To replace a failed unit. As always, off list response is appreciated.
Thanks,
William
Miller Solar
17395 Oak Road, Atascadero, CA 93422
805-438-5600
www.millersolar.com
CA Lic. 773985
___
List sponsored by Redwood Alliance
Pay optional
companies say: “Solar?
It can’t be that complicated!”
William Miller
Miller Solar
17395 Oak Road, Atascadero, CA 93422
805-438-5600
www.millersolar.com
CA Lic. 773985
*From:* RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] *On
Behalf Of *Jason Szumlanski via RE-wrenches
onk).
William
Miller Solar
17395 Oak Road, Atascadero, CA 93422
805-438-5600
www.millersolar.com
CA Lic. 773985
*From:* RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] *On
Behalf Of *Scot Arey via RE-wrenches
*Sent:* Wednesday, May 29, 2024 3:16 PM
*To:* 'RE-wrenches'
high voltage PV circuits during daylight hours is worth the added
cost and inconvenience.
With all due respect. Rant off.
William Miller
Miller Solar.com
805-438-5600
www.millersolar.com
On Fri, May 24, 2024 at 12:25 PM Dave Angelini Offgrid Solar via
RE-wrenches wrote:
> Well to me the fi
Tell that to your local fire fighters.
William Miller
Miller Solar.com
805-438-5600
www.millersolar.com
On Fri, May 24, 2024 at 12:25 PM Dave Angelini Offgrid Solar via
RE-wrenches wrote:
> Well to me the final, final straw is their stock price losing 2/3 its
> value in a year.
>
>
the Outback line will
continue as before.
That’s what I have learned this morning.
William
Miller Solar
17395 Oak Road, Atascadero, CA 93422
805-438-5600
www.millersolar.com
CA Lic. 773985
___
List sponsored by Redwood Alliance
Pay optional
based in
great part on the Optics interface. For this system to be down for days at
a time is not a good sign at all.
I will be lighting up the phone lines on Monday to find out what happened
and to emphasize this cannot become a pattern.
William
Miller Solar
17395 Oak Road, Atascadero, CA
Friends:
100% of our Optics sites are down since 11 AM yesterday. Is it just us?
William Miller
Miller Solar.com
805-438-5600
www.millersolar.com
___
List sponsored by Redwood Alliance
Pay optional member dues here: http://re-wrenches.org
List
Dave:
Have you actually used the product?
William Miller
Miller Solar.com
805-438-5600
www.millersolar.com
On Tue, May 14, 2024 at 5:38 PM Dave Angelini Offgrid Solar via RE-wrenches
wrote:
> Huge mistake to me to use high voltage battery. I am biased for offgrid.
>
>
>
>
advice?
William Miller
Miller Solar.com
805-438-5600
www.millersolar.com
On Wed, May 8, 2024 at 8:30 AM jay wrote:
> Hi William,
>
> Since the SOC isn’t being reliable maybe due to not charging correctly?
>
> I would recommend going to volts for the relay driver. Thats why I
operational decisions becomes
problematic when one can’t rely on the accuracy of the SOC value.
William Miller
Miller Solar.com
805-438-5600
www.millersolar.com
On Wed, May 8, 2024 at 7:16 AM jay wrote:
> A possible fix.
>
> You could run a DC relay on the SB PV input that would b
hour or so we reprogrammed the
system for lithium and problem resolved, at least for now.
Hopefully this trick may help one of you some day. If it does, it was
worth my time typing it out.
William
Miller Solar
17395 Oak Road, Atascadero, CA 93422
805-438-5600
www.millersolar.com
CA
panels to create one appropriately sized
discrete array into each CC. You can parallel two strings of panels
without OCPD.
William
Miller Solar
17395 Oak Road, Atascadero, CA 93422
805-438-5600
www.millersolar.com
CA Lic. 773985
*From:* RE-wrenches [mailto:re-wrenches-boun
Should be easy enough to look up on the manufacturer’s website.
William Miller
Miller Solar.com
805-438-5600
www.millersolar.com
On Fri, Apr 26, 2024 at 3:54 PM Jay via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:
> Hi all.
>
> Anyone know what the tare loss and eff
is arc fault even
more important with older PV?
Thanks in advance.
William Miller
Miller Solar.com
805-438-5600
www.millersolar.com
___
List sponsored by Redwood Alliance
Pay optional member dues here: http://re-wrenches.org
List Address: RE-wrenches
If the fan fails would there be an error message? As always, I looked this
up before posting. The manual is not clear on the matter.
William
Miller Solar
17395 Oak Road, Atascadero, CA 93422
805-438-5600
www.millersolar.com
CA Lic. 773985
-Original Message-
From: RE-wrenches
://millersolar.com/MillerSolar/Resources/Voltage_Drop.xls
William Miller
Miller Solar.com
805-438-5600
www.millersolar.com
On Wed, Apr 10, 2024 at 9:41 AM Chris Daum via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:
>
>
> The crazy things folks do. Dear people: We have a
t;
may provide some more info. If you want more details let me know.
William
Miller Solar
17395 Oak Road, Atascadero, CA 93422
805-438-5600
www.millersolar.com
CA Lic. 773985
*From:* RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] *On
Behalf Of *Dan Fink via RE-wrenches
limited.
PV Labels is so darn quick and good and reasonable I could not justify
carrying on with making my own.
William Miller
Miller Solar.com
805-438-5600
www.millersolar.com
On Sat, Mar 30, 2024 at 1:52 PM Christopher Warfel via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:
&
being laid down.
William
Miller Solar
17395 Oak Road, Atascadero, CA 93422
805-438-5600
www.millersolar.com
CA Lic. 773985
*From:* Lloyd Hoffstatter [mailto:ll...@sunstruckconsulting.com]
*Sent:* Thursday, March 28, 2024 11:34 AM
*To:* will...@millersolar.com; RE-wrenches
*Subject
225A in all new
services of 200A rating or less.
Do any of you know what new code this might be?
Thanks in advance for your time.
William
Miller Solar
17395 Oak Road, Atascadero, CA 93422
805-438-5600
www.millersolar.com
CA Lic. 773985
elpful.
Respectfully,
William Miller
Miller Solar
17395 Oak Road, Atascadero, CA 93422
805-438-5600
www.millersolar.com
CA Lic. 773985
*From:* Jason Szumlanski [mailto:ja...@floridasolardesigngroup.com]
*Sent:* Wednesday, March 27, 2024 5:28 PM
*To:* William Miller
*Cc:* Kirk Herander; RE-wr
tience.
Warm regards,
Galen Gennaria
I will update the case study when new developments occur.
William
Miller Solar
17395 Oak Road, Atascadero, CA 93422
805-438-5600
www.millersolar.com
CA Lic. 773985
___
List sponsored by Redwood Allianc
Jason:
Out of respect for everyone’s time on this forum, I try to do some research
before I post. Please post a link to these $35 interlocks for 5 breakers
(4 inverter breakers against 1 bypass breaker). Otherwise we are talking
apples against oranges.
Thank you.
William
Miller
|Principal, VT Solar, LLC*
*Celebrating our 33st Anniversary 1991-2024!!*
dba Vermont Solar Engineering
802.559.1225
On Wed, Mar 27, 2024 at 3:15 PM William Miller via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:
Jason:
Replies below.
Miller Solar
17395 Oak Road, Atas
cussion and specific recommended equipment is
appreciated.
Jason Szumlanski
Principal Solar Designer | Florida Solar Design Group
NABCEP Certified Solar Professional (PVIP)
Florida State Certified Solar Contractor CVC56956
Florida Certified Electrical Contractor EC13013208
On Wed, Mar 27, 2024 at 1
? The inverters
will detect backfeed and shut down. No harm will come of it.)
Hope this helps.
William
Miller Solar
17395 Oak Road, Atascadero, CA 93422
805-438-5600
www.millersolar.com
CA Lic. 773985
*From:* RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] *On
Behalf Of
to borrow the
thing, let me know.
William
Miller Solar
17395 Oak Road, Atascadero, CA 93422
805-438-5600
www.millersolar.com
CA Lic. 773985
___
List sponsored by Redwood Alliance
Pay optional member dues here: http://re-wrenches.org
List
the advice.
William
Miller Solar
17395 Oak Road, Atascadero, CA 93422
805-438-5600
www.millersolar.com
CA Lic. 773985
*From:* Nick A Lucchese [mailto:luccheseso...@me.com]
*Sent:* Wednesday, February 21, 2024 11:46 AM
*To:* will...@millersolar.com; RE-wrenches
*Subject:* Re: [RE
approach might work for you or at least give you something to think
about. Not everyone is willing to take the same risks. Sorry about all of
the words. I could not explain this approach any more concisely.
William
Miller Solar
17395 Oak Road, Atascadero, CA 93422
805-438-5600
alth as any other value. It is easy to obtain data
files for the FNDC in CSV format. (I suspect this is kind of like what is
done internally for the Sunny Island battery health reading.)
Have any of you pondered these questions? I am interested in your thoughts.
TIA.
William
Miller S
https://solarrackworks.com/top-of-pole-racks.html
Jeff Randall has been in the business for years and he is as solid as they
come. He started DPW.
William
Miller Solar
17395 Oak Road, Atascadero, CA 93422
805-438-5600
www.millersolar.com
CA Lic. 773985
-Original Message-
From: RE
ithium.
William
Miller Solar
17395 Oak Road, Atascadero, CA 93422
805-438-5600
www.millersolar.com
CA Lic. 773985
*From:* RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] *On
Behalf Of *Peter Giroux via RE-wrenches
*Sent:* Friday, March 1, 2024 12:53 PM
*To:* 'RE-wrenches&
Todd:
This is about batteries that exist.
William Miller
Miller Solar.com
805-438-5600
www.millersolar.com
On Wed, Feb 28, 2024 at 1:23 PM Todd Cory via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:
> Another option for grid tied with battery based systems, is to use flood
hard to
see just how high (or low) the level is. I am cogitating on a few ideas to
make this easier and more accurate, but in the meantime, what are your
favorite tricks for this?
TIA
William
Miller Solar
17395 Oak Road, Atascadero, CA 93422
805-438-5600
www.millersolar.com
CA Lic
load exceeds
that amount occasionally the inverter supplies the difference. The battery
is sized to sustain the shortfall for the expected duration.
The potential to save $300 a month provides a budget for the project.
William Miller
Miller Solar.com
805-438-5600
www.millersolar.com
On Sun, Feb 25
6 PM Jay via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:
Hi william
Fronius 7.6 kw are in stock.
I’ve installed a number of fronius with no issues.
Jay
On Feb 22, 2024, at 4:56 PM, William Miller via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:
Friends:
, AC load center or any
of the other complexities.
Any advice is appreciated.
William
Miller Solar
17395 Oak Road, Atascadero, CA 93422
805-438-5600
www.millersolar.com
CA Lic. 773985
___
List sponsored by Redwood Alliance
Pay optional member
willing to start the conversation but the call mysteriously dropped a few
minutes in and I could not reconnect…
William
Miller Solar
17395 Oak Road, Atascadero, CA 93422
805-438-5600
www.millersolar.com
CA Lic. 773985
*From:* RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org
years. Some customers stumble onto the solution
but if I look over someone’s shoulder I do not see how to log into an
existing system. Anyone know what I am missing?
Thanks in advance.
William
Miller Solar
17395 Oak Road, Atascadero, CA 93422
805-438-5600
www.millersolar.com
CA Lic
better the operation of systems with easy access to historic data and I
save a butt-load of driving. I wish the Outback and Sunny Island files
could be obtained remotely for better analysis.
William
Miller Solar
17395 Oak Road, Atascadero, CA 93422
805-438-5600
www.millersolar.com
CA Lic
ee the PV bring SOC up to the
level of near 100% where the problem exhibits. As soon as the weather gets
sunnier and the days get longer I will see what happens and report back.
William
Miller Solar
17395 Oak Road, Atascadero, CA 93422
805-438-5600
www.millersolar.com
CA Lic. 773985