Rick:


If I had to guess I’d say you have a PV wiring fault.  The PV positive may
be shorted to ground.
This would make the inverter chassis negative in relation to ground.



The logic I use is to ask what is the likely source of DC at 195 volts?  It
is most likely the PV circuits, wouldn’t you say?



If the DC Fault is not eternal then it must be internal to the inverter.
This could be a dangerous situation.  I would proceed with caution.



Try completely isolating the PV from the inverter as a start.



Good luck.



William Miller



Miller Solar

17395 Oak Road, Atascadero, CA 93422

805-438-5600

www.millersolar.com

CA Lic. 773985





*From:* RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] *On
Behalf Of *rick--- via RE-wrenches
*Sent:* Tuesday, October 15, 2024 11:09 AM
*To:* RE-wrenches
*Cc:* r...@solshineenergy.com
*Subject:* [RE-wrenches] Sol-Ark Gen Input



Back on the Sol-Ark topic again. We have a customer whose 12kW is measuring
-195VDC to ground from L1 and L2 with the Gen breaker open. L1 to L2 = 0V.
I know the Gen input can be configured as an output, but reading a high DC
voltage to ground is concerning. The generator has never been run. System
is operating normally.



Anyone have a Sol-Ark accessible that could verify what they’re reading?



Thanks in advance.



Rick Brown

Solshine Energy

Solar Electric Contracting Services

www.solshineenergy.com

Roanoke, VA

Office: 540.235.3095

Mobile: 540.808.9502

CONFIDENTIALITY NOTICE -- This email is intended only for the person(s)
named in

the message header. Unless otherwise indicated, it contains information
that is

confidential, privileged and/or exempt from disclosure under applicable
law. If you have

received this message in error, please notify the sender of the error and
delete the

message. Thank you.
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to