Stuart:


Thank you for the follow up.  Valuable information.



A generator vendor just today proposed the use of an RDT unit to place
between two generators and the input to an off-grid inverter/charger
system.  The idea is to have an automated means to start a secondary
generator if the primary generator fails to start.



I read the RDT manual and I don’t believe the RDT will do what I describe
above.  The RDT can only automatically transfer if the primary voltage
source becomes de-energized.



I did think of a way to make the RDT work for us because we will connect it
to a Sunny Island system:  We could connect Relay 1 to start generator 1 if
the SOC goes below a certain value, let’s say 30%, hypothetically.  We
could then program Relay 2  in load shed mode (Lod1SocTm1Str) to close at a
lower SOC, let’s say 20%.  This way if the primary generator does not start
at 30% SOC the secondary starts at 20%.   Once the Secondary generator
starts the RDT will transfer.  Does this seem feasible?



By the way, I recall there are upper and lower limits to the values one can
enter into Lod1SocTm1Str and Lod1SocTm1Stp.  Is my memory correct and does
anyone know what those limits are?  That information is not in the manual
that I can find.



Thanks in advance.



William Miller



Miller Solar

17395 Oak Road, Atascadero, CA 93422

805-438-5600

www.millersolar.com

CA Lic. 773985





*From:* RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] *On
Behalf Of *Stuart Kriendler via RE-wrenches
*Sent:* Friday, January 17, 2025 7:29 AM
*To:* Mac Lewis
*Cc:* Stuart Kriendler; RE-wrenches
*Subject:* Re: [RE-wrenches] ATS models to bypass GT hybrid inverters for
maintenance/faults



Many thanks again Mac and Wrenches,



This is now put to bed with confirmation the only listed 200A ATS that will
work without a 12V switching controller that I could find around the $1k
mark is indeed the Kohler RDT series.

(All currently manufactured Generac, Briggs & Stratton and Cummins ATS
options require a controller to talk to the same name brand gene to
switch/transfer, or a Mcgiver move.)



I found a supplier in Florida who gave a slight volume discount and seems
solid.
Here is a link to the product, pricing, specs and manual through them:

https://bnhgenerators.com/product/kohler-200-amp-rdt-ats-rdt-cfnc-0200a-qs7/



And another supplier option with similar pricing, and the 100A version
readily available in case helpful:

https://www.electricgeneratorsdirect.com/Kohler-RDT-CFNC-0200A-QS7/p2202.html



Best to all and thanks again.



Sunniest regards,

Stuart

441 599 2105





On Tue, 14 Jan 2025 at 21:02, Mac Lewis <maclew...@gmail.com> wrote:

Hi Stuart,



The Kohler RDT switch is a much better switch for what you are doing; it is
a power seeking switch with no accessory device communication needed.  It
is more expensive than the RXT switch because it has its own brain board.
A Kohler tech can adjust the delays for you if needed but the defaults are
good.  We have a few of them out there with no issues.    They have them
available as service entrance rated/indoor/outdoor etc.



Good Luck!



On Tue, Jan 14, 2025 at 2:55 PM August Goers via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:

Hi Stuart,



Got it, now I see you're working with the MidNite AIO. This ATS topic came
up not too long ago and I posted that we used to have success with Briggs &
Stratton ATS units back when we were installing SMA Sunny Island systems.
The Briggs unit does not need a control from an external source, it just
switches over automatically (with a few second delay) once utility power is
lost. We never had a single problem with these transfer switches.



You might check them out:
https://www.nationwidegenerators.com/briggs-stratton-071270-200-amp-se-rated-120-240v-1ph-ats/?srsltid=AfmBOorCds2ktOcsHUf3GWmX5ba70K-ynjOcm1iizzIW6X-9OkSVpfHA



I know that Briggs went through a bankruptcy a few years ago, but maybe
they're still alive and kicking now.



August





On Tue, Jan 14, 2025 at 1:29 PM Stuart Kriendler <stuartkriend...@gmail.com>
wrote:

Much appreciated August,



Yes, that fancy Enphase System Controller is a nice piece of kit, overseen
a few of those and it is nice they pass through the grid power if there is
an issue, most of the time.

;-)

I'm in love with the MN AIO, the build quality is impressive and great
value for money, with the CBI breakers and features mentioned earlier etc.
all built in.
Now seen an engineering sample do the business in an rugged off-grid
scenario for a few months and feel confident it will be a great GT hybrid
option, one catch is the need for a 3rd party ATS though.
(Hoping Midnite will make one of their own in time, as well as a wireway to
marry the PowerFlo 16 and AIO, both such nicely built solid equipment).



Hopefully the Kohler RXT or Generac can work to keep the ATS cost below
$1k!



Sunniest regards,

Stuart

441 599 2105





On Tue, 14 Jan 2025 at 16:02, August Goers <aug...@luminalt.com> wrote:

Hi Stuart -



Many grid tied PV/ESS manufacturers (Enphase, SolarEdge, Franklin, Tesla to
name a few) now have a Microgrid Interconnect Device (MID) that essentially
acts as a smart transfer switch thus eliminating the need for a 3rd party
automatic transfer switch. What brands equipment are you looking at?



Best, August



On Tue, Jan 14, 2025 at 11:10 AM Stuart Kriendler via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:

Good day Wrenches,



2025 looks to be the year for installing more grid tied (GT) battery back
up hybrid inverters on new and existing GT PV systems in a whole house
backup scenario

i.e. Utility - Hybrid Inverter - House Loads



With these newer GT hybrids so 'sensitive', any fault on the PV side can
cause them to shut down, thus stopping power to the house.

To minimise this it seems sensible to add an ATS to the system such that
if/when the hybrid faults, the ATS w switch to grid power, bypass the
hybrid, and power the house.

This could save an emergency truck roll or late night phone call for
installers.



Anyone have experience on good value-for-money Listed automatic transfer
switches that would do the job, 200A, 120/240V?



Two name brand options that came up on the less expensive end of the
spectrum are:

- Generac RXSW200A3 (
https://www.generac.com/residential-products/standby-generator-transfer-switches/automatic/rxsw200a3/
)



- *Kohler 200-amp, Service Entrance RXT ATS | RXT-JFNC-200ASEQS4 (*
https://www.kohler.com/content/dam/kohler-com-NA/Lifestyle/PDF/PDF-g11152.pdf
)



However, they each say their ATSs must be used with the corresponding
generator.



I would imagine a simple 'grid sense' functionality would mean that if the
hybrid's output was connected to the Grid/Normal lugs and the grid was
connected to the Gene/Backup lugs in the ATS it should work.

However I don't want to end up with an expensive surprise in a relatively
remote location where I operate!



Would appreciate any feedback with experience with the above or other ATS
models or how people are future proofing for this scenario?
To do future maintenance/torque checks etc. in a GT hybrid whole home
backup situation, it would be nice to bypass the inverter and keep the
house powered for safety and homeowner convenience in general.



Thanks and best.



Sunniest regards,

Stuart

441 599 2105

_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the
other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the
other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org




-- 







Mac Lewis

"Yo solo sé que no sé nada." *-Sócrates*
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to