I also have not been able to confirm that the Wagos are listed for use with DC.

We have been using them on AC circuits for almost a year now. Also not listed 
for moist or wet environments…

 

-Glenn

 

From: RE-wrenches <re-wrenches-boun...@lists.re-wrenches.org> On Behalf Of 
Chris Sparadeo
Sent: Wednesday, April 28, 2021 10:38 AM
To: RE-wrenches <re-wrenches@lists.re-wrenches.org>
Subject: Re: [RE-wrenches] MC4s are listed for THWN, right?

 

Keep in mind that Wagos, Polaris lugs, Multi-tap Burndy lugs are rated for 
600V. I can see this being a possible use for MC4 connectors in a higher 
voltage splice scenario, because of their 1000V/1500V ratings. 

 

On Wed, Apr 28, 2021 at 10:00 AM August Goers <aug...@luminalt.com 
<mailto:aug...@luminalt.com> > wrote:

Hi Allan - Good question, I noticed that too. I think it is a typo, and they 
mean 20 AWG through 10 AWG. See attached datasheet.  6 mm^2 is close to #9-#10 
AWG. There are other variants available as well with smaller conductor sizes 
for data cables and more ports for connecting in parallel.

 

August 

 

On Tue, Apr 27, 2021 at 6:10 PM Sindelar Solar <al...@sindelarsolar.com 
<mailto:al...@sindelarsolar.com> > wrote:

August,

Thank you for this suggestion. I went to the site, and under "Two Sizes for All 
Conductor Types" on that page it appears that there's a model that'll work with 
2-10AWG conductors:

"With the 6 mm2 (10 AWG) variant, you can connect all conductor types – with 
cross sections from 0.5 to 6 mm2 (2−10 AWG)".

This would contradict what you wrote below, so I'm just checking whether I 
missed something. 

Thanks, Allan

On 4/27/2021 12:55 PM, August Goers wrote:

Hi Jason - I noticed that Tesla is using the Wago connectors in their 
Powerwalls. They only go up to #10, but they certainly appear to have some 
advantages such as easy QC inspection, compactness, and price. We are in the 
process of trying a batch of these out, but I hadn't considered using them in 
exterior J-boxes. 

https://www.wago.com/global/electrical-interconnections/discover-installation-terminal-blocks-and-connectors/221

August 

 

On Tue, Apr 27, 2021 at 10:42 AM Jason Szumlanski 
<ja...@floridasolardesigngroup.com <mailto:ja...@floridasolardesigngroup.com> > 
wrote:

I'd be interested to hear thoughts on Wago 221-6XX series connectors, 
specifically for THWN to Enphase IQ/DG/TC conductor transitions or just THWN 
splices. 

 

On Mon, Apr 26, 2021, 8:40 PM Blake Gleason <bl...@sunlightandpower.com 
<mailto:bl...@sunlightandpower.com> > wrote:

Corey, 

Thank you!  Agreed, the message from Staubli's Eng dept is much less confusing 
(with the exception of the statement about THHN tending to be solid vs 
stranded).

All -

What are you folks using to transition from PV Wire to THHN/THWN-2 inside a 
junction box?  We used to use split bolts, which make an awesome electrical 
connection, but are time-consuming and not easily serviceable.  Wire nuts (the 
right ones) are Listed, but never felt reliable for that purpose.  Same for 
WAGO levers.  I hear about people using Buchanan splice caps, but I wonder 
about trading one set of crimping problems for another.  And of course, the 
only problem with using THHN in an MC4 is that the compression gland may not be 
as watertight as it is with PVWire, and the Buchanans certainly are not 
watertight.  Terminal blocks generally aren't listed, definitely aren't 
watertight, and raise inspectors' eyebrows.  Why is this so hard for me??

Best,

Blake

Thanks

 

On Mon, Apr 26, 2021 at 5:19 PM Corey Shalanski <coreso...@gmail.com 
<mailto:coreso...@gmail.com> > wrote:

Blake,

In addition to Bryan's notes, here is some unconfusing information directly 
from Stäubli's engineering dept:

The answer is categorically no: you cannot use THHN wires with MC4 connectors.  
There are several reasons for this:
1.     Certification: our MC4 connectors are certified to UL6703, which only 
covers UL4703 PV wire or USE2 cable.  Any other wire type is not covered by our 
certification
2.     Internal validation: we have no internal testing or validation of how 
MC4 or Evo2 connectors perform with THHN cables.  We therefore cannot warranty 
/ accept the use of THHN cables with our PV connectors.  The allowable cables 
and applications for our PV connectors is clearly stated in the assembly 
instructions.
3.     Construction: THHN cables use very rigid PVC insulators, which behave 
very differently than XPLE or TPE insulators that are the most widely used on 
PV wires.  PVC has a very low elastic range and easily deforms permanently 
under load/thermal cycling.  It is not a well-suited cable for higher 
temperature or high temperature fluctuating applications where compression-type 
cable seals (i.e. cable glands) are used.  Also, THHN cables tend to be 
single-conductor solid core cables, which are absolutely not allowed with crimp 
terminations like the MC4 (or any other PV connector on the market for that 
matter).  They also are not allowed by UL6703.   

These comments were forwarded to me by Jeff Wang, who works for Stäubli North 
America.

--

Corey Shalanski

Jah Light Solar

Portland, Jamaica

 

On Mon, Apr 26, 2021 at 9:23 AM <bl...@sunlightandpower.com 
<mailto:bl...@sunlightandpower.com> > wrote:

 

Bryan, 

Thank you for the link.  I am confused by the "PVC" section you referenced.  
Here's the complete text:

  For safety reasons Stäubli prohibits the use of PVC cables. Cables made from 
PVC can be connected to MC4-Evo 2 since the insulation material of the 
connector (Polyamide) is suitable to be connected to PVC. PVC cables usually 
have an upper limiting temperature of 70 °C, in fixed installations sometimes 
80 °C.  

THHN/THWN-2 is made with PVC insulation, so I assume that it falls under the 
category of a "PVC cable."

So, the first sentence seems to say that it's not allowed by Staubli.  But then 
the second sentence seems to say that is IS allowed.  And then the third 
sentence doesn't seem to be contemplating the most common PVC wire type of all 
(in the US), which is THHN/THWN-2, which has a 90 degree rating?!

Can you help un-confuse me?

Thank you!

Blake

List sponsored by Redwood Alliance
 
Pay optional member dues here: http://re-wrenches.org
 
List Address: RE-wrenches@lists.re-wrenches.org 
<mailto:RE-wrenches@lists.re-wrenches.org> 
 
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm
 
Check out or update participant bios:
http://www.members.re-wrenches.org

-- 

Allan Sindelar
al...@sindelarsolar.com <mailto:al...@sindelarsolar.com> 
NABCEP Certified PV Installation Professional
New Mexico EE98J Journeyman Electrician
Founder (Retired), Positive Energy, Inc.
505 780-2738 cell

 

_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org 
<mailto:RE-wrenches@lists.re-wrenches.org> 

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org 
<mailto:RE-wrenches@lists.re-wrenches.org> 

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

-- 

Chris Sparadeo

 

 

C_802-369-4458

H_802-728-3059

_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other: