Chris's reminder is a good oneā€”the 600V rating of most insulated
"multi-tap" connectors pretty much limits their use to residential systems.
I would also keep in mind that those connectors generally have a torque
spec. I've definitely seen examples of meltdowns caused by poor
terminations - either the compression screw isn't torqued properly or the
conductor isn't fully inserted. To help eliminate the latter case, we used
to favor the Burndy models (e.g., BIT4
<https://www.hubbell.com/burndy/en/Products/Power-Utilities/Connectors/Lugs-Terminals/Bolted/Vinyl-Insulated/BIT4/p/2021315>)
because they had a transparent case; I see that Polaris also now offers
transparent models (e.g., IT-4C
<http://www.nsiindustries.com/catalog/nsiproducts/polaris-mechanical-connectors/polaris-vision-tap/it-4c>
).

--
Corey Shalanski
Jah Light Solar
Portland, Jamaica


On Wed, Apr 28, 2021 at 7:38 AM Chris Sparadeo <sparadeo.ch...@gmail.com
> wrote:

> Keep in mind that Wagos, Polaris lugs, Multi-tap Burndy lugs are rated for
> 600V. I can see this being a possible use for MC4 connectors in a higher
> voltage splice scenario, because of their 1000V/1500V ratings.
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to