Friends:


The information from the manufacturer seems entirely untrustworthy for
these reasons:



1.   The representative is mis-informed about the prevalence of stranding
of THHN.

2.   It is my understanding the all THHN on the market is now THWN so this
designation should be used (I am ready to be corrected on this point as my
information is anecdotal).

3.   The representative focuses on the sealing of the gland portion of the
cable on the THWN insulation which ignores the existence of bulkhead mount
MC connectors (I think the nomenclature in the manufacturer’s brochure is
“receptacle”).  If you are using a bulkhead connector the gland does not
exist and any discussion of said gland is therefore irrelevant.



When I observe the conductor in a 10 AWG building wire and the conductor in
a 10 AWG PV wire I detect absolutely no difference.  I firmly believe that
you can wire-nut PV wire to building wire in a weatherproof junction box.
Gland connectors (by Heyco and others) are readily available so one can run
PV wire in a box, strip and connect.  Keep in mind weatherproof boxes are
hard to hermetically seal so a weep hole in a low point keeps them from
filling with rain water or condensate.  Weep holes are specifically allowed
in the NEC.



I detect no difference when observing an MC pin crimped on both PV wire or
THWN.  See this link
<https://millersolar.com/MillerSolar/practices/PV_wiring/PV_Cable_wiring/_PV_Cable_Wiring.html>
for an example of how we recommend transitioning from PV cable to building
wire.



William



Miller Solar

17395 Oak Road, Atascadero, CA 93422

805-438-5600

www.millersolar.com

CA Lic. 773985





*From:* RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] *On
Behalf Of *Blake Gleason
*Sent:* Monday, April 26, 2021 5:41 PM
*To:* RE-wrenches
*Subject:* Re: [RE-wrenches] MC4s are listed for THWN, right?



Corey,



Thank you!  Agreed, the message from Staubli's Eng dept is much less
confusing (with the exception of the statement about THHN tending to be
solid vs stranded).



All -

What are you folks using to transition from PV Wire to THHN/THWN-2 inside a
junction box?  We used to use split bolts, which make an awesome electrical
connection, but are time-consuming and not easily serviceable.  Wire nuts
(the right ones) are Listed, but never felt reliable for that purpose.
Same for WAGO levers.  I hear about people using Buchanan splice caps, but
I wonder about trading one set of crimping problems for another.  And of
course, the only problem with using THHN in an MC4 is that the compression
gland may not be as watertight as it is with PVWire, and the Buchanans
certainly are not watertight.  Terminal blocks generally aren't listed,
definitely aren't watertight, and raise inspectors' eyebrows.  Why is this
so hard for me??



Best,

Blake

Thanks



On Mon, Apr 26, 2021 at 5:19 PM Corey Shalanski <coreso...@gmail.com> wrote:

Blake,



In addition to Bryan's notes, here is some unconfusing information directly
from Stäubli's engineering dept:



The answer is categorically no: *you cannot use THHN wires with MC4
connectors.*  There are several reasons for this:
1.     *Certification*: our MC4 connectors are certified to UL6703, which
only covers UL4703 PV wire or USE2 cable.  Any other wire type is not
covered by our certification
2.     *Internal validation*: we have no internal testing or validation of
how MC4 or Evo2 connectors perform with THHN cables.  We therefore cannot
warranty / accept the use of THHN cables with our PV connectors.  The
allowable cables and applications for our PV connectors is clearly stated
in the assembly instructions.
3.     *Construction*: THHN cables use very rigid PVC insulators, which
behave very differently than XPLE or TPE insulators that are the most
widely used on PV wires.  PVC has a very low elastic range and easily
deforms permanently under load/thermal cycling.  It is not a well-suited
cable for higher temperature or high temperature fluctuating applications
where compression-type cable seals (i.e. cable glands) are used.  Also,
THHN cables tend to be single-conductor solid core cables, which are
absolutely not allowed with crimp terminations like the MC4 (or any other
PV connector on the market for that matter).  They also are not allowed by
UL6703.



These comments were forwarded to me by Jeff Wang, who works for Stäubli
North America.



--

Corey Shalanski

Jah Light Solar

Portland, Jamaica





On Mon, Apr 26, 2021 at 9:23 AM <bl...@sunlightandpower.com> wrote:



Bryan,



Thank you for the link.  I am confused by the "PVC" section you
referenced.  Here's the complete text:



  For safety reasons Stäubli prohibits the use of PVC cables. Cables made
from PVC can be connected to MC4-Evo 2 since the insulation material of the
connector (Polyamide) is suitable to be connected to PVC. PVC cables
usually have an upper limiting temperature of 70 °C, in fixed installations
sometimes 80 °C.



THHN/THWN-2 is made with PVC insulation, so I assume that it falls under
the category of a "PVC cable."



So, the first sentence seems to say that it's not allowed by Staubli.  But
then the second sentence seems to say that is IS allowed.  And then the
third sentence doesn't seem to be contemplating the most common PVC wire
type of all (in the US), which is THHN/THWN-2, which has a 90 degree
rating?!



Can you help un-confuse me?



Thank you!

Blake

_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the
other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org




-- 




*Blake Gleason, PE | Employee Owner*Director of Innovation and Technical
Excellence
O: 510-845-2997 x128
C: 510-867-5878

1035 Folger Ave.
Berkeley, CA 94710
www.sunlightandpower.com
License #326203

<https://bcorporation.net/>    <https://www.amicussolar.com/>
<https://calssa.org/>
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to