Enphase DOMINATES the space. I can't see any reason to go another
direction. Reliability and service just continues to improve.
If you are looking to save a few bucks, I think you will get what you pay
for. There isn't enough potential savings in a smaller brand to make it
worthwhile.
Jason Szuml
That's correct you only need one load controller to commission a sunlight
only backup system.
Strangely enough, I am sitting in the driveway of a sunlight only backup
system owner right now. I found a melted 60A solar breaker in the System
Controller (not my installation, contractor is on the run)
For you SolarEdge pros...
I have a new client with dual 7.6kW Home Hub inverters and single SolarEdge
battery. They have been replacing inverters left and right under warranty,
but now have at least one working with the help of a local electrician
friend. I helped them swap it in the monitoring po
I will blast through the certification training before Thursday and let you
know what I find. Thanks for the tips on SetApp.
Jason Szumlanski
Principal Solar Designer | Florida Solar Design Group
NABCEP Certified Solar Professional (PVIP)
Florida State Certified Solar Contractor CVC56956
Florida C
I hate to be the bearer of bad news, but this is also the case with IQ8
microinverters. The batteries must be able to sustain the load for up to 6
minutes to allow the microinverters to attempt to charge the battery. If
you have loads that exceed the battery output capacity, it could cause the
micr
That may be the case, but if the load exceeds the total battery plus
microinverter output at the time, the microgrid will still fail. Early in
the morning, having IQ8s won't make much difference versus IQ7s. It might
help at high irradiance levels.
Rather than load control, another strategy might
I don’t want to stray too far off track, but it’s worth discussing how
challenging it is to predict which manufacturers will be around in a few
years.
I know this might be a touchy subject, but Enphase is beginning to offer
full off-grid support. While I’m fully aware of the drawbacks of their
sys
t you were talking about! : )
>
> On Sat, Nov 9, 2024 at 7:16 AM Jason Szumlanski via RE-wrenches <
> re-wrenches@lists.re-wrenches.org> wrote:
>
>> I wrote in another thread about an off-grid quad Sol-Ark system that was
>> shutting down due to parallel stop when one of th
:
> Jason,
> Everything points to a internal issue maybe with a CT, ribbon connection
> or just a bad board, regardless a new inverter is the key and solark should
> really want to investigate the issue themselves anyway.
> Fun times
>
> On Sat, Nov 9, 2024, 7:16 AM Jason Szumlanski
Hi all,
This is just a PSA in case it helps someone in the future. I was under the
impression that the AC Input LED on the Sol-Ark inverters meant that there
is "good" AC detected by the inverter on the grid terminals and after some
period of delay, something should start happening based on how th
I wrote in another thread about an off-grid quad Sol-Ark system that was
shutting down due to parallel stop when one of the four inverters
experienced a DC PV fault, and how that shutdown is far from ideal. The
same system is down once again, this time due to an AC fault code.
The homeowner starte
I'm pretty sure it was mentioned in another thread that similar faults would not cause Midnite AIO paralleled inverters to fault out. I'm not familiar with their protocol used for paralleling, but if it is true, that would be far superior.At a minimum, I would think Sol-Ark inverters with CANBus co
issues
>>> yet with any gen 3 modules but the internet thing really struck a nerve as
>>> they only just recently got their internet monitoring functional.. having
>>> to go back to every site is a serious pain just to ensure what should be a
>>> basic warranty. Best of
Just a follow-up to this saga... After many many more hours of diagnostics
with tech support, often repeated on subsequent calls, I finally had to get
irritated enough to demand that they just swap out the inverter. On three
different calls they made me take the inverter out of parallel mode and ru
that wasn't
> present in the original..
>
>
>
>
> On Sat, Nov 9, 2024, 7:16 AM Jason Szumlanski via RE-wrenches <
> re-wrenches@lists.re-wrenches.org> wrote:
>
>> I wrote in another thread about an off-grid quad Sol-Ark system that was
>> shutting down
This is probably going to be largely state specific since insurance
companies are regulated by state. We use Builder's Insurance Company (I
think also known as American Builders Insurance) and we are happy with
them. The cost is always too much with insurance in my experience, but they
handled our
We get the same calls and decline to get involved. We just tell people that
consumer-grade products purchased online are geared toward the DIY market,
not professional solar installers. I am not putting my reputation on the
line for these brands.
The other call we get frequently now is about EG4 p
If it's an Enphase-based SunPower system, Enphase has a program to
transition owners to their Enlighten portal. The customer pays Enphase
directly and their field service techs will install a Gateway and get it
programmed to work with the SunPower branded microinverters. I do not
believe this retai
I haven't seen these short leads on a module yet. I would not buy these
modules due to MLPE needs. They might be viable with Tesla's MCI RSD
solution, but I can't see making up custom cables for each panel of even
each row of a ground rack. These must be for a specific segment of the
market.
Thank
hard to have all of the tools, dongles, apps
>> etc that we need on a service call these days!
>>
>> On Fri, Feb 14, 2025 at 7:01 AM Kirk Herander via RE-wrenches <
>> re-wrenches@lists.re-wrenches.org> wrote:
>>
>>> Jason,
>>>
>>> Th
y one issue with them and
>>>> it was firmware related. Unfortunately their firmware upgrade process is a
>>>> total kludge so much so that like Jason, I just let them take over my
>>>> laptop and let them handle it. It really made me appreciate Discover'
ke the limit to Midnite PowerFlo is 257kwh. (16.076kwh/unit*16units in parallel). Best,Amos
Amos Post Integrity Energy W 802.763.7023 C 802.291.2188 ienergyVT.com Facebook
On Feb 12, 2025, at 5:22 PM, Jason Szumlanski via RE-wrenches <re-wrenc...@lists.re-wrenches.org>
Hi Wrenches,
I am regretting some HomeGrid Stack'd off-grid installations right now.
There is a major flaw in the way these function in an error state. For
those of you that don't know, these 48V batteries are stacked with a single
BMS on top, covering up to 8 batteries below. Each battery module
might be able to help with.
> Tyrone Houck
> Oregon Solarworks LLC
> CCB #204937 LRT #076
> 541-787-1366
> tyr...@oregonsolarworks.com
>
>
>
> On Tue, Feb 11, 2025, 3:36 PM Jason Szumlanski via RE-wrenches <
> re-wrenches@lists.re-wrenches.org> wrote:
>
>&g
Zero sell is a bit of an ambiguous term, at least as far as inverter
manufacturers are concerned. For example, Enphase offers a "no export" grid
profile for it's microinverters, but it relies on consumption CTs that are
not completely accurate and the speed at which it can curtail solar will
inevit
Hi all,
Is anyone willing to share with me a picture or two of the Powerflo5 in a
stack configuration? I'm curious about best practices for battery cable
routing to busbars.
Regarding the Powerflo16, the manual says it must be wall/floor mounted
with some of the weight supported by the floor, and
I'm looking for a suggestion for a good all-around charger for service
purposes. I would consider a 240V or 120V option. The purpose is primarily
to charge 5kWh lithium batteries.
I would probably just pick up an EG4 Chargeverter, but it is back-ordered.
Something more portable would be nice.
Ja
ies are going to drop
> coverage? Has that actually happened? Once again, don't over think it,
> respond my friends to actual problems, not ones we dream up in our late
> night fevers.
>
> We are the installers of the solution, we are not the problem.
>
> Ray Walters
>
ing fine in our
> installs. It has only been a year or so, so the jury is still out. But all the
> same features I described above apply.
>
>
> Aloha,
>
>
> Lou Russo
> Owner
> l...@spreesolarsystems.com [l...@spreesolarsystems.com]
> Office - 808 345 6762
> Spree
ere's the Midnite AIO and
>> Powerlo16s. I've done several GTBB systems and like that combo for that
>> application. Bill's post reminded me of the Rosie/Barcelona. I'm wondering
>> what the pro's and cons are between the AIO and R/B for off-grid. Not many
>&g
e calls wanting to understand how we misled them into Enphase.
>> I guess Enphase managed to stay in business though
>>
>> Matt
>>
>> Sent via the Samsung Galaxy S22 Ultra 5G, an AT&T 5G smartphone
>> Get Outlook for Android <https://aka.ms/AAb9ysg>
When I fill out the online form to transfer an existing SolarEdge system to
my company for monitoring, the site now takes me to a payment form
demanding $99 to transfer the site monitoring.
I have been told that as of 2/17/2025, SolarEdge has a new policy, and now
changes for transferring a site t
isn't a promising prospect..
>
> Tyrone Houck
> Oregon Solarworks LLC
> CCB #204937 LRT #076
> 541-787-1366
> tyr...@oregonsolarworks.com
>
>
>
> On Wed, Feb 19, 2025, 3:20 PM Jason Szumlanski via RE-wrenches <
> re-wrenches@lists.re-wrenches.org> wrot
eir top clamps.
>
> August
>
> On Fri, Feb 21, 2025 at 6:11 AM Jason Szumlanski via RE-wrenches <
> re-wrenches@lists.re-wrenches.org> wrote:
>
>> I was contacted by a homeowner with a bunch of spr-x21-350-blk-d-ac that
>> were removed for roof replacement right a
I was contacted by a homeowner with a bunch of spr-x21-350-blk-d-ac that
were removed for roof replacement right around the time that SunPower went
bankrupt. All the cabling is missing, and I'm not sure if the monitoring
system is even viable anymore.
Any suggestions for how to handle this? I thin
ese mods up with non-SunPower
>> racking such as IronRidge and their top clamps.
>>
>> August
>>
>> On Fri, Feb 21, 2025 at 6:11 AM Jason Szumlanski via RE-wrenches <
>> re-wrenches@lists.re-wrenches.org> wrote:
>>
>>> I was contacted by a
> Feel free to check the math with a Schneider XW with 3 VH MPPT
> controllers, a gateway, a SCP, and lithium batteries running closed loop.
> Oh, the Schinder does not have any smart loads like most AIO do.
>
> My 2 cents.
>
> Logan
>
>
>
> On Sat, Feb 22, 2025 at
I have been thinking a lot recently about the reasons off-grid systems can
shut down, and working on strategies to prevent these nuisances that
require manual intervention.
Ideally, a BMS should never shut down due to low voltage/SOC because a
properly programmed inverter should reach it's cut off
t, and
> the current interrupter on the individual cell will open up and drop that
> string, and you will lose capacity.
>
> Like everything else, it's a race to the bottom on cost; this affects
> quality and features... Everyone wants the "Bells & Whistles," but they
&g
Dana,
This is appreciated information. Right now, I have a Wi-Fi extender connected to
a Starlink because the Sol-Ark would not connect to Starlink. So I have the
Sol-Ark going through the extender's 2.4Ghz network. I would like to eliminate
the Wi-Fi extender because it's just one more thing to
I can confirm the part about needing a Kohler dealer to get into some
functions. I recently removed a transfer switch for a Kohler and converted
it to a two-wire start (which was dead easy), but I could not get it to
stop throwing an error stating that the transfer switch was not found. It
did not
p.
> Oh, the Schinder does not have any smart loads like most AIO do.
>
> My 2 cents.
>
> Logan
>
>
>
> On Sat, Feb 22, 2025 at 12:03 PM Jason Szumlanski via RE-wrenches <
> re-wrenches@lists.re-wrenches.org> wrote:
>
>> The voltage cliff is a real issue. Ev
Around here, AHJs require that the GEC is not connected to the service
disconnect or any supply-side interconnected PV AC disconnect. They require
a GEC from the meter socket enclosure to the GE system with a N-G bond in
the meter enclosure (the N and G lugs are one and the same typically anyway
in
This is a PSA for Enphase installers. There is a known issue with new
systems that have a mix of two firmwares out of the box. The last few
systems we have installed had microinverters from different batches with
the below two firmwares. It causes all of the r06 microinverters to
intermittently sto
I guess Enphase managed to stay in business though
>
> Matt
>
> Sent via the Samsung Galaxy S22 Ultra 5G, an AT&T 5G smartphone
> Get Outlook for Android <https://aka.ms/AAb9ysg>
> --
> *From:* RE-wrenches on behalf
> of Jason Sz
I just wrote a scathing blog post, notified my staff not to take on new
SolarEdge service clients, and blasted out messages and DMs on social media
about this despicable new move by SolarEdge. Imagine being one of the many
system owners impacted by solar contractors going out of business, only to
f
Does anyone have a reasonably priced source for 600V cable to run through
wiring troughs to parallel inverters?
Thanks,
Jason Szumlanski
Principal Solar Designer
Florida Solar Design Group
___
List sponsored by Redwood Alliance
Pay optional member dues
uple gateways and
> you’re in business….
>
>
>
> Matt
>
>
>
>
>
>
>
> *From:* RE-wrenches *On
> Behalf Of *Jason Szumlanski via RE-wrenches
> *Sent:* Tuesday, February 18, 2025 5:05 PM
> *To:* RE-wrenches
> *Cc:* Jason Szumlanski
> *Subject:* Re: [RE-w
bout the Elevators
>
> On Tue, Feb 18, 2025, 2:24 PM Jason Szumlanski via RE-wrenches <
> re-wrenches@lists.re-wrenches.org> wrote:
>
>> Yes, but the PV system would need to be split, and inevitably, the
>> balance of PV and battery assigned to each distribution pa
> <http://members.sti.net/offgridsolar/>
> e-mail offgridso...@sti.net
> text 209 813 0060*
>
>
> On 2025-02-18 8:05 am, Jason Szumlanski via RE-wrenches wrote:
>
> There are many 4,000 sq ft pool homes in my area with electric pool
> heating and electric everything
There are many 4,000 sq ft pool homes in my area with electric pool heating
and electric everything else where 25kW would just cover the electric bill.
Some larger homes around here can definitely require more. Florida Power &
Light allows up to 50kW on 120/240V split phase service, but only if
exp
ir power system. No Bueno for sure! Stay Safe !
>
>
>
> *Dave Angelini Offgrid Solar
> "we go where powerlines don't"
><http://members.sti.net/offgridsolar/>https://offgridsolar1.com/
> <https://offgridsolar1.com/> <http://members.sti.net/offgridsolar/
land, 22 systems starting
>> with M250's. Average project is 16 modules. I have had only one
>> microinverter failure, and it emailed me to let me know and then ordered
>> the replacement. The experiences do seem installer specific. Chris
>> On 2/19/2025 9:29 PM, Jas
t;
>
>
>Amos Post
>Integrity Energy
> W 802.763.7023
>C 802.291.2188
> ienergyVT.com <http://www.ienergyvt.com>
> Facebook <https://www.facebook.com/integrityenergyllp?ref=hl>
>
> On Mar 2, 2025, at 4:58 PM, Jason Szumlanski via
I had a person contact me years ago who said her solar installer put a
system up that caused popping noises everyday on her roof. It was a shingle
roof, older home, and ultimately we chalked it up to expansion and
contraction. Everything was secure and there were no indications of
structural, cosme
hind a cloud. With vinyl siding or
> metal roofs, I'll sometimes hear the expansion and contraction but it has
> to be a very quick change in temperature and I only hear it on those quick
> transitions from sun to clouds.
>
> Good luck tracking it down!
> Cheers,
> Dave
>
201 - 256 of 256 matches