[RE-wrenches] SMA Rapid Shutdown and Secure Power Supply

2022-04-27 Thread Dave Tedeyan via RE-wrenches
Hi All, The last SMA-41 inverter I commissioned, had the option for SunSpec rapid shutdown with Secure Power Supply. I just talked to a level one tech who was not particularly familiar, but told me that with a sunspec rapid shutdown device like the JMS-F, you can still use the Secure Power Supply

[RE-wrenches] wire management on Qcell AC module

2022-06-02 Thread Dave Tedeyan via RE-wrenches
Hi All, I just got some of the Qcell 360w AC modules that have the Enphase microinverter factory applied to the back. The module is the half cut cell type with the DC leads coming from either side of the middle of the module. The modules come with the wires taped to the back of the module. If you

Re: [RE-wrenches] wire management on Qcell AC module

2022-06-02 Thread Dave Tedeyan via RE-wrenches
they would not sag enough to touch the roof, or is the tape the only thing > preventing the leads from touching the roof? > > Jason Szumlanski > Florida Solar Design Group > > > > > On Thu, Jun 2, 2022 at 9:37 AM Dave Tedeyan via RE-wrenches < > re-wrenches@list

Re: [RE-wrenches] wire management on Qcell AC module

2022-06-02 Thread Dave Tedeyan via RE-wrenches
nspector > > On Thu, Jun 2, 2022 at 6:37 AM Dave Tedeyan via RE-wrenches < > re-wrenches@lists.re-wrenches.org> wrote: > >> Hi All, >> >> I just got some of the Qcell 360w AC modules that have the Enphase >> microinverter factory applied to the back. The modu

Re: [RE-wrenches] wire management on Qcell AC module

2022-06-30 Thread Dave Tedeyan via RE-wrenches
them > statically remain in location without the tape, the loop will prevent > drooping and if properly located rest on the rail. > Jerry > > On Wed, Jun 29, 2022 at 1:07 PM Dave Tedeyan via RE-wrenches < > re-wrenches@lists.re-wrenches.org> wrote: > >> Hi all, >>

[RE-wrenches] Enphase production CT with Sunpower PVS5

2022-07-01 Thread Dave Tedeyan via RE-wrenches
Hi All, I am expanding on an existing Sunpower system, with non Sunpower equipment (SMA inverters). In order to get their consumption monitoring to work properly, I would like to install a production CT for the PVS5. Does anyone know whether you can use an Enphase production CT with a Sunpower PVS5

[RE-wrenches] EG4

2022-07-28 Thread Dave Tedeyan via RE-wrenches
Hi all, Does anyone have any experience with EG4 products? I am doing an off-grid consultation for someone who plans on getting EG4 inverter and lithium batteries. The equipment seems so cheap, yet appears to be somewhat legit. They do at least have UL1741 listing. But their 6500w inverter/charger

[RE-wrenches] Vent fan for Conext MPPT 80-600

2022-09-30 Thread Dave Tedeyan via RE-wrenches
Hi All, I need to get some replacement vent fans for a Schneider CC. Tech support gave me the replacement part number as Sunon pf80251b1--a99. Looking around online, I cannot find anything with that exact part number, but I have found a bunch that is off by one digit - Sunon pf80251b1-000*U*

[RE-wrenches] AC coupled grid tie only inverter

2022-10-07 Thread Dave Tedeyan via RE-wrenches
Hi All, I've got someone who wants to tie their off-grid system with a Magnum inverter (which I think is a 4024 PAE inverter) to the grid. Since the Magnum inverter cannot be grid tied, I was wondering if there is some kind of simple grid tie inverter that can be the grid interface, while keeping

Re: [RE-wrenches] AC coupled grid tie only inverter

2022-10-07 Thread Dave Tedeyan via RE-wrenches
stallation Professional > --- > > > > On 2022-10-07 11:42, Dave Tedeyan via RE-wrenches wrote: > > Hi All, > > I've got someone who wants to tie their off-grid system with a Magnum > inverter (which I think is a 4024 PAE inverter) to the grid. Since the > Magnu

[RE-wrenches] Locus to Vision meter swap

2022-11-09 Thread Dave Tedeyan via RE-wrenches
Hi All, I have a service request to replace a Locus LGate120 with a Vision CatM1 meter. I have never used the Vision meters, and have not used an LGate120 in many years. Does anyone know if this will be a 1 to 1 swap? As in, is the meter specific to the meter enclosure, or can I just pull out the

Re: [RE-wrenches] SMA inverterters with SPS

2022-12-12 Thread Dave Tedeyan via RE-wrenches
I have heard from my distributor that SMA is in the process of ending the -41 line and will be coming out with a new line of inverter that is UL1741-SB certified. I've been told SMA says Q2 next year is when the new line will be available, but my vendor says that it always slips. This is a bummer f

[RE-wrenches] Enphase consumption data

2022-12-20 Thread Dave Tedeyan via RE-wrenches
Hi All, I have a system where the solar panels (with Enphase IQ8) are on a detached garage and the IQ gateway is in the house. The gateway is in the house so that it can gather consumption data, and there is an internet connection there. There are other loads in the garage, so it is impossible to

Re: [RE-wrenches] SMA SB-41 without WLAN

2023-01-19 Thread Dave Tedeyan via RE-wrenches
Hi Jeremy, I've seen that whitepaper from SMA about using the USB to power a Vonets wifi adapter. It does not work well at all. I tried this and it worked great for about a week. Then one of the two inverters stopped being able to power the Vonets at all, and the other Vonets device could not stay

[RE-wrenches] Voltage Rise

2023-02-23 Thread Dave Tedeyan via RE-wrenches
Hi All, I've got a customer who is having issues with high voltage at their house. This first became an issue after installing 23.1kw of AC solar output. They have some GREE heat pumps which have been having some failures. The heat pump people are saying that the problem is that the voltage is abo

Re: [RE-wrenches] Voltage Rise

2023-02-23 Thread Dave Tedeyan via RE-wrenches
ch if there is a drop and how much. Now turn off everything and > power up the solar again watch the voltage at the meter if it climbs up and > close to limit it might be the feeders. It's all process of elimination. > Lots of fun > > > On Thu, Feb 23, 2023, 9:03 AM Dave Tede

Re: [RE-wrenches] Voltage Rise

2023-03-09 Thread Dave Tedeyan via RE-wrenches
> close to limit it might be the feeders. It's all process of elimination. >> Lots of fun >> >> >> On Thu, Feb 23, 2023, 9:03 AM Dave Tedeyan via RE-wrenches < >> re-wrenches@lists.re-wrenches.org> wrote: >> >>> Hi All, >>> >>&

Re: [RE-wrenches] Attaching Array To or Through Ply

2023-03-29 Thread Dave Tedeyan via RE-wrenches
Hi Matt, I've used these in the past when on a comp roof and there was no good way to get into the rafters (or TJI's in this case) https://sunmodo.com/nanomount/ You might want to replace the screws with something shorter and beefier though to get more grip if you are only going into 1/2" plywood.

Re: [RE-wrenches] Retail price lists

2023-05-18 Thread Dave Tedeyan via RE-wrenches
If a customer wants to use some of their own parts, I'll need to add some amount of hours for managing them and their purchase list, and make it clear in the contract that issues arising from incomplete or incorrect parts is on them. Or you can do what I saw at my mechanic shop the other day: Labor

Re: [RE-wrenches] Bonding Metal Roofs Part II

2023-06-08 Thread Dave Tedeyan via RE-wrenches
Also being in NYS, I have been familiar with this requirement for a long time. I believe the idea is that just like how any metal part in a system needs to be grounded, metal roof panels under solar panels are kind of part of the system. What if a wire comes loose and touches the roof? You would no

Re: [RE-wrenches] Bonding Metal Roofs Part II

2023-06-14 Thread Dave Tedeyan via RE-wrenches
nomous Energies | Owner/Operator > www.AutonomousEnergies.com <http://www.autonomousenergies.com> > (518) 567-1468 > > > > > On Thu, Jun 8, 2023 at 2:33 PM Dave Tedeyan via RE-wrenches < > re-wrenches@lists.re-wrenches.org> wrote: > >> Also being in NYS, I have

Re: [RE-wrenches] AFCI tripping on SB 4000US-12

2023-06-19 Thread Dave Tedeyan via RE-wrenches
William, If you swap strings, does the fault stay with the string, or with the input? and if you do run without the string for a while can you determine that the arc faults stop? Just figure it is worth making 100% sure the fault is actually in the DC side of that one string you have isolated, and

[RE-wrenches] AC coupling with Solar Edge, pre HD Wave

2023-06-30 Thread Dave Tedeyan via RE-wrenches
Hi all, Does anyone know if you can make the SolarEdge inverters (the A series, before the HD wave inverters) respond to frequency control? I cannot find a way to update the grid settings, and was wondering if anyone else has AC coupled these inverters to a non-SolarEdge battery system. If not, it

Re: [RE-wrenches] AC coupling with Solar Edge, pre HD Wave

2023-06-30 Thread Dave Tedeyan via RE-wrenches
Sam, Thanks for pointing me in that direction. It looks like you can update some of the grid protection settings, although I am not sure if that will allow for freq-watt control. My LG rep told me to use CA rule 21 grid profile, but I am not sure if there is something like that on the old A series

Re: [RE-wrenches] Testing strings with Tigo

2023-07-06 Thread Dave Tedeyan via RE-wrenches
Hi William, I recently installed these connected to an FM100, and also on a couple grid tied systems in the past year. I think that as long as you are getting the expected 0.6V per module you know that everything is connected as it should be. Unfortunately I do not think that you will be able to d

Re: [RE-wrenches] Damaged PV module cells

2023-07-18 Thread Dave Tedeyan via RE-wrenches
It was a bunch of years ago, but I had seen many of these "snail trails" on some modules. I actually took a curve tracer to them, and they functioned essentially the same as the other modules there that did not have the snail trails. Maybe these will be sources of premature failure in the future, b

[RE-wrenches] Nuance ground racking

2023-10-09 Thread Dave Tedeyan via RE-wrenches
Hi all, I am going to try out the Nuance OSPREY PowerRack as a ground mount option that does not require an excavator. I am wondering two things about it: 1. Does anyone have experience with this, and do you like it? 2. What drill do you use for the drive rod? It seems like the Milwaukee 2" SDS

Re: [RE-wrenches] Nuance ground racking

2023-10-12 Thread Dave Tedeyan via RE-wrenches
> >> Thanks, >> Kienan >> >> *Green-Go Solar Wholesale Distribution LLC* >> >> *kienan@dist.solar* >> >> *(801) 631-5584(Cell)* >> >> *www.distribution.solar* >> >> On Oct 9, 2023, at 8:33 AM, Dave Tedeyan via RE-wrenches < &

Re: [RE-wrenches] Cable sizing for high current modules? NEC interpretation/guidance?

2023-11-09 Thread Dave Tedeyan via RE-wrenches
Fascinating. I emailed the list a little while back asking if anyone knew of a way to make a warranty claim with Solarworld. We had a system with 36 of these panels, and basically every module to module connector was crispy and deformed as Ray mentioned. I never was successful in getting in touch w

Re: [RE-wrenches] Cable sizing for high current modules? NEC interpretation/guidance?

2023-11-10 Thread Dave Tedeyan via RE-wrenches
Mine was a roof mount. We had very few SolarWorld projects. In fact, this might be our only one. On Fri, Nov 10, 2023, 8:10 AM Chris Schaefer via RE-wrenches < re-wrenches@lists.re-wrenches.org> wrote: > I'd be curious to know of the connector failures y'all have experienced, > were the majority

Re: [RE-wrenches] Fortress remote monitoring

2023-11-30 Thread Dave Tedeyan via RE-wrenches
Kirk, I know that with the Guardian Battery monitor the app is working, but they are doing a major overhaul on the website. My login info does not work on the website right now, and I am told that it will not be available until the new year. The website is: https://app.fortresspower.io/ Cheers, D

Re: [RE-wrenches] Fortress remote monitoring

2023-11-30 Thread Dave Tedeyan via RE-wrenches
Interesting on the "mesh" wifi. That is good to know. And yes, the site I linked is for the Guardian data. I don't know if there is a separate site for the Envy data, but I'll find out in a couple weeks when I install my first Envy inverter system. For what it's worth, their tech support has been e

Re: [RE-wrenches] Grid Tied Inverter back feed to Generator

2023-12-01 Thread Dave Tedeyan via RE-wrenches
Jeremy, It is my understanding that if the generator wakes up the grid tied inverter and loads are more than the solar then maybe nothing bad would happen. Although I would never do that because you don't have any control over the loads. And if the solar production is more than the loads, then the

[RE-wrenches] SMA TL-22 insulation resistance error

2023-12-13 Thread Dave Tedeyan via RE-wrenches
Hi All, I am curious to hear if anyone else has run into this: This is the system I posted about a little while ago that had the SolarWorld modules and all the module to module connectors were swollen and melted. One of the inverters was giving an insulation resistance error, and so after seeing

Re: [RE-wrenches] SMA TL-22 insulation resistance error

2023-12-13 Thread Dave Tedeyan via RE-wrenches
, 2023 at 9:07 AM Jay via RE-wrenches < > re-wrenches@lists.re-wrenches.org> wrote: > >> I think that using a megger etc to test the panels and wires is what I’d >> do before I yanked out all the >> Wires. >> >> They are not that expensive anymore and m

Re: [RE-wrenches] SMA String inverters

2024-01-09 Thread Dave Tedeyan via RE-wrenches
We also stopped using the -41's in 2023 due to the -SB requirement in NY. We moved to Enphase for grid tied systems. I am hearing from Greentech that the new Sunny Boy units, up to 7.7kw, should be available very soon. These will have a secure power supply capability. But the larger KW units and th

Re: [RE-wrenches] Fortress

2024-02-15 Thread Dave Tedeyan via RE-wrenches
I also have been having some issues with reported SOC through the Guardian with Fortress. Fortress is generally responsive, although no one has specifically addressed my concern yet. What I have seen with two recent eFlex installations (replacing an existing battery bank on an off-grid system) is t

Re: [RE-wrenches] Fortress

2024-02-15 Thread Dave Tedeyan via RE-wrenches
Kirk, That site looks specifically for the Envy inverters. Do you know if the Guardian site is working? My credentials will not get me in at this time. www.app.fortresspower.io My sites have no comms between the batteries and the inverter, since it is an Outback system. And yes, there is certain

[RE-wrenches] Anyone in the Maryland region want lots of used solar panels?

2024-03-01 Thread Dave Tedeyan via RE-wrenches
If anyone in the Maryland region is interested in lots of used solar panels in the 235-300w range, send me a direct message. Sounds like they are upgrading some older sites. Here is a message I received from an old friend: As part of some of our upcoming portfolios there are old panels that we mig

Re: [RE-wrenches] TPM Search

2024-03-08 Thread Dave Tedeyan via RE-wrenches
Another one out there that is worth looking at is MT Solar. Cheers, Dave On Fri, Mar 8, 2024, 5:51 PM Kent via RE-wrenches < re-wrenches@lists.re-wrenches.org> wrote: > Jeremy, > > I think the Solar RacksWorks TPMs are virtually identical to the DPW TPMs. > My go to TPM is General Specialties > <

[RE-wrenches] Insurance for solar design and inspections

2024-03-10 Thread Dave Tedeyan via RE-wrenches
Hi All, I have an insurance question and am very curious about how others deal with this, or don't. People will sometimes ask us to either do some design work for a system that we will not be installing, or to inspect a system and give my professional opinion about it. These are two separate work

Re: [RE-wrenches] Insurance for solar design and inspections

2024-03-11 Thread Dave Tedeyan via RE-wrenches
tion to shop > around is a good one. NABECP I THINK, has some leads on firms for this. > > > Chris > On 3/10/2024 6:23 PM, Dave Tedeyan via RE-wrenches wrote: > > Hi All, > > I have an insurance question and am very curious about how others deal > with this, or do

Re: [RE-wrenches] Evaluating battery health

2024-03-11 Thread Dave Tedeyan via RE-wrenches
Hi William, Thinking out loud here, and I am guessing that there are reasons why not to do this. But what about putting a voltage tester across each battery and running a quick test? I mention this because just a couple days ago, I went to check on a grid tied battery backup system where capacity

Re: [RE-wrenches] Sol-Ark 15K AC Output

2024-03-26 Thread Dave Tedeyan via RE-wrenches
I may be wrong, but I was under the impression that most inverter/chargers are either being an inverter or a charger at any given time, but not both. So, once the inverter sees the AC voltage from the generator, then it will switch to being a charger and use the generator AC power to charge the bat

[RE-wrenches] Grid-Tied Radian Force Discharge

2024-04-23 Thread Dave Tedeyan via RE-wrenches
Hi All, I have an AC coupled Radian that is used to back up certain loads when the grid is down. It is paired with the Northstar Blue (Outback) batteries. The system sits in float nearly all the time. During a recent grid outage, the batteries had less than half the capacity that I would have expe

Re: [RE-wrenches] Grid-Tied Radian Force Discharge

2024-04-24 Thread Dave Tedeyan via RE-wrenches
ries after 13 >> years and most of them are still viable. >> >> As a precaution, For AC coupling, I also install a high battery AUX port >> controlled relay that drops the AC coupling input circuit. >> >> Thank you, >> >> Maverick >> >> Ma

Re: [RE-wrenches] Grid-Tied Radian Force Discharge

2024-04-25 Thread Dave Tedeyan via RE-wrenches
atteries >>> instead of zero AC loads. >>> >>> The third choice is to program something called FlexTime where you set >>> the schedule of the AC input mode from grid tide to red zero or off grid, >>> etc. >>> >>> It’s the system is on Opt

Re: [RE-wrenches] Grid-Tied Radian Force Discharge

2024-04-26 Thread Dave Tedeyan via RE-wrenches
06 >> Maverick Solar Enterprises, Inc. >> • Solar Commander Remote Power >> • SunFlow Systems Cathodic Protection >> maver...@mavericksolar.com >> 512-460-9825 >> >> >> >> On Apr 25, 2024, at 5:57 PM, Dave Tedeyan via RE-wrenches < >>

Re: [RE-wrenches] Primo with tigos Arc fault issue

2024-05-24 Thread Dave Tedeyan via RE-wrenches
This winter we were fixing up a system with a fronius primo inverter and adding rapid shutdown. Fronius very much recommended against using Tigo. They recommended we use Fire Raptors. They have been working fine. Cheers, Dave On Thu, May 23, 2024, 8:27 PM Chris Sparadeo via RE-wrenches < re-wren

Re: [RE-wrenches] NOS SMA-41

2024-05-28 Thread Dave Tedeyan via RE-wrenches
John, Just an FYI, the new SBSE inverters are available in the up to 7.7kw models. I believe the SPS is possible with them right now, but the more involved backup options are not yet available. Cheers, Dave On Tue, May 28, 2024 at 1:50 PM John Blittersdorf via RE-wrenches < re-wrenches@lists.re-wr

Re: [RE-wrenches] Sunpower connectors

2024-08-01 Thread Dave Tedeyan via RE-wrenches
Evan, I am not sure if this is the same issue, but I have seen a lot of arc fault issues with the E20-327 modules paired with SMA inverters. Every system that we have done repairs on have had the Yukita junction boxes, and there were a handful of failed solder joints on the diodes in the junction b

[RE-wrenches] vent fan with Sol-Ark

2024-08-08 Thread Dave Tedeyan via RE-wrenches
Hi All, What do you all do to power an inline vent fan to vent a flooded lead acid battery bank with a Sol-Ark inverter? On Outback equipment, this is very straightforward to program a 12V relay in the equipment. I don't see anything similar in the Sol-Ark manual, and just tried calling them and p

[RE-wrenches] ESS and generator install in Concord, MA

2024-08-08 Thread Dave Tedeyan via RE-wrenches
Hi All, Is anyone interested in, or can recommend someone, for an ESS and generator installation in Concord MA? It is not a good site for solar, and they are grid connected. If so, please contact me off list at d...@sungineersolar.com . Cheers, Dave -- [image: Logo]

[RE-wrenches] small battery on 208V three phase

2024-08-15 Thread Dave Tedeyan via RE-wrenches
Hi All, I am working on sorting out equipment for a roughly 70kw 208V three phase system, where they also want a very small battery backup for some 120V loads. It seems like it may be a bit overkill to have all 70kw worth of solar going through battery based inverters, when I need only a small amo

[RE-wrenches] Print Pro Solar labels

2024-08-23 Thread Dave Tedeyan via RE-wrenches
Hi All, Has anyone heard of Print Pro before? https://printproaz.com/ I got a cold call from them (and surprisingly actually picked it up). They are offering a $200 gift card, and their prices seem really cheap. It smells slightly scammy to me, but maybe they are just trying to get started. Their

Re: [RE-wrenches] Blue Planet Energy

2024-09-16 Thread Dave Tedeyan via RE-wrenches
It was about a month ago that I tried reaching out and was getting that weird phone message that does not allow you to get anywhere. I called my sales rep who told me off the record that they basically imploded and all employees were told not to come in. He is now working somewhere else. A couple w

Re: [RE-wrenches] UL3741

2024-10-08 Thread Dave Tedeyan via RE-wrenches
Hi Lou, It looks like Ironridge with the Midnite's MNSSR-600S-SS and some Solis Inverters (or Tesla) are compatible. But that is all I know of off the top of my head. https://www.ironridge.com/2024/02/27/flush-mount-systems-listed-to-ul-3741/ I have not actually pursued this yet, but would be cur

Re: [RE-wrenches] Lead acid batteries taking too much current

2024-10-04 Thread Dave Tedeyan via RE-wrenches
Is the 5% adjustable or the adjustment is in the battery capacity? > > Thx > Jay > > > > On Oct 4, 2024, at 8:30 AM, Dave Tedeyan via RE-wrenches < > re-wrenches@lists.re-wrenches.org> wrote: > >  > Hi All, > > I have inherited and done some work on an

Re: [RE-wrenches] Lead acid batteries taking too much current

2024-10-07 Thread Dave Tedeyan via RE-wrenches
-battery-engineering> >> <http://www.instagram.com/RollsBattery> >> <http://www.instagram.com/RollsBattery> >> -- >> CONFIDENTIALITY: The information transmitted herein is intended only for >> the addressee and may contain confiden

Re: [RE-wrenches] 208V residential service

2024-10-18 Thread Dave Tedeyan via RE-wrenches
Hi all, Unfortunately this sounds like it is occasionally done on purpose by the utility, and I don't have much leverage to get them to change it. Good to know. I am trying to get details from them though about whether they would drop in a 240V transformer and what the cost will be. In the meanti

Re: [RE-wrenches] Overpowered mppt landing in a SMA-41?

2024-10-21 Thread Dave Tedeyan via RE-wrenches
Hi Bill, Those SMA inverters can handle a max Isc of 18A. Check your module datasheet, but I would assume that you would be under this limit. I've had strings with an Imp of 11-12A and the inverter just adjusts where it is on the MPPT curve to keep the current to under 10A. So there is a little bi

[RE-wrenches] 208V residential service

2024-10-17 Thread Dave Tedeyan via RE-wrenches
Hi All, I was just out of town installing a system for a friend just North of NYC. I was confused when checking phase for consumption CT's when I found that there was 120V L-N, but 206V L-L. I went and found the transformer, and there was in fact one transformer for all the houses that I could see

Re: [RE-wrenches] sol ark battery

2024-10-10 Thread Dave Tedeyan via RE-wrenches
Also, does anyone know the warranty period for those Powerflo batteries? I see a number of cycles specified, but not a number of years. Cheers, Dave On Thu, Oct 10, 2024 at 4:17 PM jay via RE-wrenches < re-wrenches@lists.re-wrenches.org> wrote: > HI Michael, > > Thats good news. > > Can you monit

Re: [RE-wrenches] All-In-Ones / Sol-Ark fail

2024-10-10 Thread Dave Tedeyan via RE-wrenches
Yikes! I cannot speak to the AIO's in general. However, I do still always install some sort of inverter bypass in battery based systems. Then in case of a failure like this you can at least continue to power the house off the generator as long as someone is there to throw the switch. Cheers, Dave

[RE-wrenches] Lead acid batteries taking too much current

2024-10-04 Thread Dave Tedeyan via RE-wrenches
Hi All, I have inherited and done some work on an off-grid system with a Sol-Ark 8k inverter and now has a new set of 16 Rolls S6 L16-HC batteries (only about a month old). There is only 3.9kw of solar, and there is a 12kw generator. First of all, thanks to Steve for putting out that webinar a li

Re: [RE-wrenches] Enphase excess solar for IQ system controller

2024-09-26 Thread Dave Tedeyan via RE-wrenches
ing on a possible workaround to make something work, but I would not > hold your breath. I even wrote this article when the issue first came to > light: > > https://floridasolardesigngroup.com/enphase-iq7-versus-iq8-microinverters/ > > > Jason Szumlanski > Principal Solar Designer | Flor

Re: [RE-wrenches] SunPower Warranty and Monitoring

2024-09-27 Thread Dave Tedeyan via RE-wrenches
Hi All, I talked to Enphase recently about this. They will be providing warranty support at least for Sunpower's microinverters. They do not know how long Sunpower's monitoring will continue to work. But they have figured out a way to use their Gateway to monitor Sunpower's microinverters, even th

Re: [RE-wrenches] SunPower Warranty and Monitoring

2024-09-27 Thread Dave Tedeyan via RE-wrenches
he said. They also have an upgrade program to > switch over to Enphase monitoring for $699 as you mention, but that is only > for IQ7AS and IQ7HS according to Parker. Were you able to get more info on > the potential monitoring for the C and D units? > > Best, > > August > &

Re: [RE-wrenches] SunPower Warranty and Monitoring

2024-09-30 Thread Dave Tedeyan via RE-wrenches
t;> the potential monitoring for the C and D units? >> >> Best, >> >> August >> >> >> >> >> On Fri, Sep 27, 2024 at 8:05 AM Dave Tedeyan via RE-wrenches < >> re-wrenches@lists.re-wrenches.org> wrote: >> >>> Hi All,

[RE-wrenches] Enphase excess solar for IQ system controller

2024-09-25 Thread Dave Tedeyan via RE-wrenches
Hi all, All this talk about Enphase recently and I have a design question that I am having trouble getting a straightforward answer to. The IQ system controller can take up to 64A of PV AC output on the DER port (coming from the IQ combiner for example). When there is more solar on site, the quest

Re: [RE-wrenches] [EXTERNAL] 208V residential service

2024-11-08 Thread Dave Tedeyan via RE-wrenches
of Outback inverters that wouldn't work because of low AC voltage. They > had to swap them out for an inverter that would work at 208. > -- > *From:* RE-wrenches on behalf > of Dave Tedeyan via RE-wrenches > *Sent:* Thursday, October 17, 2024 8:2

Re: [RE-wrenches] SunPower Warranty and Monitoring

2024-11-14 Thread Dave Tedeyan via RE-wrenches
there are a lot of nuances to all of the possibilities, so I'm > happy that we're able to chat about it here on Wrenches. I'm also looking > forward to receiving more documentation from Enphase as they sort this all > out. > > Best, > > August > >

Re: [RE-wrenches] SunPower Warranty and Monitoring

2024-11-14 Thread Dave Tedeyan via RE-wrenches
#x27;re dealing with failed solder joints or diodes issues, I would think > that's a Maxeon issue. > > Best, > > August > > > > > On Thu, Nov 14, 2024 at 9:49 AM Dave Tedeyan via RE-wrenches < > re-wrenches@lists.re-wrenches.org> wrote: > >>

Re: [RE-wrenches] Sunny Portal

2024-12-03 Thread Dave Tedeyan via RE-wrenches
As of a couple weeks ago, when you try to login, you should get redirected to sign up for an SMA ID. You need to go through this to log on to the SMA websites. Cheers, Dave On Tue, Dec 3, 2024, 5:45 AM david quattro via RE-wrenches < re-wrenches@lists.re-wrenches.org> wrote: > SMA monitoring i

Re: [RE-wrenches] IQ8: Envoy needed for California installations

2025-01-21 Thread Dave Tedeyan via RE-wrenches
Hi William, I am 100% sure that the IQ7 would work without a Gateway. I am nearly sure that the IQ8's will as well. I'll sometimes turn the solar on before the gateway is fully installed just to test the strings, and the microinverters do seem to wake up. I am not sure what California might have t

[RE-wrenches] Solar Edge system not working after Tesla installation

2025-01-23 Thread Dave Tedeyan via RE-wrenches
Hi all, I am going to be checking out a site next week where there is an old Solar Edge system not producing. It stopped working when someone installed a Tesla battery system. I was not part of either installation, but am being called in to get the solar working again. Supposedly the Tesla install

[RE-wrenches] Sunpower monitoring down?

2025-01-23 Thread Dave Tedeyan via RE-wrenches
Hi All, At the moment, I cannot seem to be able to get into any of the Sunpower monitoring sites. mySunpower app seems to work on my phone at the moment, but not on the computer. Does anyone know if this is permanent, or whether there is some other hidden way to view the data? Cheers, Dave --

Re: [RE-wrenches] Outback radian inverter with FM 100 ground fault

2025-01-20 Thread Dave Tedeyan via RE-wrenches
It's fortunate that you have two charge controllers, which makes troubleshooting easier. If there is a solid ground fault, it should be easy to track down. Assuming that it is intermittent, you can start to do things like swap which PV input goes to which charge controller. Then see if the fault st

Re: [RE-wrenches] Portable Home Back-Ups

2025-01-20 Thread Dave Tedeyan via RE-wrenches
Hi Michael, I have also gotten some calls from people asking me to install equipment if they purchase it on their own. Specifically a few calls about the EcoFlow equipment. It sounds like it even has some of the required UL listings (I have not looked into it too closely). But I tell them to do it

Re: [RE-wrenches] PV watts question

2025-01-27 Thread Dave Tedeyan via RE-wrenches
If anything, I'd be surprised that a 1.2 ratio is better than a 1.0 ratio. Although, maybe the fact that an inverter is generally more efficient when loaded closer to its rating compensates for some of the clipping with a higher DC to AC ratio. On Mon, Jan 27, 2025, 4:04 PM Rebekah Hren via RE-wre

Re: [RE-wrenches] Seeking Advice on LG Solar Panel RMA Process

2024-12-23 Thread Dave Tedeyan via RE-wrenches
Hi Lou, I had to reach out to them recently about an AC module of theirs that stopped working. I did send the RMA form to so...@lgsupport.com. It took them 4 days to respond. Turns out they were able to reset it remotely to get it working again. I am attaching the RMA form that I have. And here i

[RE-wrenches] Sol-Ark parallel 8k and 12k

2025-04-05 Thread Dave Tedeyan via RE-wrenches
Hi All, I have just gotten myself into a pickle and so am posting this both as a note/warning too all, as well as seeing if anyone has tried this. I installed a small system with a Sol-Ark 12k a few years ago. The customer recently asked us to add some more power. An 8k was more than enough, so w

Re: [RE-wrenches] Insulation Resistance Testing with Klein ET600

2025-04-06 Thread Dave Tedeyan via RE-wrenches
Can you swap the strings in each inverter? Then you'll know whether the issue truly lies in the inverter or the array. Cheers, Dave On Sun, Apr 6, 2025, 1:35 PM Jason Szumlanski via RE-wrenches < re-wrenches@lists.re-wrenches.org> wrote: > I should mention that the other inverter also has three

Re: [RE-wrenches] Insulation Resistance Testing with Klein ET600

2025-04-06 Thread Dave Tedeyan via RE-wrenches
How quick do the faults take to show up? If you can just wire nut on temporary jumpers while you are on site, you can swap the strings at the inverters. With an ungrounded array, you can touch one hot wire at a time without getting zapped. But put on your gloves to be extra safe. I would not leave

Re: [RE-wrenches] Enphase PCS

2025-04-17 Thread Dave Tedeyan via RE-wrenches
Hi Mac, Enphase's Power Control System (PCS) based limiting lives inside the IQ gateway, not the system controller. So you can still implement this on a standard grid tie system without the System Controller. Every system should have a Gateway. Cheers, Dave On Thu, Apr 17, 2025 at 8:56 AM Mac Le

Re: [RE-wrenches] Popping Sounds From Roof

2025-03-05 Thread Dave Tedeyan via RE-wrenches
Jason, You mentioning popping sounds reminds me of two separate systems that I was called in to service recently where the homeowner was reporting popping sounds. These were coming from the ground, not the roof, so it may not apply. Both systems were roughly 10 years old, and the original installer

[RE-wrenches] EG4 and Bolt Car Charger

2025-03-05 Thread Dave Tedeyan via RE-wrenches
Hi All, I've got an acquaintance with a somewhat kludged together off grid system within his grid tied house. (We do not need to get into the random design decisions that went into that...) It is an EG4 3kw 120v off grid inverter, with one of the EG4 server rack batteries. The system runs most th

Re: [RE-wrenches] Midnite AIO Generator Functionality

2025-05-12 Thread Dave Tedeyan via RE-wrenches
Jason, Cant you just make the AGS turn on the generator before the inverter gets to the LBCO? Maybe this is more difficult if you do not have closed loop comms and the SOC drifts. I am just working through my first Midnite AIO setup now, so I cannot speak to the nuances of how it will work with tha

Re: [RE-wrenches] Cell damage leading to ground fault?

2025-05-09 Thread Dave Tedeyan via RE-wrenches
anufacturer I know of that > requires this. Water vapor roses into the circuit boards.I used to get > a couple different error codes until we packed the conduits. >Good luck, and let us know! > > > > On Thu, May 8, 2025 at 12:22 PM Dave Tedeyan via RE-wrenches < &g

Re: [RE-wrenches] Cell damage leading to ground fault?

2025-05-08 Thread Dave Tedeyan via RE-wrenches
ming. Fun stuff. > > > > Jason Szumlanski > Principal Solar Designer | Florida Solar Design Group > NABCEP Certified Solar Professional (PVIP) > Florida State Certified Solar Contractor CVC56956 > Florida Certified Electrical Contractor EC13013208 > > On Thu, May

[RE-wrenches] Sol-Ark battery calibration

2025-05-28 Thread Dave Tedeyan via RE-wrenches
Does anyone know whether you can calibrate the battery voltage on Sol-Ark inverters? I am on site with two 12k-p inverters. My meter agrees with one of them, and the other inverter (the master) is displaying 0.6v lower than both my meter and the other inverter. I have gone through two tech support

Re: [RE-wrenches] Sol-Ark battery calibration

2025-05-29 Thread Dave Tedeyan via RE-wrenches
– d...@solarwork.com > > W - www. greatsolarworks.com www.solarwork.com > > *“Responsible Technologies for Responsible People since 1988!”* > > > > > > ------ Forwarded message -- > From: Dave Tedeyan via RE-wrenches > To: RE-wrenches > Cc: Dav

[RE-wrenches] battery vent control for lead acid

2025-06-03 Thread Dave Tedeyan via RE-wrenches
Hi all, What are people using these days for venting a good ol' 48v flooded lead acid battery box? I am upgrading an off grid system. There is a one year old set of flooded lead acid batteries, so those will stay, but everything else will be new. I plan on using a Sol-Ark inverter. The existing ba

Re: [RE-wrenches] battery vent control for lead acid

2025-06-03 Thread Dave Tedeyan via RE-wrenches
3, 2025 at 3:12 PM Glenn wrote: > Dave, I just pulled one of those out in a battery retrofit, I don't know > what the customer did with it... > Maybe a Morningstar relay controller could be setup using system voltage? > > > > -Glenn > > On Jun 3, 2025 14:22, Dav

Re: [RE-wrenches] Sol-Ark battery calibration

2025-05-29 Thread Dave Tedeyan via RE-wrenches
> Assuming a it’s closed loop. > Jay > > On May 29, 2025, at 10:41 AM, Dave Tedeyan via RE-wrenches < > re-wrenches@lists.re-wrenches.org> wrote: > >  > Dana, > Having two inverters makes this a little easier in a sense. One inverter > matches my meter. The ot

[RE-wrenches] Sol-Ark Dark Mode

2025-07-10 Thread Dave Tedeyan via RE-wrenches
Hi All, Does anyone know what it means when a Sol-Ark display goes into dark mode? Instead of the normal white background and coloring, the background goes to black, and the arrows are purple. I've talked to tech support, and all they would tell me is that it is "not good". We reset the dongle and