Hi All,

I have inherited and done some work on an off-grid system with a Sol-Ark 8k
inverter and now has a new set of 16 Rolls S6 L16-HC batteries (only about
a month old). There is only 3.9kw of solar, and there is a 12kw generator.

First of all, thanks to Steve for putting out that webinar a little while
ago on how to program a Sol-Ark with lead acid batteries! I followed that
for the programming of this inverter.

Recently, the generator kicked on when it should. But it never turned
itself off. I had to go into the battery settings and turn off grid and gen
charging to get the generator to turn off. From looking at the monitoring,
even once the batteries were full, they were still accepting over 40A of
current. A few hours later, the batteries were accepting almost 50A of
current.

The battery bank has a capacity of 890AH, but based on the FLA
recommendations I set the capacity to 70% of that, or 650AH so that it
absorbs longer. Based on the Sol-Ark programming, it will run the generator
until the batteries are accepting 5% of that, or 32.5A. It seems that since
the system never got down to that little amount of current, it never turned
off the generator and never stopped charging. I had the customer check the
water level and they said it was low, but not below the level of the
plates.

Does anyone know why the batteries might have been accepting so much
current even when fully charged? And in order to get the final amps that
the inverter is looking for to turn off the generator, I would need to set
the capacity up to about 780AH or about 90% of the rated capacity. Is
upping the capacity the recommended action to prevent this from happening
in the future?

I also have a follow up question. Being that there is not a ton of solar
here, the recommendation for a full absorb every few days ends up being
about 7 hours of absorb time. I am wondering if there is a way to force the
inverter to do an EQ cycle (although we are really just using the EQ
function on the inverter to get a full absorb cycle every few days) when we
know it will be a sunny day? I would also like to be able to start an EQ
cycle and also start the generator to give a good top off. It seems that
you can choose the EQ frequency, but you don't know exactly when it will
try to EQ.

Thanks in advance!
Cheers,
Dave
-- 

[image: Logo] <https://www.sungineersolar.com/>
Dave Tedeyan, P.E.
Owner | Sungineer Solar
p: he | him | his
a: 1653 Slaterville Rd. | Ithaca, NY 14850
w: www.sungineersolar.com <http://www.sungineersolar.com/>
c: (607) 270-0370
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to