You are correct.

The air vent is required on each wet pipe system.

If we look at the definitions in chapter 3, you have separate systems each 
floor.

R/
Matt

Please rate our customer 
service<https://survey.medallia.com/?emailsignature&fc=3539&bg=Fire%20and%20Fabrication>

Matthew J. Willis, CWBSP, CET
Engineering Manager – Southwest Region
FERGUSON FIRE DESIGN, LLC
A Wholly Owned Subsidiary of Ferguson Fire & Fabrication, LLC
3508 Hwy. 557
West Monroe, LA. 71292
C: 307-236-8249
[email protected]<mailto:[email protected]>
www.FergusonFire.com<http://www.fergusonfire.com/>


From: Ken Wagoner <[email protected]>
Sent: Monday, October 9, 2023 11:43 AM
To: [email protected]
Subject: [Sprinklerforum] Air venting

Forumites,

I'm working on a multi-story building protected per NFPA 13.  As each floor has 
a separate control valve, is a means to vent trapped air required on each 
floor?  Or is it only required at the highest level of the building?

My thinking is that each floor has a separate fire sprinklers system.

Any thoughts?