You are correct. The air vent is required on each wet pipe system.
If we look at the definitions in chapter 3, you have separate systems each floor. R/ Matt Please rate our customer service<https://survey.medallia.com/?emailsignature&fc=3539&bg=Fire%20and%20Fabrication> Matthew J. Willis, CWBSP, CET Engineering Manager – Southwest Region FERGUSON FIRE DESIGN, LLC A Wholly Owned Subsidiary of Ferguson Fire & Fabrication, LLC 3508 Hwy. 557 West Monroe, LA. 71292 C: 307-236-8249 [email protected]<mailto:[email protected]> www.FergusonFire.com<http://www.fergusonfire.com/> From: Ken Wagoner <[email protected]> Sent: Monday, October 9, 2023 11:43 AM To: [email protected] Subject: [Sprinklerforum] Air venting Forumites, I'm working on a multi-story building protected per NFPA 13. As each floor has a separate control valve, is a means to vent trapped air required on each floor? Or is it only required at the highest level of the building? My thinking is that each floor has a separate fire sprinklers system. Any thoughts? Ken Wagoner, SET Parsley Consulting 500 West Mechanic Street Harrisonville, Missouri 64701-2235 Phone: (760) 745-6181 Visit the website<https://linkprotect.cudasvc.com/url?a=http%3a%2f%2fwww.parsleyconsulting.com%2f&c=E,1,Y5zKJKPEh1mBEBqSR-VE9cUKl5y-eyP8BpvmE_5j9ZqW2eJbNphYzrCMBZ-2YuX6d-RRkHI4gQ1FV-cvOeCfRC58uZS9NiToZv2mx7909oCqLvCW_n5hDHeK&typo=1>