Re: [RE-wrenches] Magnum inverters (not really a power factor issue)

2009-08-01 Thread Matt Tritt
are the most exotic things plugged in. The run to the pump is adequately sized - - - - - in other words, it all seems run of the mill, except that the pump only ran successfully one time and not on any further attempts. Golly.. Matt boB Gudgel wrote: Larry Crutcher, Starlight Solar wrote: H

Re: [RE-wrenches] Magnum inverters (not really a power factor issue)

2009-08-01 Thread Matt Tritt
n SW, right? They all have an odd ability to loosen the DC inverter cables over time because of this harmonic vibe, especially the Al lugs they used to use back in the day. I had several problems with tripping (no, not that kind) breakers before I changes to better cable lugs. Matt Darryl T

Re: [RE-wrenches] Magnum inverters (not really a power factor issue)

2009-08-01 Thread Matt Tritt
Yeah, boB - I think this sounds like a good trail to follow. Matt boB Gudgel wrote: Darryl Thayer wrote: Don't know if this will help, but an experiance of mine on starting a large motor, using a battery and inverter. The motor would not start, or if it did if would quit in 10, or 2

Re: [RE-wrenches] Magnum inverters (not really a power factor issue)

2009-08-03 Thread Matt Tritt
I'm hoping that it WILL be embarrassingly simple! I'm glad this wasn't something I installed since you all know what it's like to find errors is someone else's work. ;-) Matt d...@foxfire-energy.com wrote: Boy, This reminds me of a problem I had a few years a

Re: [RE-wrenches] solid vs stranded AC vs DC

2009-08-03 Thread Matt Tritt
Darryl, Say what?! This would seem to indicate that solid core is actually better for DC than stranded wire. Can this possibly be true?? Matt Darryl Thayer wrote: I looked in the code book and found stranded wire has about 2% higher DC resistance than solid, Chapter 9 table 8, and that

Re: [RE-wrenches] solid vs stranded AC vs DC

2009-08-04 Thread Matt Lafferty
RE: 2% loss over 25 years is significant Amen. Sorta makes one wonder how they've allowed and accepted <50% efficient combustion-cycle turbine plants all these years... That's before taking transmission losses of minimum 8%. 24/7 x 365.

Re: [RE-wrenches] PV System Design Compromises (was solid vs stranded AC vs DC)

2009-08-05 Thread Matt Tritt
a low price to pay for being able to connect the bits and pieces to each other. Non? Matt T Joel Davidson wrote: Dave, I agree. but are we talking about 2% voltage drop, resistance, or power loss? What I got from this discussion about solid vs. stranded wire (1) use solid copper wire and (2

Re: [RE-wrenches] solar roof lift experience?

2009-08-12 Thread Matt Lafferty
es and racking over and over. Your own "kit" if you will. At least in the beginning. This gives your team (survey, design, installation) the chance to streamline the process. Once you've got the key pieces worked out, applying the process to a different module type isn't a big

Re: [RE-wrenches] Dealing with snow

2009-08-14 Thread Matt Lafferty
laminate sites and two framed poly sites. I like it. Would use it on my own system (if the landlord would let us install one!) Matt Lafferty -Original Message- From: re-wrenches-boun...@lists.re-wrenches.org [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Chris Daum Sent: F

Re: [RE-wrenches] solar roof lift experience?

2009-08-22 Thread Matt Lafferty
sure the ones you're using are totally adequate. -Matt Lafferty _ From: re-wrenches-boun...@lists.re-wrenches.org [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Ron Young Sent: Wednesday, August 19, 2009 11:16 PM To: RE-wrenches Subject: Re: [RE-wrenches] solar r

Re: [RE-wrenches] Helix Wind

2009-08-23 Thread Matt Tritt
Jeeze.Come to think of it, what a great way to make everyone happy; We pay you to look at our bogus equipment, and you can't tell anyone what a piece of crud it is! (:>/ Matt T boB Gudgel wrote: Keith Cronin wrote: http://www.helixwind.com/en/index.php Anyone have any fee

Re: [RE-wrenches] Helix Wind

2009-08-24 Thread Matt Tritt
cake by creating the need for sliprings on a timy, spinning PV module that should blow the mind of any known MPPT controller available. PT Barnum would have loved this thing. Matt T Allan Sindelar wrote: There's a company here in Santa Fe that fits that description: Bluenergy Sola

Re: [RE-wrenches] wind generators

2009-08-28 Thread Matt Tritt
Hi Kirk, Contact me on the marketing list about this. In the meantime, forget the RAUM! They are sub-SWWP quality, but are really cheap. There are good turbines on the market. Matt T Kirk Herander, VSE wrote: Despite my vow to never install another wind generator, I have been called to

Re: [RE-wrenches] Power 4 Home

2009-09-01 Thread Matt Tritt
Come on now, Todd. I'm really happy after buying his other book: Make Your Own Newkular Power from Garage Sale Components! I never knew it could be so easy! I also liked his first effort: Making Energy from Perpetual Motion; (They said it couldn't be done!) Matt T Todd Cory wro

Re: [RE-wrenches] American made

2009-09-02 Thread Matt Tritt
Some of the small Solectrias are made in Taiwan. Matt T Michael Kelly wrote: Mike, Solectria grid-tie inverters are made in the USA. They have three-phase 13kW and 15kW units. Web site: www.solren.com. - Mike -- Michael Kelly Project Manager / Project Engineer NABCEP Certified Solar PV

Re: [RE-wrenches] Fwd: 2011 NEC Articles 690 and 705: ROP and Draft Code

2009-09-13 Thread Matt Lafferty
Final date for comments on Proposals is 10/23/2009, as noted in John W's original message below. -Matt Lafferty -Original Message- From: Michael Welch Sent: Saturday, September 12, 2009 9:56 AM To: re-wrenc...@re-wrenches.org Subject: [RE-wrenches] Fwd: 2011 NEC Articles 690 and 705

Re: [RE-wrenches] wire gauge reducers

2009-09-21 Thread Matt Lafferty
ume of the enclosure and the turning room is insufficient for #4 in the first place. If you go this route, I suggest torquing the terminals, letting them sit for awhile, then re-torquing them. Hope this is helpful, Matt Lafferty _ From: re-wrenches-boun...@lists.re-wrenches.org [ma

Re: [RE-wrenches] ASTM PV installation standards

2009-10-14 Thread Matt Lafferty
Hi Joel, Is this part of the work being done on ASTM WK25362? If not, can you provide the reference and source? Thanks! Matt Lafferty ___ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Options & settings:

[RE-wrenches] Meter Socket Recall Notice

2009-10-19 Thread Matt Lafferty
FYI - Product safety recall Milbank 9090 Series Meter Sockets recalled due to safety hazard. Affected Model Numbers include: U9090-O or R9090-O. These are 200 Amp, 4-jaw sockets. Affected products were sold via electrical suppliers in NY, PA, VT, and MA from May 2009 - August 2009. There were rep

[RE-wrenches] Shade Mitigating DC Device Application

2009-10-28 Thread Matt Lafferty
Esteemed Wrenches, Your collective wisdom & conjecture is sought in resolving the following riddle: There once was a home in the hills. With morning sun the roof is filled. Blasted mountain rising in the west, Makes a shady mess at very best. "Onward! Fear not!", sayeth the man. "Twenty-four

Re: [RE-wrenches] Tape for attaching NEC Labels

2009-11-17 Thread Matt Lafferty
electrical equipment manufacturers (Square D, GE, Cutler-Hammer, Etc) use mechanical fasteners to attach their signage! -Matt Lafferty _ From: re-wrenches-boun...@lists.re-wrenches.org [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Bob Clark Sent: Monday, November 16, 2009

Re: [RE-wrenches] strings of older solar panels

2009-11-18 Thread Matt Lafferty
Lee, They are good to go @600V. Depending on vintage, they may be configurable for 6 or 12 Volt in the J-box. You might want to consider going the 6V route and only using 1 string. This would serve to keep your string voltage "up" if you lose a module or two down the road. Either way, as mentione

Re: [RE-wrenches] "its a UL listed assembly"

2009-11-20 Thread Matt Lafferty
n the load jaws. You will need to get them to buy off on it, but most utilities will accept it, though they may want to put a lock on it. The trick is getting your neutral conductor routed through it. It's a place to start... Matt Lafferty _ From: re-wrenches-boun...@lists.re-wren

Re: [RE-wrenches] Hotel Exclusion?

2009-12-15 Thread Matt Lafferty
For anyone who might be interested... It appears that hotels and motels run as busninesses are eligible for the 1603 grant. Below is the response from Treasury to my inquiry on the matter. Cheers, Matt Lafferty From: 1603questi...@do.treas.gov [ <mailto:1603questi...@do.treas.gov>

Re: [RE-wrenches] Hotel Exclusion?

2009-12-15 Thread Matt Lafferty
of business taxation and/or property taxes. (Hello Santa Monica, et al). Perhaps there is some overlap or confusion in interpretation related to this??? Apartments might be a different story since the real property is classified as residential rental property, but that's still business activity

Re: [RE-wrenches] DC disconnect placement

2009-12-20 Thread Matt Lafferty
to a dead short. Cheers, Matt Lafferty _ From: re-wrenches-boun...@lists.re-wrenches.org [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of William Miller Sent: Sunday, December 20, 2009 11:02 AM To: RE-wrenches Subject: [RE-wrenches] DC disconnect placement Friends

Re: [RE-wrenches] Hotel Exclusion?

2009-12-21 Thread Matt Lafferty
FWIW - My wife's project will be a go. They are happy with either the grant or the ITC. Must be nice to own a family-owned, up-scale motel in the SF Marina District for the last 70 years... Please let us know how your situation turns out. Cheers, Matt Lafferty _ From: re-w

Re: [RE-wrenches] DC disconnect placement

2009-12-21 Thread Matt Lafferty
Walt, You are so right. Thanks for reminding us all that, when using a charge controller, we need to make sure we have overcurrent protection on that end of the PV Output circuit. Seasons Greetings everyone, Matt Lafferty _ From: Walt Ratterman [mailto:wratter

Re: [RE-wrenches] kwh meters

2010-01-28 Thread Matt Lafferty
ve friends who work in the meter shop of the local electric utility, you might want to talk with them. Hint: If you get a blank stare from the meter guy when you say "Net Meter" Just smile, excuse yourself, and go get a donut. 2) If #1 doesn't pan out, find a meter that doe

Re: [RE-wrenches] sales commissions

2010-02-11 Thread Matt Lafferty
alesperson has the potential to cost you more money than anyone else in the company. * Your salesperson has the potential to make you more money than anyone else in the company. * Matt's preferred structure for system sales: Modest base salary + % project margin + annual bonus based on compan

Re: [RE-wrenches] Solar rights precedent

2010-02-26 Thread Matt Lafferty
Don't be a Solar Bully! Have the homeowner file for the Zoning Waiver so it gets on the City Council (or whatever body) agenda ASAP. Flapping your arms and being disgusted with the Planning folks ain't gonna get your project online. I don't think we should automatically assume that the building/p

Re: [RE-wrenches] Cost per kWh

2010-03-06 Thread Matt Lafferty
m in Years and the O&M costs during that period. Like I said, my crystal ball ain't that good. I can share that Hope this is helpful, Matt Lafferty ___ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org

[RE-wrenches] Arc Flash Hazards

2010-03-23 Thread Matt Lafferty
PA 70e are dancing to the same song, has this affected your operations? If so, in what way? Keep it Safe and Sunny! -Matt Lafferty ___ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Options & settings:

Re: [RE-wrenches] NABCEP Exam was: PV excellent battery charger

2010-03-29 Thread Matt Lafferty
I wholeheartedly agree with and can confirm what Bob-O said. -Matt Lafferty _ From: re-wrenches-boun...@lists.re-wrenches.org [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Bob-O Schultze Sent: Sunday, March 28, 2010 9:19 AM To: RE-wrenches Subject: [RE-wrenches

[RE-wrenches] AEI Solaron Inverters - DC Grounded or Ungrounded

2010-05-03 Thread Matt Lafferty
Wrenches, Can anyone DEFINITIVELY tell me whether the DC systems on AEI Solaron based plants is grounded or ungrounded during operation? Have you tested your theory in the field? What marking requirements do you suggest for the neutrals? Thanks! Matt Lafferty

Re: [RE-wrenches] Any experience with Kaneka PV arrays?

2010-05-03 Thread Matt Lafferty
doesn't jinx something) When up-front $/W ain't the only thing to consider, consider Kaneka. $0.02001, Matt Lafferty -Original Message- From: re-wrenches-boun...@lists.re-wrenches.org [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Dan Fink Sent: Monday, May 0

Re: [RE-wrenches] suggested scary language

2010-05-04 Thread Matt Lafferty
here: http://www.tycoelectronics.com/aboutus/news/getpdf.asp?id=1363&f=solar_label s_flyer_final.pdf Pray for Sun! Matt Lafferty DC Disconnect Warning: Electric Shock Hazard DO NOT TOUCH TERMINALS Terminals on both Line and Load sides may be energized in open position DC VOLTAGE IS ALWAYS PRE

Re: [RE-wrenches] AEI Solaron Inverters - DC Grounded or Ungrounded

2010-05-04 Thread Matt Lafferty
nclusively demonstrate that system voltage is <600V. I have followed up with a request for AEI's position on the 690.35 matter as well as their recommendation(s) for marking of the neutral conductors. I guess I will have to follow up with a request to disseminate, too. Opinions &am

Re: [RE-wrenches] Any experience with Kaneka PV arrays?

2010-05-04 Thread Matt Lafferty
f the frames included. Matt Lafferty -Original Message- From: Joel Davidson [mailto:joel.david...@sbcglobal.net] Sent: Monday, May 03, 2010 7:23 PM To: gilliga...@gmail.com; RE-wrenches Subject: Re: [RE-wrenches] Any experience with Kaneka PV arrays? Matt, When Kaneka first attempt

Re: [RE-wrenches] calculating DC voltage drop

2010-07-22 Thread Matt Lafferty
Most appropriate is Ip-max. If you are "operating" @ ISC or above, your voltage has already dropped to zero... AKA 100% voltage drop. Pray for Sun! Matt Lafferty -  Sent from my Palm Pre On Jul 22, 2010 12:22 PM, Marco Mangelsdorf <ma...@pvthawaii.com> wrote: When calcula

[RE-wrenches] SWWP Whisper 200 - Looking for a Short to Ground

2013-10-14 Thread Matt Sherald
he Wrench community might have had a similiar conundrum at one time. I'd appreciate hearing from you if you have. Many thanks in advance. Matt Sherald PIMBY: Power In My BackYard NABCEP Certified Solar PV Installer® m...@getpimby.com (304) 704-5943 www.getpimby.blogs

Re: [RE-wrenches] SWWP Whisper 200 - looking for a short to ground.

2013-11-03 Thread Matt Sherald
Those familiar will appreciate that we had an old Easy-Wire Power System from World Power Technologies Inc. that we could pull out of retirement. With a new cable and an old charge controller the Whisper is back in action. Thanks to all for your time and suggestions! Matt Sherald PIMBY: Power

Re: [RE-wrenches] Split bolt

2014-06-25 Thread Matt Sherald
also think that proper torquing of the wire connection is easier on something like an Ilsco ClearTap or similar. Glad all ended well! -Matt Matt Sherald PIMBY: Power In My BackYard NABCEP Certified Solar PV Installer® m...@getpimby.com (304) 704-5943 www.getpimby.blogspot.com www.ge

Re: [RE-wrenches] Mate 3 web interface

2014-08-02 Thread Matt Partymiller
want to call them before trying to setup the Mate3. Matt On Sat, August 2, 2014 8:06 am, Kirk Herander wrote: > I want to set up a mate 3 for web monitoring. The Outback site is lacking > in clarity of this procedure. Can anyone fill me in on any special > software or hardware required, etc

Re: [RE-wrenches] Sunny Island: Reliability / Error Codes

2014-08-25 Thread Matt Partymiller
ut, the SI relay fails and the house is in the dark. SMA should really recall those products. My contact at SMA for their SI can be reached at 916-316-7170. He may be far more helpful. Matt On Mon, August 25, 2014 2:48 pm, William Miller wrote: > Friends: > > > > > It was

Re: [RE-wrenches] Inverters Maximum Input Ratings

2014-08-26 Thread Matt Partymiller
, it would be nice to hear from more inverter manufacturers on the subject. Matt Matthew Partymiller Solar Energy Solutions LLC (877) 312-7456 m...@solar-energy-solutions.com On Mon, August 25, 2014 7:40 pm, Jason Szumlanski wrote: > I had a tough customer recently that grilled me on how we ca

Re: [RE-wrenches] Inverters Maximum Input Ratings

2014-08-27 Thread Matt Partymiller
could clip potential max power production. This may balance those instances where inverter temp derating would result in production loss. I would be curious to see how subhourly data could affect a simulation. Admittedly not something I have thought about. Matt Matthew Partymiller Solar Energy

Re: [RE-wrenches] Modules over vents

2014-09-25 Thread Matt Partymiller
Carl, In our shared region plumbing code requires vents be 12" above roof line. Electrical inspectors probably won't catch this, plumbing inspectors probably won't get on a roof, but still there is a code concern. You might exercise some caution. Matt Matthew Partymill

Re: [RE-wrenches] outback radian on 120v

2014-09-25 Thread Matt James
HI Jay, The Radian requires a 120/240 source in order to pass through AC power and charge the batteries. Hope this helps! Matt James Applications Engineering Manager OutBack Power Technologies Inc. -Original Message- From: RE-wrenches [mailto:re-wrenches-boun...@lists.re

Re: [RE-wrenches] Outback AGS & eq

2015-02-13 Thread Matt James
Hi All, I confirmed that a Mate3 with 002.017.000 firmware or later will stop after an EQ cycle if the AGS gen control function is changed from Manual to Auto after the genny is started. It may also work with earlier firmware revs, but I only had a 2.17 rev close by for testing. Matt James

Re: [RE-wrenches] Outback quad stack X240 breaker tripping

2015-03-17 Thread Matt James
are imbalanced, one possible solution is to disconnect the neutral from the generator at the power system end. This presents a pure 240v load to the genset, which will force the currents to be balanced on both phases. Feel free to contact me directly if you have any problems or questions.

Re: [RE-wrenches] Wire protection for ground mount

2015-04-17 Thread Matt Sherald
Adam, I've used aluminum perforated sheet metal in the past. It matches the other aluminum on the ground mount and it can be zipped up with self drilling screws. Looks pretty sharp when it is done - kinda like it was meant to be there all along. -Matt On Fri, Apr 17, 2015 at 7:20 AM, AE

Re: [RE-wrenches] Milwaukee Sub Scanner versus Bosch D-Tect versus others?

2015-05-10 Thread Matt Partymiller
We have tried a number of products. The D-Tect is in amazing stud finder but did very little on shingle roofs. The mechanism by which you run it across a surface is clearly not made for shingles. It is basically a $1000 sculpture on the top shelf in our shop. I am still not aware of any great m

Re: [RE-wrenches] Lightning Strike Fries Array

2015-05-21 Thread Matt Sherald
to get to the diodes. The homeowners insurance covered the loss and I replaced the modules with something similar (SW had since stopped manufacturing 175s). It would have been nice to have had access to the diodes. -- Matt Sherald PIMBY Energy, LLC NABCEP Certified Solar PV Installer® 304-704

Re: [RE-wrenches] Repetitive and unknown arc-fault codes with this combination...Sunpreme bi-facial and Fronius IG

2015-06-18 Thread Matt Partymiller
How quickly, after reset, do you see a new arc-fault error? Same day? Month later? Have you tested string volts/amps? On Thu, June 18, 2015 8:30 am, Howard \"Scot\" Arey wrote: > I need some help please! I'm quickly losing credibility with two of my > customers. > > > > We have two installatio

Re: [RE-wrenches] to flash or not to flash

2015-08-06 Thread Matt Partymiller
roper flashings. Good poll. Matt Matthew Partymiller Solar Energy Solutions LLC (877) 312-7456 m...@solar-energy-solutions.com On Thu, August 6, 2015 12:47 pm, Daniel Young wrote: > Writing the subject above, it seems like I've heard this question on the > wrench list before, but I could n

Re: [RE-wrenches] Serviceable equipment on a roof

2015-08-13 Thread Matt Partymiller
Perhaps try asking your panel manufacturer for a letter stating no maintenance is expected or can be performed on the modules. Matt Matthew Partymiller Solar Energy Solutions LLC (877) 312-7456 m...@solar-energy-solutions.com On Thu, August 13, 2015 10:51 am, Daniel Young wrote: >

[RE-wrenches] AC-coupling Enphase/XW Causes Flickering of Lights

2015-09-21 Thread Matt Sherald
s a way to mitigate the flicker I would also love to hear it. Many thanks! -- Matt Sherald PIMBY Energy, LLC NABCEP Certified Solar PV Installer® 304-704-5943 www.getpimby.blogspot.com www.getpimby.com ___ List sponsored by Redwood Alliance List Address: R

Re: [RE-wrenches] Outback customer service?

2015-12-08 Thread Matt Partymiller
st an anecdotal observation. No hard data. Best of luck. Matt On Tue, December 8, 2015 5:15 pm, Starlight Solar Power Systems wrote: > Hi Peter, > > > I only had the option to leave a message and after about 1 hour on hold I > did so. That was a week ago. I had not heard of c

Re: [RE-wrenches] demolition hammer drills

2016-01-07 Thread Matt Sherald
I've been happy with my Bosch 11316EVS. It is heavy enough to drive rods and that is what it gets used for mostly. -Matt On Wed, Jan 6, 2016 at 4:29 PM, jay wrote: > HI All, > > Any recommendations for a demo hammer, and where to get. > > I don’t use it much, but fo

Re: [RE-wrenches] 1000V rated 6AWG wire

2016-01-28 Thread Matt Partymiller
The cheapest solution I have been able to find for this over the past 12 months has been PV wire. The other problem you might find is 1000V listed components to transition from PV wire to other types of wire. Matt On Thu, January 28, 2016 7:48 am, Kirpal Khalsa wrote: > Hello Friends! >

Re: [RE-wrenches] Whisper Turbine Replacement

2016-05-07 Thread Matt Sherald
ches.org > > List-Archive: > http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html > > List rules & etiquette: > www.re-wrenches.org/etiquette.htm > > Check out or update participant bios: > www.members.re-wrenches.org > > -

Re: [RE-wrenches] supply side connection - Tap connector recommendations

2016-05-10 Thread Matt Partymiller
Ilsco has some great options. See: https://www.platt.com/CutSheets/Ilsco/Ilsco-InsulationPiercingConnectors-CatalogPage.pdf Matt Matthew Partymiller Solar Energy Solutions LLC (877) 312-7456 m...@solar-energy-solutions.com On Tue, May 10, 2016 1:27 pm, Kirpal Khalsa wrote: > Hi Folks, &

Re: [RE-wrenches] supply side connection - Tap connector recommendations

2016-05-11 Thread Matt Partymiller
Mac, Is this a utility or AHJ prohibition? In most jurisdictions we work in (not CO) the utilities prohibit taps in the meter base but take no responsibility for conductors once they leave the meter base. Matt On Wed, May 11, 2016 11:44 am, Mac Lewis wrote: > Hi Kirpal, > > > Sou

Re: [RE-wrenches] Optics RE reliability

2016-05-16 Thread Matt Partymiller
while others are starting to get it right, Outback is still having difficulty. Matt On Mon, May 16, 2016 3:57 pm, William Miller wrote: > Friends: > > > > > We just installed our first Optics RE systems. They are both at the same > location connected to a satellite data

Re: [RE-wrenches] !000 volt wire for trench-buried extended runs - what type?

2016-05-18 Thread Matt Partymiller
You will probably use PVwire. As far as I am aware it will be your least expensive option. Get it in aluminum, direct-burial rated if you want. Or pre-sleeved in PVC conduit. Matt On Tue, May 17, 2016 6:52 pm, Howard Arey wrote: > Good day, wrenches. > > > > > I am install

Re: [RE-wrenches] MPPT over amp

2016-06-03 Thread Matt Partymiller
. Matt Matthew Partymiller Solar Energy Solutions LLC (877) 312-7456 m...@solar-energy-solutions.com On Fri, June 3, 2016 11:24 am, frenergy wrote: > Hey Folks, > > > I'm afraid getting through to SMA service has gone the path > of many othershow long can you wait and wait a

Re: [RE-wrenches] service call reimbursement

2016-06-16 Thread Matt Partymiller
ave a message I never get a return call. SMA service used to be good. Right now it is about the worst in our industry. Their saving grace is a product that works well (except the Arc Fault detection). Matt Matthew Partymiller Solar Energy Solutions LLC (877) 312-7456 m...@solar-energy-solutions.com

Re: [RE-wrenches] array overloading of an inverter

2016-07-13 Thread Matt Partymiller
DC:AC ratio perform as well as our older 1:1 systems. Not that I use Enphase often but they have some research/whitepapers on the topic since their micros tend to undershoot 60 cell module power ratings. Good luck! Matt Matthew Partymiller Solar Energy Solutions LLC (877) 312-7456 m...@solar

[RE-wrenches] Solectria 3.8 Inverter Failures

2016-07-25 Thread Matt Partymiller
installing Solectria 3.8s have seen this error or had a high failure rate as of late. Thanks, Matt Matthew Partymiller Solar Energy Solutions LLC (877) 312-7456 m...@solar-energy-solutions.com ___ List sponsored by Redwood Alliance List Address: RE

Re: [RE-wrenches] Getting ready for 2014 NEC rapid shut down with string inverters

2016-08-29 Thread Matt Partymiller
August, I am not answering your question but SMA tech support folk have specifically told me that putting our 600V jacketed control wire in the same EMT as the DC strings is leading to false arc fault trips. Matt On Mon, August 29, 2016 3:42 pm, August Goers wrote: > Hi Wrenches, > >

[RE-wrenches] Troubleshooting Stumper - Homerun Interference in Conduit/Inverter Turning Off/On Rapidly

2016-09-07 Thread Matt Partymiller
nch can provide technical support/advice. Thanks, Matt Matthew Partymiller Solar Energy Solutions LLC (877) 312-7456 m...@solar-energy-solutions.com ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change l

Re: [RE-wrenches] Troubleshooting Stumper - Homerun Interference in Conduit/Inverter Turning Off/On Rapidly

2016-09-07 Thread Matt Partymiller
itself and both strings work fine when not in conduit, I tend to believe them. I just don't appreciate how having 20' of undamaged homerun wire in conduit as opposed to free air can make an inverter stop operating. Thanks, Matt On Wed, September 7, 2016 8:58 pm, jay wrote: > hate

Re: [RE-wrenches] Troubleshooting Stumper - Resolved

2016-09-28 Thread Matt Partymiller
e that hopefully we will never encounter again. Thanks again, Matt On Wed, September 7, 2016 11:33 pm, Matthew Sirum wrote: > Greetings Matt, > > > I like the troubleshooting thoughts others have given. If all else > leaves you with the issue persisting I would also consider check

Re: [RE-wrenches] SMA Arc-Fault

2016-11-10 Thread Matt Partymiller
. If the arc fault is intermittent don't be afraid to conclude the problem is the inverter, not your install. Good luck. Matt On Thu, November 10, 2016 1:14 pm, Dave Tedeyan wrote: > Hi All, > > > Maybe someone will have some ideas for why a couple inverters keep arc > fault

Re: [RE-wrenches] Equipment for rapid shutdown NEC 690.12

2016-12-14 Thread Matt Partymiller
expensive than microinverters for systems over 4 kW though not necessarily less expensive than standard modules, strings inverters, and rapid disconnect enclosures. We have been trying to specify these module-integral products. Curious to hear how others are proceeding. Matt On Wed, December 14, 2016

Re: [RE-wrenches] SB -40 Wi-Fi

2016-12-19 Thread Matt Sherald
ting these jobs and I've found that over-the-phone troubleshooting with customers is pretty smooth. Anyway, I'd trade all the web connectivity and wifi capability for a similar built-in display on today's inverters. -Matt On Thu, Dec 15, 2016 at 2:39 PM, William Miller wrote: &g

[RE-wrenches] Hydro Off-grid Battery Sizing

2017-04-26 Thread Matt Sherald
presume that since the charging source is fairly consistent (day-to-day and hour-to-hour) that I could then reduce the days of autonomy to 2-days. I'm curious though if anyone has advice for sizing a battery bank for hydro. Any suggestions would be greatly appreciated. Thank you! -- Matt Sh

Re: [RE-wrenches] SMA and Tigo

2017-05-15 Thread Matt Partymiller
said, the ideal solution are module-integrated Tigos which a number of manufacturers make but which never seem to be available in the US. Trinasmarts for instance. Matt On Mon, May 15, 2017 9:48 am, Mark Frye wrote: > I was looking at the SMA web-site and it appears that the solution to > add

Re: [RE-wrenches] SMA and Tigo

2017-05-16 Thread Matt Partymiller
plug your Cloud Connect into a UPS you can also offer your customer a functioning SMA SPS. Moving forward it seems like SMA is integrating the Cloud Connect into the inverter which obviously prevents easily wiring it in to a UPS. Matt On Tue, May 16, 2017 3:53 pm, rh...@abundantsolar.com wrote

Re: [RE-wrenches] AC dump loads

2008-07-21 Thread Matt Tritt
Hey Dick, Mr. Berdner is no longer with SMA! Matt T Richard L Ratico wrote: Darryl, Check this out: http://download.sma.de/smaprosa/dateien/4439/SL6000-11-EE2807_Internet.pdf As far as I know, and I asked SMA directly 9 months ago, this is not presently available in the US. I wish it was

Re: [RE-wrenches] MX60 output trips with load

2008-08-04 Thread Matt Tritt
Phil, Have you clamped this circuit to see what the actual amps are? Matt T Phil Schneider wrote: Wrenches, We have an off-grid system (quad OB 3648s, two MX60s) with an MX60 output breaker that is tripping unexpectedly, and haven't been able to troubleshoot the problem. The MX60 ci

Re: [RE-wrenches] Inverter temp spec for cold regions

2008-08-31 Thread Matt Lafferty
n't pass muster These practices aren't good for the bottom line, no matter what kind of beans you're counting. Sunshine Wishes, Matt L _ From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of David Palumbo Sent: Thursday, August 28, 2008 5:57 AM To: RE-wrenches Subje

Re: [RE-wrenches] Followup to Surrette Battery Question

2008-09-06 Thread Matt Tritt
Jamie, And since the vast majority of groundwater and artificial lake water is very high in calcium chloride out here in the far West, using untreateted tap water is like murdering your batteries. Matt James Surrette wrote: Hi Matt et al, Sorry for missing my que to respond. As

Re: [RE-wrenches] Followup to Surrette Battery Question

2008-09-06 Thread Matt Tritt
U-Bet, Ray. It's not like the bloody things are cheap! =(:>/ Matt R. Walters wrote: Matt; I've used the watering systems for years as well, but never the tap connect. We have hard water here too, good to know that our distilled water mania is not in vain. Ray On Sep 4, 200

Re: [RE-wrenches] Followup to Surrette Battery Question

2008-09-08 Thread Matt Tritt
Chris, RO systems do NOT remove disolved minerals from water! Calcium carbonate is a disolved mineral, so I would suspect that by now you have a pretty good Ca buildup going. Matt Chris Schaefer wrote: Jamie, I suspect that most if not all Off-Grid clients have well water. My

Re: [RE-wrenches] Fake Email solar orders

2008-09-10 Thread Matt Tritt
Yes, we get these every day as well. If therre is anything in the message body about "credit", I file it in my Nigerian Opportunities folder. :-) Matt T Chris @ the Oasis wrote: Hi Folks: Because of our (cursedly) good web presence, we get perhaps 4 to 6 of these a day. When I

Re: [RE-wrenches] Fake Email solar orders

2008-09-11 Thread Matt Tritt
hings going on for the authorities to be able to get much of a handle on it. Matt T Joel Davidson wrote: Bob is right. Forward their emails to your state's attorney general. - Original Message - From: "boB Gudgel" <[EMAIL PROTECTED]> To: Sent: Thursday, September 11,

Re: [RE-wrenches] S5 Clamps

2008-09-18 Thread Matt Lafferty
slope roof, 85 mph basic, cat B exposure, good screws, high-quality roof profile, and a strong clip... I've seen it done. But it doesn't get near a 2X safety factor... Keep in mind the "S-5! WARNING... The S-5! clamp is a handy gadget for a great many uses, but will not perfor

Re: [RE-wrenches] Personal project: roofing colors

2008-09-24 Thread Matt Tritt
from becoming baked chicken - it worked really well. If you use a double roof as described, it doesn't matter what the roofing color is, as long as the eaves are open and you have a good ridge vent to allow proper circulation, and an air gap of about 3". The only issue being the added

Re: [RE-wrenches] Personal project: roofing colors

2008-09-24 Thread Matt Lafferty
shingle will reduce the heat that is absorbed by the roof covering, which reduces the amount of heat that transfers into the sheathing and attic space. Adequate attic ventilation is a larger issue. Same principle that Matt Tritt mentioned... Do NOT skimp on attic ventilation! Lotsa eave (low-side)

Re: [RE-wrenches] SMA Sunny Island

2008-10-13 Thread Matt Tritt
Nearly everyone is in San Diego this week. Matt T Glenn Burt wrote: Thanks Mike, They appear to be off today as I have called them a number of times and only get their voicemail machines... -Glenn -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of

Re: [RE-wrenches] crystalline VS uni-solar

2008-10-31 Thread Matt Tritt
this applies to entire strings as well. Because of this, they are a great choice for locations that might experience transient shading from utility poles, chimneys, trees, etc. Matt T jay peltz wrote: Hi Geoff, In regards to the performance between Unisolar and crystalline, there is a si

Re: [RE-wrenches] Pt valves as overheat control

2008-11-11 Thread Matt Tritt
ling! Matt Roy Butler wrote: Hi guys, I have been using the SS water loop in my Amish wood cookstove for my domestic hot water for 9 years now. My tank is a 40 gallon electric water heater (space saver unit) and is configured for thermo siphon operation. The P/T valve is all I have for protection a

Re: [RE-wrenches] Pt valves as overheat control

2008-11-11 Thread Matt Tritt
gular residential variety. Cheers, Matt Roy Butler wrote: Matt, Good suggestion.real hard water here. My water coil needs cleaning twice each heating seasona royal PITA. In addition to the weeping, the P/T valves also start leaking around the valve post too, so I figure I'm better off

Re: [RE-wrenches] tankless hot water and pumping question

2008-11-14 Thread Matt Tritt
big problem with the tankless heater - without a standing pilot - is that it might have the opportunity to freeze if not used for a significant period of time. Matt T Ian Woofenden wrote: Hi Todd and all, Since this is a renewable energy list, I think it's worth mentioning that install

Re: [RE-wrenches] tankless hot water and pumping question

2008-11-14 Thread Matt Tritt
n the marketing list. Matt Todd Cory wrote: I am working on a semi-volunteer job for a local non-profit. It is off grid with water being trucked in and stored in a ground level polyethylene tank. I need recommendations for: 1) A 24 volt DC pressure pump. This is a single residence so c

Re: [RE-wrenches] permit denied since no grid connection

2008-11-14 Thread Matt Lafferty
Source for the loads). Best of luck to the homeowner! Matt Lafferty ___ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Options & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

Re: [RE-wrenches] Golden Genesis question

2008-11-23 Thread Matt Tritt
Well Alan, all I remember about the Coors guys' efforts pretty much matches your description. Except that everyone called them Golden Genitals. ;-) Matt T Allan Sindelar wrote: Old time Wrenches, I need a history lesson, please... We removed a Y2K system installed by someone else, bef

Re: [RE-wrenches] More on AC coupling

2008-11-25 Thread Matt Tritt
rent). I know this doesn't answer your questions, but for similar applications in the future it would be good to take a close look at the SunnyIsland system. They're cool. Matt T Mark Dickson wrote: Hello Wrenches, On the heels of the previous thread: We just got finished instal

<    1   2   3   >