Jason,

This does not exactly answer your question but SMA Sunny Design indicates
a 70% power ratio (ac rating/dc wattage) as the threshold.  SMA has a
letter indicating installing below 70% will not invalidate warranty (as
long as other design practices like 600V DC are met).

I have not been pushing the boundaries much myself (waiting for others to
validate success) but I have not thought twice about approaching 80% power
ratio (which is similar to your example).  Now that panel prices are
cheaper this should be a best practice in many regions.  PVsyst production
simulation for this type of power ratio does not show significant loss.  I
have spoken with SMA and ABB about the matter and neither manufacturer has
stated that there would be reduced inverter life.  In many systems
approaching 70% power ratio can reduce cost per kWh assuming no additional
O&M costs.

Like you suggest, it would be nice to hear from more inverter
manufacturers on the subject.

Matt


Matthew Partymiller
Solar Energy Solutions LLC
(877) 312-7456
m...@solar-energy-solutions.com

On Mon, August 25, 2014 7:40 pm, Jason Szumlanski wrote:
> I had a tough customer recently that grilled me on how we can put a 270W
> solar module on a 215W inverter. Fortunately, Enphase has a wonderful
> white paper on the subject. However, it got me thinking... Enphase has
> demonstrated that higher output panels in many climates (hot SW Florida
> included) can benefit from modules that far exceed the inverter rating,
> and even exceed the inverter's "recommended input" rating. Enphase has
> shown that 270W+ modules can show energy harvest on the M215 where it
> makes sense to "oversize" the module.
>
> I also received a similar query from a rather uninformed plan reviewer in
>  an area AHJ along similar lines. Fortunately I was within the
> "recommended
> input" rating on the spec sheet of 270W with a 265W module, but I wonder
> what would happen if I had paired the M215 with a 280W module on my
> plans, which are becoming readily available now in 60 cell modules with
> 300W
> modules on the near horizon. I'm pretty sure my plan would have been
> kicked back for exceeding the manufacturer's recommendation.
>
> My question, which applies to string inverters and microinverters, is how
>  much is too much, what would happen if you paired an array that far
> exceeded the rating, and how do inverter manufacturers determine the
> recommended and/or maximum rating of the connected module or array? Also,
>  why do some manufacturers have a simple recommendation while others have
> a "maximum" rating?
>
>
>
> Jason Szumlanski
>
>
> ​Fafco Solar​ _______________________________________________
> List sponsored by Redwood Alliance
>
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.ht
> ml
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>





_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to