Best Regards,
John Berdner
General Manager, North America
[cid:image001.jpg@01CDFD3C.B73855C0]
SolarEdge Technologies, Inc.
3347 Gateway Boulevard, Fremont CA 94538 USA (*Please note of our new address.)
T: 510.498.3200, X 747
M: 530.277.4894
From: re-wrenches-boun...@lists.re-wrenches.org
[mai
tance between the
supply and the inverter to get it to track right.
Best Regards,
John Berdner
General Manager, North America
SolarEdge Technologies, Inc.
3347 Gateway Boulevard, Fremont CA 94538 USA (*Please note of our new address.)
T: 510.498.3200, X 747
M: 530.277.4894
-Original Me
SMA Sunny Island also does this but also discharges battery in parallel with
the generator to create a "virtual generator" that is larger than the actual
generator.
Just set the max generator current and it does the rest.
Best Regards,
John Berdner
General Manager, North America
[ci
typically while charging not when inverting and I set the
current limit so that I do not exceed ampacity of 2/0.
In my experience it takes >= 14kW generator to drive a pair of SI's to full
power while charging
Best Regards,
John Berdner
General Manager, North America
SolarEdge Technolo
,
John Berdner
General Manager, North America
[cid:image001.jpg@01CE0302.850C5940]
SolarEdge Technologies, Inc.
3347 Gateway Boulevard, Fremont CA 94538 USA (*Please note of our new address.)
T: 510.498.3200, X 747
M: 530.277.4894
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches
otor starting) this will not be
an issue.
48 kVA seems like one heck of a surge but, then again, I have not seen the
customer's home :)
Best Regards,
John Berdner
General Manager, North America
[cid:image001.jpg@01CE09F2.47122470]
SolarEdge Technologies, Inc.
3347 Gateway Boulevard, Fr
Light soaking = exposed to sunlight for some period of time in order to
complete light induced degradation (or apparently light induced enhancement).
Best Regards,
John Berdner
General Manager, North America
[cid:image001.jpg@01CE0E09.55EDDEB0]
SolarEdge Technologies, Inc.
3347 Gateway
suppliers of directional 2.4 Ghz antennas.
Here is a link to a 24 dB antenna from a local CA retail electronics house.
http://www.frys.com/product/7411495;jsessionid=5vsRnGBpd1iiZqjr7HmfLg__.node2?site=sr:SEARCH:MAIN_RSLT_PG
Best Regards,
John Berdner
General Manager, North America
SolarEdge
lator as a backup to conventional
charge control.
A simple on off relay to an AC hot water or space heater can dissipate a lot of
power relatively simply and inexpensively.
Best Regards,
John Berdner
General Manager, North America
SolarEdge Technologies, Inc.
3347 Gateway Boulevard, Fremont CA
Hi Jeremy,
The GJ series is a F-Frame Breaker. Rainshadow has distributed that breaker
for the past 15 years. We also stock the E-Frame, Q-Frame, and D-Frame
breakers that are commonly used in the solar industry. You can reach us at
Rainshadowsolar.comyou can write me atjohn@.
We
Larry:
The Code requires parallel breakers to be designed for this application
(internally ganged).
Just using a handle tie does not allow you to use the poles in parallel.
Best Regards,
John Berdner
General Manager, North America
SolarEdge Technologies, Inc.
3347 Gateway Boulevard, Fremont
-insulated ferrules from ferrules
direct.
http://www.ferrulesdirect.com/
Best Regards,
John Berdner
General Manager, North America
SolarEdge Technologies, Inc.
3347 Gateway Boulevard, Fremont CA 94538 USA (*Please note of our new address.)
T: 510.498.3200, X 747
M: 530.277.4894
From: re-wre
high current bus bar connections but I rarely see
them used on batteries.
Best Regards,
John Berdner
General Manager, North America
SolarEdge Technologies, Inc.
3347 Gateway Boulevard, Fremont CA 94538 USA (*Please note of our new address.)
T: 510.498.3200, X 747
M: 530.277.4894
From: re-wre
;
Best Regards,
John Berdner
General Manager, North America
SolarEdge Technologies, Inc.
3347 Gateway Boulevard, Fremont CA 94538 USA (*Please note of our new address.)
T: 510.498.3200, X 747
M: 530.277.4894
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-w
r than the
"standard sized wires"
Conduit is not an issue @ 1000V but switchgear, combiners and fuses are a bit
harder to find (but not impossible).
Not sure of the specifics of the system so it is hard to make detailed
recommendations.
Best Regards,
John Berdner
General Manager, Nort
000Vdc inverters are all available today.
I believe 600Vdc commercial and utility scale systems will rapidly become
uncompetitive and, within a few years, the exception rather than the rule.
Best Regards,
John Berdner
General Manager, North America
SolarEdge Technologies, Inc.
3347 Gateway B
ss washers in the current
path, i.e. not between the terminal and the cable ends.
It might seem ok during basic testing but during a long high current charge or
discharge the stainless washer will get very hot and bad things can happen.
Best Regards,
John Berdner
General Manager, North America
/0 each, etc.
There are some related requirements for conductor routing and equipment ground
conductors as well.
Best Regards,
John Berdner
General Manager, North America
SolarEdge Technologies, Inc.
3347 Gateway Boulevard, Fremont CA 94538 USA (*Please note of our new address.)
T: 510.498.3200
equivalency
to a single larger conductor.
Best Regards,
John Berdner
General Manager, North America
SolarEdge Technologies, Inc.
3347 Gateway Boulevard, Fremont CA 94538 USA (*Please note of our new address.)
T: 510.498.3200, X 747
M: 530.277.4894
From: re-wrenches-boun...@lists.re
Ray:
Adjustable ramp times are becoming a common requirement in EU countries with
high penetration PV.
We can adjust in the seconds to minutes (a few thousand seconds) time frame.
I can dig up details if relevant.
Best Regards,
John Berdner
General Manager, North America
SolarEdge
- (all ungrounded conductors).
I am pretty sure the SI is not internally bonded to ground.
This is normal in the rest of the world.
Mine are running with an ungrounded battery and there isolation between battery
and ground.
Best Regards,
John Berdner
General Manager, North America
SolarEdge
inside.
I have also used empty paint cans to good effect.
I put a card inside with my contact info on it so the guy who has to do it
years from now knows who to call for support.
Best Regards,
John Berdner
General Manager, North America
SolarEdge Technologies, Inc.
3347 Gateway Boulevard, Fremont
at string
will be lower.
Since the current changes as the modules move towards Voc you will need to
iterate the calculation a couple of times to get close to the actual operating
point and estimated reductions in energy yield.
Best Regards,
John Berdner
General Manager, North America
SolarEd
from the IV curves for each string.
A couple of iterations should get you really close to where the array will be
and let you estimate the reduction in energy yield compared to an optimal MPP
on each string or module.
Best Regards,
John Berdner
General Manager, North America
SolarEdge Technologies,
PV Watts does not account for shading / etc.
The NREL SAM model does a better job but is complex (as are most of the good
models).
We use PVSyst which has models for module level electronics.
Best Regards,
John Berdner
General Manager, North America
SolarEdge Technologies, Inc.
3347 Gateway
still doing fine.
John Blittersdorf
Central Vermont Solar & Wind
Sent from my iPhone
On May 29, 2013, at 9:08 AM, Hilton Dier III wrote:
> Greetings wrenches,
>
> I'm sure many of you have seen this article in the New York Times:
> http://www.nytimes.com/2013/
eaker.
--
John Stimac | Corvallis, OR
Renewable Energy Associates LLC
541-754-2001 Office/Fax
j...@renewableassociates.com
www.renewableassociates.com
-Original Message-
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Pekka
instrumentation and that it does carry current.
I don't believe there are any exceptions in code for downsizing your neutral
in regards to upsizing the conductors to account for voltage drop but I
could be wrong.
--
John Stimac | Corvallis, OR
Renewable Energy Associates LLC
541-754
nd fast service. P
John
Cvsolar.
Sent from my iPhone
On Jul 7, 2013, at 9:58 AM, jay peltz wrote:
> Hi Kirk
>
> One trick I learned from my generator guy is to hook up the remote start to
> the manual on position
> This bypass's the auto position and the extra load on th
have had Many service calls with
premature bad cells in Trojans, especially the high performance models.
John Blittersdorf
CV Solar
Sent from my iPhone
On Jul 15, 2013, at 9:58 PM, Drake wrote:
> Hello Wrenches,
>
> A 1 1/2 year old bank of Trojan L-16s had a battery with a dea
ild, never started up by me. The wireless display has
only been used briefly in my shop.
Contact me off-list if you have any interest.
Regards,
John Raynes
RE Solar
Torrey UT
435-425-2110
___
List sponsored by Home Power magazine
RE-wrenche
will be small, probably about 10 a/h and will be used for a
transponder.
Can anyone enlighten me about the feasibility of this application.
cheers,
John Veix, N.Z.___
of bad
grammar, or "Dear Sir/Ma", almost as if to cue any savvy dealer, whom
they would not want to deal with. They're only trolling for rank
newbies, I would think.
John Raynes
RE Solar
Torrey, UT
At 01:00 PM 9/10/2008, you wrote:
I am wondering if any of you are receiving fak
tuff to wire in but that should always work as a last resort.
John Raynes
RE Solar
At 02:46 PM 10/31/2008, you wrote:
Hi boB,
The Kohler RES is is a very simple 2 wire start as are all of the
Kohler's that I know of. These Kohler's have worked very easily with
OutBack and Trace inv
, although one advantage of concrete is
you have lots of time to tweak the post alignments if necessary while
the concrete sets. I would think a helical screw would be prone to
walking just a little, unless the drive apparatus is extremely well-anchored.
John Raynes
RE Solar
Torrey, UT
At 08:45
have two separate PDF rendering drivers, but they
do. Anyway, I've found that often, when I have some problem or
another with the output of PDF writer, that Distiller does a better
job of rendering. It's worth a try if it shows up in your print driver list.
John Raynes
RE Solar
ay be well within specified
load limits, count on things not going well.
I'm generally satisfied with the Magnum MS4448, but this is one the
two key shortcomings that I see with the product. The other is the
idle power draw when not in search.
John Raynes
RE Solar
Torrey, UT
At 11:16 A
getting more difficult due to lack of parts. All my scrapped
units due to tower crashes are mostly all cannibalized. Still close to 30
still running. Wind turbines do work well in hot dry winds which seem to be
increasing these days.
John Blittersdorf
CV Wind Service
On Sun, Sep 13, 2020 at 4:28
e I have had to talk the
renters through manually starting a generator or rebooting a battery,
saving me a 3 hour round trip service call.
John Blittersdorf
NABCEP Certified Solar PV Installer™
CV Wind Service (and solar)
200 West Road
N Chittenden, VT 05763
On Mon, Oct 12, 2020 at 11:01 PM
or higher amperage controller.
John Blittersdorf
On Sat, Oct 17, 2020 at 10:11 AM Bradley Bassett
wrote:
> I think there is a jumper in the FM100 that will allow the Mate3s to
> communicate with it. I don't remember off hand where it is and am not at a
> computer with that info,
Allan,
Zonna Energy stocks most Outback parts.
John Blittersdorf
CV Wind Service
On Wed, Nov 11, 2020 at 6:10 PM Sindelar Solar
wrote:
> Esteemed Wrenches:
>
> Where can I purchase a replacement cooling fan for an older Outback MX-60
> controller?
>
> Thanks, Allan
>
>
outback
devices such as an Iota charger or wind input and install another TriMetric
to parse out that info for the customer in big red numbers. The customer
will see net on the TriMetric and you can see the solar detail on the Mate
3.
John Blittersdorf
NABCEP Certified Solar PV Installer™
CV Wind
in
dark places and has a sharper screen showing the waveform than the last one
I had.
John Blittersdorf
CV Wind Service
On Sun, Jan 24, 2021 at 5:33 PM jay wrote:
> HI All,
>
> Someone just told me about some small inexpensive Oscope.
>
> I’m wondering if anyone has any recommen
exposed AC board, and the 8 screws holding the case
to the inverter base removed and lift the case up part way until you can
see the fan wire.
John Blittersdorf
CV Wind Service
On Sun, Feb 14, 2021 at 8:15 PM Ron Young wrote:
> Hi Wrenches, I have a client with an Outback GVFX3524 inverter t
Chad, what ballpark price for the Dewalt crimped. Does it handle 4/0 heavy
duty lugs. I’m getting too old for my hand crumper.
John Blittersdorf
On Sun, Feb 21, 2021 at 7:05 PM Chad Waits
wrote:
> We bought the DeWalt version not too long ago. Makes great crimps and much
> easier t
. OpticRE works
great for monitoring.
John Blittersdorf
On Wed, Mar 3, 2021 at 1:19 AM William Miller
wrote:
> Friends:
>
>
>
> I am getting asked more often to provide design for grid-tied battery
> backup systems. I generally try to talk clients out of battery backup
> becau
g them. It is still running fine at my
customers place.
What I really want is for the PIKA to be put back in production. It was
a perfect off grid supplement with no issues that I could see.
John Blittersdorf
NABCEP Certified Solar PV Installer™
CV Wind Service (and solar)
200 West Ro
t like the water dripping between the panels when it rained
and had an orphan 245 so order the Genesun which lives under the seat next
to the batteries.
John Blittersdorf
.
On Mon, Apr 12, 2021 at 1:43 PM Jason Szumlanski <
ja...@floridasolardesigngroup.com> wrote:
> I want to charge a
party auto start module?
John Blittersdorf
___
List sponsored by Redwood Alliance
Pay optional member dues here: http://re-wrenches.org
List Address: RE-wrenches@lists.re-wrenches.org
Change listserver email address & settings:
http://list
Dave,
An Alternate solution might be to find two good used VFX3524's. All
circuit boards are available from Zonna if they need repair. I have one if
you could find another somewhere.
Contact me off list if interested.
John Blittersdorf
NABCEP Certified Solar PV Installer™
CV Wind Se
be off when
I arrived and it wasn’t always the same one. When one shut off due to over
voltage, the voltage would drop and the second one would stay on. Both had
the exact same upper voltage limit.
John B
On Thu, May 20, 2021 at 3:23 PM August Goers wrote:
> Hi James -
>
> Is there a
.
Owner is sure that this loose box will be found by the inspector and jinx
the sale. Anybody know of a super adhesive that will hold up?
John Blittersdorf
___
List sponsored by Redwood Alliance
Pay optional member dues here: http://re-wrenches.org
List
Jay,
Lorentz still has two people in texas. I can’t find an active dealer but
they do provide excellent tech support 24/7. I have to buy from a dealer
but the ones that I have called only get one if specified on a new well
they are drilling. They didn’t know much about them.
John B
On Tue
BMS which I carefully installed and
it has worked fine since. Had I seen this photo first, I may have not been
so eager to see the inside of that battery.
John Blittersdorf
On Wed, Jun 16, 2021 at 6:13 PM Chris Worcester
wrote:
> https://www.redwoodmaterials.com/recyclewithus
> these fol
I have a Honda 3000i for my off grid system that shows 84 vac output. I
suspect that the inverter is failing. Just checking to see if any of you
have seen this failure mode?
John Blittersdorf
___
List sponsored by Redwood Alliance
Pay optional member
You may have alteady checked this but make sure AGS is enabled. I had that
problem just this morning and after checking continuity of the wires again
noticed that AGS was disabled.
John Blittersdorf
On Tue, Sep 14, 2021 at 1:55 PM Michael Morningstar
wrote:
> Wrenches,
>
> I’ve got
.
John B
On Tue, Nov 2, 2021 at 9:41 PM jay wrote:
> You can find the temperature compensation voltage in the battery hot
> button.
> It might be a bad temp sensor
>
> jay
>
> peltz power
>
> On Nov 2, 2021, at 2:46 PM, Jason Szumlanski <
> ja...@floridasolarde
If the need is for a second VFX inverter to add to an existing one to
double charge rate for a new LiFePO battery, then it is worth 3 Iota
chargers ~ $1000.
On Saturday, December 11, 2021, Jay wrote:
> Hi Drake
>
> Just like with Allan’s remote, I couldn’t find any used ones on line to
> even
or last one was?
John Blittersdorf
___
List sponsored by Redwood Alliance
Pay optional member dues here: http://re-wrenches.org
List Address: RE-wrenches@lists.re-wrenches.org
Change listserver email address & settings:
http://lists.re-wrenches
Allan,
The new VFXR has updatable firmware through the MATE3 but the old series
has firmware on the control board but not updatable. I have run into this
before but lucked out that both older inverters had the same firmware.
John
On Sun, Mar 20, 2022 at 10:55 AM Sindelar Solar
wrote
20, 2022 at 10:55 AM Sindelar Solar
> wrote:
>
>> John,
>> I've never faced your situation so can't address it directly. However, I
>> don't think matching firmware requires replacing a control board. Can't you
>> just update the firmware to the la
>
> The system is 120v only from the generator and the house is 120 only.
>
John
> ___
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches@lists
my Viasat and need internet at the guest cabin.
John Blittersdorf
On Mon, Mar 14, 2022 at 2:52 PM Dan Fink wrote:
> I concur with Luke Christy below - I have had great success with Ubiquiti
> wireless bridges. If the line of sight is not completely clear, their 2 and
> 5gHz dish
There used to be a chart – supplied years ago – that listed all the metals and
showed what was compatible – or not compatible with different metals.
Sadly I can’t seem to find it, but one of the older guys might still have a
copy of that chart.
Cheers – John Veix, N.Z.
From: RE-wrenches
Marco,
Try Hialeah Meter in FL:
http://www.hialeahmeter.com/info.html
'Call us toll free at 800-654-0821. Fax us at 305-887-6542. Email us at
sa...@hialeahmeter.com'
John McNicholas
NABCEP Certified Solar PV Installer ™
Key Power Services, Inc.
On Jul 27, 2010, at 5:39 PM, Marco M
Coming to a hardware store near you.
http://www.cnn.com/2010/TECH/innovation/08/17/plug.in.solar.energy/index.html?hpt=C2
John McNicholas
NABCEP Certified Solar PV Installer ™
Key Power Services, Inc.
___
List sponsored by Home Power magazine
We have been using a digital unit for a few years - Sper Scientific 300055
Pocket Digital Refractometer - expensive ($300+), but it appears to be very
accurate. has built-in temperature compensation.
John McNicholas
NABCEP Certified Solar PV Installer ™
Key Power Services, Inc.
Begin
I have the 180s on my own home, good production, flimsy frames. But
also concerned about financial strength - seems MA is propping them up:
http://www.boston.com/business/technology/articles/2009/10/17/mass_has_bet_millions_on_evergreen_solar_which_is_now_facing_financial_uncertainty/
John
Also try:
Hialeah Meter Co
www.hialeahmeter.com
450 W 28th St # 4
Hialeah, FL 33010-1317
(305) 887-6542
John
Begin forwarded message:
From: "Glenn Burt"
Date: November 19, 2009 7:32:15 PM EST
To: "'RE-wrenches'"
Subject: Re: [RE-wrenches] 240V - 3 Phase
This is very common down here on the coast with the SMAs for us - two inverters
we fired up yesterday took 20 and 27 minutes respectively to clear the GFDI
error. After that, no problems we use the time to eat lunch
John
NABCEP Certified Solar PV Installer ™
President
Key Power Services
We have been working on a similar project - we picked up 10,000 solar pathway
lights on the cheap and have removed the little modules. been a bit
tedious, but should be well worth the savings
John McNicholas
NABCEP Certified Solar PV Installer ™
Key Power Services, Inc.
Begin forwarded
d he was less than honest with me'. I would like to see #2 replaced with something more upbeat. 'Were you happy with the installation process and do you feel that the overall experience reflected the efforts of a true professional in this field?'John
John McNicholasNABCEP Certifie
On the topic of AC modules - has anyone installed the Westinghouse
Instant-Connect AC modules that have the
inter-module cable connectors built-in to the frames? Feedback?
Thanks,
John McNicholas
NABCEP Certified Solar PV Installer ™
Key Power Services
Begin forwarded message:
From: Jason
sites - when the
batteries run down, the generator runs, how loads affect both; we can get
emails and/or text messages to keep track of generator run time (think failure
to auto-stop), etc.
John McNicholas
From: Chris Mason
Date: December 27, 2012 4:16:13 PM EST
To: RE-wrenches
Subject
screwed up. They also have
a good video to walk you through it if you haven't done one before.
John McNicholas
NABCEP Certified PV Installation Professional™
Key Power Services, Inc.
160 Tahiti Street
Naples, FL 34113
(239) 290-6040
(305) 359-9590 fax
FL Lic. CVC56676
keypower
pathway without having to change any charger settings in
the inverter.
John B
On Fri, Jun 10, 2022 at 7:08 AM Matt Sherald via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:
> Hello Wrenches,
>
> I've got customers with an ailing battery bank and I'm working to s
Awhile back there was a thread about a micro inverter that could be used to
connect directly to an electric hot water heater. Can someone steer me to
that thread or the inverter manufacturer?
John Blittersdorf
___
List sponsored by Redwood Alliance
Glen, You are correct. It is an electric tank water heater according to
Home Depot.
Thanks for Cybo.
John
On Tue, Jun 28, 2022 at 7:23 PM Glenn Burt wrote:
> Hi John,
>
> Cybo inverters.
>
> You hit a pet peeve in your post and I must comment as we really need to
> be lead
, nice comment that we don't have any reason to charge
full now.
John Blittersdorf
On Sat, Nov 19, 2022 at 1:10 PM Dana Orzel via RE-wrenches
wrote:
>
> Another issue is what charge controller are you using? I know for me with
> Outback products I’ve had to switch from an FM 80 to t
Todd has the right answer. The AC2 input will not sell to the grid as you
would not want to sell to the generator.
On Mon, Dec 19, 2022 at 12:21 PM Foxfire Energy via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:
> I’m thinking the simple fix is to just make sure the breaker between the
).
John
On Tue, Jan 3, 2023 at 9:16 AM Jay via RE-wrenches
wrote:
>
> Has anyone had a vfx sort of not pay attention to it charging current
> settings,
>
> I have a customer who’s older vfx will do the following
>
> Settings are 5 amps ac, 5 amp ac charge
>
> It
I would vote for Outback FX series. FIELD REPAIRABLE. Only down side
is if he is using the multiple relays for a 3 wire start generator.
John
On Tue, Jan 3, 2023 at 11:42 AM Jerry Shafer via RE-wrenches
wrote:
>
> Wrenches, Chris
> I would only look at outback, Date available an
It all comes back to voltage.Learned that with the TriMetric a long
time ago. I have a dozen eVaults out there, mostly singles but one set up
with 3, all working just fine using voltage control.
John Blittersdorf
On Thu, Feb 9, 2023 at 8:57 PM Howie Michaelson via RE-wrenches <
re-wrenc
Howie,
I use the QO612 small breaker box with two double pole breakers and the
QO2DTI toggle.
John Blittersdorf
On Thu, Mar 2, 2023 at 8:11 PM Howie Michaelson via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:
> Does anyone know of any bypass switch/breaker setup for
many years.
JohnBlittersdorf
CV Wind Service
John Blittersdorf
CV Wind Service.
On Sun, Mar 26, 2023 at 1:18 PM Kirpal via RE-wrenches
wrote:
>
> Greetings folks!
> Anybody have a recommendation for a small decent quality wind turbine
> manufacturer with decent quality equipment? We had a small SW
inverter got to be too much trouble. I ran all with
lithium settings but I’m retiring the L16s and putting in a second eFlex.
2 eFlex or 3 Simpliphis do a great job replacing the 8. The 3 simpliphis
will be leaving for their summer home at a fishing club. Hi
John B
On Thu, Apr 6, 2023 at 11:50 AM
On Mon, Apr 10, 2023 at 2:14 PM Kienan Maxfield via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:
> Here’s my two cents,
>
> If you do end up putting in two new batteries, and you leave everything
> wired the way it is, you’d better really watch the rest of the batteries
> that are in th
that the owner is willing to sell. I can't
wait to get it back on my tower!
Specs are still found on NAZ website. Google PIKA T701
John Blittersdorf
On Thu, Aug 17, 2023 at 12:04 PM Jay via RE-wrenches
wrote:
>
> Yeah just kinda of sad they are gone.
>
> Like others, a frie
m Told them to get the original installing company to check it out.
I'm about to rip my problem child off the wall and put in a Radian. I've
installed dozens with only 2 needing any attention with power supply board
and a power module, all quick fixes.
John Blittersdorf
On Fri, Oct 13,
Chris,
I have a shelf full. Contact me off list.
John Blittersdorf
NABCEP Certified Solar PV Installer™
CV Wind Service (and solar)
200 West Road
N Chittenden, VT 05763
802-770-8625
www.offgridvermont.com
john.blittersd...@gmail.com
On Wed, Nov 8, 2023 at 4:47 PM Chris Schaefer via
good Mate3. Works perfectly giving us AGS start and stop
voltage settings and basic battery voltage graph. I would be interested in
other ways to remote control generators with non Outback inverters. FlexNet
DC?
John Blittersdorf
___
List sponsored by
need to placate clients, the days of solar martyrdom needs to end! "
Being in the darkest time of year, I spend way too much time placating.
John Blittersdorf
On Mon, Dec 11, 2023 at 9:56 AM AE Solar via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:
> Wrenches
> W
Thankyou Kirk.
On Mon, Dec 18, 2023 at 6:26 PM Kirk Herander via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:
> use the full URL, meaning www.opticsre.com, not just opticsre.com. It
> works fine for me this way., just discovered this. Somehow related to their
> recent upgrade.
>
> On M
t but my wife always
keeps a hawk eye on the Trimetric as we manually start our backup
generator. The mid range voltages are
plus or minus 20% but at the low end start to change more quickly with
about a 3 hour window to start the generator before LBCO.
John Blittersdorf
offgridvermont.com
On Sun
too hard.
I
John Blittersdorf
NABCEP Certified Solar PV Installer™
CV Wind Service (and solar)
200 West Road
N Chittenden, VT 05763
802-770-8625
www.offgridvermont.com
On Wed, Feb 7, 2024 at 3:56 PM Chris Daum via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:
> Hi fol
Only one failure an it was the Atkinson unit.
John Blittersdorf
NABCEP Certified Solar PV Installer™
CV Wind Service (and solar)
200 West Road
N Chittenden, VT 05763
802-770-8625
www.offgridvermont.com
On Fri, Feb 9, 2024 at 7:13 PM Roy Butler via RE-wrenches <
re-wrenches@lists.re-wrench
from very high lead acid
settings on the Outback Radian when installing the Fortress batteries.
They nicely shut down at 60 volts and turned back on after I stopped the
overcharge.
John Blittersdorf
On Thu, Feb 8, 2024 at 12:17 AM Ray Walters via RE-wrenches <
re-wrenches@lists.re-wrenches.or
e of their transmitter data. Their load is about 300
watts 24/7 with it dropping off a little late at night.
It is a repeater site for business band radios, police, emergency etc.
John Blittersdorf
CV Wind Service.
On Wed, Feb 21, 2024 at 2:02 PM Mark Frye via RE-wrenches <
re-wrenches@lists.re
a replacement
> for the old Bergey XL1 to offer clients.
>
> Thanks,
>
> Ray Walters
> Remote Solar
> On 2/21/2024 7:20 PM, John Blittersdorf via RE-wrenches wrote:
>
> As far as wind is concerned, I recommend SuperWind, made in Germany. It
> is well built and designe
I just tried to get Outback tech support and the message was if the product
is under warranty, stay on the line for next available rep. If not
warranty. contact Zonna Energy or NAZ Solar !
On Wed, Feb 21, 2024 at 10:14 PM Bradley Bassett via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wr