I have noticed on several Magnum Installations that the charge rate is low compared to the inverter rated output. Typically I would assume the charge rate should be up to about 70 to 80 % of the inverter capacity, but I am getting only about 1400 watts (26 amps DC) from it with a 14kw generator. Is there some setting I am missing that would limit it other than the charge %. I know of one system where they added a 2nd Magnum inverter and then had problems with them working together consistently. I have used the 8 kilowatt Radians for any off grid with significant loads and battery capacity and easily get 6000 charging watts from a large generator. I also needed remote control of the generator (Generac EcoGen 15 kw so a quick inexpensive but clunky solution I came up with was to add an old (2003 vintage) used MX-60 to the system purely to use the Aux relay with a used HUB and old but good Mate3. Works perfectly giving us AGS start and stop voltage settings and basic battery voltage graph. I would be interested in other ways to remote control generators with non Outback inverters. FlexNet DC?
John Blittersdorf
_______________________________________________ List sponsored by Redwood Alliance Pay optional member dues here: http://re-wrenches.org List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org There are two list archives for searching. When one doesn't work, try the other: https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/ http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: http://www.re-wrenches.org/etiquette.htm Check out or update participant bios: http://www.members.re-wrenches.org