work will seek to add the C10 license, as would I. Until then, I will join CalSSA in advocating for the status quo.Thanks for sharing, Jason. Peter, you can reach me through Byers Solar, we're a CalSSA member and C46 contractor (under my license).Eric StikesSunHar
California Wrenchers,I have a C-46. A company with which I subcontract has a C-10 but uses non-licensed, non-journeyman, non-apprenticed laborers to complete all phases of their PV installations, including the final tie-in and commissioning. These guys are working under no supervision. I have the u
Anyone have a recommendation for a PV module that doubles as a skylight, i.e.,
has a clear backsheet? I have a client who would like to explore the option of
putting solar on his greenhouse. I mentioned that the sunlight transmission
would be significantly reduced but he saw it in action somewhe
ently we have projects in Rwanda, Ecuador,
India, and here in the USA. We donate materials and labor to communities,
schools, medical facilities, and tribal nations. Help us help those in need.
Don't throw it away, recycle it!
Eric Stikes
Founding Director
Good Sun Solar, A CA non-p
ing for a home for the old 2kW Sharps, we have a
project ready to go. Thanks!
Eric Stikes
Founding Director & CEO
Good Sun Solar, A CA non-profit corp.
www.goodsun.life
(530)798-3738
- Original Message - Subject: Old or Damaged Modules
From: "Garrison Riegel"
Date
urvey with a P.G. stamp?
What is the AHJ going to be looking for? As always, I appreciate any input!
Eric Stikes
Founding Director & CEO
Good Sun Solar, A CA non-profit corp.
www.goodsun.life
(530)798-3738
___
List sponsored by Redwood Alliance
Lis
(conductor ampacity aside).
Cheers,
Eric Stikes
Founding Director & CEO
Good Sun Solar, A CA non-profit corp.
www.goodsun.life
(530)798-3738
___
List sponsored by Redwood Alliance
List Address: RE-wrenches@lists.re-wrenches.org
Change listserver e
Picking up this issue after some time has passed...
Has anyone found, or received any news on, a replacement for the Solmetric
SunEye other than Pathfinder?
Eric Stikes
Founding Director & CEO
Good Sun Solar, A CA non-profit corp.
www.goodsun.life
(530)798-3738
- Original Mes
believe you made the
right call by refusing to do the work as you may be liable in the (however
unlikely) event of catastrophic failure at the mod in question. The array won't
look so nice anymore if half of it is melted and charred. Play it safe. Get rid
of it.
Eric Stikes
Founding Dir
the
autotransformer continuous per-phase current rating or
42 percent of the continuous-current rating of any seriesconnected
devices in the autotransformer neutral connection.
Eric Stikes
Founding Director & CEO
Good Sun Solar, A CA non-profit corp.
www.goo
ing a max OCPD
size, right?...unless I am missing something.
I won't blame you if you decide you have more important things to attend than
educating me on the nuances of the NEC. I'm still learning and I do greatly
appreciate your insight!
Eric
- Original Message ---
rning, always learning,
Eric Stikes
Founding Director & CEO
Good Sun Solar, A CA non-profit corp.
www.goodsun.life
(530)798-3738
- Original Message - Subject: Re: [RE-wrenches] Undercurrent
Protection?
From: e...@harvesthesun.com
Date: 11/1/16 11:01 am
To: "RE-wren
x27;s assessment regarding limited ampacity of the
6AWG Romex. Can someone illuminate this issue for me as to whether or not NM
cable is rated at 90 degrees AND therefore a 6AWG conductor in NM cable would
have a 75A rating?
Cheers,
Eric
SunHarvest
___
seeing this? Wondering if this is an
industry-wide issue regarding a Polaris manufacturing defect or if we're still
in the realm of isolated flukes.
Eric
SunHarvest
(530) 559-5023
___
List sponsored by Redwood Alliance
List Address: RE-wre
gate the Miller method. William has never led me astray!
Eric Stikes
SunHarvest
- Original Message - Subject: Re: [RE-wrenches] Polaris gone
bad?
From: "William Miller"
Date: 4/8/17 2:48 pm
To: "RE-wrenches"
Wrenches:
I am wondering why the proliferat
w/ no UL)...? I
am on a serious hunt here and i'm coming up short. Are there NO glass on
glass modules that are UL or similarly listed besides the Sanyos and the
SiE's? I even have the feelers out in Germany!
Thanks,
--
Eric Thomas
Solar Design Tech
Solar Epiphany LLC
Hello,
We are bidding an 8kW grid tied PV system that will interconnect with a
"split panel". The panel has a main lug on the top portion and branch
circuits on the lower portion. Does anyone have experience with backfeedig
these panels? What's the best method?
Thanks,
Er
h the effects on producion
from the thin shadow cast by the powerline?
Thanks
Eric Thomas
Solar Epiphany LLC
Seattle
(206)919-3014
___
List sponsored by Home Power magazine
List Address: RE-wrenches@lists.re-wrenches.org
Options & settings:
http:/
Or am I just up too late reading code?
Thanks for being a resource.
--
Eric Thomas
Solar Epiphany LLC
(206) 919-3014
www.solarepiphany.com
___
List sponsored by Home Power magazine
List Address: RE-wrenches@lists.re-wrenches.org
Options &
itions. My biggest concern is the four independent strings shorting
together somehow. I guess technically 4 strings of 8A for a total of 32A
doesn't exceed the ampacity of 10AWG XHHW-2until you derate it for roof
temps.
So whats the consensus?
--
Eric Thomas
Solar Epiphany LLC
ut of
SolaDeck on roof two, grab 3 more micros, back into SolaDeck, into attic for
home run. The whip from the SolDeck to the last 3 micros needs to be male...
any suggestions? EnPhase does not want us to cut an extension that has
connectors on both ends...
Thanks,
Eric Thomas
Solar Epiphany
Se
parallel sub arrays.
Eric
___
List sponsored by Home Power magazine
List Address: RE-wrenches@lists.re-wrenches.org
Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://lists.re-wrenches
our Subject line so it is more specific
> than "Re: Contents of RE-wrenches digest..."
>
>
> When responding to posts within the Digest, be sure to restore the
Subject: line to the original, and please edit out any extraneous lines from
the quoted message.
>
>
> Today
s far as warranty..I
think they will last the test of time.
Eric Thomas
Solar Epiphany
(206)919-3014
www.solarepiphany.com
___
List sponsored by Home Power magazine
List Address: RE-wrenches@lists.re-wrenches.org
Options & settings:
http:/
Generator so the power should be fairly clean. Any experiences are
appreciated.
Take Care,
Eric Thomas
Solar Epiphany LLC
(206) 919-3014
www.solarepiphany.com
___
List sponsored by Home Power magazine
List Address: RE-wrenches@lists.re-wrenches.or
!
--
Eric Thomas
Solar Epiphany LLC
(206) 919-3014
www.solarepiphany.com
___
List sponsored by Home Power magazine
List Address: RE-wrenches@lists.re-wrenches.org
Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches
be helpful.
Thanks,
Eric Thomas
Solar Epiphany
Seattle
NABCEP Certified PV
WA Electrical Contractor SOLAREL911NR
___
List sponsored by Home Power magazine
List Address: RE-wrenches@lists.re-wrenches.org
Options & settings:
http://lists.re-wrenches.o
t have a three phase inverter option due to Made in WA
req's.
Thanks!
Eric Thomas
Solar Epiphany LLC
___
List sponsored by Home Power magazine
List Address: RE-wrenches@lists.re-wrenches.org
Options & settings:
http://lists.re-wrenches.o
if im
barking up the wrong tree ir not.
Thanks for the insight.
Eric Thomas
Founder
Solar Epiphany LLC
NABCEP Certified PV Installer
WA Electrical Contractor # SOLAREL911NR
___
List sponsored by Home Power magazine
List Address: RE-wrenches@lists.re-wrenche
? I've
searched around on the internet but I can't find any good information.
Eric Youngren
Rainshadow Solar
Island Energy Systems
Orcas Island, WA
capillary.systems
___
List sponsored by Redwood Alliance
List Address: RE-wrenches@lists.re-wr
nd 3-pole breakers but everything is pretty much 1-phase I believe. I'm
wondering if I should consider reconfiguring the system with 1-Ph inverters
tied in to only 2 of the utility legs. I asked SolarEdge weeks ago but
getting nothing from them. Any thoughts? Thanks!
Eric Stikes
SunHarvest Sola
shuts down.
Has any of you done this kind of thing? Any suggestions on equipment or
best practices? THANKS!
Eric Youngren
___
List sponsored by Redwood Alliance
List Address: RE-wrenches@lists.re-wrenches.org
Change listserver email address &
loads directly (and charges the battery),
there are no pass-through loads on the inverter output.
On Wed, May 23, 2018 at 12:16 PM William Miller
wrote:
> Eric:
>
> Any reason not putting these loads on a gen-fed panel?
>
> William
>
> > On May 23, 2018, at 12:28 PM
tern U.S. but if you look for them, you're likely to find others like us
closer to you. Organizations like RecyclePV are focused more on recycling
for mods that are not reusable. There are options. So please be responsible
and do not throw used mods in the landfill.
Thanks for giving me a soapbox
of in Myanmar.
All the best
Eric
On Sun, May 26, 2019 at 5:22 AM Kirk Herander wrote:
> Hi All,
>
> I have a premium client I’ve done multiple systems for over the years with
> multiple inverter monitoring platforms (SolarEdge, Enphase, Fronius,
> Outback, etc.). I have b
32 V.
The problem is when Equalize is enabled, the system goes through Bulk and
Absorption just fine. However, when it switches to Equalize it doesn't
actually equalize. What I observed was the voltage actually decreased to
0.5 V below the Absorption Voltage setting.
Eric Smiley, P.Eng.
er to compensate clients and installers who have
wasted far too much time and money trying to make it work as promised.
Eric Smiley, P.Eng.
Project Manager, North Island
E: e...@vecoop.ca
T: 1-888-386-0116 ext 702 (toll free)
C: 250-703-6004
W: viridianenergy.ca <http://www.viridiane
s
our Canadian EC requires) which is hundreds of feet away. In this
circumstance but without back-up, we would usually just use an AC
disconnect near the meter to initiate RS, but now we're facing the prospect
of running a new control circuit all the way back to the pole or requesting
a varia
I have been using DraftSight. It's an AutoCAD LT clone. Handy for when
clients that send me AutoCAD (dwg) files.
However, they have brought out a 3D version.
Eric Smiley, P.Eng.
Project Manager, North Island
E: e...@vecoop.ca
T: 1-888-386-0116 ext 702 (toll free)
C: 250-703-60
Draftsight is pretty good if you're familiar with AutoCad. The basic
version is an autocad Lt clone.
Eric Smiley, P.Eng.
Project Manager, North Island
E: e...@vecoop.ca
T: 1-888-386-0116 ext 702 (toll free)
C: 250-703-6004
W: viridianenergy.ca
On Thu., Jun. 18, 2020, 4:14 p.m. Jamie R
I'm looking for a Watt-hour meter that is hard-wired (not a Kill-O-Watt
plugin) and resembles a kW-h utility meter for a trade-show display.
Eric R. Andrews
NABCEP Certified PV Installer
Eco Solar, Inc.
www.ecosolarnow.com
PO Box 5194
Klamath Falls, OR 97601
541-281-8252 cell
541-273
I'm searching for a WATT-hour meter.. Not a "KILOWATT-hour" meter. So that
folks can see the meter spin or numbers turn when running small loads. ie.
CFL bulb vs. incandescent bulb. demo purposes.
Thanks all!
Eric R. Andrews
___
Li
orth
the money? Do they work?Put it at the PV combiner or at the
controller?
Sorry for the long-winded post.I'd appreciate any thoughts y'all might
have on anything I've mentioned here, or anything else that comes to mind.
Thanks!
best energy,
Eric
--
Eric Youngren
NABCEP
over X size. The IRS Q
& A folks aren't giving a clear answer. The only time we normally use a PE
is for structural (design load calcs.) purposes. These are not large
utility sized systems.
Eric R. Andrews
NABCEP Certified PV Installer
Eco Solar, Inc.
www.ecosolarnow.com
PO
We have found that using white USE wire is very helpful, time saving and
reduces any potential confusion for DC string wiring. Platt Electric supply
carries.
Eric R. Andrews
Klamath Falls, OR 97601
>>>
Wrenches,
Has anyone located a source of wrap-around labels, to label + and -
been called in
AFTER the homeowner's "buddy" helped him cobble together a bunch of parts
and "everything worked great, until"Any pictures or ideas or leads
on where to find such a gallery online would be great. Thanks!
Best Energy,
Eric
--
Eric Youngren
Is
Nick-
Just downsize the main breaker. For example, a 200 amp panel w/ a 200 amp main
breaker could be reduced to a 150 amp main breaker to allow for more solar to
be connected. You need to calculate for the 120% rule.
Eric R. Andrews
NABCEP Certified PV Installer
te being brought into the situation
before work has been done.
Also, if the service panel is rated for 100 amps then you can legally
interconnect 20 x .8 = 16.7 amps per the 120% rule. 30A and 40A breakers?
Eric R. Andrews
NABCEP Certified PV Installer
>>
>>
Downsize the main
eners w/ washer.
Your engineer can verity the fastening system/screw length. Overall, I like
the product.
Eric R. Andrews
NABCEP Certified PV Installer
Eco Solar, Inc.
www.ecosolarnow.com
PO Box 5194
Klamath Falls, OR 97601
541-281-8252 cell
541-273-3200 office
<mailto:e...@ecosola
Wrenches,
I reeaally need to find a bead on BP SX3190B Modules. I've tried all the
big names on the west coast to no avail.
Thanks
___
List sponsored by Home Power magazine
List Address: RE-wrenches@lists.re-wrenches.org
Options & settings:
http:/
do know it
usually results in the need to replace the batteries.
Rgds
_
Eric Bentsen | Schneider Electric | Solar Business | UNITED
STATES | Technical Support Representative
Phone: +(650) 351-8237
not seem to be "absorbing" the charge happens
more often with sealed batteries. Maybe it is related to the degree of
sulfation.
Rgds
_
Eric Bentsen | Schneider Electric | Solar Business | UNIT
Hi ,
Deger 5000HD and Sentinel Solar make large trackers.
http://www.dommelvalley.ca/data/DEGERtraker-5000HD-dommelvalley.pdf
http://www.sentinelsolar.com/
Eric
_
Eric Bentsen | Schneider Electric
Hi Allen,
The absorption time is actually only 1 hour for the C-series controllers.
Battery manufacturers are always the final authority on
how their batteries should be charged. If they say you can charge at
14.2-14.4V indefinitely, then increase the float setting.
Eric
Hi Eric,
Sounded like bad batteries to me also (I think he called in this AM). He
has (2) XW6048 units that are
capable of 200ADC between them, and he also has 1260Ah of flooded
capacity. DC Start V is set for 46.5V, so if we assume he was close to 50%
discharge (depending on load), it
sulfation easier?
Rgds,
_
Eric Bentsen | Schneider Electric | Solar Business | UNITED
STATES | Technical Support Representative
Phone: +(650) 351-8237 ext. 001# |
Email: eric.bent...@schneider
e.
866-519-1470
Rgds,
_____
Eric Bentsen | Schneider Electric | Solar Business | UNITED
STATES | Technical Support Representative
Phone: +(650) 351-8237 ext. 001# |
Email: eric.bent...@schneider-electri
/L16REA_TrojanRE_Data_Sheets.pdf
http://www.trojanbatteryre.com/PDF/datasheets/T105_TrojanRE_Data_Sheets.pdf
Rgds,
_
Eric Bentsen | Schneider Electric | Solar Business | UNITED
STATES | Technical
he SW uses "Absorption Time" for stop
parameter, but if set to "0" would accomplish
the same as stop absorb.
Eric
_
Eric Bentsen | Schneider Electric | Solar Business | UNITED
,
_
Eric Bentsen | Schneider Electric | Solar Business | UNITED
STATES | Technical Support Representative
Phone: +(650) 351-8237 ext. 001# |
Email: eric.bent...@schneider-electric.com | Site:
www.schneider-electric.com/solar
% discharge
more accurately, and minimizes user interaction. Try to calculate the
total daily kWhrs and match the demand with RE as
closely as possible.
Hope that helps,
Rgds,
_
Eric Bentsen | Schneider
power
for Xanbus (AUX port can be used for this).
Rgds,
_
Eric Bentsen | Schneider Electric | Solar Business | UNITED
STATES | Technical Support Representative
Phone: +(650) 351-8237 ext. 001
Hi Allen,
Conext SW is available in 24V models only (not 12V).
Rgds,
_
Eric Bentsen | Schneider Electric | Solar Business | UNITED
STATES | Technical Support Representative
Phone: +(650) 351-8237
because certain loads require continuous AC,
i.e. the clock on your microwave, or a fridge,etc.
The power draw in search is 8W, and no load draw when inverting is approx
25W.
Hope that helps,
Eric
_
Eric Bentsen
,
_
Eric Bentsen | Schneider Electric | Solar Business | UNITED
STATES | Technical Support Representative
Phone: +(650) 351-8237 ext. 001# |
Email: eric.bent...@schneider-electric.com | Site:
www.schneider-electric.com/solar | Address
,
_
Eric Bentsen | Schneider Electric | Solar Business | UNITED
STATES | Technical Support Representative
Phone: +(650) 351-8237 ext. 001# |
Email: eric.bent...@schneider-electric.com | Site:
www.schneider-electric.com/solar
Rgds,
_
Eric Bentsen | Schneider Electric | Solar Business | UNITED
STATES | Technical Support Representative
Phone: +(650) 351-8237 ext. 001# |
Email: eric.bent...@schneider-electric.com | Site:
www.schneider-electric.com/solar | Ad
uld contact their lawmakers in Congress to pass a federal law so these
utility companies will stop obstructing
clean energy.
Rgds,
_
Eric Bentsen | Schneider Electric | Solar Business | UNITED
Hi Eric,
Sounds like a bad control board.
Swap the inverter and you should be back in business.
Rgds,
_
Eric Bentsen | Schneider Electric | Solar Business | UNITED
STATES | Technical Support
sign anything until then.
Sometimes, the manufacturer may "step up" and cover shipping damage
to keep the customer happy.
Eric
_
Eric Bentsen | Schneider Electric | Solar Business | UNIT
Hi Kirpal,
All Square D safety switches are UL tested in the Vertical position ONLY,
so if someone is trying to install a switch in any other position other
than vertical, that will be between them and the inspector. Hope this
helps.
Eric
ted.
Rgds,
_
Eric Bentsen | Schneider Electric | Solar Business | UNITED
STATES | Technical Support Representative
Phone: +(650) 351-8237 ext. 001# |
Email: eric.bent...@schneider-electric.com | Site:
www.schneider-el
may be able to repair
at a component level, you need to email them for a quote :
phantompowerservices.com
Rgds,
_
Eric Bentsen | Schneider Electric | Solar Business | UNITED
STATES | Technical
live/?key=Q2uU2oQ0vI6a>.
best regards,
Eric
On Thu, Dec 5, 2013 at 1:03 PM, Davis Terrell wrote:
> Hi Wrenches,
>
>
>
> I am evaluating remote monitoring solutions for an off-grid project and
> wanted to get any feedback people were willing to share. I see my three
> m
ion as
much as possible. That's the idea, anyway. I'd appreciate any advice
from you all. Thanks!
Wishing you all a happy and productive 2014!
Best energy,
Eric
___
List sponsored by Home Power magazine
List Address: RE-wrenches@lists.re-wr
them in the systems we are offering for this tender.
Thanks again folks! Lets hope we win the bid!
Eric
On Tue, Dec 31, 2013 at 12:01 PM, Ray Walters wrote:
> I'll chime back in on a few points:
>
> To MPPT or not: It all gets down to the budget: I find the tipping point
>
Hi Jason,
Both the XW MPPT60 (865-1030-1) and MPPT80 (865-1032) models can have the
charge % adjusted using the SCP (865-1050).
Advanced Settings>Charger Settings>Max Chg Rate
Rgds,
_
Eric B
repairable, although parts supplies are dwindling. The
cost of true sine wave inverters has come down significantly in recent
years. That way you don't need to worry about compatibility.
Rgds,
_
Eric Be
Hi Larry,
We may still have a few display boards left.
Call in to the number below and we can check P & A.
Rgds,
Eric
_
Eric Bentsen | Schneider Electric | Customer Care Center | Advanced
Techn
, 135.5CFM/12VDC/3000RPM
Rgds,
_
Eric Bentsen | Schneider Electric | Customer Care Center | Advanced
Technical Support | Technical Support Engineer
Phone: 866-519-1470 option #1 | Schneider
most part, and continue to sell back.
This would be up to AHJ.
Rgds,
_____
Eric Bentsen | Schneider Electric | Customer Care Center | Advanced
Technical Support | Technical Support Engineer
Phone: 866-519
Hi William,
Please remember the GTI is not compatible with SW models manufactured
prior to 2002.
Rgds.
_
Eric Bentsen | Schneider Electric | Customer Care Center | Advanced
Technical Support
and a good value.
All the best,
Eric
*Eric YoungrenSolar Nexus International*
PO Box 894
1016 Discovery Way
Eastsound, WA 98245
USA
(360) 376-6842
www.solarnexusinternational.com
w <http://www.solarnexus.wordpress.com/>ww.picopowerboss.com
Skype name: ericyoungren
On Fri, Feb 6, 2015 a
he cooker can be used with wood or other biomass
during cloudy weather or at night.That is more of a project than your
friends in Guatemala will probably be able to tackle but I think its a cool
innovation in solar cooking.
all the best,
Eric
On Wed, Mar 11, 2015 at 11:54 PM, Allan Sindelar
w
e most difficult and time consuming part.The McElroy
equipment is much easier, faster and reliable for professional use.
Best,
Eric
On Sun, Nov 22, 2015 at 3:55 PM, jay wrote:
> I’m looking into buying a poly pipe welding/fusing machine.
> 1”-2” sizes
>
> Does anyone hav
conditions of the system.
I've adjusted the Bulk set point on the CC but that doesn't seem to make a
difference.
I doubt this is part of the problem but the generator is problematic as
well (it has it's own array of maladies).
Any insight is greatly appreciated. Thanks!
--
Eric St
this or any other ideas to bring to the table.
Any ideas? Thanks!
Eric Youngren
Solar Nexus International
www.solarnexusinternational.com
___
List sponsored by Home Power magazine
List Address: RE-wrenches@lists.re-wrenches.org
Options & settings:
I like OmniGraffle
<http://www.omnigroup.com/products/omnigraffle/features/> Pro
for 2D schematics and layout drawings on a Mac. and SketchUp is great for
3D drawings and renderings
Eric Youngren
On Mon, Oct 22, 2012 at 3:15 PM, Jonathan Hill wrote:
> Inkscape doesn't appear to
e and haul them up, or secure them on a sloped roof before installation.
How many installers would be interested in something like that??
How much would you be willing to pay for it?
Eric
Solar Nexus International
On Thu, Feb 7, 2013 at 12:03 PM, Garrison Riegel <
garri...@solarserviceinc.co
n your business? Would ETL/UL
listing make a difference in your markets?Small scale off-grid systems
are often (usually?) not inspected, so maybe listing is not a
requirement... I'd love any advice or feedback you guys might have.
Thanks.
Best energy,
Eric
battery types,
it should allow the module to operate very close to Vmp.
Typically, MPPT controllers require a higher Vmp than the target charge
voltage.
Eric Bentsen
_
Eric Bentsen | Schneider Electric
s.
I guess it boils down to what the customer wants. You can always sell the
Trace inverter to someone off grid and use the proceeds toward a new
grid-tie inverter.
Eric
_
Eric Bentsen | Schneider Ele
eciate the feedback.
Eric Bentsen
_
Eric Bentsen | Schneider Electric | Solar Business | UNITED
STATES | Technical Support Representative
Phone: +(650) 351-8237 ext. 001# |
Email: eric.bent...
Hi Will,
Flooded (or wet cell batteries) are typically much more forgiving than a
sealed battery. Check S.G. (≈1.265 at rest) and load test.
Equalize if necessary (if >.05 difference in S.G. cell-to-cell).
E
olarity of grounded conductor.
Eric
_
Eric Bentsen | Schneider Electric | Solar Business | UNITED
STATES | Technical Support Representative
Phone: +(650) 351-8237 ext. 001# |
Email: eric.bent...
Hi Lee,
The MC version is similar to the standard SW, but does not have grid usage
menu (no sell/lbx), and does not give AC1 priority (assuming both inputs
are present). It will support the generator with battery power whenever
the load exceeds the AC2 Amps setting in Menu 11.
Eric
.
Rgds,
Eric
_
Eric Bentsen | Schneider Electric | Solar Business | UNITED
STATES | Technical Support Representative
Phone: +(650) 351-8237 ext. 001# |
Email: eric.bent...@schneider-electric.com
n a vented enclosure if off-gassing will
be an issue.
Eric
_
Eric Bentsen | Schneider Electric | Solar Business | UNITED
STATES | Technical Support Representative
Phone: +(650) 351-8237 ext. 001#
I'm looking for recommendation of banks or lenders who are favorable to work
with when loaning on solar projects (large or small) so that I can direct my
customers. Any good? Or bad?
Thanks.
Eric R. Andrews
NABCEP Certified PV Installer
Klamath Falls, OR
A local real estate appraiser should have that info... ask if they have any
"matched paired analysis" data between similar houses with and without
solar. If an appraiser is not available, a seasoned realtor will be able to
give you a good idea.
Eric R. Andrews
NABCEP Certified PV
1 - 100 of 157 matches