Wrenches, Can anyone shed guidance on the following for me? Should these strings be fused:
Total Modules: 44 Total Strings: 4 strings of 11 Total Inverters: 2 Modules: Silicon Energy 195 Watt @ 8A Each string feeding an independent MPPT input on an Aurora PVI 4.2kW Inverter (there are 2 / Aurora) Inverter is transformerless (READ 690.35 (B)) Each strings passes through a shared SolaDeck jbox, no combining, and head directly to their own dedicated GE THN2261RDC DC Disconnect before entering a dedicated MPPT input on the inverter. My big question is 690.9 (A) exception (b) which states I don't need ocpd as long as "The short circuit currents from all sources do not exceed the ampacity of the conductors." Because all four strings pass through the same jboxs and conduit before reaching their disconnect and could potentially short together, should I fuse each string? Or am I just up too late reading code....? Thanks for being a resource. -- Eric Thomas Solar Epiphany LLC (206) 919-3014 www.solarepiphany.com
_______________________________________________ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Options & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org