Good discussion here. I will not rule out loose connections entirely but I will 
say that our installers know that can be an issue and really tighten their 
connections. I like William's suggestion of fabricating an MC-type connector at 
the PV Wire to THWN transition. At least I presume that's what he's suggesting. 
Indeed we've moved away from the screw-type Polaris and are not interested in 
the old-fashioned wire nut. We're 100% Sunpower and they recommend the 
Buchannon's so that's what we're installing today. However, I'm going to 
investigate the Miller method. William has never led me astray!
 
Eric Stikes
SunHarvest
 
 
--------- Original Message --------- Subject: Re: [RE-wrenches] Polaris gone 
bad?
From: "William Miller" <will...@millersolar.com>
Date: 4/8/17 2:48 pm
To: "RE-wrenches" <re-wrenches@lists.re-wrenches.org>

  
Wrenches:
 
I am wondering why the proliferation of splices in PV leads?  We all know 
splices are a weak link. 
 
We allow only one connection between a module and the feeder destination-- be 
it a combiner, inverter or optimizer-- and it is an MC connector, one side of 
which is factory-made and provided by the module manufacturer. 
 
If one plans and pulls PV circuits with forethought, splices should not be 
necessary.   
 
If anyone wants to know more about how this can be accomplished, look at our 
web site or contact me off list. 
 
William

On Apr 8, 2017, at 10:05 AM, Glenn Burt <glenn.b...@glbcc.com> wrote:


   It is also worth noting that many of the SMA installation manuals 
specifically say do not use wire nuts on DC wiring. 
Of course choosing to ignore the manufacturers installation instructions would 
be a NEC violation.

From: Drake
Sent: &lrm;4/&lrm;8/&lrm;2017 12:10
To: RE-wrenches
Subject: Re: [RE-wrenches] Polaris gone bad?



 At 01:35 PM 4/6/2017, you wrote:
 Recently we interfaced with another solar install firm that has gone back to 
wire nuts due to this same problem. 
 Wire nuts have the advantage of holding the wires tight with a spring. The 
spring follows the cold flow of the copper over the years. A screw type 
connection does not. 

 When I service an old breaker box, usually the wires are loose under the screw 
connections, especially on the neutral and grounding bars. Often they are very 
loose, and I bet that the screws were tight after the initial installation of 
the equipment. 

 On old industrial control equipment, I've learned the hard way to tighten all 
screws before doing anything in the box, as wires are prone to fall out of the 
loose screw connections. Again, these connections have the weakness of being 
held by terminal screws, with no spring to follow the cold flow of the metal. 

 With wire nuts, it can be a bit tricky to know if you have a good connection, 
as the connection is hidden under the plastic cap. It is good to pull hard on 
each wire separately to be sure it is securely under the spring. It is crucial 
never to mix copper and aluminum under a wire nut unless it is one specifically 
designed for the purpose. Unless specifically listed, all out door wire nuts 
should be in a weather proof box, and preferably taped. 

 Drake Chamberlin
 Athens Electric LLC
 OH License 44810
 CO License 3773
 NABCEP Certified Solar PV 
 740-448-7328
 http://athens-electric.com/ 
 
     Virus-free. www.avast.com   
 

  _______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org


 _______________________________________________ List sponsored by Redwood 
Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver 
email address & settings: 
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 
List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html 
List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out or update 
participant bios: www.members.re-wrenches.org
_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to