[RE-wrenches] Inverter Harmonic Distortion

2010-08-30 Thread August Goers
Hi Wrenches, Is anyone familiar with inverter Total Harmonic Distortion (THD) specs? I see that SMA, Fronius, etc have THD listed on their spec sheets but I'm looking for a spec that details requirements for grid tied inverters. Thanks in advance. Best, August August Goers Luminalt E

Re: [RE-wrenches] Delta LAs

2010-09-14 Thread August Goers
List-Archive: > http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org > > List rules & etiquette: > www.re-wrenches.org/etiquette.htm > > Check out participant bios: > www.members.re-wrenches.org > > -- August Goers

Re: [RE-wrenches] GEC for Enphase inverters

2010-09-14 Thread August Goers
ttp://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org > > List rules & etiquette: > www.re-wrenches.org/etiquette.htm > > Check out participant bios: > www.members.re-wrenches.org > > > > ___ > List sponso

Re: [RE-wrenches] Delta LAs

2010-09-14 Thread August Goers
lso live in a area without much lightning, however I install one in most > systems for the simple reason of insurance. > If there is lightning damage, the insurance company can't use that as a way > to not pay any claims. > ie cheap insurance. > > jay > > peltz power &g

Re: [RE-wrenches] Delta LAs

2010-09-20 Thread August Goers
Joel - I'm interested in seeing the archived discussion but I don't have your email address to email you off list. Thanks, August August Goers Luminalt Energy Corporation 1320 Potrero Avenue San Francisco, CA 94110 m: 415.559.1525 o: 415.641.4000 aug...@luminalt.com

Re: [RE-wrenches] lifting shingles

2010-10-07 Thread August Goers
them on comp shingles but I imagine that you could use a little extra M-1 to glue them down to assure that the self-leveling one part sealant doesn't leak out between the shingle layers. -August August Goers Luminalt Energy Corporation 1320 Potrero Avenue San Francisco, C

Re: [RE-wrenches] Code reference needed

2010-10-26 Thread August Goers
Allan - I believe you are referring to NEC 110.26(A)(3) Height of Working Space. They talk about the 6" plane in that section. -August August Goers Luminalt Energy Corporation 1320 Potrero Avenue San Francisco, CA 94110 m: 415.559.1525 o: 415.641.4000 aug...@luminal

[RE-wrenches] small offgrid pv kit

2010-10-28 Thread August Goers
Hi Wrenches, I have a DIY client who is looking for a small $10 to $15k complete off grid battery backup kit he can install himself. Email me off list if you have any sources or thoughts. Thanks! -August ___ List sponsored by Home Power magazine

Re: [RE-wrenches] small offgrid pv kit

2010-10-28 Thread August Goers
of tea - I can foresee way too much technical support, code violations, etc for me to want to get involved. Best, August PS: I used to install off grid systems in the late 90s in your neck of the woods (Atascadero, SLO County CA) too. August Goers Luminalt Energy Corporation 1320

[RE-wrenches] low batteries with a sunny island

2010-11-17 Thread August Goers
;t even turn on. SMA tech support is recommending that we charge the batteries and then turn the system back on. Any ideas about the best way to charge a 48 V battery bank? Thanks for your advice, -August -- August Goers VP, Engineering Luminalt Energy Corporation 1320 Potrero Avenue San Franci

Re: [RE-wrenches] low batteries with a sunny island

2010-11-18 Thread August Goers
series/parallel for 12 volt nominal, that pack could handle the > output from a 60 amp 12v charger intended for deep cycle AGM's but if > an automotive type 12v charger is all you can come up with > readily...use that...since you're only trying to bootstrap the system. > >

Re: [RE-wrenches] low batteries with a sunny island

2010-11-18 Thread August Goers
.org > > List rules & etiquette: > www.re-wrenches.org/etiquette.htm > > Check out participant bios: > www.members.re-wrenches.org > > -- August Goers VP, Engineering Luminalt Energy Corporation 1320 Potrero Avenue San Francisco, CA 94110 O: 415.641.4000 M: 415.559.1

Re: [RE-wrenches] Tranformless inverter

2010-12-10 Thread August Goers
itive and negative lines on the DC side. In SMA's case I'm guessing that their new transformerless inverters with integrated DC disconnects and fuses may already take of all the requirements? Best, August August Goers Luminalt Energy Corporation 1320 Potrero Avenue San Francis

Re: [RE-wrenches] Tranformless inverter

2010-12-10 Thread August Goers
d that there's a June 2010 revision of the Square D disconnect guide. A bit of clarification since the 9/09 edition I had. http://ecatalog.squared.com/pubs/Electrical%20Distribution/Safety%20Switches/Solar%20Disconnect%20Switches/3110DB0401.pdf August Goers wrote: > Hi Bill and Wrenches - >

Re: [RE-wrenches] Tranformless inverter

2010-12-10 Thread August Goers
t; > DC conductors - #10 to #6 > > They recommend operating the DC disconnect once a year, 10 times to keep > the contacts clean > > > > FYI – thought I’d share. > > > > -Glenn Burt > > > > > > *From:* re-wrenches-boun...@lists.re-wrenches.org

Re: [RE-wrenches] Low grid voltage fix

2010-12-20 Thread August Goers
Hi Joel - Have you tried getting PG&E out to check the line voltages? I believe they need to be +/- 5% steady state (ANSI Range A) or possibly +/- 10% (Range B) or they need to fix it. 105 V is way too low. Here in the Bay Area I have found that PG&E is very receptive to resolving line voltage is

[RE-wrenches] Xslent?

2011-01-06 Thread August Goers
Hi All - Have any of you heard of the Xslent XPX-A1000 microinverter? http://www.xetenergy.com/#Tab-2_link-1 We're going up against them on a 10 kW system and I'm trying to figure out if their claims about producing reactive power mean anything to us in the real world. They are saying that their

Re: [RE-wrenches] Xslent?

2011-01-07 Thread August Goers
Hi All - Thanks for the helpful info! We did a little more research on our end and I guess Apparent is the new brand name for the Xslent product. What baffles me is the chart where they show that they're producing power before and after sunrise and sunset: http://www.apparent.com/products/mgi.htm

[RE-wrenches] 2011 NEC and impact in the field

2011-01-13 Thread August Goers
ly there will be new reasonably priced label sources available. I'm sure I'm not alone in saying that it's always been hard to find cost effective labels which can hold up through the elements. The grounding section also looks substantially updated. As always, fun new things coming our

Re: [RE-wrenches] 2011 NEC and impact in the field

2011-01-13 Thread August Goers
530) 401-8024 www.berkeleysolar.com -Original Message- From: re-wrenches-boun...@lists.re-wrenches.org [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of August Goers Sent: Thursday, January 13, 2011 8:35 AM To: RE-wrenches Subject: [RE-wrenches] 2011 NEC and impact in the field Hi All

Re: [RE-wrenches] AC coupled, grid-tied Sunny Island - contactor & bypass

2011-01-14 Thread August Goers
for tying the PV into the main and using a relay to switch to the critical loads panel during a power outage? Best, August August Goers Luminalt Energy Corporation 1320 Potrero Avenue San Francisco, CA 94110 m: 415.559.1525 o: 415.641.4000 aug...@luminalt.com -Original Message- From

Re: [RE-wrenches] AC coupled, grid-tied Sunny Island - contactor & bypass

2011-01-14 Thread August Goers
for your description. This certainly sounds simpler than my plan. -Kelly Kelly Keilwitz, P.E. Whidbey Sun & Wind Renewable Energy Systems ke...@whidbeysunwind.com 360-678-7131 On Jan 14, 2011, at 7:23 AM, August Goers wrote: > Hi Kelly - > > Sounds like a fun project. We

[RE-wrenches] Sharp Warranty in Marine Environment

2011-01-18 Thread August Goers
Hi Wrenches, I recently heard a rumor that Sharp modules may not be warranted in a marine environment. This could be completely false but I thought I would reach out and see if anyone on the list has any experience in this area. Best, August ___ List s

Re: [RE-wrenches] EnPhase male whips

2011-01-20 Thread August Goers
We cut the extensions too. What other options are there when you have multiple sub arrays all over the place? Enphase told us not to cut the inverter leads which makes sense but I don't see any problem in cutting the extensions. Best, August August Goers Luminalt Energy Corpor

[RE-wrenches] Odd Inverter Behavior

2011-02-03 Thread August Goers
Hi Wrenches - We were called out today to check out an under performing system installed by another contractor. This is an odd case. The system has 24 Suntech 180s in three strings of 8 and a SMA Sunnyboy 4000us. Open circuit voltage for each string was about 330 Volts and we verified that everyt

Re: [RE-wrenches] Odd Inverter Behavior

2011-02-04 Thread August Goers
get a rough check on that is to disconnect the panels and temporarily haywire an extra panel in series from another string. I suspect the array might have to be rewired for 2 x 12. *From:* August Goers *Sent:* Thursday, February 03, 2011 5:01 PM *To:* RE-wrenches *Subject:* [RE-wrenches] Odd

Re: [RE-wrenches] NABCEP marketing

2011-02-08 Thread August Goers
nches.org > > Northern Arizona Wind & Sun - Electricity from the sun since 1979 > > Online Solar Store <http://store.solar-electric.com/> > Free Solar Discussion Forum <http://www.wind-sun.com/ForumVB/>

Re: [RE-wrenches] NEC Plus

2011-02-15 Thread August Goers
We subscribed to NECplus about a month ago. At the time they were giving a free hard copy of the code book along with the subscription which is a great deal. I would definitely recommend signing up if they are still offering that deal. It's always nice being able to flip through a real book but the

Re: [RE-wrenches] NEC Plus

2011-02-17 Thread August Goers
Drake - Yea, you can always cancel the subscription if it isn't to your liking. A number of us use it around the office here and some are dead set on the hard copy while others like the searchable online version... Good luck. -August *From:* re-wrenches-boun...@lists.re-wrenches.org [mailto:

[RE-wrenches] (no subject)

2011-02-17 Thread August Goers
Hi Off Grid Wrenches, Does anyone have any feedback on what brands and or models of small 12v charge controllers they like? I'm looking at setting up a small emergency power shed with a couple of PV modules and deep cycle batteries and perhaps a Morningstar or Xantrex small charge controller. We

Re: [RE-wrenches] Small Charge controllers, WAS (no subject)

2011-02-17 Thread August Goers
Fafco Solar *From:* re-wrenches-boun...@lists.re-wrenches.org [mailto: re-wrenches-boun...@lists.re-wrenches.org] *On Behalf Of *August Goers *Sent:* Thursday, February 17, 2011 3:00 PM *To:* RE-wrenches *Subject:* [RE-wrenches] (no subject) Hi Off Grid Wrenches, Does anyone have any

Re: [RE-wrenches] Seam clamps with or w/o rails

2011-02-18 Thread August Goers
Drake - We've done lots of systems both ways - using rails such as Unirac solarmount or ProSolar is definately more forgiving compared to mounting directly on the seams. The adjustability of the Unirac L-foot is particularly nice. If you mount directly to the seams you need to mount in landscape

Re: [RE-wrenches] Seam clamps with or w/o rails

2011-02-18 Thread August Goers
And I guess I should mention that the relatively new Unirac SolarMount-I might be a good fit too. We just got our first set but haven't installed it yet - my first impression is that it looks quick and simple but won't have the same flexibility in adjustment compared to the Solarmount L-foot. -Augu

Re: [RE-wrenches] grounding the Enphase inverter

2011-03-04 Thread August Goers
common in the industry to run bare 10AWG between the modules and racks. Does this still seem acceptable to you? Best, August August Goers Luminalt Energy Corporation 1320 Potrero Avenue San Francisco, CA 94110 m: 415.559.1525 o: 415.641.4000 aug...@luminalt.com -Original Message- From

[RE-wrenches] Generators?

2011-03-16 Thread August Goers
ch out and see what products and manufacturers are popular out there. Thanks, August August Goers Luminalt Energy Corporation 1320 Potrero Avenue San Francisco, CA 94110 m: 415.559.1525 o: 415.641.4000 aug...@luminalt.com ___ List sponsored by

Re: [RE-wrenches] Fire Access lane for ground mount

2011-03-17 Thread August Goers
This isn't just a matter of leaving a gap wide enough for a big fire truck to drive on the grass or is the terrain not suitable to drive on? -August *From:* re-wrenches-boun...@lists.re-wrenches.org [mailto: re-wrenches-boun...@lists.re-wrenches.org] *On Behalf Of *Bill Brooks *Sent:* Thursday,

[RE-wrenches] FW: Fire Access lane for ground mount

2011-03-22 Thread August Goers
Hi Wrenches - See feedback below from fire Captain Matt Paiss of San Jose. Matt, thanks for your input. Best, August -Original Message- From: Matthew Paiss [mailto:mpa...@earthlink.net] Sent: Monday, March 21, 2011 11:07 PM To: aug...@luminalt.com Subject: Re: [RE-wrenches] Fire Access la

Re: [RE-wrenches] Rail concerns (was: Top of POST mount)

2011-03-23 Thread August Goers
You definitely have a point from a basic engineering point of view that bolts through the module bottom holes is technically the most robust option. However, the main racking companies have been selling top down clamps for a very long time and the two big ones, Unirac and Pro Solar, haven't changed

Re: [RE-wrenches] Panduit C-TAP (now crimping tools and taps)

2011-03-29 Thread August Goers
for reference numbers if your supplier carries another line. Any other wrenches out there like other similar products? Happy crimping! -August PS: once you start using these you won't believe you lived without them August Goers Luminalt Energy Corporation 1320 Potrero Avenu

Re: [RE-wrenches] Sanyo problems

2011-04-01 Thread August Goers
Marco - I'd like to see the pdf as well if you don't mind. Thanks, August aug...@luminalt.com *From:* re-wrenches-boun...@lists.re-wrenches.org [mailto: re-wrenches-boun...@lists.re-wrenches.org] *On Behalf Of *Marco Mangelsdorf *Sent:* Thursday, March 31, 2011 7:31 PM *To:* 'RE-wrenches' *Su

Re: [RE-wrenches] Sanyo problems (now email etiquette question)

2011-04-01 Thread August Goers
Michael - This has come up before. I'm probably missing something simple but the problem for me is that Wrenches emails do not contain the senders original address in a way that I've been able to find it. Any suggestions about where I can find the senders email? Best, August -Original Messag

Re: [RE-wrenches] Sunny boy 1800

2011-04-06 Thread August Goers
t; http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org > > List rules & etiquette: > www.re-wrenches.org/etiquette.htm > > Check out participant bios: > www.members.re-wrenches.org > > -- August Goers Luminalt Energy Corporation 1320 Potrero Avenue San Fr

Re: [RE-wrenches] Paint for Rubber Flashings

2011-06-09 Thread August Goers
Roofers often use this type of aluminum paint here in the Bay Area - http://www.gardner-gibson.com/linedetails.aspx?id=57 I think a good quality outdoor latex paint works fine too. Best, August August Goers Luminalt Energy Corporation 1320 Potrero Avenue San Francisco, CA

Re: [RE-wrenches] Ballpark Cost/Watt

2011-06-10 Thread August Goers
Hi Wrenches - Most of you already know this, but California solar data, including installed costs, is public information found here: http://www.californiasolarstatistics.org/current_data_files/ Searching for data on other ~ 1MW systems will help you hone in on at least a ballpark figure bu

Re: [RE-wrenches] smart meters/bidirectional

2011-06-14 Thread August Goers
Hi All - We run into smart meters before we install PV here in CA all the time. The smart meter hardware is typically bidirectional in that the arrow on the display will indicate which direction power is flowing. I say "typically" because there seems to be several meter brands that the utility is

Re: [RE-wrenches] Stiebel Eltron SHW Collector condensation issue

2011-06-21 Thread August Goers
Hi David - Doesn't sound fun. We experienced a similar problem with a 10-collector system with Schuco Slim-Vs about 3 years ago. The collectors had lots of condensation build up in them, especially during the rainy season. Schuco stepped up and gave us new 2nd generation collectors under warrant

Re: [RE-wrenches] Fronius IG vs IG Plus inverters

2011-06-28 Thread August Goers
Hi Howe, Why are you still interested in the original IG? We've had a fairly high failure rate with the original IG and I wouldn't recommend going back to them unless you're getting some sort of amazing inventory clearance price... We have over 100 IG+s in the field with only two failures to dat

Re: [RE-wrenches] Odd Inverter Behavior

2011-07-01 Thread August Goers
at to high a voltage above the Vmp voltage, I replaced the inverter and problem fixed. ------ *From:* August Goers *To:* RE-wrenches *Sent:* Thu, February 3, 2011 6:01:11 PM *Subject:* [RE-wrenches] Odd Inverter Behavior Hi Wrenches - We were called out today t

[RE-wrenches] working spaces for disconnects and meter sockets

2011-08-17 Thread August Goers
maybe the switch needs to be mounted above a sloped driveway. Any opinions and interpretations would be appreciated. Thanks, August August Goers Luminalt Energy Corporation 1320 Potrero Avenue San Francisco, CA 94110 m: 415.559.1525 o: 415.641.

[RE-wrenches] SHW collector absorber plate issue

2011-09-23 Thread August Goers
Hi Wrenches, We have several installations from a few years ago where we're noticing strange discoloration around the corners of the absorber plate: I'll keep the manufacturer anonymous at this point but I'm wondering if any of you have experience with this and if so what the problem might

Re: [RE-wrenches] under performing Enphase inverters

2011-11-04 Thread August Goers
We have over 1000 Enphase units installed of multiple types - mostly M210s and M190s. We just had our first overt failure of an M190. It just went dead after a couple of months of operation. I'll keep my eye out for underperforming units but haven't noticed any yet. -August *From:* re-wrenche

Re: [RE-wrenches] Outdoor rated insulation covering for Solar Water Heating Systems

2017-11-07 Thread August Goers
As other Wrenches have noted, there are UV paints available as well as UV rated insulation itself: http://www.armacell.us/products/armaflexwbfinish/ http://www.armacell.us/products/utsolaflex/ The problem with both of these solutions is that few folks keep up with the required maintenance over t

Re: [RE-wrenches] Breaker trip

2017-12-06 Thread August Goers
Hi Mac, What size breaker is tripping? I assume you are running at 48 v? August On Wed, Dec 6, 2017 at 4:18 AM, Mac Lewis wrote: > Hello wrenches, > > I've got a mysterious breaker tripping that I need some ideas on how to > fix. > > Original system: > Array 6 x 235W Kyocera modules > 1 x Ou

Re: [RE-wrenches] Concrete Tile Roof Solar Installation - Oregon - Engineering requirements

2017-12-19 Thread August Goers
nything over 10 years old should be inspected by a roofer. The best bet is to have a roofer waterproof your stanchions. August *August Goers* Luminalt Energy Corporation On Tue, Dec 19, 2017 at 9:54 AM, Jerry Shafer wrote: > Fellow Wrenches > Some time back we were doing concrete tile ins

Re: [RE-wrenches] SolarEdge change over with SunPower Modules??

2017-12-19 Thread August Goers
Tom - I was just asking a SunPower rep about this. My understanding is that a PID (Potential Induced Degredation) discharge device is required to use SunPower positively grounded modules with a transformerless inverter. These are expensive and not listed for the US market. Long story short, I don't

Re: [RE-wrenches] Remote monitoring via landline

2018-01-03 Thread August Goers
William, Can the phone company install a DSL modem to get your equipment regular internet? August *August Goers* Luminalt On Tue, Jan 2, 2018 at 9:49 PM, William Miller wrote: > Friends: > > > > I am designing a remote off-grid system to run some traffic lights. Due to

Re: [RE-wrenches] Wire management with S5! Railless System

2018-01-11 Thread August Goers
Ray - I agree with the others that S5 clamps with rails is the way to go on standing seam roofs. We buy our S5 clamps through LMCurbs and I've found their pricing and service to be good: http://www.lmcurbs.com/ We go though a good deal of effort to determine the exact standing seam make/model and

Re: [RE-wrenches] 1,000V combiners

2018-01-19 Thread August Goers
Chris - Two ideas: One, call Fronius to see what they recommend. We haven't used this particular inverter, but we've used lots of the smaller Symos and Pirmos and with some of them you can fit fuse holders right in the wire box onto a din rail. Otherwise, I've had good results working with SolarBO

Re: [RE-wrenches] experience with the Tesla Powerwall

2018-02-13 Thread August Goers
ptive. The design flexibility of the Gateway setup, the small size, minimal labor to install, and performance blow other systems out of the water. I hope that other manufacturers are able to catch up with this type of design. Best, August *August Goers* Luminalt Energy Corporation o: 41

Re: [RE-wrenches] experience with the Tesla Powerwall

2018-02-13 Thread August Goers
Cheers, > > Dave > > > > > > *--* > > > > > > *Dave Tedeyan* > > *Senior Engineer* > > > > *Taitem Engineering, PC* > > 10 Verizon Lane, Lansing, NY 14882 > > Voice: (607) 930-3481 x6 > > www.taitem.com > > > >

Re: [RE-wrenches] Experience with the Tesla Powerwall

2018-02-13 Thread August Goers
running the PWs in back-up power only mode or > daily cycling mode? > > In either case, the addition of PW does not add to the generating capacity > of the solar facility. > > marco > > On Tuesday, February 13, 2018, August Goers wrote: > >> Marco, >> >

Re: [RE-wrenches] Experience with the Tesla Powerwall

2018-02-13 Thread August Goers
hang up? And are running the PWs in back-up power only mode >>> or daily cycling mode? >>> >>> In either case, the addition of PW does not add to the generating >>> capacity of the solar facility. >>> >>> marco >>> >>> On Tuesda

Re: [RE-wrenches] Powerwall and other Li

2018-02-15 Thread August Goers
Hi Hilton, We've done the math for our installed cost on the Powerwall 2. Certainly, it wouldn't make sense to purchase it just for energy savings alone with current California residential electricity tariffs. However, most folks are buying it primarily for backup purposes and then a little bit of

Re: [RE-wrenches] heating a lithium battery bank

2018-02-28 Thread August Goers
h per heating cycle depending on temps?). I understand that Tesla's offgrid Powerwall isn't ready for prime time yet. August *August Goers* Luminalt Energy Corporation On Wed, Feb 28, 2018 at 8:55 AM, Bill Hoffer wrote: > Daniel > > Why are we having to deal with lo

Re: [RE-wrenches] TJI rafters

2018-03-03 Thread August Goers
Hi All - We tie into TJIs commonly, if you Google "TJI solar" you'll find manufacturer docs on how to properly lag in. August On Mar 2, 2018 1:24 PM, "Jerry Caldwell" wrote: > Dear Wrenches, > > I have a customer with a low slope roof supported by TJI beams. Does > anyone have experience permit

Re: [RE-wrenches] Clearance clarification please

2018-04-04 Thread August Goers
at is supposed to be corrected. August *August Goers* www.luminalt.com On Tue, Apr 3, 2018 at 10:36 PM, William Miller wrote: > Darryl: > > > > If you are talking about California, I must respectfully disagree. If you > are not talking about California, I am ignorant. >

Re: [RE-wrenches] Chevy Bolt

2018-04-23 Thread August Goers
As a separate item to check, make sure the grounding electrode system and neutral are all up to shape at the site. We've had problems with this with various EVs giving an error when atempting to charge. August Luminalt On Mon, Apr 23, 2018 at 11:45 AM, Ray wrote: > Pretty sure the Magnum will w

Re: [RE-wrenches] Painting anodized rails?

2018-06-11 Thread August Goers
Aluminum takes well to spray paint primer followed by a coating of exterior spray paint such as Rust-Oleum. As I'm sure others will point out, I'm not sure how long it actually lasts. August Luminalt On Mon, Jun 11, 2018 at 8:10 AM cwarfel wrote: > A customer has asked that I look into painting

Re: [RE-wrenches] 208V single-phase inverter options

2018-07-16 Thread August Goers
Hi Andrew, Fronius Primo inverters go up to 15 kW 208 v single phase, but are limited to 13750 VA output in 208 volt operation. I'm not aware of larger single phase 208 v inverters, although it is certainly possible that they are out there. http://www.fronius.com/en-us/usa/photovoltaics/products/

Re: [RE-wrenches] M210 Enphase

2018-07-30 Thread August Goers
We have many M210 and M190 micros installed and deal with replacements frequently. If you're seeing physical signs of oozing or swelling, it's only a matter of time before they stop working. Enphase should replace them under warranty, especially if you explain that now is the time to get them swapp

Re: [RE-wrenches] Bi-Directional / Netmetering question

2018-08-16 Thread August Goers
Jason, In our territory the utility (PG&E) starting switching to digital smart meters five to ten years ago. In order to function properly with a PV system, meters need to be programmed for Net Energy Metering (NEM). If you run a PV system prior to receiving Permission To Operate (PTO) from the ut

Re: [RE-wrenches] Tapping Parallel Conductors

2018-08-21 Thread August Goers
Hi Garrison, This is a new one for me - normally we always balance everything when dealing with paralleled conductors. NEC 310.10(H) talks about conductors in parallel and I can't see anything the explicitly forbids what you explained. To be safe, I think it is worth contacting the PE to double ch

Re: [RE-wrenches] Removing graffiti from modules

2018-09-09 Thread August Goers
If your modules don't have anti reflective coating then you can scrape them with a sharp razor blade scraper. Goo Gone or one of the similar products might help at well. August Luminalt On Sun, Sep 9, 2018 at 8:30 AM frenergy wrote: > Help us with this Benn. Are we talking spray paint, airg

Re: [RE-wrenches] Conduit Bending

2018-11-02 Thread August Goers
Don't forget about YouTube - a quick search for "conduit bending" yields dozens of helpful videos, some professionally produced. August Luminalt On Fri, Nov 2, 2018 at 4:00 PM Dana wrote: > I too have been perplexed on the art of conduit bending. One of my > favorite master electricians in CO

[RE-wrenches] Equipment ideas for very large residential PV and battery backup

2019-01-08 Thread August Goers
nd of equipment would you recommend? I'm thinking maybe Sunny Islands with Blue Ion LiFePO4 batteries? Best, August *August Goers* Luminalt Energy Corporation ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.o

Re: [RE-wrenches] Equipment ideas for very large residential PV and battery backup

2019-01-11 Thread August Goers
or www.energport.com They have models up to 60 kW > and 120 kWh > > > > > On Tue, Jan 8, 2019 at 2:49 PM August Goers wrote: > >> Hi Wrenches, >> >> We have a new potential client who wants a 60 kW PV system and a battery >> backup system with 200 kWh

Re: [RE-wrenches] Equipment ideas for very large residential PV and battery backup

2019-01-11 Thread August Goers
> On Jan 11, 2019, at 6:40 AM, August Goers wrote: > > Thanks All for the ideas. For the battery inverters, I'm most interested > in sticking with SMA or Schneider which I've had good experience with in > the past. Over the past year and a half our experience has

Re: [RE-wrenches] Curved solar mounting

2019-02-07 Thread August Goers
Hi Jason - We've used Unirac SunFrame for similar applications. I'm not certain that the shared rail can accommodate the slight different in angle between module rows due to the curve, but it might be worth checking out if you haven't already: https://unirac.com/sunframe/ August On Thu, Feb 7,

Re: [RE-wrenches] Curved solar mounting

2019-02-08 Thread August Goers
er Z-purlins or I-beams. I have to mount the > modules in landscape. I guess what I'm really looking for is standard > hardware that I can bolt to the purlins/beams and bolt or clip to the > module frame. > > These will likely be AC modules, so I also need to consider wire > ma

Re: [RE-wrenches] Multiple inverters

2019-02-27 Thread August Goers
ge was a mistake corrected in 2107, or what > the thinking was of the authors. Regardless, we live by the language, not > the intent. > > > Thank you as well to all who responded. > > > William Miller > > > > > > > > > *From:* August Goers [mailto:aug...@lumin

Re: [RE-wrenches] Plated versus unplated eyelets

2019-04-09 Thread August Goers
Hi William - I would stick with tin coated copper battery cable lugs. The tin coating adds corrosion resistance to the copper - this is especially important for battery connections which already have a tendency to corrode. The ground lugs we all historically used on our racking systems should have

Re: [RE-wrenches] Cutting rail

2019-06-13 Thread August Goers
I'll chime in on the cordless bandsaw revolution - they're the best! We have been using DeWalt 20v products and they make both a large deep-cut version and a smaller version. The large bandsaw is great for the roof and the small one is great for electrical work such as cutting conduit (like butter)

Re: [RE-wrenches] AC/DC coupling on conext

2019-06-24 Thread August Goers
Andrew - I imagine you've already considered a StorEdge and LG Chem battery? August Luminalt On Mon, Jun 24, 2019 at 11:18 AM Andrew wrote: > Wrenches, > > I got a situation where I got a client who wants to get > solar with battery backup but where he is located the grid canno

Re: [RE-wrenches] AC/DC coupling on conext

2019-06-25 Thread August Goers
; > Andrew Perkins > > Greenwired > > P: 707-923-2001 ext. 100 > > 1150 #1 Evergreen Rd > > Redway, CA 95560 > > www.greenwired.com > > [image: Description: signature] > > > > > > > > *From:* RE-wrenches [mailto:re-wrenches-boun...@lists.re-wr

Re: [RE-wrenches] spaghetti mat

2019-07-02 Thread August Goers
Hi Bruce, Yes, we use yellow spaghetti mat daily to protect the roof. Carpet scraps available from flooring dealers also work well. Both are good for up to about 30 degrees (7/12 roof). Spaghetti mat can be reused many times but can be slippery when wet. Thermo-ply or some other relatively thin bo

Re: [RE-wrenches] DC Bonding battery systems

2019-07-23 Thread August Goers
Hi William - This article is a few years old, but I think describes ground fault detection issues well: http://www.solarabcs.org/about/publications/reports/blindspot/pdfs/inverter_groundfault-2013.pdf I don't have experience (at least since the late 90s) with the type of GFD breaker you describe

Re: [RE-wrenches] DC Bonding battery systems

2019-07-23 Thread August Goers
t; I read the referenced report. It does not address the concern I raised— > that is the breaker specified unbonds a system that I believe is supposed > to be bonded. > > William > > On Jul 23, 2019, at 8:38 AM, August Goers wrote: > > Hi William - > > This article is a

Re: [RE-wrenches] Large Off-Grid Residential System and ciculating currents

2019-07-24 Thread August Goers
Hi William - Yea, your kWh calculation is correct. However, the 16 kWh Blue Ion is comparable to eight L16 (6 volt x 333 Ah each) batteries, not one - nameplate rating. Typically you can go way deeper discharge with the lithium products, so the Blue Ion might be more comparable to sixteen (or even

Re: [RE-wrenches] Enphase and Tesla Powerwall

2019-07-25 Thread August Goers
Hi Marco - We have dozens of systems with this combo, so far no problem. Tesla's AC coupling mechanism in general seems to be very robust - we've paired them with many inverter types and brands, and they always seem to couple up during our grid-off tests. Since the vast majority of our systems are

Re: [RE-wrenches] 230Vac load on OB FX2524T system

2019-07-25 Thread August Goers
Many appliances, motors, AC units, etc are rated for 230 volts, but really they work for our modern 240 volt services. If you do a quick web search, it appears that US standard voltages over the years have morphed from 110 to 115, to 120 volt: https://forums.tesla.com/forum/forums/difference-betwe

Re: [RE-wrenches] Enphase and Tesla Powerwall

2019-07-25 Thread August Goers
d use their envoy box and SunPower uses the PV Supervisor 6. August On Thu, Jul 25, 2019 at 10:53 AM Marco Mangelsdorf wrote: > Sounds encouraging, August. Mahalo. > > Are any of those systems zero export by any chance? > > marco > > On Thursday, July 25, 2019, August G

[RE-wrenches] remote project in northeast India

2019-08-19 Thread August Goers
onnect you. Best, August *August Goers* Principal Luminalt Energy Corporation o: 415.792. www.luminalt.com ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: h

Re: [RE-wrenches] Power wall

2019-08-24 Thread August Goers
Hi Jay - We are a Tesla Powerwall/Powerpack dealer. We buy equipment direct from Tesla just like any normal vendor relationship and then sell a complete turnkey installation for our customers. Our customers don't buy equipment directly from Tesla. Tesla allows customers to place a deposit for Power

Re: [RE-wrenches] connector mismatch

2019-09-09 Thread August Goers
Jason - I'm curious about your statement on cutting off module connectors. Can you elaborate? Best, August Luminalt On Sat, Sep 7, 2019 at 7:52 AM Jason Fisher (STC) wrote: > Kent, I don’t see an answer to Brian’s question about the LG module’s > original connector configuration. We’re these

Re: [RE-wrenches] connector mismatch

2019-09-10 Thread August Goers
] Please > print only if necessary. > > > > NOTE: This email message and any attachments are for the sole use of the > intended recipient(s) and may contain confidential and/or privileged > information. Any unauthorized review, use, disclosure or distribution is > prohibited.

Re: [RE-wrenches] Good Tablets for the Solar Installer

2019-09-17 Thread August Goers
We've experimented around with various devices, and I'll agree that the Microsoft Surface line is a good choice. You can find 3rd party heavy duty protective cases on Amazon that are worthwhile if you plan on using it in the field. Also note that the current Surface Pro 6th gen product only has one

Re: [RE-wrenches] SolarReady Service Panel vs adding Supply Side connection?

2019-10-23 Thread August Goers
Replying on list, I had mistakenly only replied to Jeff off list. -August On Wed, Oct 23, 2019 at 6:26 AM August Goers wrote: > Hi Jeff - I think technically you can try a supply side connection per NEC > 705.12(A) if you can find equipment with provisions to both feed your > existin

Re: [RE-wrenches] NEC 2020 not available as a portable PDF?

2020-01-08 Thread August Goers
I've heard from multiple sources and confirmed myself that you can't get the portable pdf of the NEC starting with the 2020 edition. The link that Lorenzo shared seems to indicate that older versions including 2017 edition are available in a digital format. [image: image.png] August Luminalt On

Re: [RE-wrenches] Inverter Output Circuit OCPD Meltdown

2020-01-21 Thread August Goers
Hi Jason - It certainly appears that there was some sort of surge or short. We've had a few cases where microinverter branch circuit end termination caps were left off or fell off and shorted out during rain storms. You might want to double check that those are all in place. We've also had cases w

Re: [RE-wrenches] Inverter Output Circuit OCPD Meltdown

2020-01-23 Thread August Goers
Jason - Thanks for sharing - this is a good lesson for all Wrenches. Years ago we had a dual string inverter installation where the DC positives and negatives were mixed between the two interters. String 1 positive went to inverter 1, string 1 negative went to inverter 2 and vice versa. The invert