Yes, PG&E. The Self Generation Incentive Program (SGIP) created a flood of
applications and PG&E is having a hard time keeping up. Hopefully it will
get easier.

We are enabling self-consumption and backup modes. The Powerwall charges
daily from the solar and then discharges to a owner-set minimum reserve
capacity.

August

*August*

Luminalt Energy Corporation

o: 415.641.4000

www.luminalt.com



On Tue, Feb 13, 2018 at 8:30 AM, Marco Mangelsdorf <ma...@pvthawaii.com>
wrote:

> Hey August.
>
> By utility I assume that you are talking about PG&E.
>
> What's the hang up?  And are running the PWs in back-up power only mode or
> daily cycling mode?
>
> In either case, the addition of PW does not add to the generating capacity
> of the solar facility.
>
> marco
>
> On Tuesday, February 13, 2018, August Goers <aug...@luminalt.com> wrote:
>
>> Marco,
>>
>> Thanks for sharing, it is good to hear details from an installer who is
>> living with a Powerwall. We starting selling the Powerwall 2 in 2017 and
>> have worked up a large pipeline. We have about 20 installed so far, but are
>> still waiting on utility permission to operate which is taking a long time.
>> We have spent a good deal of time commissioning and testing each system.
>> For the most part, our experience has been good although the commissioning
>> software and internet connectivity features have been buggy. Hopefully
>> those are issues that will be ironed out by Tesla. Otherwise, we've had the
>> systems correctly operate in on-grid and off-grid modes with both Solaredge
>> and SunPower Equinox AC coupled systems.
>>
>> We installed conventional lead acid battery backup systems for over 10
>> years and I can confidently say that Tesla's Powerwall and Gateway setup
>> is truly market-disruptive. The design flexibility of the Gateway setup,
>> the small size, minimal labor to install, and performance blow other
>> systems out of the water. I hope that other manufacturers are able to catch
>> up with this type of design.
>>
>> Best,
>>
>> August
>>
>> *August Goers*
>>
>> Luminalt Energy Corporation
>>
>> o: 415.641.4000 <(415)%20641-4000>
>>
>> www.luminalt.com
>>
>>
>>
>> On Sat, Feb 10, 2018 at 12:23 PM, Marco Mangelsdorf <ma...@pvthawaii.com>
>> wrote:
>>
>>>
>>>
>>> *Aloha Wrenches,*
>>>
>>>
>>> *I thought I'd share my own experiences with the Powerwall as my company
>>> is now launching a program to add PW to existing NEM systems since the vast
>>> majority of them do not have storage which means that if the grid goes
>>> down, so does their PV system.  (With the exception of the SMA SB line and
>>> their Secure Power Supply.)*
>>>
>>>
>>> *And no, I'm not a shill or toadie for Tesla.*
>>>
>>>
>>> *marco *
>>>
>>> *I wanted to walk my own talk.  Before we launched adding Powerwall to
>>> existing Net Energy Metered solar electric systems, I wanted to make sure
>>> that what was promised on paper would work in the real world.  I added
>>> Powerwall to my NEM system last year and have been monitoring and testing
>>> it during normal grid-on and grid outage modes.  And I’m very pleased to
>>> report that Powerwall has performed flawlessly and as expected.*
>>>
>>>
>>>
>>> *When used in a NEM system, Powerwall is programmed to be in “Backup”
>>> mode.  When utility power is on, Powerwall stands ready in a full state of
>>> charge for any power outage.  During normal grid-on conditions, my Powerall
>>> takes about .6 kilowatt-hours every other day to stay fully charged.  Over
>>> the course of the month, this Powerwall’s electricity consumption comes to
>>> about 9 kWhs or about $3/month at the current HELCO R rate.*
>>>
>>>
>>>
>>> *I have turned the utility power off to my home on a number of occasions
>>> in order to experience how Powerwall would perform in a simulated grid
>>> outage.  When the grid goes down, my house effectively becomes a
>>> self-generating micro-grid.  That is, my photovoltaic system (solar modules
>>> and inverters) and Powerwall (battery storage and integrated inverter) form
>>> a power grid with energy being created and stored and then consumed by my
>>> electric loads.*
>>>
>>>
>>>
>>> *Several things I noted from my simulated grid outages:*
>>>
>>> *·         I purposefully overloaded Powerwall by turning on my electric
>>> dryer and electric oven at the same time.  As expected, since the maximum
>>> output of Powerwall is 5 kilowatts, it shutdown.  Meaning that all the
>>> power in my house went off.  Within seconds, Powerwall reset itself and the
>>> power came back on, with the dryer and oven having shut down after the
>>> power went off.  If power does not come back on after your Powerwall trips
>>> off, you will need to turn off those high-power loads and reset Powerwall
>>> by turning its black on-off switch, located on the right side of the unit,
>>> from on to off and then on again.  The important takeaway: during a utility
>>> outage, you will need to be careful as far as operating heavy electric
>>> loads, especially 240 volt appliances both from the perspective of
>>> overloading your Powerwall and rapidly drawing down the battery capacity,
>>> especially at night.*
>>>
>>> *·         The magic of frequency shifting.  Without getting into too
>>> much techno-talk, this is the story of frequency shifting.  Normal utility
>>> frequency is 60 hertz (Hz).  PV inverters require the utility frequency to
>>> be at or near 60 Hz in order to operate.  During a grid outage, Powerwall
>>> effectively establishes grid quality power (120/240 volts at 60 Hz),
>>> allowing a micro grid to operate with solar providing power to your house
>>> loads (during daylight hours) and charge Powerwall as needed.  During the
>>> day with the loads being met by your PV system and Powerwall being at or
>>> near full state of charge (97-100 percent), Powerwall will shift the
>>> frequency from 60 to 66 Hz in order to turn off the PV inverter(s).  That
>>> is, the PV inverter(s) see the frequency out of spec and shut down as
>>> they’re expected and required to do.  Why? Because with Powerwall at or
>>> near full and the house loads being met, there’s nowhere for any additional
>>> solar generation to go.  Powerwall will wait for its the state of charge to
>>> drop below 96-97 percent before shifting the frequency back to 60 Hz which
>>> allows the PV system to restart and generate solar power again.   This
>>> frequency shifting can take place repeatedly over the course of the day
>>> depending on load demands, solar potential and Powerwall state of charge
>>> and is perfectly normal and does not damage the PV inverters.*
>>>
>>> *·         **66 Hz and home appliances: when Powerwall is at 66 Hz,
>>> some of your house loads may be affected.  What I and other Powerwall
>>> owners have noticed, while not a comprehensive list, can include:
>>> electronic clocks running fast, motors sounding different (microwave,
>>> washing machine, pumps), uninterruptible power sources (UPS) not charging
>>> and going into back-up power mode, appliances having a computer behaving
>>> unusually.*
>>>
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>>
>>> List Address: RE-wrenches@lists.re-wrenches.org
>>>
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>
>>> List-Archive: http://www.mail-archive.com/re
>>> -wrenc...@lists.re-wrenches.org/maillist.html
>>>
>>> List rules & etiquette:
>>> www.re-wrenches.org/etiquette.htm
>>>
>>> Check out or update participant bios:
>>> www.members.re-wrenches.org
>>>
>>>
>>>
>>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.
> org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
>
_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to