Hi Mac,

What size breaker is tripping? I assume you are running at 48 v?

August



On Wed, Dec 6, 2017 at 4:18 AM, Mac Lewis <maclew...@gmail.com> wrote:

> Hello wrenches,
>
> I've got a mysterious breaker tripping that I need some ideas on how to
> fix.
>
> Original system:
> Array 6 x 235W Kyocera modules
> 1 x Outback FM60 charge controller
> 1 x Magnum MS 4024 PAE inverter
>
> Upgraded system we stacked a second inverter to accommodate an air
> compressor:
> Array 6 x 235W Kyocera modules
> 1 x Outback FM60 charge controller
> *2 x Magnum MS 4024 PAE inverter*
>
> There have been no changes to the solar array, just to the inverter side of
> the system.  We have been getting intermittent breaker tripping (a couple
> of weeks between) on the battery breaker side of the charge controller.
> The basics have been checked and rechecked.  Torque is good on all sides of
> the breaker all the way to the battery bussing.
>
> The only thing that I can think of is that during a surge on the AC side
> its sucking enough current out of the charge controller caps to trip this
> breaker occasionally.
>
> Has anyone experienced this?  The only way I can see to fix it is to go
> with a larger breaker ampacity, but maybe there is something better.  Does
> anyone no how quickly the max current setting in the Outback can respond,
> would dropping this help?
>
> Thanks
>
> --
>
>
>
> Mac Lewis
>
> *"Yo solo sé que no sé nada." -Sócrates*
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.
> org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to