Re: [RE-wrenches] Batteries and Working Spaces

2021-03-27 Thread Chris Worcester
9. Original message From: Jason Szumlanski Date: 3/27/21 8:12 AM (GMT-08:00) To: RE-wrenches Subject: Re: [RE-wrenches] Batteries and Working Spaces Not an option.  Limited garage space. On Sat, Mar 27, 2021, 3:01 AM Chris Worcester wrote:Can you add a catwalk with hand

Re: [RE-wrenches] Batteries and Working Spaces

2021-03-27 Thread Glenn Burt
Can you lay them on their sides?-GlennSent from my 'smart'phone, so please excuse typos and spelling errors.-- Original message--From: Jason SzumlanskiDate: Sat, Mar 27, 2021 11:12 AMTo: RE-wrenches;Cc: Subject:Re: [RE-wrenches] Batteries and Working SpacesThat's problem

Re: [RE-wrenches] Batteries and Working Spaces

2021-03-27 Thread Dave Angelini Offgrid Solar
I would ask Fortress about the heights! If this was offgrid and not inspected, I would have signage indicating there is a battery breaker/disco above this sign. If that breaker is tripped, I would think other things may be wrong and only qualified people should re-energize the breaker. That ma

Re: [RE-wrenches] Batteries and Working Spaces

2021-03-27 Thread Chris Sparadeo
;> Original message >> From: Jason Szumlanski >> Date: 3/26/21 12:41 PM (GMT-08:00) >> To: RE-wrenches >> Subject: [RE-wrenches] Batteries and Working Spaces >> >> I am planning a battery backup system using Fortress 18.5kWh eVaults. Due &g

Re: [RE-wrenches] Batteries and Working Spaces

2021-03-27 Thread Jason Szumlanski
> > Original message > From: Jason Szumlanski > Date: 3/26/21 12:41 PM (GMT-08:00) > To: RE-wrenches > Subject: [RE-wrenches] Batteries and Working Spaces > > I am planning a battery backup system using Fortress 18.5kWh eVaults. Due > to flood level

Re: [RE-wrenches] Batteries and Working Spaces

2021-03-27 Thread Jason Szumlanski
That's problematic I think. I guess the next question would be, if I need to keep this breaker at 6'7", I don't see that being accessible be someone standing in front of it anyway without a portable ladder, so what height IS acceptable? Also, maybe I don't need to mount the whole battery above the

Re: [RE-wrenches] Batteries and Working Spaces

2021-03-27 Thread Chris Worcester
Can you add a catwalk with handrails in front of it for maintenance?Chris Worcester chris@solarwindworks.com530-448-9692Sent from my Samsung Galaxy s9. Original message From: Jason Szumlanski Date: 3/26/21 12:41 PM (GMT-08:00) To: RE-wrenches Subject: [RE-wrenches

Re: [RE-wrenches] Batteries and Working Spaces

2021-03-26 Thread Dave Angelini Offgrid Solar
Earthquake safety requirements in CA. Probably not an issue in Florida. Ask your building department! Dave Angelini Offgrid Solar "we go where powerlines don't" http://members.sti.net/offgridsolar/ [1] e-mail offgridso...@sti.net [2] text 209 813 0060 On Fri, 26 Mar 2021 19:08:18 -0400, Chris

Re: [RE-wrenches] Batteries and Working Spaces

2021-03-26 Thread Chris Sparadeo
Hi Jason, There is a 250A breaker located inside a compartment on the top of the unit. Keeping that reasonably accessible would be important. Also, just out of curiosity, how are you planning of getting these battery cabinets onto their 4’ platform? Forklift? Ramp? On Fri, Mar 26, 2021 at 3:40 P

[RE-wrenches] Batteries and Working Spaces

2021-03-26 Thread Jason Szumlanski
I am planning a battery backup system using Fortress 18.5kWh eVaults. Due to flood level requirements, these are going to need to be mounted about 48 inches above the garage floor on a shelf/platform. That puts the tops of the battery cabinets well above 6'7". But I believe that these do not fall u

Re: [RE-wrenches] Batteries in 4' tall crawl space

2018-08-03 Thread Dana
nting this email. From: RE-wrenches On Behalf Of Ray Sent: Wednesday, August 01, 2018 10:23 PM To: re-wrenches@lists.re-wrenches.org Subject: Re: [RE-wrenches] Batteries in 4' tall crawl space Never laid on my stomach, I just have kneel pad I use for lots of stuff but it works good here

Re: [RE-wrenches] Batteries in 4' tall crawl space

2018-08-03 Thread Dave Angelini Offgrid Solar
018 3:32 PM TO: re-wrenches@lists.re-wrenches.org [4] SUBJECT: Re: [RE-wrenches] Batteries in 4' tall crawl space Article 110.26 covering clearances in front of electrical equipment applies. I worked on a couple like that, and I didn't like it. Very hard to move the batteries, and C

Re: [RE-wrenches] Batteries in 4' tall crawl space

2018-08-03 Thread Jerry Caldwell
  From: RE-wrenches On Behalf Of Ray Sent: Monday, July 30, 2018 3:32 PM To: re-wrenches@lists.re-wrenches.org Subject: Re: [RE-wrenches] Batteries in 4' tall crawl space   Article 110.26 covering clearances in front of electrical equipment applies.  I worked on a couple like that,

Re: [RE-wrenches] Batteries in 4' tall crawl space

2018-08-01 Thread Ray
like to service them you would have to lay on your stomach and get your face right in there? Not my idea of a good time! -Glenn *From:*RE-wrenches *On Behalf Of *Ray *Sent:* Monday, July 30, 2018 3:32 PM *To:* re-wrenches@lists.re-wrenches.org *Subject:* Re: [RE-wrenches] Batteries in 4'

Re: [RE-wrenches] Batteries in 4' tall crawl space

2018-08-01 Thread Glenn Burt
g this email. From: RE-wrenches <mailto:re-wrenches-boun...@lists.re-wrenches.org> On Behalf Of Jerry Caldwell Sent: Saturday, July 28, 2018 6:10 PM To: re-wrenches@lists.re-wrenches.org <mailto:re-wrenches@lists.re-wrenches.org> Subject: [RE-wrenches] Batteries in 4' tal

Re: [RE-wrenches] Batteries in 4' tall crawl space

2018-07-31 Thread Ray
I've seen several instances with AGMs, where a dead cell overheated and blew the top of the case off the battery.  Looked pretty bad, but I wasn't there when they blew.  I think the prevention is to regularly check separate battery voltages to identify weak or dying cells before they blow.   8

Re: [RE-wrenches] Batteries in 4' tall crawl space

2018-07-31 Thread Ken Schaal
And thank you Steve for reminding folks of all those nasty effects of outgassing hydrogen..I figured someone would, necessarily. These are sealed AGM, which I realize is not a guarantee of no hydrogen , but certainly not a constant hazzard. ALSO.. .these are large spaces...full length of house craw

Re: [RE-wrenches] Batteries in 4' tall crawl space

2018-07-31 Thread Steve Higgins
Hello Wrenches... Since Ken brought it up Inverters are the most common of the ignition sources, with loose connections being a close second... Inside each inverter/charger is a transfer relay, this relay when it transfers to or from grid will spark. This sparking action can cause Hydrogen g

Re: [RE-wrenches] Batteries in 4' tall crawl space

2018-07-31 Thread Ken Schaal
I have a set of AGM's installed near the inverter, on a roll out dolly, under the landing, up 5 steps from the garage to the 1st fl.. Another set of AGM's in a 4-5' crawl space. Was a bit of a tussle last year to replace those four, but then I was 72 with achy knees. 8 ' from access door to batte

Re: [RE-wrenches] Batteries in 4' tall crawl space

2018-07-30 Thread Ray
*To:* re-wrenches@lists.re-wrenches.org *Subject:* [RE-wrenches] Batteries in 4' tall crawl space Wrenches, I have a customer who wants to have batteries installed in a 4' tall crawl space / short basement. Are there any accessibility code issues with installing batteries in a crawl

[RE-wrenches] Batteries in 4' tall crawl space

2018-07-30 Thread Dana
r the environment before printing this email. From: RE-wrenches On Behalf Of Jerry Caldwell Sent: Saturday, July 28, 2018 6:10 PM To: re-wrenches@lists.re-wrenches.org Subject: [RE-wrenches] Batteries in 4' tall crawl space Wrenches, I have a customer who wants to have batteries

Re: [RE-wrenches] Batteries in 4' tall crawl space

2018-07-29 Thread frenergy
Jerry,             I serviced a system that (who became my) customer installed just like that. To me, it doesn't really matter what the NEC thinks about it. It was great because it showed me what I would *never* duplicate in my repertoire of installs. Bill On 7/28/2018 5:10 PM, Jerry Caldw

[RE-wrenches] Batteries in 4' tall crawl space

2018-07-29 Thread Jerry Caldwell
Wrenches, I have a customer who wants to have batteries installed in a 4' tall crawl space / short basement. Are there any accessibility code issues with installing batteries in a crawl space? Does the NEC address this? Thanks, Jerry Caldwell ___ List

Re: [RE-wrenches] Batteries

2015-12-12 Thread Roy Rakobitsch
I would think the 1 gal sprayer would be perfect for customers with smaller banks. When you start going through two, three or four gallons of distilled water at a time, i could see it getting tedious. Ive used an elevated 5Gal polyethylene tank with a 1/4" food grade hose connected to a small polye

Re: [RE-wrenches] Batteries

2015-12-12 Thread Roy Butler
Dan, We've been using the garden sprayer method for the last 14 years and it works great! Be sure to buy a sprayer with a plastic wand..the brass wands can create a bit too much excitement. Roy Butler NABCEP Certified Solar PV Installer® NYSERDA eligible

Re: [RE-wrenches] Batteries

2015-12-12 Thread Dan Fink
Hi Jerry; That's a great idea, I'm going to get one and try it next time I hit Home Depot. I also do not use automatic or central battery watering systems, as I feel they give a false sense of security. Nobody is in there regularly checking for loose connections and corrosion. My most important bat

[RE-wrenches] Batteries

2015-12-11 Thread Jerry Shafer
Wrenches, There has been allot of talk about batteries, i use allot of FLA and Edison type batteries. When we do an install i aways include a one gallon pump weed sprayer with distilled water, we cut the sprayer tip off and it is an easy and fast way to fill batteries, this is a cheap way too. Batt

Re: [RE-wrenches] Batteries in a dwelling - Venting Concorde AGMs

2014-07-29 Thread Dave Click
other non sparking conductive metals are great! -Original Message- From: re-wrenches-boun...@lists.re-wrenches.org <mailto:re-wrenches-boun...@lists.re-wrenches.org> [mailto:re-wrenches-boun...@lists.re-wrenches.org <mailto:re-wrenches-boun...@lists.re-wrenches.org>

Re: [RE-wrenches] Batteries in a dwelling - Venting Concorde AGMs

2014-07-29 Thread Glenn Burt
.@lists.re-wrenches.org] On Behalf Of Drake Sent: Tuesday, July 29, 2014 12:01 PM To: RE-wrenches Subject: Re: [RE-wrenches] Batteries in a dwelling - Venting Concorde AGMs This is a reply to a post by Alan from June 21st. I'm replying because I've had to deal with this issue also. It seems

Re: [RE-wrenches] Batteries in a dwelling - Venting Concorde AGMs

2014-07-29 Thread Steve Higgins
29, 2014 9:01 AM To: RE-wrenches Subject: Re: [RE-wrenches] Batteries in a dwelling - Venting Concorde AGMs This is a reply to a post by Alan from June 21st. I'm replying because I've had to deal with this issue also. It seems to me that the 2014 NEC Handbook is fairly clear that we ar

Re: [RE-wrenches] Batteries in a dwelling - Venting Concorde AGMs

2014-07-29 Thread Drake
opper, aluminum, and other non sparking conductive metals are great! -Original Message- From: <mailto:re-wrenches-boun...@lists.re-wrenches.org>re-wrenches-boun...@lists.re-wrenches.org [mailto:re-wrenches-boun...@lists.re-wrenches.org]On Behalf Of <mailto:will...@millersolar.

Re: [RE-wrenches] Batteries in a dwelling - Venting Concorde AGMs

2014-06-21 Thread Jerry Shafer
---Original Message- > *From:* re-wrenches-boun...@lists.re-wrenches.org [ > mailto:re-wrenches-boun...@lists.re-wrenches.org > ]*On Behalf Of * > will...@millersolar.com > *Sent:* April 4, 2014 9:29 AM > *To:* RE-wrenches > *Subject:* [RE-wrenches] Batteries in a dwelling > >

Re: [RE-wrenches] Batteries in a dwelling - Venting Concorde AGMs

2014-06-21 Thread Bob Clark
uctive metals are great! > > > > -Original Message- > From: re-wrenches-boun...@lists.re-wrenches.org > [mailto:re-wrenches-boun...@lists.re-wrenches.org]On Behalf Of > will...@millersolar.com > Sent: April 4, 2014 9:29 AM > To: RE-wrenches > Subject: [R

[RE-wrenches] Batteries in a dwelling

2014-04-04 Thread william
Friends: I am proposing installation of vented batteries in a first floor garage of a dwelling. The dwelling areas are on the second floor. I am nervous about the cohabitation of batteries and humans. I reviewed the NEC and could not find any prohibition. Do any of you have any advice on

Re: [RE-wrenches] Batteries and customer service

2013-03-18 Thread Lou Russo
Wrenches, Thanks for all insight. Cheers, Lou On Fri, Mar 15, 2013 at 1:49 PM, Larry Crutcher, Starlight Solar Power Systems wrote: > Lou, > > In addition to what Allan said, if you perform the discharge test, measure > the terminal voltage across each battery. If you find one battery that

Re: [RE-wrenches] Batteries and customer service

2013-03-15 Thread Larry Crutcher, Starlight Solar Power Systems
Lou, In addition to what Allan said, if you perform the discharge test, measure the terminal voltage across each battery. If you find one battery that drops in voltage more than the others, continue to check/record that voltage over time. This method will expose a weak or bad cell in a series s

Re: [RE-wrenches] Batteries and customer service

2013-03-15 Thread William Miller
Lou: Allan presents the better advice below. Ignore my previous post until you are sure the battery is bad. William Miller At 02:57 PM 3/15/2013, you wrote: Lou, There is nothing in your message that definitively tells me that you have either a bad cell or a bad battery. "Minor corrosion

Re: [RE-wrenches] Batteries and customer service

2013-03-15 Thread William Miller
Lou: At 1 year you are just within the allowable window. I would monitor the bank over the next two months after replacement to see if the SG remains consistent from cell to cell. William Miller At 01:38 PM 3/15/2013, you wrote: Hello Wrenches, Assuming the one battery is bad, is it wo

Re: [RE-wrenches] Batteries and customer service

2013-03-15 Thread Allan Sindelar
Lou, There is nothing in your message that definitively tells me that you have either a bad cell or a bad battery. "Minor corrosion on one terminal" is normal behavior, especially if the installer didn't coat the terminals at installation. "One cell was not using

[RE-wrenches] Batteries and customer service

2013-03-15 Thread Lou Russo
Hello Wrenches, This is my first go around here in the mailing list. I ve been a "lurker" for years, I much appreciate all the insight you all have provided. Here is the situation: I have a client with 12 Interstate UL16HCs (24v system, 3 x 4 battery bank) purchased and installed exactly 12 mont

[RE-wrenches] Batteries, between 7s and 8s

2011-08-25 Thread William Miller
Friends: I went to a customer's home last week that was reporting batteries boiling dry. I found that he had removed one battery and not replaced it. There was one string of 8 L-16s paralleled with one string of 7 L-16s. Needless to say, the seven batteries were toast. I thought I had see

Re: [RE-wrenches] Batteries in parrallel Failure

2011-04-20 Thread bob ellison
From: re-wrenches-boun...@lists.re-wrenches.org [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Brian Teitelbaum Sent: Wednesday, April 20, 2011 2:50 PM To: RE-wrenches Subject: Re: [RE-wrenches] Batteries in parrallel Failure Does anyone know of a manufacturer or

Re: [RE-wrenches] Batteries in parrallel Failure

2011-04-20 Thread R Ray Walters
rather than multiple strings. My design rule: > no more than two strings in parallel. > > Larry Crutcher > Starlight Solar Power Systems > www.starlightsolar.com > 928-342-9103 > > ----- Original Message ----- > From: Darryl Thayer > To: RE-wrenches > Sent: Tuesday,

Re: [RE-wrenches] Batteries in parrallel Failure

2011-04-20 Thread Starlight Solar, Larry Crutcher
: Tuesday, April 19, 2011 7:29 PM Subject: [RE-wrenches] Batteries in parrallel Failure Batteries in parallel, How to protect from catastrophic failure. I just got contacted to commission a solar system off grid not of my design. Eight battery strings in parallel, AGM batteries, 24 volts @ 12

Re: [RE-wrenches] Batteries in parrallel Failure

2011-04-20 Thread Hugh
At 21:18 -0600 19/4/11, Dan Fink wrote: He instinctively hit the main DC buss bar breakers, which was logical but didn't of course help the fire situation.and the result was that all Outback electronics from charge controllers to the 2 inverter set being fried from too high DC volt

Re: [RE-wrenches] Batteries in parrallel Failure

2011-04-20 Thread Brian Teitelbaum
-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Tom Elliot Sent: Wednesday, April 20, 2011 11:36 AM To: RE-wrenches Subject: Re: [RE-wrenches] Batteries in parrallel Failure What? No royalties? Damn...(but thanks for the props) Sorry I misunderstood what you meant. My installs of buss bars

Re: [RE-wrenches] Batteries in parrallel Failure

2011-04-20 Thread Tom Elliot
failure, though I guess that’s how we learn. Tom From: R Ray Walters Sent: Wednesday, April 20, 2011 8:16 AM To: RE-wrenches Subject: Re: [RE-wrenches] Batteries in parrallel Failure Tom; That's exactly what Daryl and I were suggesting: all strings paralleled to a central combiner box

Re: [RE-wrenches] Batteries in parrallel Failure

2011-04-20 Thread Bob-O Schultze
nsiderations are > pretty minor and cheap insurance against disaster. > > Tom > > > > From: R Ray Walters > Sent: Tuesday, April 19, 2011 6:01 PM > To: RE-wrenches > Subject: Re: [RE-wrenches] Batteries in parrallel Failure > > I like the fused paralle

Re: [RE-wrenches] Batteries in parrallel Failure

2011-04-20 Thread R Ray Walters
> > > From: R Ray Walters > Sent: Tuesday, April 19, 2011 6:01 PM > To: RE-wrenches > Subject: Re: [RE-wrenches] Batteries in parrallel Failure > > I like the fused parallel idea; could save the system, and would make battery > troubleshooting nice. > I would su

Re: [RE-wrenches] Batteries in parrallel Failure

2011-04-20 Thread jay peltz
HI Dan, I"m really curious about what the CC saw. Can you tell us, was it hydro, pv or wind and what was the voc? jay peltz power On Apr 19, 2011, at 8:18 PM, Dan Fink wrote: > We almost had a house fire in the neighborhood a couple months ago from a > parallel battery bank failurean agi

Re: [RE-wrenches] Batteries in parallel Failure

2011-04-19 Thread William Miller
Friends: I have seen 200 A T series fuses bolted directly to the battery terminals (I've even bolted a 175A breaker to a flag terminal!). Might this be a crude but effective method to obtain inter-array OC protection? Wm At 08:41 PM 4/19/2011, you wrote: I have now been close to three batt

Re: [RE-wrenches] Batteries in parrallel Failure

2011-04-19 Thread Tom Elliot
safety standpoint those considerations are pretty minor and cheap insurance against disaster. Tom From: R Ray Walters Sent: Tuesday, April 19, 2011 6:01 PM To: RE-wrenches Subject: Re: [RE-wrenches] Batteries in parrallel Failure I like the fused parallel idea; could save the system, and would

Re: [RE-wrenches] Batteries in parrallel Failure

2011-04-19 Thread R Ray Walters
I like the fused parallel idea; could save the system, and would make battery troubleshooting nice. I would suggest #6 jumpers with 50 to 60 amp breakers, so the system could be operated on just a few strings if needed. R. Walters r...@solarray.com Solar Engineer On Apr 19, 2011, at 8:29 PM

Re: [RE-wrenches] Batteries in parrallel Failure

2011-04-19 Thread Darryl Thayer
.  From: Dan Fink To: RE-wrenches Sent: Tue, April 19, 2011 10:18:48 PM Subject: Re: [RE-wrenches] Batteries in parrallel Failure We almost had a house fire in the neighborhood a couple months ago from a parallel battery bank failurean aging 2x8 L16 48v battery bank (16 of

Re: [RE-wrenches] Batteries in parrallel Failure

2011-04-19 Thread Dan Fink
We almost had a house fire in the neighborhood a couple months ago from a parallel battery bank failurean aging 2x8 L16 48v battery bank (16 of them), and one bat in bank one got a short and thermal runaway. I teach in my firefighter safety classes that thermal runaway is really rare, but i

[RE-wrenches] Batteries in parrallel Failure

2011-04-19 Thread Darryl Thayer
Batteries in parallel, How to protect from catastrophic failure. I just got contacted to commission a solar system off grid not of my design.   Eight battery strings in parallel, AGM batteries, 24 volts @ 120 AH each string (two 12 volt in series)  New system, new batteries, Silent POwer Inverte

[RE-wrenches] Batteries with no charge controller

2009-12-02 Thread Larry Crutcher, Starlight Solar
Remember when? Yes, just yesterday. I get more than a few tightwad, penny pinchers in our store and no matter what I say they are going to do it THEIR way. Quote: "I watch my meter and unhook the panel if it get's to 13 volts" I'm not kidding. Another quote: "Life's tough, ...it's even toughe

Re: [RE-wrenches] batteries

2009-03-06 Thread Ezra Auerbach
00 Ahr @20 hour rate battery. Jamie says they should be shipping with in next few weeks. Contact me off list FNI. Sent via BlackBerry by AT&T -Original Message- From: "Jeff Blick" Date: Thu, 5 Mar 2009 20:45:46 To: Subject: [RE-wrenches] batteries __

Re: [RE-wrenches] batteries

2009-03-05 Thread tump
Surrette has a new 2 volt "L 16" size,1100 Ahr @20 hour rate battery. Jamie says they should be shipping with in next few weeks. Contact me off list FNI. Sent via BlackBerry by AT&T -Original Message- From: "Jeff Blick" Date: Thu, 5 Mar 2009 20:45:46 To

Re: [RE-wrenches] batteries

2009-03-05 Thread William Miller
Jeff: Can your client maintain batteries? The IBE 85N-13 is 627 AH of FLA. One string is too small, two strings is too large, so you may need to keep looking. I would add that we have had only one failure in 20 plus years of use. The MK-8A8DLTP Deka is 245 amp hours of AGM. Three strings

[RE-wrenches] batteries

2009-03-05 Thread Jeff Blick
Hi wrenches, I am looking for a quality battery to use in the 700-900 amp hour range. Anyone have any suggestions as to a good product in this range? Jeff Blick Lead PV Installer Sunlight Solar Energy, Inc. direct: 541-306-4196 fax: 541-322-1911 jeff.bl...@sunlightsolar.com www.sunlights