Jeff:

Can your client maintain batteries?

The IBE 85N-13 is 627 AH of FLA. One string is too small, two strings is too large, so you may need to keep looking. I would add that we have had only one failure in 20 plus years of use.

The MK-8A8DLTP Deka is 245 amp hours of AGM. Three strings would meet your requirements and is within most installers recommended string maximum. We have had excellent results with the VRLA batteries although the oldest sites are floating on grid. The off-grid installations we have (that cycle daily) are newer so we have less data.

Good luck.

William Miller


At 08:45 PM 3/5/2009, you wrote:
Hi wrenches,
I am looking for a quality battery to use in the 700-900 amp hour range. Anyone have any suggestions as to a good product in this range?

Jeff Blick
_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to