Re: [RE-wrenches] Sol-Ark Dark Mode

2025-07-10 Thread Poole, Jharen via RE-wrenches
, July 10, 2025 10:29 AM To: RE-wrenches Cc: rol...@renewablenergy.com ; RE-wrenches Subject: Re: [RE-wrenches] Sol-Ark Dark Mode Caution: This email is from an external source. This is an issue with there newest module si believe SN starting with 24 and on, you just need to call them for a

Re: [RE-wrenches] Sol-Ark Dark Mode

2025-07-10 Thread Roland - RES via RE-wrenches
This is an issue with there newest module si believe SN starting with 24 and on, you just need to call them for a firmware update to resolve issue.Roland ShackelfordPresident / OwnerNABCEP PVIP #091209-162Office 808.775.7410Mobile 808.938.9239Power Solutions for Generations Renewable Energy Service

Re: [RE-wrenches] Sol-Ark Dark Mode

2025-07-10 Thread MDElectricSolar via RE-wrenches
The new -LV units have been coming that way for some reason. It takes specific firmware updates to resolve. We've had to deal with Solark Tech Support during this process multiple times now. There is no ultimate downside to the darker screen but it is strange that it is even happening.Michael D Nel

Re: [RE-wrenches] Sol-Ark Dark Mode

2025-07-10 Thread Jay via RE-wrenches
Faulty display?On Jul 10, 2025, at 7:39 AM, Dave Tedeyan via RE-wrenches wrote:Hi All, Does anyone know what it means when a Sol-Ark display goes into dark mode? Instead of the normal white background and coloring, the background goes to black, and the arrows are purple. I've talked to tech suppo

[RE-wrenches] Sol-Ark Dark Mode

2025-07-10 Thread Dave Tedeyan via RE-wrenches
Hi All, Does anyone know what it means when a Sol-Ark display goes into dark mode? Instead of the normal white background and coloring, the background goes to black, and the arrows are purple. I've talked to tech support, and all they would tell me is that it is "not good". We reset the dongle and

Re: [RE-wrenches] Sol-Ark 15K Gen on Grid Terminal (with GTBB)

2025-07-03 Thread Jay via RE-wrenches
Sent: Thursday, July 3, 2025 3:10:07 PM To: RE-wrenches <re-wrenches@lists.re-wrenches.org> Cc: Jason Szumlanski <ja...@floridasolardesigngroup.com> Subject: Re: [RE-wrenches] Sol-Ark 15K Gen on Grid Terminal (with GTBB)   This guy wants the smart load capability, too. Jason

Re: [RE-wrenches] Sol-Ark 15K Gen on Grid Terminal (with GTBB)

2025-07-03 Thread Jason Szumlanski via RE-wrenches
lLlCOGet Outlook fo <https://aka.ms/o0ukef> > -- > *From:* RE-wrenches on behalf > of Jason Szumlanski via RE-wrenches > *Sent:* Thursday, July 3, 2025 3:10:07 PM > *To:* RE-wrenches > *Cc:* Jason Szumlanski > *Subject:* Re: [RE-wrenches] Sol-Ark 15K Gen on G

Re: [RE-wrenches] Sol-Ark 15K Gen on Grid Terminal (with GTBB)

2025-07-03 Thread Lloyd Hoffstatter via RE-wrenches
Jason Szumlanski via RE-wrenches Sent: Thursday, July 3, 2025 3:10:07 PM To: RE-wrenches Cc: Jason Szumlanski Subject: Re: [RE-wrenches] Sol-Ark 15K Gen on Grid Terminal (with GTBB) This guy wants the smart load capability, too. Jason On Thu, Jul 3, 2025 at 8:42 AM Jay via RE-wrenches mailto:re-wr

Re: [RE-wrenches] Sol-Ark 15K Gen on Grid Terminal (with GTBB)

2025-07-03 Thread Jason Szumlanski via RE-wrenches
This guy wants the smart load capability, too. Jason On Thu, Jul 3, 2025 at 8:42 AM Jay via RE-wrenches < re-wrenches@lists.re-wrenches.org> wrote: > It’s got generator input terminals. > Why not use them for the generator? > > > On Jul 3, 2025, at 5:05 AM, Jason Szumlanski via RE-wrenches <

Re: [RE-wrenches] Sol-Ark 15K Gen on Grid Terminal (with GTBB)

2025-07-03 Thread Jay via RE-wrenches
It’s got generator input terminals. Why not use them for the generator? > On Jul 3, 2025, at 5:05 AM, Jason Szumlanski via RE-wrenches > wrote: > >  > The attached wiring diagram from the manual shows both a generator and grid > connected to the Sol-Ark Grid input with a transfer switch to

Re: [RE-wrenches] Sol-Ark Technical Question

2025-06-18 Thread Drake Chamberlin via RE-wrenches
E-wrenches on behalf of Jason Szumlanski via RE-wrenches Sent: Wednesday, June 4, 2025 10:10 AM To: RE-wrenches Cc: Jason Szumlanski ; Wodenrobert23 Subject: Re: [RE-wrenches] Sol-Ark Technical Question Caution: This email is from an external source. If I understand the question correctly, y

Re: [RE-wrenches] Sol-Ark Tech Support - Getting Nowhere

2025-06-16 Thread Peter Giroux via RE-wrenches
From: RE-wrenches On Behalf Of Jason Szumlanski via RE-wrenches Sent: Sunday, June 15, 2025 5:28 PM To: david quattro Cc: Jason Szumlanski ; RE-wrenches Subject: Re: [RE-wrenches] Sol-Ark Tech Support - Getting Nowhere I'm not sure that I have standing. I did not purchase the inverter.

Re: [RE-wrenches] Sol-Ark Tech Support - Getting Nowhere

2025-06-15 Thread Jason Szumlanski via RE-wrenches
I'm not sure that I have standing. I did not purchase the inverter. And I do not own the inverter. I simply installed it. But I do like the idea. I have not tried to switch the master slave relationship of the system, but that is not really the issue. Sol-Ark can see the dongle on their end, but t

Re: [RE-wrenches] Sol-Ark Tech Support - Getting Nowhere

2025-06-15 Thread david quattro via RE-wrenches
sounds like you don’t want to take them to small claims court. I found it to be easy and very effective. Did you try switching which inverter is the lead vs follower? On Tue, Jun 10, 2025 at 4:07 PM Jason Szumlanski via RE-wrenches < re-wrenches@lists.re-wrenches.org> wrote: > I’m once again

[RE-wrenches] Sol-Ark Tech Support - Getting Nowhere

2025-06-10 Thread Jason Szumlanski via RE-wrenches
I’m once again dealing with a painful support experience from Sol-Ark that’s confirming the broader concerns we’ve all been talking about. Today a customer's system went completely down due to an AC coupling issue that seems to have been triggered by a factory reset I was instructed to perform on

Re: [RE-wrenches] Sol-Ark Technical Question

2025-06-04 Thread William Miller via RE-wrenches
enches > *Cc:* Jason Szumlanski ; Wodenrobert23 > > *Subject:* Re: [RE-wrenches] Sol-Ark Technical Question > > Caution: This email is from an external source. > > > If I understand the question correctly, you can use Time of Use to set the > maximum charge or sell powe

Re: [RE-wrenches] Sol-Ark Technical Question

2025-06-04 Thread Poole, Jharen via RE-wrenches
lf of Jason Szumlanski via RE-wrenches Sent: Wednesday, June 4, 2025 10:10 AM To: RE-wrenches Cc: Jason Szumlanski ; Wodenrobert23 Subject: Re: [RE-wrenches] Sol-Ark Technical Question Caution: This email is from an external source. If I understand the question correctly, you can use Time of Use t

Re: [RE-wrenches] Sol-Ark Technical Question

2025-06-04 Thread Jason Szumlanski via RE-wrenches
If I understand the question correctly, you can use Time of Use to set the maximum charge or sell power in watts for up to 6 time slots. I believe this will limit only the battery charge or discharge rate, however. I don't believe this will limit the total input (loads plus battery charging). You c

[RE-wrenches] Sol-Ark Technical Question

2025-06-04 Thread Drake Chamberlin via RE-wrenches
Sol-Ark has not been available to answer a question. We need to reduce the AC amperage input and output on a system. Tech support had assured us that this can be done, prior to installing the system. It is unclear how to do this. Does anyone know how to adjust the AC in and AC out maximum a

Re: [RE-wrenches] Sol-Ark Warranty Support

2025-06-04 Thread Daryl DeJoy via RE-wrenches
To me, and in our experience, Solaredge has the title in "jump through all our hoops, then when you've done that, we have more for you to jump through" along with long wait times for call backs and an absolutely useless chat feature. Daryl DeJoy Island Energy Storage On Wed, Jun 4, 2025, 10:15 AM

Re: [RE-wrenches] Sol-Ark Warranty Support

2025-06-04 Thread Tyrone Houck via RE-wrenches
That's interesting that you say Sol-Ark has been fast and competent in comparison to solaredge... that hasn't been my experience at all. In my dealings Sol-Ark has been responsive only when pressured repeatedly and confidently, required a large deposit for RMAs, reluctant to provide return labels,

Re: [RE-wrenches] Sol-Ark Warranty Support

2025-06-04 Thread david quattro via RE-wrenches
SMA, Fronius, and Generac all pay labor reimbursement. On Wed, Jun 4, 2025 at 6:09 AM Lou Russo via RE-wrenches < re-wrenches@lists.re-wrenches.org> wrote: > Aloha All, > > Unfortunately, we have found that emailing or calling Sol-Ark (and most > other manufacturers) daily about RMA's is the on

Re: [RE-wrenches] Sol-Ark Warranty Support

2025-06-04 Thread Lou Russo via RE-wrenches
Aloha All, Unfortunately, we have found that emailing or calling Sol-Ark (and most other manufacturers) daily about RMA's is the only way to move the ball forward. Even doing that it is, taking us about a month from the first tech support call to receiving the RMA unit. They did charge us a deposi

Re: [RE-wrenches] Sol-Ark Warranty Support

2025-06-04 Thread david quattro via RE-wrenches
A few years ago I took SolArk to small claims court. I kept meticulous records, logging months of their disappointing denials and botched tech support. SolArk legal department tried to shift legal jurisdiction from my local country to their Texas jurisdiction. It was an insult to my intelligence. N

[RE-wrenches] Sol-Ark Warranty Support

2025-06-04 Thread Jason Szumlanski via RE-wrenches
We have had this discussion before. I'm afraid to say – it's not getting any better. I have been dealing with a faulty 15K for months. I replaced boards after waiting an inordinate amount of time for parts. I fought with tech support over getting the unit replaced. They finally relented. Now all I

Re: [RE-wrenches] Sol-Ark battery calibration

2025-05-30 Thread Poole, Jharen via RE-wrenches
-wrenches] Sol-Ark battery calibration Caution: This email is from an external source. Dave I would say this: Few bible days ago, I worked in Semiconductor Manufacturing Equipment Service. We would send our Fluke DVMs, recorders and other measuring tools off to a lab to get calibrated so when we

Re: [RE-wrenches] Sol-Ark battery calibration

2025-05-29 Thread Maverick Brown via RE-wrenches
DaveI would say this:Few bible days ago, I worked in Semiconductor Manufacturing Equipment Service. We would send our Fluke DVMs, recorders and other measuring tools off to a lab to get calibrated so when we measured something, we knew what we were measuring. I’m not saying your DVM is out of calib

Re: [RE-wrenches] Sol-Ark battery calibration

2025-05-29 Thread Dave Tedeyan via RE-wrenches
3 E – d...@solarwork.com >> >> W - www. greatsolarworks.com www.solarwork.com >> >> *“Responsible Technologies for Responsible People since 1988!”* >> >> >> >> >> >> -- Forwarded message -- >> From: Dave Tedeyan via RE-wrenche

Re: [RE-wrenches] Sol-Ark battery calibration

2025-05-29 Thread Jay via RE-wrenches
e 1988!”   -- Forwarded message --From: Dave Tedeyan via RE-wrenches <re-wrenches@lists.re-wrenches.org>To: RE-wrenches <re-wrenches@lists.re-wrenches.org>Cc: Dave Tedeyan <d...@sungineersolar.com>Bcc: Date: Wed, 28 May 2025 19:32:13 +0000Subject: [RE-wrenches] Sol-Ark batte

Re: [RE-wrenches] Sol-Ark battery calibration

2025-05-29 Thread Dave Tedeyan via RE-wrenches
e Tedeyan > Bcc: > Date: Wed, 28 May 2025 19:32:13 + > Subject: [RE-wrenches] Sol-Ark battery calibration > Does anyone know whether you can calibrate the battery voltage on Sol-Ark > inverters? I am on site with two 12k-p inverters. My meter agrees with one > of them, and t

Re: [RE-wrenches] Sol-Ark battery calibration

2025-05-29 Thread Dana Orzel via RE-wrenches
Verify with a second or third meter. _ Dana OrzelGREAT SOLAR WORKS! C - 208.721.7003 E - d...@solarwork.com W - www. greatsolarworks.com www.solarwork.com "Respons

[RE-wrenches] Sol-Ark battery calibration

2025-05-28 Thread Dave Tedeyan via RE-wrenches
Does anyone know whether you can calibrate the battery voltage on Sol-Ark inverters? I am on site with two 12k-p inverters. My meter agrees with one of them, and the other inverter (the master) is displaying 0.6v lower than both my meter and the other inverter. I have gone through two tech support

[RE-wrenches] Sol-Ark parallel 8k and 12k

2025-04-05 Thread Dave Tedeyan via RE-wrenches
Hi All, I have just gotten myself into a pickle and so am posting this both as a note/warning too all, as well as seeing if anyone has tried this. I installed a small system with a Sol-Ark 12k a few years ago. The customer recently asked us to add some more power. An 8k was more than enough, so w

Re: [RE-wrenches] Sol-Ark parallel 8k and 12k

2025-03-20 Thread Michael Morningstar via RE-wrenches
I once did an install with eight 12Ks. Upon commissioning the system would throw a parallel fault and shut everything down. After a huge amount of time spent, going round and round with Sol-Ark we figured out that three of the inverters were 8Ks mislabeled as 12Ks. No worky! On Thu, Mar 20, 2025 a

Re: [RE-wrenches] Sol-Ark 12 integration

2024-11-20 Thread Maverick Brown via RE-wrenches
Ron What is the primary goal? To get more power on your loads? To get more grid export? I have installed a bunch of outback products and you can’t beat the surge capacity and longevity. As you well know. Solark has an excellent grid zero feature with CTs. Outback and Solark both will work wi

Re: [RE-wrenches] Sol-Ark 12 integration

2024-11-20 Thread solareagle--- via RE-wrenches
Just to further clarify, the Sol-Ark would be replacing the Outback stack and Rolls batteries, not trying to integrate those. Ron earthRight Solar - Solareagle.com > On Nov 20, 2024, at 1:35 PM, solareagle--- via RE-wrenches > wrote: > > I have a Sol-Ark 12, old stock, that I’m thinking of i

Re: [RE-wrenches] Sol-Ark 12 integration

2024-11-20 Thread Peter Giroux via RE-wrenches
...@solareagle.com Subject: [RE-wrenches] Sol-Ark 12 integration I have a Sol-Ark 12, old stock, that I’m thinking of installing at my residence, I have 14kW grid tie with enphase micro’s but want to add some Homegrid batteries for a backup option. I know it’s redundant to have the micros and the Sol-Ark

[RE-wrenches] Sol-Ark 12 integration

2024-11-20 Thread solareagle--- via RE-wrenches
I have a Sol-Ark 12, old stock, that I’m thinking of installing at my residence, I have 14kW grid tie with enphase micro’s but want to add some Homegrid batteries for a backup option. I know it’s redundant to have the micros and the Sol-Ark but I also have a separate system with nearly 4kW off

[RE-wrenches] Sol-Ark 12K AC Input LED Meaning

2024-11-09 Thread Jason Szumlanski via RE-wrenches
Hi all, This is just a PSA in case it helps someone in the future. I was under the impression that the AC Input LED on the Sol-Ark inverters meant that there is "good" AC detected by the inverter on the grid terminals and after some period of delay, something should start happening based on how th

Re: [RE-wrenches] Sol-Ark Gen Input

2024-10-28 Thread rick--- via RE-wrenches
Any decent meter will have a high input impedance on the Volts setting otherwise it would provide an inaccurate reading. Our customer, who first reported this, is an engineer with a well-known charge controller/inverter company. He used a cheap meter whereas I used a Fluke 87-5. Both had the same r

Re: [RE-wrenches] Sol-Ark Gen Input

2024-10-28 Thread Darryl Thayer via RE-wrenches
My first thought is what meter are you using? Some meter will have high input impedance and give false value On Tue, Oct 15, 2024 at 1:09 PM rick--- via RE-wrenches < re-wrenches@lists.re-wrenches.org> wrote: > Back on the Sol-Ark topic again. We have a customer whose 12kW is > measuring -195VDC

Re: [RE-wrenches] Sol-Ark Gen Input

2024-10-28 Thread rick--- via RE-wrenches
the roof wired to the DC inputs of your Sunny Boy? >>>>>> >>>>>> 2. Think to yourself: What component(s) on this project could possibly >>>>>> produce high voltage DC? >>>>>> >>>>>> I think the answer to bot

Re: [RE-wrenches] Sol-Ark Gen Input

2024-10-28 Thread Jay via RE-wrenches
CA 93422805-438-5600www.millersolar.comCA Lic. 773985  From: r...@solshineenergy.com [mailto:r...@solshineenergy.com] Sent: Tuesday, October 15, 2024 12:03 PMTo: will...@millersolar.com; RE-wrenchesSubject: Re: [RE-wrenches] Sol-Ark Gen Input William, There’s no PV on this system. It’s AC coupled to

Re: [RE-wrenches] Sol-Ark Gen Input

2024-10-28 Thread rick--- via RE-wrenches
ion that is producing the DC voltage on the Gen >>>> inputs. >>>> >>>> While you are at it, check DC voltages between the Sunny Boy DC inputs to >>>> ground and between the Sunny Boy Chassis and ground. >>>> >>>> Chec

Re: [RE-wrenches] Sol-Ark Gen Input

2024-10-16 Thread William Miller via RE-wrenches
between the Sunny Boy Chassis and ground. > > > Check your GEC, GEC bonding conductor and all of the system EGCs. > > > I would also check the GFDI fuse on the Sunny Boy. > > > William Miller > > > Miller Solar > 17395 Oak Road, Atascadero, CA 93422 > 805-438-5

Re: [RE-wrenches] Sol-Ark Gen Input

2024-10-16 Thread rick--- via RE-wrenches
PMTo: will...@millersolar.com; RE-wrenchesSubject: Re: [RE-wrenches] Sol-Ark Gen Input William, There’s no PV on this system. It’s AC coupled to an SMA SB5.0.  As a test, we turned off the Grid input, Load output, and turned off the battery breaker. As expected, the high voltage DC eventually bled to

Re: [RE-wrenches] Sol-Ark Gen Input

2024-10-16 Thread rick--- via RE-wrenches
shineenergy.com> > [mailto:r...@solshineenergy.com <mailto:r...@solshineenergy.com>] > Sent: Tuesday, October 15, 2024 12:03 PM > To: will...@millersolar.com <mailto:will...@millersolar.com>; RE-wrenches > Subject: Re: [RE-wrenches] Sol-Ark Gen Input > > Will

Re: [RE-wrenches] Sol-Ark Gen Input

2024-10-15 Thread William Miller via RE-wrenches
Oak Road, Atascadero, CA 93422 805-438-5600 www.millersolar.com CA Lic. 773985 *From:* r...@solshineenergy.com [mailto:r...@solshineenergy.com] *Sent:* Tuesday, October 15, 2024 12:03 PM *To:* will...@millersolar.com; RE-wrenches *Subject:* Re: [RE-wrenches] Sol-Ark Gen Input William

Re: [RE-wrenches] Sol-Ark Gen Input

2024-10-15 Thread rick--- via RE-wrenches
-wrenches.org > <mailto:re-wrenches-boun...@lists.re-wrenches.org>] On Behalf Of rick--- via > RE-wrenches > Sent: Tuesday, October 15, 2024 11:09 AM > To: RE-wrenches > Cc: r...@solshineenergy.com <mailto:r...@solshineenergy.com> > Subject: [RE-wrenches] Sol-Ark Gen

Re: [RE-wrenches] Sol-Ark Gen Input

2024-10-15 Thread William Miller via RE-wrenches
805-438-5600 www.millersolar.com CA Lic. 773985 *From:* RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] *On Behalf Of *rick--- via RE-wrenches *Sent:* Tuesday, October 15, 2024 11:09 AM *To:* RE-wrenches *Cc:* r...@solshineenergy.com *Subject:* [RE-wrenches] Sol-Ark Gen Input

[RE-wrenches] Sol-Ark Gen Input

2024-10-15 Thread rick--- via RE-wrenches
Back on the Sol-Ark topic again. We have a customer whose 12kW is measuring -195VDC to ground from L1 and L2 with the Gen breaker open. L1 to L2 = 0V. I know the Gen input can be configured as an output, but reading a high DC voltage to ground is concerning. The generator has never been run. Sys

Re: [RE-wrenches] sol ark battery

2024-10-10 Thread Poole, Jharen via RE-wrenches
f Michael Morningstar via RE-wrenches Sent: Thursday, October 10, 2024 2:33 PM To: RE-wrenches Cc: Michael Morningstar Subject: Re: [RE-wrenches] sol ark battery Caution: This email is from an external source. Just installed an AIO/Pflo16. The build quality and attention to detail make Sol-Ark

Re: [RE-wrenches] sol ark battery

2024-10-10 Thread Dave Tedeyan via RE-wrenches
Also, does anyone know the warranty period for those Powerflo batteries? I see a number of cycles specified, but not a number of years. Cheers, Dave On Thu, Oct 10, 2024 at 4:17 PM jay via RE-wrenches < re-wrenches@lists.re-wrenches.org> wrote: > HI Michael, > > Thats good news. > > Can you monit

Re: [RE-wrenches] sol ark battery

2024-10-10 Thread jay via RE-wrenches
HI Michael, Thats good news. Can you monitor the individual battery cells volts/temp from the app or inverter? I can’t get an answer on that one. jay > On Oct 10, 2024, at 1:33 PM, Michael Morningstar via RE-wrenches > wrote: > > Just installed an AIO/Pflo16. The build quality and attenti

Re: [RE-wrenches] sol ark battery

2024-10-10 Thread Michael Morningstar via RE-wrenches
Just installed an AIO/Pflo16. The build quality and attention to detail make Sol-Ark look like what I've always considered them to be, CCC. Had one glitch and Rick and Logan were there for me immediately. There's nothing like talking to an engineer that designed their gear. We'll be installing a fe

Re: [RE-wrenches] sol ark battery

2024-10-10 Thread Nick Lucchese via RE-wrenches
Wonderful to hear Howie. I have high hopes for many projects with Powerflo's. Hard to believe we can finally offer a battery solution with so many positive attributes by a trusted partner like Midnite for just $.25 a watt hour on the retail level. Discover has been saying it for a bit on some of th

Re: [RE-wrenches] sol ark battery

2024-10-10 Thread Howie Michaelson via RE-wrenches
Installed my first production model Midnite AIO with 2 PowerFlo 16 batteries, off grid. Still learning to finess the program structure, but the integration was plug and play and flawless. No internet at site yet and the internet monitoring app isn't released yet for general use, but the Bluetooth

Re: [RE-wrenches] sol ark battery

2024-10-10 Thread Nick Lucchese via RE-wrenches
Definitely appears that Midnite's new Powerflo batteries would be applicable as well since it supports the Pylon protocol. Appears to be a true game changer but have not received my first shipment yet for a full review. Nick On Wed, Oct 9, 2024 at 11:32 AM jay via RE-wrenches < re-wrenches@lists

Re: [RE-wrenches] sol ark battery

2024-10-10 Thread Carl Hansen via RE-wrenches
I've put in about Ten EG4 LL banks in the last 2 years, no problems with any of them, tech support is very good, they have a dedicated number for installers and someone always picks up, I like the digital screen with access to battery cell voltages, cell temps, amps, battery voltage and %.  The

Re: [RE-wrenches] sol ark battery

2024-10-10 Thread Mac Lewis via RE-wrenches
I like the Homegrid and the Sol-Ark communication seems perfect. However, the conduit entry for a code compliant installation is not logical at all, very awkward if you want it in conduit. Not sure what the intent was for a US installation to be inspected. Also, its a bit unclear how to ground i

Re: [RE-wrenches] sol ark battery

2024-10-10 Thread Dana Orzel via RE-wrenches
My first question & complaint for the Homegrid battery _ Dana OrzelGREAT SOLAR WORKS! C - 208.721.7003 E - d...@solarwork.com W - www. greatsolarworks.com www.solarwork.com

Re: [RE-wrenches] sol ark battery

2024-10-09 Thread Jason Szumlanski via RE-wrenches
To clarify, there IS closed loop comms between Sol-Ark and EG4, but the problem is the batteries mess up settings in the Sol-Ark that can cause erratic behavior. Sol-Ark recommends against implementing closed loop. It could plausibly work in some simple scenarios. But I don't physically connect it

Re: [RE-wrenches] sol ark battery

2024-10-09 Thread Jay via RE-wrenches
Good to know they don’t closed loop communicate, definitely preferably but not that big a deal in the end. So is the sol ark building a SOC or reading the battery SOC but it’s not able to use it for charging algorithm?I probably have either what I’ve sold or advised 200 x 5 kWh blocks or some versi

Re: [RE-wrenches] sol ark battery

2024-10-09 Thread Jay via RE-wrenches
Yes good call. The other major brands already figured that out by bussing internally which brings its own sort of issues. JayOn Oct 9, 2024, at 5:32 PM, Andrew Perkins wrote:Dont forget the Sol-Ark 15K Busbar kit.Andrew PerkinsGreenwired P: 707-923-2001 ext. 1001150 #1 Evergreen RdRedway, CA 9556

Re: [RE-wrenches] sol ark battery

2024-10-09 Thread Jason Szumlanski via RE-wrenches
I'm watching for responses with interest. Great question. We usually put a Jbox very close to the battery and use two glands to bring the cables in. I have a situation right now with a HomeGrid stack that has temporary cables run to it, and I need to protect the cables over a 10 foot run to the in

Re: [RE-wrenches] sol ark battery

2024-10-09 Thread Chris Sparadeo via RE-wrenches
Question for all you Homegrid installers…has anyone found a succinct way to run conduit from the battery enclosure to the Sol Ark? On Wed, Oct 9, 2024 at 7:39 PM Jason Szumlanski via RE-wrenches < re-wrenches@lists.re-wrenches.org> wrote: > Jay, > > I should mention I have a couple of customers w

Re: [RE-wrenches] sol ark battery

2024-10-09 Thread Jason Szumlanski via RE-wrenches
Jay, I should mention I have a couple of customers with big EG4 LifePower battery banks (i.e. 120kWh+, 80kWh, etc) and Sol-Arks. The clients purchased the batteries directly, so I didn't have a choice. I will say that the systems are performing flawlessly, but forget about closed loop comms and SO

Re: [RE-wrenches] sol ark battery

2024-10-09 Thread jay via RE-wrenches
Thats all super helpful, appreciate the advice everyone. I’ve not used the sol ark 15 and just wanted to make sure I wasn’t missing anything about battery options. And specifically the ones that don’t seem to play well. Jay > On Oct 9, 2024, at 2:56 PM, Jason Szumlanski via RE-wrenches >

Re: [RE-wrenches] sol ark battery

2024-10-09 Thread Jason Szumlanski via RE-wrenches
HomeGrid works great with Sol-Ark. Closed loop comms reports battery SOC from BMS. Parallel stacks install easily. Customer support is competent and patient, in my experience. The best part is the ability to easily add batteries. On Sunday I had a client with two stacks of five batteries each call

Re: [RE-wrenches] sol ark battery

2024-10-09 Thread MDElectricSolar via RE-wrenches
We’ve been installing the Tesla power wall 3 and have had zero issues, a very robust product, downside is no generator support.Michael D NelsonMD Electric & Solar, Inc.707-684-0064 mobile707-884-1862 officewww.mdelectricsolar.comwww.facebook.com/mdelectricandsolarOn Oct 9, 2024, at 1:24 PM, Dana Or

Re: [RE-wrenches] sol ark battery

2024-10-09 Thread Jerry Shafer via RE-wrenches
> > W - www. greatsolarworks.com www.solarwork.com > > *“Responsible Technologies for Responsible People since 1988!”* > > > > > > -- Forwarded message -- > From: david quattro via RE-wrenches > To: RE-wrenches > Cc: david quattro > Bcc:

Re: [RE-wrenches] sol ark battery

2024-10-09 Thread Dana Orzel via RE-wrenches
2 - Homegrid both required quite a bit of programming assistance not everyone who answered the phone was knowledgeable enough to get the fixes installed. 2 - Pytes fired up fine no issues. 2 - Solar Edge both required assistance, quick & simple fixes with Tech staff. I have a client who has start

Re: [RE-wrenches] sol ark battery

2024-10-09 Thread david quattro via RE-wrenches
I’ve had good experience with Homegrid so far. > > On Oct 9, 2024, at 11:32 AM, jay via RE-wrenches < > re-wrenches@lists.re-wrenches.org> wrote: > > > > HI All > > > > > > Wondering what people are using for lithium battery and sol ark? > > > > And no, LA is not a option for this system. > >

Re: [RE-wrenches] sol ark battery

2024-10-09 Thread Lou Russo via RE-wrenches
Discover Rack Mount (you have to buy the outdoor rated enclosure separately) - Software is great and firmware is easily updated, standard rack mount aesthetics (not great looking) when installed without enclosure. HomeGrid (outdoor rated included) - Software is half baked and firmware is a pain to

Re: [RE-wrenches] sol ark battery

2024-10-09 Thread MDElectricSolar via RE-wrenches
Discover, Fortress, Simpliphi (briggs and Stratton) Michael D Nelson MD Electric & Solar, Inc. 707-684-0064 mobile 707-884-1862 office www.mdelectricsolar.com www.facebook.com/mdelectricandsolar > On Oct 9, 2024, at 11:32 AM, jay via RE-wrenches > wrote: > > HI All > > > Wondering what peop

[RE-wrenches] sol ark battery

2024-10-09 Thread jay via RE-wrenches
HI All Wondering what people are using for lithium battery and sol ark? And no, LA is not a option for this system. Outdoor rated would be preferred, heated isn’t needed. thanks in advance jay ___ List sponsored by Redwood Alliance Pay optional

Re: [RE-wrenches] Sol-Ark 15K AC Coupling

2024-08-24 Thread david quattro via RE-wrenches
Sorry I just noticed that you’re dealing with 15Ks. My scenario was with a 12K ___ List sponsored by Redwood Alliance Pay optional member dues here: http://re-wrenches.org List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address

Re: [RE-wrenches] Sol-Ark 15K AC Coupling

2024-08-24 Thread Jason Szumlanski via RE-wrenches
That's interesting on two fronts. I believe the documentation says you can AC couple when off-grid with load side interconnected inverters. It would have to have some mechanism to turn off AC coupled sources for that to work. And it also says there is no modulation and it's on or off only. Strange

Re: [RE-wrenches] Sol-Ark 15K AC Coupling

2024-08-24 Thread david quattro via RE-wrenches
last year SolArk tech support told me only the Gen ports have the freq/volt modulation, and only when you program the master “AC Couple on GEN” ___ List sponsored by Redwood Alliance Pay optional member dues here: http://re-wrenches.org List Address: RE

Re: [RE-wrenches] Sol-Ark 15K AC Coupling

2024-08-24 Thread Jason Szumlanski via RE-wrenches
Hi Kirpal, This is hugely helpful. More than you can imagine. I actually brought this up with tech support because two of the inverters have Savant insignia on them. The first slave inverter does not have this insignia. I did not supply these inverters, as the customer already had them from anothe

Re: [RE-wrenches] Sol-Ark 15K AC Coupling

2024-08-24 Thread Kirpal Khalsa via RE-wrenches
Jason... We had a similar situation with a dual SolArk 15K system. After approximately an hour of turning system on we would get the F41 error on the master ‐ the slave inverter would show an error and then the master would shut down with the paralleling error F41 because the slave inverter had sho

Re: [RE-wrenches] Sol-Ark 15K AC Coupling

2024-08-24 Thread Peter Giroux via RE-wrenches
. Peter Giroux American Solar From: RE-wrenches On Behalf Of Jason Szumlanski via RE-wrenches Sent: Saturday, August 24, 2024 5:07 PM To: RE-wrenches Cc: Jason Szumlanski Subject: Re: [RE-wrenches] Sol-Ark 15K AC Coupling Good information. Thank you. I don't believe the Sol-A

Re: [RE-wrenches] Sol-Ark 15K AC Coupling

2024-08-24 Thread Jason Szumlanski via RE-wrenches
is possible that the Enphase system is not > responding, and the Inverter is shutting down to protect the batteries. > > Pieter Huebner > > Project Manager > > Off grid Enterprises > > > > *From:* RE-wrenches *On > Behalf Of *Jason Szumlanski via RE-wrenches >

Re: [RE-wrenches] Sol-Ark 15K AC Coupling

2024-08-24 Thread pieter offgridenterprises.org via RE-wrenches
Subject: [RE-wrenches] Sol-Ark 15K AC Coupling Hi all, Over the last three days I have had one of this infuriating and frustrating experiences with Sol-Ark where you talk to 3 people and get 10 different answers. At least I think I finally got the right one today. Here is the scenario and

[RE-wrenches] Sol-Ark 15K AC Coupling

2024-08-24 Thread Jason Szumlanski via RE-wrenches
Hi all, Over the last three days I have had one of this infuriating and frustrating experiences with Sol-Ark where you talk to 3 people and get 10 different answers. At least I think I finally got the right one today. Here is the scenario and problem I was experiencing: At a (very) remote locatio

Re: [RE-wrenches] Sol Ark 12 k PV monitoring

2024-07-29 Thread William Miller via RE-wrenches
-wrenches *Subject:* Re: [RE-wrenches] Sol Ark 12 k PV monitoring Does this unit have a touchscreen? Can you touch the settings wheel and get into the settings that way? Michael D Nelson MD Electric & Solar, Inc. 707-684-0064 mobile 707-884-1862 office www.mdelectricsolar.com www.facebook

Re: [RE-wrenches] Sol Ark 12 k PV monitoring

2024-07-29 Thread MDElectricSolar via RE-wrenches
ject: Re: [RE-wrenches] Sol Ark 12 k PV monitoring On the touchscreen, touch the battery icon, you will find it there. On Mon, Jul 29, 2024 at 8:52 PM William Miller via RE-wrenches <re-wrenches@lists.re-wrenches.org> wrote:Friends: I have been through the manual and I can’t find anywhere where

Re: [RE-wrenches] Sol Ark 12 k PV monitoring

2024-07-29 Thread William Miller via RE-wrenches
.com; RE-wrenches *Subject:* Re: [RE-wrenches] Sol Ark 12 k PV monitoring On the touchscreen, touch the battery icon, you will find it there. On Mon, Jul 29, 2024 at 8:52 PM William Miller via RE-wrenches < re-wrenches@lists.re-wrenches.org> wrote: Friends: I have been through the ma

Re: [RE-wrenches] Sol Ark 12 k PV monitoring

2024-07-29 Thread MD Electric & Solar via RE-wrenches
On the touchscreen, touch the battery icon, you will find it there. On Mon, Jul 29, 2024 at 8:52 PM William Miller via RE-wrenches < re-wrenches@lists.re-wrenches.org> wrote: > Friends: > > > > I have been through the manual and I can’t find anywhere where you can see > on the inverter front pane

[RE-wrenches] Sol Ark 12 k PV monitoring

2024-07-29 Thread William Miller via RE-wrenches
Friends: I have been through the manual and I can’t find anywhere where you can see on the inverter front panel the PV volts or amps for each of the MPPT inputs. Am I missing something? Thanks, William Miller Miller Solar 17395 Oak Road, Atascadero, CA 93422 805-438-5600 www.millers

Re: [RE-wrenches] Sol-Ark with 800A Service

2024-07-18 Thread Chris Sparadeo via RE-wrenches
FYI Sol Ark sales engineer has suggested the following: “For the 15K, we've recommended AcuCT R Series - AcuCT-4161R-800:100mA | Accuenergy with 100mA output. On the inverter, you will need to adjust the CT ratio to 8000:1. Also note t

Re: [RE-wrenches] Sol-Ark with 800A Service

2024-07-18 Thread Kirk Herander via RE-wrenches
As an aside, I ran into this with a Fortress True 12kw. (As of several months ago) They have not tested parallel CTs, nor have they tested single CTs in any service above 200A. They would not approve my plan to parallel CTs on a parallel conductor, 400A service. Fortress does have an input for a 3

Re: [RE-wrenches] Sol-Ark with 800A Service

2024-07-18 Thread Jason Szumlanski via RE-wrenches
You should be able to parallel 6 CTs (3 per phase) as long as you get the phases and directions right. The question really comes down to whether the Sol-Ark can handle the current from 800A at the CT ratio (which I believe is 2000:1). For practical purposes, on an 800A service, particularly residen

Re: [RE-wrenches] Sol-Ark with 800A Service

2024-07-18 Thread Chris Sparadeo via RE-wrenches
Hi Jason, Sorry for not clarifying. This is a export limited scenario, so CTs would still be required. On Thu, Jul 18, 2024 at 6:51 AM Jason Szumlanski < ja...@floridasolardesigngroup.com> wrote: > This may or may not be helpful, but are you sure you need the CTs? They > are not always require

Re: [RE-wrenches] Sol-Ark with 800A Service

2024-07-18 Thread Jason Szumlanski via RE-wrenches
This may or may not be helpful, but are you sure you need the CTs? They are not always required. You would need them for power export limiting or grid peak shaving, but for straight grid-tied with or without battery backup, you don't need them. Jason Szumlanski Florida Solar Design Group On We

Re: [RE-wrenches] Sol-Ark with 800A Service

2024-07-17 Thread david quattro via RE-wrenches
Hi Chris, I’ve asked them if they are compatible with rope CTs and they aren’t…. Please share the solution you arrive at, as I know I’ll need to repeat it soon. David ___ List sponsored by Redwood Alliance Pay optional member dues here: http://re-wre

[RE-wrenches] Sol-Ark with 800A Service

2024-07-17 Thread Chris Sparadeo via RE-wrenches
Hey there wrenchers, I am working on a larger project with 6 Sol-Ark 15K units and an 800A service. The main service conductors are 3 parallel runs of 400 kcmil. I am wondering how to CT these conductors from the master inverter. Sol Ark tech support has not been very helpful so far. I have the in

Re: [RE-wrenches] Sol-Ark 15k solar panel frame grounding

2024-06-06 Thread Christopher Warfel via RE-wrenches
essage. *From:* RE-wrenches on behalf of William Miller via RE-wrenches *Sent:* Wednesday, June 5, 2024 12:53:52 PM *To:* RE-wrenches *Cc:* William Miller *Subject:* Re: [RE-wrenches] Sol-Ark 15k solar panel frame grounding Friends: On a r

Re: [RE-wrenches] Sol-Ark 15k solar panel frame grounding

2024-06-05 Thread david quattro via RE-wrenches
in their installation manuals, SolArk indicates black and red colors for PV conductors. ___ List sponsored by Redwood Alliance Pay optional member dues here: http://re-wrenches.org List Address: RE-wrenches@lists.re-wrenches.org Change listserver email

Re: [RE-wrenches] Sol-Ark 15k solar panel frame grounding

2024-06-05 Thread Eric Smiley via RE-wrenches
complicated!” > > > > William Miller > > > > Miller Solar > > 17395 Oak Road, Atascadero, CA 93422 > > 805-438-5600 > > www.millersolar.com > > CA Lic. 773985 > > > > > > *From:* RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org]