Yes, that’s my expectation. The output is at such a high impedance that as soon 
as you put any load on it, it would drop to 0.

> On Oct 28, 2024, at 9:49 AM, Jay via RE-wrenches 
> <re-wrenches@lists.re-wrenches.org> wrote:
> 
> It would be interesting to see if there is power there. Like put a low 
> wattage 120v incandescent light bulb on it. 
> 
> If it was static wouldn’t the meter drain the volts?  
> 
> Jay
> 
>> On Oct 28, 2024, at 7:31 AM, rick--- via RE-wrenches 
>> <re-wrenches@lists.re-wrenches.org> wrote:
>> 
>> An update on this “issue”. Sol-Ark Tech Support said that the high voltage 
>> DC is normal and not a concern. I believe they said it was a “static” 
>> voltage. They didn’t really provide an answer as to why it’s present. But I 
>> stick to my hypothesis that the source is the H-Bridge drive circuitry. 
>> 
>> William, to your point, I’m not thrilled that there’s a DC voltage on the AC 
>> output. But given that these units have been in operation for years without 
>> issue related to this input/output I’m not too worried.
>> 
>> Thanks everyone!
>> 
>>> On Oct 16, 2024, at 11:09 PM, William Miller <will...@millersolar.com> 
>>> wrote:
>>> 
>>> Rick:
>>> 
>>> You’re OK leaving this random high voltage DC on the AC output?
>>> 
>>> William Miller
>>> Miller Solar.com
>>> 805-438-5600
>>> www.millersolar.com <http://www.millersolar.com/>
>>> 
>>> 
>>> On Wed, Oct 16, 2024 at 6:09 PM r...@solshineenergy.com 
>>> <mailto:r...@solshineenergy.com> <r...@solshineenergy.com 
>>> <mailto:r...@solshineenergy.com>> wrote:
>>>> Confirmed! Reading the same points on a different inverter yielded the 
>>>> same results. At a different site, I measured -188.8VDC to ground on both 
>>>> L1 and L2. 
>>>> 
>>>> My suspicion is that there’s leakage current via the H-bridge output. Just 
>>>> a thought. 
>>>> 
>>>> Case closed, thanks. 
>>>> 
>>>> Rick Brown
>>>> Solshine Energy 
>>>> Solar Electric Contracting Services 
>>>> www.solshineenergy.com <http://www.solshineenergy.com/>
>>>> Roanoke, VA
>>>> Office: 540.235.3095
>>>> Mobile: 540.808.9502
>>>> CONFIDENTIALITY NOTICE -- This email is intended only for the person(s) 
>>>> named in
>>>> 
>>>> the message header. Unless otherwise indicated, it contains information 
>>>> that is
>>>> 
>>>> confidential, privileged and/or exempt from disclosure under applicable 
>>>> law. If you have
>>>> 
>>>> received this message in error, please notify the sender of the error and 
>>>> delete the
>>>> 
>>>> message. Thank you.
>>>> 
>>>> 
>>>> 
>>>>> On Oct 16, 2024, at 3:49 PM, r...@solshineenergy.com 
>>>>> <mailto:r...@solshineenergy.com> wrote:
>>>>> 
>>>>> Sorry I wasn’t clear. There’s no PV tied directly to the Sol-Ark however 
>>>>> the Sunny Boy has 5.52 kW of PV. Again the SB is AC coupled to the 
>>>>> Sol-Ark via its Load input/output.
>>>>> 
>>>>> I can assure you that the DC is not coming from an external source. There 
>>>>> are no faults at either inverter (measured or indicated by the 
>>>>> inverter(s)). Both systems are operating normally.
>>>>> 
>>>>> I’ll be looking at another site to verify whether these readings are 
>>>>> consistent or an anomaly.
>>>>> 
>>>>> Thanks,
>>>>> Rick
>>>>> 
>>>>>> On Oct 15, 2024, at 3:49 PM, William Miller via RE-wrenches 
>>>>>> <re-wrenches@lists.re-wrenches.org 
>>>>>> <mailto:re-wrenches@lists.re-wrenches.org>> wrote:
>>>>>> 
>>>>>> Rick:
>>>>>>  
>>>>>> Two questions:
>>>>>>  
>>>>>> 1.   If you don’t have PV on this system, what are those glassy, flat 
>>>>>> things on the roof wired to the DC inputs of your Sunny Boy?
>>>>>>  
>>>>>> 2.   Think to yourself: What component(s) on this project could possibly 
>>>>>> produce high voltage DC?
>>>>>>  
>>>>>> I think the answer to both questions is… PV panels.  I highly suspect 
>>>>>> you have a PV ground fault.  Proceed with caution.
>>>>>>  
>>>>>> On the Sunny Boy I would check the DC voltage between L1 and ground, 
>>>>>> between L2 and ground and between neutral and ground.  Do this in the 
>>>>>> operational configuration that is producing the DC voltage on the Gen 
>>>>>> inputs.
>>>>>>  
>>>>>> While you are at it, check DC voltages between the Sunny Boy DC inputs 
>>>>>> to ground and between the Sunny Boy Chassis and ground.
>>>>>>  
>>>>>> Check your GEC, GEC bonding conductor and all of the system EGCs.
>>>>>>  
>>>>>> I would also check the GFDI fuse on the Sunny Boy.  
>>>>>>  
>>>>>> William Miller
>>>>>>  
>>>>>> Miller Solar
>>>>>> 17395 Oak Road, Atascadero, CA 93422
>>>>>> 805-438-5600
>>>>>> www.millersolar.com <http://www.millersolar.com/>
>>>>>> CA Lic. 773985
>>>>>>  
>>>>>>  
>>>>>> From: r...@solshineenergy.com <mailto:r...@solshineenergy.com> 
>>>>>> [mailto:r...@solshineenergy.com <mailto:r...@solshineenergy.com>] 
>>>>>> Sent: Tuesday, October 15, 2024 12:03 PM
>>>>>> To: will...@millersolar.com <mailto:will...@millersolar.com>; RE-wrenches
>>>>>> Subject: Re: [RE-wrenches] Sol-Ark Gen Input
>>>>>>  
>>>>>> William,
>>>>>>  
>>>>>> There’s no PV on this system. It’s AC coupled to an SMA SB5.0. 
>>>>>>  
>>>>>> As a test, we turned off the Grid input, Load output, and turned off the 
>>>>>> battery breaker. As expected, the high voltage DC eventually bled to 0V. 
>>>>>> Turning things on in this order: Battery, Grid, then Load resulted in 
>>>>>> the high voltage appearing once the Grid relay kicked on. Actually, the 
>>>>>> high voltage ramped up slowly once the Grid relay turned on.
>>>>>>  
>>>>>> We’ve been installing these for years and have never seen this. Then 
>>>>>> again, we’ve never measured that point.
>>>>>> 
>>>>>> 
>>>>>> On Oct 15, 2024, at 2:32 PM, William Miller via RE-wrenches 
>>>>>> <re-wrenches@lists.re-wrenches.org 
>>>>>> <mailto:re-wrenches@lists.re-wrenches.org>> wrote:
>>>>>>  
>>>>>> Rick:
>>>>>>  
>>>>>> If I had to guess I’d say you have a PV wiring fault.  The PV positive 
>>>>>> may be shorted to ground.  
>>>>>> This would make the inverter chassis negative in relation to ground.  
>>>>>>  
>>>>>> The logic I use is to ask what is the likely source of DC at 195 volts?  
>>>>>> It is most likely the PV circuits, wouldn’t you say?
>>>>>>  
>>>>>> If the DC Fault is not eternal then it must be internal to the inverter. 
>>>>>>  This could be a dangerous situation.  I would proceed with caution.
>>>>>>  
>>>>>> Try completely isolating the PV from the inverter as a start.
>>>>>>  
>>>>>> Good luck.
>>>>>>  
>>>>>> William Miller
>>>>>>  
>>>>>> Miller Solar
>>>>>> 17395 Oak Road, Atascadero, CA 93422
>>>>>> 805-438-5600
>>>>>> www.millersolar.com <http://www.millersolar.com/>
>>>>>> CA Lic. 773985
>>>>>>  
>>>>>>  
>>>>>> From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org 
>>>>>> <mailto:re-wrenches-boun...@lists.re-wrenches.org>] On Behalf Of rick--- 
>>>>>> via RE-wrenches
>>>>>> Sent: Tuesday, October 15, 2024 11:09 AM
>>>>>> To: RE-wrenches
>>>>>> Cc: r...@solshineenergy.com <mailto:r...@solshineenergy.com>
>>>>>> Subject: [RE-wrenches] Sol-Ark Gen Input
>>>>>>  
>>>>>> Back on the Sol-Ark topic again. We have a customer whose 12kW is 
>>>>>> measuring -195VDC to ground from L1 and L2 with the Gen breaker open. L1 
>>>>>> to L2 = 0V. I know the Gen input can be configured as an output, but 
>>>>>> reading a high DC voltage to ground is concerning. The generator has 
>>>>>> never been run. System is operating normally. 
>>>>>>  
>>>>>> Anyone have a Sol-Ark accessible that could verify what they’re reading?
>>>>>>  
>>>>>> Thanks in advance. 
>>>>>>  
>>>>>> Rick Brown
>>>>>> Solshine Energy 
>>>>>> Solar Electric Contracting Services 
>>>>>> www.solshineenergy.com <http://www.solshineenergy.com/>
>>>>>> Roanoke, VA
>>>>>> Office: 540.235.3095
>>>>>> Mobile: 540.808.9502
>>>>>> CONFIDENTIALITY NOTICE -- This email is intended only for the person(s) 
>>>>>> named in
>>>>>> 
>>>>>> the message header. Unless otherwise indicated, it contains information 
>>>>>> that is
>>>>>> 
>>>>>> confidential, privileged and/or exempt from disclosure under applicable 
>>>>>> law. If you have
>>>>>> 
>>>>>> received this message in error, please notify the sender of the error 
>>>>>> and delete the
>>>>>> 
>>>>>> message. Thank you.
>>>>>> 
>>>>>>  
>>>>>> _______________________________________________
>>>>>> List sponsored by Redwood Alliance
>>>>>> 
>>>>>> Pay optional member dues here: http://re-wrenches.org 
>>>>>> <http://re-wrenches.org/>
>>>>>> 
>>>>>> List Address: RE-wrenches@lists.re-wrenches.org 
>>>>>> <mailto:RE-wrenches@lists.re-wrenches.org>
>>>>>> 
>>>>>> Change listserver email address & settings:
>>>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>>>> 
>>>>>> There are two list archives for searching. When one doesn't work, try 
>>>>>> the other:
>>>>>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>>>>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>>>> 
>>>>>> List rules & etiquette:
>>>>>> http://www.re-wrenches.org/etiquette.htm
>>>>>> 
>>>>>> Check out or update participant bios:
>>>>>> http://www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
>>>>>>  
>>>>>> rick brown
>>>>>> SolShine Energy Alternatives, LLC
>>>>>> Electrical & Solar Contracting Services
>>>>>> www.SolShineEnergy.com <http://www.solshineenergy.com/>
>>>>>> Roanoke, VA
>>>>>> Office: 540.235.3095
>>>>>> Mobile: 540.808.9502
>>>>>> 
>>>>>> VA Class A Contractor Lic# 2705147660
>>>>>> VA Master Electrician Lic# 2710062762
>>>>>> VA Alternative Energy Systems Installer  
>>>>>> NABCEP Certified PV Installation Professional 110112-21
>>>>>> 
>>>>>> CONFIDENTIALITY NOTICE -- This email is intended only for the person(s) 
>>>>>> named in
>>>>>> the message header. Unless otherwise indicated, it contains information 
>>>>>> that is
>>>>>> confidential, privileged and/or exempt from disclosure under applicable 
>>>>>> law. If you have
>>>>>> received this message in error, please notify the sender of the error 
>>>>>> and delete the
>>>>>> message. Thank you.”
>>>>>>  
>>>>>> _______________________________________________
>>>>>> List sponsored by Redwood Alliance
>>>>>> 
>>>>>> Pay optional member dues here: http://re-wrenches.org 
>>>>>> <http://re-wrenches.org/>
>>>>>> 
>>>>>> List Address: RE-wrenches@lists.re-wrenches.org 
>>>>>> <mailto:RE-wrenches@lists.re-wrenches.org>
>>>>>> 
>>>>>> Change listserver email address & settings:
>>>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>>>> 
>>>>>> There are two list archives for searching. When one doesn't work, try 
>>>>>> the other:
>>>>>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>>>>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>>>> 
>>>>>> List rules & etiquette:
>>>>>> http://www.re-wrenches.org/etiquette.htm
>>>>>> 
>>>>>> Check out or update participant bios:
>>>>>> http://www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
>>>>> rick brown
>>>>> SolShine Energy Alternatives, LLC
>>>>> Electrical & Solar Contracting Services
>>>>> www.SolShineEnergy.com <http://www.solshineenergy.com/>
>>>>> Roanoke, VA
>>>>> Office: 540.235.3095
>>>>> Mobile: 540.808.9502
>>>>> 
>>>>> VA Class A Contractor Lic# 2705147660
>>>>> VA Master Electrician Lic# 2710062762
>>>>> VA Alternative Energy Systems Installer  
>>>>> NABCEP Certified PV Installation Professional 110112-21
>>>>> 
>>>>> CONFIDENTIALITY NOTICE -- This email is intended only for the person(s) 
>>>>> named in
>>>>> the message header. Unless otherwise indicated, it contains information 
>>>>> that is
>>>>> confidential, privileged and/or exempt from disclosure under applicable 
>>>>> law. If you have
>>>>> received this message in error, please notify the sender of the error and 
>>>>> delete the
>>>>> message. Thank you.”
>>>>> 
>>>>> _______________________________________________
>>>>> List sponsored by Redwood Alliance
>>>>> 
>>>>> Pay optional member dues here: http://re-wrenches.org 
>>>>> <http://re-wrenches.org/>
>>>>> 
>>>>> List Address: RE-wrenches@lists.re-wrenches.org 
>>>>> <mailto:RE-wrenches@lists.re-wrenches.org>
>>>>> 
>>>>> Change listserver email address & settings:
>>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>>> 
>>>>> There are two list archives for searching. When one doesn't work, try the 
>>>>> other:
>>>>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>>>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>>> 
>>>>> List rules & etiquette:
>>>>> http://www.re-wrenches.org/etiquette.htm
>>>>> 
>>>>> Check out or update participant bios:
>>>>> http://www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
>>>>> 
>> 
>> rick brown
>> SolShine Energy Alternatives, LLC
>> Electrical & Solar Contracting Services
>> www.SolShineEnergy.com
>> Roanoke, VA
>> Office: 540.235.3095
>> Mobile: 540.808.9502
>> 
>> VA Class A Contractor Lic# 2705147660
>> VA Master Electrician Lic# 2710062762
>> VA Alternative Energy Systems Installer  
>> NABCEP Certified PV Installation Professional 110112-21
>> 
>> CONFIDENTIALITY NOTICE -- This email is intended only for the person(s) 
>> named in
>> the message header. Unless otherwise indicated, it contains information that 
>> is
>> confidential, privileged and/or exempt from disclosure under applicable law. 
>> If you have
>> received this message in error, please notify the sender of the error and 
>> delete the
>> message. Thank you.”
>> 
>> _______________________________________________
>> List sponsored by Redwood Alliance
>> 
>> Pay optional member dues here: http://re-wrenches.org
>> 
>> List Address: RE-wrenches@lists.re-wrenches.org
>> 
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> 
>> There are two list archives for searching. When one doesn't work, try the 
>> other:
>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>> 
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>> 
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>> 
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> Pay optional member dues here: http://re-wrenches.org
> 
> List Address: RE-wrenches@lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> There are two list archives for searching. When one doesn't work, try the 
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> http://www.members.re-wrenches.org
> 

rick brown
SolShine Energy Alternatives, LLC
Electrical & Solar Contracting Services
www.SolShineEnergy.com
Roanoke, VA
Office: 540.235.3095
Mobile: 540.808.9502

VA Class A Contractor Lic# 2705147660
VA Master Electrician Lic# 2710062762
VA Alternative Energy Systems Installer  
NABCEP Certified PV Installation Professional 110112-21

CONFIDENTIALITY NOTICE -- This email is intended only for the person(s) named in
the message header. Unless otherwise indicated, it contains information that is
confidential, privileged and/or exempt from disclosure under applicable law. If 
you have
received this message in error, please notify the sender of the error and 
delete the
message. Thank you.”

_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to