True, for 2016 it's "Installed with the deflectors at or above the bottom of the structural member to a maximum of 22 in. (550 mm) below the ceiling/roof deck where the sprinkler is installed in conformance with 8.6.5.1.2" my reason for commenting was item 2 allows 22" even if it's above the bottom of the structural member if the obstruction rules can be followed which wasn't how I had read your comment but I may have been mistaken.
Mike Morey CFPS 3229 • NICET S.E.T. 123677 Project Manager • Fire Protection Group Shambaugh & Son, LP an EMCOR Company 7614 Opportunity Drive • Fort Wayne, IN • 46825 direct 260.487.7824 / cell 260.417.0625 / fax 260.487.7991 email [email protected] [Image] ________________________________ From: Ken Wagoner <[email protected]> Sent: Friday, February 9, 2024 7:25:00 PM To: [email protected] <[email protected]> Subject: [Sprinklerforum] Re: Concrete Beams -- NFPA 13, 2016 Crossing editions, Mike, 10. 2. 7. 2 is referenced in the '22 edition, and Jackie was discussing the '16. Everything in the '16 edition, chapter 10 deals with underground, and there is no such section. If Jackie can apply the '22 edition, then ZjQcmQRYFpfptBannerStart This Message Is From an External Sender This message originated outside your organization. ZjQcmQRYFpfptBannerEnd Crossing editions, Mike, 10.2.7.2<https://urldefense.com/v3/__http://10.2.7.2__;!!FaxH778!YSx89xek3F8GWateOAJvfxxXT23NXVY6mGfyOQ2Jgm4o1L1-7rPnZ6L0wVxwI6mKzzEo6bMN9eBhZnQG6cfX$> is referenced in the '22 edition, and Jackie was discussing the '16. Everything in the '16 edition, chapter 10 deals with underground, and there is no such section. If Jackie can apply the '22 edition, then your comment is spot on. Ken Wagoner, SET Parsley Consulting 500 West Mechanic Street Harrisonville, Missouri 64701-2235 Phone: (760) 745-6181 Visit the website<https://urldefense.com/v3/__https://linkprotect.cudasvc.com/url?a=http*3a*2f*2fwww.parsleyconsulting.com*2f&c=E,1,Y5zKJKPEh1mBEBqSR-VE9cUKl5y-eyP8BpvmE_5j9ZqW2eJbNphYzrCMBZ-2YuX6d-RRkHI4gQ1FV-cvOeCfRC58uZS9NiToZv2mx7909oCqLvCW_n5hDHeK&typo=1__;JSUlJQ!!FaxH778!YSx89xek3F8GWateOAJvfxxXT23NXVY6mGfyOQ2Jgm4o1L1-7rPnZ6L0wVxwI6mKzzEo6bMN9eBhZmZ7dn8g$> On 2/9/2024 4:17 PM, Mike Morey wrote: Item 2 allows 22" when the obstruction clearances of 10.2.7.2<https://urldefense.com/v3/__http://10.2.7.2__;!!FaxH778!YSx89xek3F8GWateOAJvfxxXT23NXVY6mGfyOQ2Jgm4o1L1-7rPnZ6L0wVxwI6mKzzEo6bMN9eBhZnQG6cfX$> can be satisfied which should be easy enough at a 2" difference in elevation. Mike Morey CFPS 3229 • NICET S.E.T. 123677 Project Manager • Fire Protection Group Shambaugh & Son, LP an EMCOR Company 7614 Opportunity Drive • Fort Wayne, IN • 46825 direct 260.487.7824 / cell 260.417.0625 / fax 260.487.7991 email [email protected]<mailto:[email protected]> [Image] ________________________________ From: Ken Wagoner <[email protected]><mailto:[email protected]> Sent: Friday, February 9, 2024 5:02:25 PM To: [email protected]<mailto:[email protected]> <[email protected]><mailto:[email protected]> Subject: [Sprinklerforum] Re: Concrete Beams -- NFPA 13, 2016 Jackie, I echo the thoughts of Anthony, Matt, and my good friend Cliff. All the sections I note are from the '16 edition of NFPA 13 Obstructed construction per §3. 7. 1, §A. 3. 7. 1(1), as you have concrete beams, spaced between 3' and 7½" apart. ZjQcmQRYFpfptBannerStart This Message Is From an Untrusted Sender You have not previously corresponded with this sender. ZjQcmQRYFpfptBannerEnd Jackie, I echo the thoughts of Anthony, Matt, and my good friend Cliff. All the sections I note are from the '16 edition of NFPA 13 * Obstructed construction per §3.7.1, §A.3.7.1(1), as you have concrete beams, spaced between 3' and 7½" apart. * Sprinklers required in each bay, per §8.6.4.1.2(3), as it's not possible to reach the 22" maximum in (1) or (2) as the beam depth is 24" Hope that lines up with what others have to say. And, except for the section numbers this is fairly unchanged in the '22 edition. sincerely, Ken Wagoner, SET Parsley Consulting 500 West Mechanic Street Harrisonville, Missouri 64701-2235 Phone: (760) 745-6181 Visit the website<https://urldefense.com/v3/__https://linkprotect.cudasvc.com/url?a=http*3a*2f*2fwww.parsleyconsulting.com*2f&c=E,1,Y5zKJKPEh1mBEBqSR-VE9cUKl5y-eyP8BpvmE_5j9ZqW2eJbNphYzrCMBZ-2YuX6d-RRkHI4gQ1FV-cvOeCfRC58uZS9NiToZv2mx7909oCqLvCW_n5hDHeK&typo=1__;JSUlJQ!!FaxH778!YFCUu-j6odPrO_X-MFMR8WKY_8xg-wufPwm_LbKuEFfCR6JMnCumBY8kS_LdFkJ8r0qgPptUttn45O4JDvdP$> This message is for the named person's use only. It may contain confidential, proprietary or legally privileged information. No confidentiality or privilege is waived or lost by any mistransmission. If you receive this message in error, please immediately delete it and all copies of it from your system, destroy any hard copies of it and notify the sender. You must not, directly or indirectly, use, disclose, distribute, print, or copy any part of this message if you are not the intended recipient. _________________________________________________________ SprinklerForum mailing list: https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org<https://urldefense.com/v3/__https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org__;!!FaxH778!YSx89xek3F8GWateOAJvfxxXT23NXVY6mGfyOQ2Jgm4o1L1-7rPnZ6L0wVxwI6mKzzEo6bMN9eBhZmMvA4jY$> To unsubscribe send an email to [email protected]<mailto:[email protected]>
_________________________________________________________ SprinklerForum mailing list: https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org To unsubscribe send an email to [email protected]