Everything in the '16 edition, chapter 10 deals with underground, and there is no such section.
If Jackie can apply the '22 edition, then your comment is spot on.
Ken Wagoner, SET
Parsley Consulting
500 West Mechanic Street
Harrisonville, Missouri 64701-2235
Phone: (760) 745-6181
Visit the website
Parsley Consulting
500 West Mechanic Street
Harrisonville, Missouri 64701-2235
Phone: (760) 745-6181
Visit the website
On 2/9/2024 4:17 PM, Mike Morey wrote:
Item 2 allows 22" when the obstruction clearances of 10.2.7.2 can be satisfied which should be easy enough at a 2" difference in elevation.
Mike Morey
CFPS 3229 • NICET S.E.T. 123677
Project Manager • Fire Protection Group
Shambaugh & Son, LP an EMCOR Company7614 Opportunity Drive • Fort Wayne, IN • 46825
direct 260.487.7824 / cell 260.417.0625 / fax 260.487.7991
email [email protected]
From: Ken Wagoner <[email protected]>
Sent: Friday, February 9, 2024 5:02:25 PM
To: [email protected] <[email protected]>
Subject: [Sprinklerforum] Re: Concrete Beams -- NFPA 13, 2016Jackie,This Message Is From an Untrusted SenderYou have not previously corresponded with this sender.
I echo the thoughts of Anthony, Matt, and my good friend Cliff.
All the sections I note are from the '16 edition of NFPA 13
- Obstructed construction per §3.7.1, §A.3.7.1(1), as you have concrete beams, spaced between 3' and 7½" apart.
- Sprinklers required in each bay, per §8.6.4.1.2(3), as it's not possible to reach the 22" maximum in (1) or (2) as the beam depth is 24"
Hope that lines up with what others have to say. And, except for the section numbers this is fairly unchanged in the '22 edition.
sincerely,
Ken Wagoner, SET
Parsley Consulting
500 West Mechanic Street
Harrisonville, Missouri 64701-2235
Phone: (760) 745-6181
Visit the website
This message is for the named person's use only. It may contain confidential, proprietary or legally privileged information. No confidentiality or privilege is waived or lost by any mistransmission. If you receive this message in error, please immediately delete it and all copies of it from your system, destroy any hard copies of it and notify the sender. You must not, directly or indirectly, use, disclose, distribute, print, or copy any part of this message if you are not the intended recipient.
_________________________________________________________ SprinklerForum mailing list: https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org To unsubscribe send an email to [email protected]
_________________________________________________________ SprinklerForum mailing list: https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org To unsubscribe send an email to [email protected]