I forgot to mention this is a shell floor in an outpatient clinic that will be 
finished out at a later date



Thank you,

Jackie “JW” Ward
1-405-240-7076

From: Jackie Ward <[email protected]>
Sent: Friday, February 9, 2024 3:38 PM
To: [email protected]
Subject: [EXTERNAL] [Sprinklerforum] Concrete Beams -- NFPA 13, 2016

________________________________
WARNING:This message came from an external source. Please exercise caution when 
opening any attachments or clicking on links.
________________________________
I have 18” wide concrete beams extending 24” from the bottom of the deck on 
7’-0” centers.

NFPA-13 (2016) 8.6.4.1.2 Obstructed Construction (5)* Installed with deflectors 
of sprinklers under concrete tee construction with stems spaced less than 71⁄2 
ft (2.3 m) on centers, regardless of the depth of the tee, located at or above 
a horizontal plane 1 in. (25 mm) below the bottom of the stems of the tees and 
complying with Table 8.6.5.1.2.

A.8.6.4.1.2(5) For concrete joists spaced less than 3 ft (900 mm) on center, 
the rules for obstructed construction shown in 8.6.4.1.2 apply. For concrete 
tee construction with stems spaced less than 7 ft 6 in. (2.3 m) on center, the 
sprinkler deflector can be located at or above a horizontal plane 1 in. (25 mm) 
below the bottom of the stems of the tees. This includes sprinklers located 
between the stems. [See Figure A.8.6.4.1.2(5).]

I am getting caught up in semantics with the wording.  Would a concrete beam be 
interpreted the same as a concrete tee?

Am I allowed to install the deflectors above one-inch below the bottom of the 
beam in accordance with Table 8.6.5.1.2 as I would be if they were concrete 
tees, or will pocket protection be required?







Sincerely;

Jackie "JW" Ward; SET
1-405-240-7076
[email protected]<mailto:[email protected]>
NICET  IV Cert. No. 104187
Victaulic Vortex Integrator

Firetrol Protection Systems
108 NW 132nd Street; Oklahoma City, OK 73114
405-752-2330  Ext. 10230  Fax:405-752-2297
License No: AR-FSS-162, LA-F415, OK-863 & 302, TX - ECR-1751432, ACR-1751168, 
SCR-G-0292

[cid:[email protected]][Firetrol Oklahoma City 
BACK][cid:[email protected]]


_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to