Jackie,


For a quick answer ---



Concrete tees are a specific type of construction.  They are generally 
fabricated off-site and shipped in and set in place.  They will look like the 
snapshot below.







If the concrete beams on your project aren’t like this and are poured in-place 
on the job site, you will need sprinklers in each bay unless you can meet the 
beam blocking rule.



Cliff Whitfield, SET

President



Fire Design, Inc.

940 Summerbrooke Dr

Tallahassee, FL 32312

Ph: 828-284-4772





From: Jackie Ward <[email protected]>
Sent: Friday, February 9, 2024 4:38 PM
To: [email protected]
Subject: [Sprinklerforum] Concrete Beams -- NFPA 13, 2016



I have 18” wide concrete beams extending 24” from the bottom of the deck on 
7’-0” centers.



NFPA-13 (2016) 8.6.4.1.2 Obstructed Construction (5)* Installed with deflectors 
of sprinklers under concrete tee construction with stems spaced less than 71⁄2 
ft (2.3 m) on centers, regardless of the depth of the tee, located at or above 
a horizontal plane 1 in. (25 mm) below the bottom of the stems of the tees and 
complying with Table 8.6.5.1.2.



A.8.6.4.1.2(5) For concrete joists spaced less than 3 ft (900 mm) on center, 
the rules for obstructed construction shown in 8.6.4.1.2 apply. For concrete 
tee construction with stems spaced less than 7 ft 6 in. (2.3 m) on center, the 
sprinkler deflector can be located at or above a horizontal plane 1 in. (25 mm) 
below the bottom of the stems of the tees. This includes sprinklers located 
between the stems. [See Figure A.8.6.4.1.2(5).]



I am getting caught up in semantics with the wording.  Would a concrete beam be 
interpreted the same as a concrete tee?



Am I allowed to install the deflectors above one-inch below the bottom of the 
beam in accordance with Table 8.6.5.1.2 as I would be if they were concrete 
tees, or will pocket protection be required?















Sincerely;



Jackie "JW" Ward; SET

1-405-240-7076

 <mailto:[email protected]> [email protected]

NICET  IV Cert. No. 104187

Victaulic Vortex Integrator



Firetrol Protection Systems

108 NW 132nd Street; Oklahoma City, OK 73114

405-752-2330  Ext. 10230  Fax:405-752-2297

License No: AR-FSS-162, LA-F415, OK-863 & 302, TX - ECR-1751432, ACR-1751168, 
SCR-G-0292











--
This email has been checked for viruses by Avast antivirus software.
www.avast.com
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to