Sounds like Obstructed construction
8.6.4.1.2 Obstructed Construction. Under obstructed construction, the sprinkler 
deflector shall be located in accordance with one of the following arrangements:
(1) Installed with the deflectors within the horizontal planes of 1 in. to 6 
in. (25 mm to 150 mm) below the structural members and a maximum distance of 22 
in. (550 mm)below the ceiling/roof deck
(2) Installed with the deflectors at or above the bottom of the structural 
member to a maximum of 22 in. (550 mm)below the ceiling/roof deck where the 
sprinkler is in-stalled in conformance with 8.6.5.1.2
(3) Installed in each bay of obstructed construction, with the deflectors 
located a minimum of 1 in. (25 mm) and a maximum of 12 in. (300 mm) below the 
ceiling
Anthony Carrizosa
Project Manager | Fire Protection
7855 S 206th St Kent, WA 98032
Cell: 206-679-5283 | Office Dir: 253-341-4593
[cid:[email protected]]
https://archerconstruction.com<https://linkprotect.cudasvc.com/url?a=https%3a%2f%2farcherconstruction.com%2f&c=E,1,Wdb65AWzMgSBzW3HDw91SfcRQCtxDUQKoJf-UowQ-WnB_WMosgG-8W7eLePJ42PwWQvLiQx16Pls052VqwHO7tKm-_u5AnWly0ewkNiMkxn-AjQb1JI,&typo=1>

From: Jackie Ward <[email protected]>
Sent: Friday, February 9, 2024 1:38 PM
To: [email protected]
Subject: [Sprinklerforum] Concrete Beams -- NFPA 13, 2016

I have 18” wide concrete beams extending 24” from the bottom of the deck on 
7’-0” centers.

NFPA-13 (2016) 8.6.4.1.2 Obstructed Construction (5)* Installed with deflectors 
of sprinklers under concrete tee construction with stems spaced less than 71⁄2 
ft (2.3 m) on centers, regardless of the depth of the tee, located at or above 
a horizontal plane 1 in. (25 mm) below the bottom of the stems of the tees and 
complying with Table 8.6.5.1.2.

A.8.6.4.1.2(5) For concrete joists spaced less than 3 ft (900 mm) on center, 
the rules for obstructed construction shown in 8.6.4.1.2 apply. For concrete 
tee construction with stems spaced less than 7 ft 6 in. (2.3 m) on center, the 
sprinkler deflector can be located at or above a horizontal plane 1 in. (25 mm) 
below the bottom of the stems of the tees. This includes sprinklers located 
between the stems. [See Figure A.8.6.4.1.2(5).]

I am getting caught up in semantics with the wording.  Would a concrete beam be 
interpreted the same as a concrete tee?

Am I allowed to install the deflectors above one-inch below the bottom of the 
beam in accordance with Table 8.6.5.1.2 as I would be if they were concrete 
tees, or will pocket protection be required?







Sincerely;

Jackie "JW" Ward; SET
1-405-240-7076
[email protected]<mailto:[email protected]>
NICET  IV Cert. No. 104187
Victaulic Vortex Integrator

Firetrol Protection Systems
108 NW 132nd Street; Oklahoma City, OK 73114
405-752-2330  Ext. 10230  Fax:405-752-2297
License No: AR-FSS-162, LA-F415, OK-863 & 302, TX - ECR-1751432, ACR-1751168, 
SCR-G-0292

[cid:[email protected]][Firetrol Oklahoma City 
BACK][cid:[email protected]]


_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to