Jackie,
As I read this section. it says that your deflector can be no more than 1" below the bottom of the concrete tee.  If it is above the bottom of the tee, than it must comply with the beam rule.  If the sprinkler is _<_ 12" away than it can be set at 0" above the tee, if it is 1' to <18" than it can be no more than 2-1/2" above the tee, and etc....


/Thank you,
Bob Knight, CET III//
/*/Fire by Knight, LLC/*/
//208-318-3057/
FIREBYKNIGHT
On 2/9/2024 2:37 PM, Jackie Ward wrote:

I have 18” wide concrete beams extending 24” from the bottom of the deck on 7’-0” centers.

NFPA-13 (2016) 8.6.4.1.2 Obstructed Construction (5)* Installed with deflectors of sprinklers under concrete tee construction with stems spaced less than 71⁄2 ft (2.3 m) on centers, regardless of the depth of the tee, located at or above a horizontal plane 1 in. (25 mm) below the bottom of the stems of the tees and complying with Table 8.6.5.1.2.

A.8.6.4.1.2(5) For concrete joists spaced less than 3 ft (900 mm) on center, the rules for obstructed construction shown in 8.6.4.1.2 apply. For concrete tee construction with stems spaced less than 7 ft 6 in. (2.3 m) on center, the sprinkler deflector can be located at or above a horizontal plane 1 in. (25 mm) below the bottom of the stems of the tees. This includes sprinklers located between the stems. /[See Figure A.8.6.4.1.2(5).]/

//

I am getting caught up in semantics with the wording.  Would a concrete beam be interpreted the same as a concrete tee?

Am I allowed to install the deflectors above one-inch below the bottom of the beam in accordance with Table 8.6.5.1.2 as I would be if they were concrete tees, or will pocket protection be required?

Sincerely;

Jackie "JW" Ward; SET

1-405-240-7076

[email protected] <mailto:[email protected]>

NICET  IV Cert. No. 104187

Victaulic Vortex Integrator

Firetrol Protection Systems

108 NW 132nd Street; Oklahoma City, OK 73114

405-752-2330 Ext. 10230  Fax:405-752-2297

License No: AR-FSS-162, LA-F415, OK-863 & 302, TX - ECR-1751432, ACR-1751168, SCR-G-0292

Firetrol Oklahoma City BACK


_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email [email protected]


--
This email has been checked for viruses by AVG antivirus software.
www.avg.com
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to