I’ll also add to Ken’s comment in that much of what FM produces has 
dependencies on other requirements as well.  Building construction, 
ventilation, etc. can also be part of the specific requirements related to a 
fire protection data sheet.  Read the whole data sheet to be sure there aren’t 
other requirements outside of your scope that can influence the FP design.  
Additionally, make sure your local AHJ will accept the design criteria in the 
FM data sheet if it varies from NFPA. I deal with one jurisdiction that will 
not accept any FM Data sheet criteria, only NFPA due to NFPA being the only 
referenced standards in their adopted codes.

Have you looked at Chapter 21, specifically 21.3.2 and 21.3.3?

Craig Prahl | Jacobs | Group Lead/SME – Fire Protection | 
[email protected]<mailto:[email protected]> | 
www.jacobs.com<https://urldefense.com/v3/__http:/www.jacobs.com/__;!!KZTdOCjhgt4hgw!-_khxU8gU0_6jc895I7kRbnU8JghRDsWgqOblZ4jr7Qp2IVbR30VYw_hWvNFtphnl0uWpB9KIvbYi1pvZz4$>
1041 East Butler Road   Greenville, South Carolina  29606
CONTACT BY: Phone 1-864-676-5252, Email or MS TEAMS


From: Ken Wagoner <[email protected]>
Sent: Friday, May 19, 2023 11:43 AM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]>; BRUCE VERHEI <[email protected]>; 
å... .... <[email protected]>
Subject: [EXTERNAL] [Sprinklerforum] Re: Plastics in Bin Box storage

Bruce,

And your comment prompts this caveat from me regarding the application of 8-9.

Quite some time ago I learned from FM Global, that to appropriately use 8-9 as 
establishing the criteria for protection of storage that the entire fire 
sprinkler system has to meet FM Global guide documents.  It isn't a matter of 
designing/installing a system per -13 and selecting the protection criteria for 
storage from 8-9.

The system has to conform to all of the FM Global data sheets, beginning with 
2-0.

sincerely,
Ken Wagoner, SET
Parsley Consulting
500 West Mechanic Street
Harrisonville, Missouri 64701-2235
Phone: (760) 745-6181
Visit the 
website<https://urldefense.com/v3/__https:/linkprotect.cudasvc.com/url?a=http*3a*2f*2fwww.parsleyconsulting.com*2f&c=E,1,Y5zKJKPEh1mBEBqSR-VE9cUKl5y-eyP8BpvmE_5j9ZqW2eJbNphYzrCMBZ-2YuX6d-RRkHI4gQ1FV-cvOeCfRC58uZS9NiToZv2mx7909oCqLvCW_n5hDHeK&typo=1__;JSUlJQ!!B5cixuoO7ltTeg!DJeai_sUJalxW9YJDfMcmooADU2d3Gm6qqAmmrs7jSnGgO8VggeW61iDcTkfZ9EkBUf6jCSlA-84MBkjZ6qSgg$>


On 5/19/2023 10:31 AM, BRUCE VERHEI wrote:
For the AHJ types skulking out there, I would back up Scot’s comments, and add 
the late Joe Hankins to list of highly respected FM P.E.’s.
The one comment I do have is that’s #13 is intended to be used as a standard, 
and 8-9 et al as guidance to FM’s engineers and insured. It much more expects 
good intent, and is not to be applied for those who go looking for what-if 
loopholes.
We accepted 8-9 all the time, while still applying the seismic etc standards 
from #13.

Best.

Bruce Verhei

On 05/18/2023 3:34 PM PDT å... .... 
<[email protected]><mailto:[email protected]> wrote:



If the client resticts their bin-box (open-top) containers to only the lowest 
level of storage, there are onerous work-arounds.

I would take my design directions from FM, as most of their high-piled plastic 
storage advice becomes NFPA 13.  Simply FM Global has been leader sin qua non, 
in sprinkler protection of industrial rack storage for scores-and-more of years.

FM Global invokes the Bayesian far more often and far faster than NFPA 13 (i.e. 
FM Global changes their mind to update their guess when presented with new 
evidence).  While it would appear that FM Global procurement of evidence is 
biased, because they literally record their own fire test data, I have found 
the integrity and the personal effort offered by their personnel as a paramount 
case study in information sharing for the fire safety community.  At the risk 
of tainting their reputations by association with this writer, I can not 
recommend enough the personal contributions Prateep Chatterjee and Weston Baker 
of FM Global, have made to our industry.

Section 2.2.4.3 of FM Global's Data Sheet 8-9 talks to us on your subject.  You 
are in good care with their share.

Collusion exposure statement:   Scot Deal has no financial links to FM Global 
either through payments or client  procurement collaborations. Scot Deal is 
financially linked to NFPA through subscription fees.

Scot Deal
Excelsior Risk and Fire Engineering
gms:  +420 606 872 129<tel:+420606872129>

Si vis pacem, para vinum




On Thu, May 18, 2023 at 11:47 PM Steve Leyton 
<[email protected]<mailto:[email protected]>> wrote:
I want to be sure that I’ve got this right:   A client is moving into a 
brand-new ESFR protected warehouse space and they want to build a two level 
bin-box system.   I explained that they would have to fire protect below the 
walkways and they’ve come back to me asking whether or not building just the 
lower level of the system would alleviate the need to make sprinkler system 
improvements.   The CMSA and ESFR protection tables in Chapter 14 (2016 
edition) don’t include bin-box or plastics in the application range, Only 
palletized and solid pile, Classes 1-4.    If they want to use a bin-box 
system, do they have to change roof sprinklers out for CMDA?  Or can the ESFR 
remain and CMDA sprinklers would be installed under walkways when they’re built?

I miss the little bitty book and pipe scheduled systems…

[cid:[email protected]]
Steve Leyton, President
T  |  619.255.8964<tel:619.255.8964> x 102  |  
www.protectiondesign.com<https://urldefense.com/v3/__http:/www.protectiondesign.com/__;!!B5cixuoO7ltTeg!DJeai_sUJalxW9YJDfMcmooADU2d3Gm6qqAmmrs7jSnGgO8VggeW61iDcTkfZ9EkBUf6jCSlA-84MBkCbZ5NbQ$>
2851 Camino Del Rio South  |  Suite 210  |  San Diego, CA  92108
Fire Protection System Design | Consulting | Planning | Training


_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org<https://urldefense.com/v3/__https:/lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org__;!!B5cixuoO7ltTeg!DJeai_sUJalxW9YJDfMcmooADU2d3Gm6qqAmmrs7jSnGgO8VggeW61iDcTkfZ9EkBUf6jCSlA-84MBkbglz0ww$>
To unsubscribe send an email to 
[email protected]<mailto:[email protected]>

_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org<https://urldefense.com/v3/__https:/lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org__;!!B5cixuoO7ltTeg!DJeai_sUJalxW9YJDfMcmooADU2d3Gm6qqAmmrs7jSnGgO8VggeW61iDcTkfZ9EkBUf6jCSlA-84MBkbglz0ww$>
To unsubscribe send an email to 
[email protected]<mailto:[email protected]>





_________________________________________________________

SprinklerForum mailing list:

https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org<https://urldefense.com/v3/__https:/lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org__;!!B5cixuoO7ltTeg!DJeai_sUJalxW9YJDfMcmooADU2d3Gm6qqAmmrs7jSnGgO8VggeW61iDcTkfZ9EkBUf6jCSlA-84MBkbglz0ww$>

To unsubscribe send an email to 
[email protected]<mailto:[email protected]>


________________________________

NOTICE - This communication may contain confidential and privileged information 
that is for the sole use of the intended recipient. Any viewing, copying or 
distribution of, or reliance on this message by unintended recipients is 
strictly prohibited. If you have received this message in error, please notify 
us immediately by replying to the message and deleting it from your computer.
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to