For the AHJ types skulking out there, I would back up Scot’s comments, and add 
the late Joe Hankins to list of highly respected FM P.E.’s. 

The one comment I do have is that’s #13 is intended to be used as a standard, 
and 8-9 et al as guidance to FM’s engineers and insured. It much more expects 
good intent, and is not to be applied for those who go looking for what-if 
loopholes. 

We accepted 8-9 all the time, while still applying the seismic etc standards 
from #13.
 
Best.

Bruce Verhei
 

> On 05/18/2023 3:34 PM PDT å... .... <[email protected]> wrote:
>  
>  
>  
> If the client resticts their bin-box (open-top) containers to only the lowest 
> level of storage, there are onerous work-arounds.
>  
> I would take my design directions from FM, as most of their high-piled 
> plastic storage advice becomes NFPA 13.  Simply FM Global has been leader sin 
> qua non, in sprinkler protection of industrial rack storage for 
> scores-and-more of years.
>  
> FM Global invokes the Bayesian far more often and far faster than NFPA 13 
> (i.e. FM Global changes their mind to update their guess when presented with 
> new evidence).  While it would appear that FM Global procurement of evidence 
> is biased, because they literally record their own fire test data, I have 
> found the integrity and the personal effort offered by their personnel as a 
> paramount case study in information sharing for the fire safety community.  
> At the risk of tainting their reputations by association with this writer, I 
> can not recommend enough the personal contributions Prateep Chatterjee and 
> Weston Baker of FM Global, have made to our industry.
>  
> Section 2.2.4.3 of FM Global's Data Sheet 8-9 talks to us on your subject.  
> You are in good care with their share. 
>  
> Collusion exposure statement:   Scot Deal has no financial links to FM Global 
> either through payments or client  procurement collaborations. Scot Deal is 
> financially linked to NFPA through subscription fees.
>  
> Scot Deal 
> Excelsior Risk and Fire Engineering
> gms:  +420 606 872 129 tel:+420606872129
>  
> Si vis pacem, para vinum
>  
>  
>  
> 
> On Thu, May 18, 2023 at 11:47 PM Steve Leyton <[email protected] 
> mailto:[email protected]> wrote:
> 
> > 
> > I want to be sure that I’ve got this right:   A client is moving into a 
> > brand-new ESFR protected warehouse space and they want to build a two level 
> > bin-box system.   I explained that they would have to fire protect below 
> > the walkways and they’ve come back to me asking whether or not building 
> > just the lower level of the system would alleviate the need to make 
> > sprinkler system improvements.   The CMSA and ESFR protection tables in 
> > Chapter 14 (2016 edition) don’t include bin-box or plastics in the 
> > application range, Only palletized and solid pile, Classes 1-4.    If they 
> > want to use a bin-box system, do they have to change roof sprinklers out 
> > for CMDA?  Or can the ESFR remain and CMDA sprinklers would be installed 
> > under walkways when they’re built?
> > 
> >  
> > 
> > I miss the little bitty book and pipe scheduled systems…
> > 
> >  
> > 
> > Steve Leyton, President
> > T  |  619.255.8964 tel:619.255.8964 x 102  |  www.protectiondesign.com 
> > http://www.protectiondesign.com/
> > 2851 Camino Del Rio South  |  Suite 210  |  San Diego, CA  92108
> > Fire Protection System Design | Consulting | Planning | Training
> > 
> >  
> > 
> > 
> > _________________________________________________________
> > SprinklerForum mailing list:
> > https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
> > To unsubscribe send an email to 
> > [email protected] 
> > mailto:[email protected]
> > 
> 
> _________________________________________________________
> SprinklerForum mailing list:
> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
> To unsubscribe send an email to [email protected]
> 
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to