Steve, what storage height are they talking about?
  
  
  
  
  
  
  

  
  
>   
> On May 18, 2023 at 5:47 PM,  <Steve Leyton 
> (mailto:[email protected])>  wrote:
>   
>   
>           
>   
>
> I want to be sure that I’ve got this right:      A client is moving into a 
> brand-new ESFR protected warehouse space and they want to build a two level 
> bin-box system.      I explained that they would have to fire protect below 
> the walkways and they’ve come back to me asking whether or not building just 
> the lower level of the system would alleviate the need to make sprinkler 
> system improvements.      The CMSA and ESFR protection tables in Chapter 14 
> (2016 edition) don’t include bin-box or plastics in the application range, 
> Only palletized and solid pile, Classes 1-4.        If they want to use a 
> bin-box system, do they have to change roof sprinklers out for CMDA?    Or 
> can the ESFR remain and CMDA sprinklers would be installed under walkways 
> when they’re built?
>
>   
>
>   
>
>   
>
> I miss the little bitty book and pipe scheduled systems…
>
>   
>
>   
>
>   
>
>
>
>   
>
>    Steve Leyton, President
>  T    |   619.255.8964    x 102      |       www.protectiondesign.com 
> (http://www.protectiondesign.com/)
>      2851 Camino Del Rio South      |    Suite 210      |    San Diego, CA    
> 92108
> Fire Protection System Design    |    Consulting    |    Planning    |    
> Training
>
>   
>
>   
>
>   
>  _________________________________________________________ SprinklerForum 
> mailing list: 
> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org 
> To unsubscribe send an email to [email protected]
>   
  
  
     
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to