Re: [RE-wrenches] Battery Backup for Older Enphase Systems

2017-11-09 Thread Dave Tedeyan
You could go with a Sonnen. That is meant to be AC coupled, and its a very simple install. Nice piece of equipment, but its expensive. We just installed one that has right around 8kw of Enphase M215 inverter output. So far, no issues. Cheers, Dave *--* *Dave Tedeyan* *Project Engineer

Re: [RE-wrenches] Battery Backup for Older Enphase Systems

2017-11-20 Thread Dave Tedeyan
able glitches in the Sonnen's distributed AC? > > I am assuming the Enphase ON transitions are more graceful because of > the UL1741 prove-in period and the individual ramp-up of the individual > microinverters. > > Regards, > > Gary Willett PE > Icarus Engineering &

Re: [RE-wrenches] AFCI Faults, SMA Inverters, Solectria RSB's, & RF Signals

2018-01-25 Thread Dave Tedeyan
was less than 6 months ago and some of these will arc fault about once per year. Cheers, Dave *--* *Dave Tedeyan* *Senior Engineer* *Taitem Engineering, PC* 10 Verizon Lane, Lansing, NY 14882 Voice: (607) 930-3481 x6 www.taitem.com On Thu, Jan 25, 2018 at 8:52 AM, Steven Lawrence wrote

Re: [RE-wrenches] Looking for Solar Ready pedestal

2018-01-25 Thread Dave Tedeyan
and have never had an issue. Then you get 65A of backfeed capacity. Cheers, Dave *--* *Dave Tedeyan* *Senior Engineer* *Taitem Engineering, PC* 10 Verizon Lane, Lansing, NY 14882 Voice: (607) 930-3481 x6 www.taitem.com On Wed, Jan 24, 2018 at 1:28 AM, William Miller wrote: > Frie

Re: [RE-wrenches] experience with the Tesla Powerwall

2018-02-13 Thread Dave Tedeyan
the up front expense scares many people away. We are located in upstate NY which may have something to do with it. Cheers, Dave *--* *Dave Tedeyan* *Senior Engineer* *Taitem Engineering, PC* 10 Verizon Lane, Lansing, NY 14882 Voice: (607) 930-3481 x6 www.taitem.com On Tue, Feb 13, 2018 at 10

Re: [RE-wrenches] rail less standing seam attachments

2018-04-02 Thread Dave Tedeyan
: https://www.fallprotectionpros.com/guardian-two-way-standing-seam-roof-anchor.html Cheers, Dave *--* *Dave Tedeyan* *Senior Engineer* *Taitem Engineering, PC* 10 Verizon Lane, Lansing, NY 14882 Voice: (607) 930-3481 x6 www.taitem.com On Sat, Mar 31, 2018 at 1:19 PM, Ray wrote: > Hi B

Re: [RE-wrenches] PV Cell Temperature Variation

2018-05-21 Thread Dave Tedeyan
south of the array casting a thin shadow. The hot cell pattern did not specifically follow the shade pattern on the front of the module. Cheers, Dave *--* *Dave Tedeyan* *Senior Engineer* *Taitem Engineering, PC* 10 Verizon Lane, Lansing, NY 14882 Voice: (607) 930-3481 x6 www.taitem.com On Fri

Re: [RE-wrenches] 5 battery strings

2018-07-24 Thread Dave Tedeyan
cost effective than just getting a whole new battery bank right off the bat when they have 10 batteries that have essentially never been used. Cheers, Dave *--* *Dave Tedeyan* *Senior Engineer* *Taitem Engineering, PC* 10 Verizon Lane, Lansing, NY 14882 Voice: (607) 930-3481 x6 www.taitem.com

Re: [RE-wrenches] Bi-Directional / Netmetering question

2018-08-16 Thread Dave Tedeyan
have the wrong voltage reference. Cheers, Dave *Dave Tedeyan* Senior Engineer | Taitem Engineering, PC 10 Verizon Lane | Lansing, NY 14882 o. *607.930.3481* x6 f. 607.277.2119 www.taitem.com Solar • Sustainability • Energy • Design B-Corporation Best for the World 2018 Honoree On Thu, Aug 16,

[RE-wrenches] PV210 Curve Tracer Issues

2018-09-24 Thread Dave Tedeyan
Seaward, and they gave me a free calibration, even though it had been well under a year since I owned it. But they did not address the issue I am seeing here. So does anyone know why I might not be getting a good curve, and if there is anything that can be done about it? Thanks, Dave *Dave Tedeyan

Re: [RE-wrenches] Multiple inverters

2019-02-25 Thread Dave Tedeyan
. No inspectors here seem to care as long as the labeling shows what is happening. Although we are also fortunate that most inspectors around here will not make us fix old work as long as we did not touch it and it presents no safety hazard. Cheers, Dave *Dave Tedeyan, PE* Senior Engineer | Taitem

[RE-wrenches] large(ish) AC coupled battery backup

2019-05-03 Thread Dave Tedeyan
whether this will be a whole home backup or just a subset of their loads, but they have two 200A panels on a single 200A service. Thanks, Dave *Dave Tedeyan, PE* Senior Engineer | Taitem Engineering, PC 110 South Albany Street | Ithaca, NY 14850 o. *607.277.1118 x121* f. 607.277.2119

Re: [RE-wrenches] large(ish) AC coupled battery backup

2019-05-03 Thread Dave Tedeyan
paralleled, does that jump up to a single 12kw input, or are you just limited to two 6kw inputs? Cheers, Dave *Dave Tedeyan, PE* Senior Engineer | Taitem Engineering, PC 110 South Albany Street | Ithaca, NY 14850 o. *607.277.1118 x121* f. 607.277.2119 www.taitem.com Solar • Sustainability • Energy

Re: [RE-wrenches] large(ish) AC coupled battery backup

2019-05-03 Thread Dave Tedeyan
m the solar all the way back to the house. Cheers, Dave *Dave Tedeyan, PE* Senior Engineer | Taitem Engineering, PC 110 South Albany Street | Ithaca, NY 14850 o. *607.277.1118 x121* f. 607.277.2119 www.taitem.com Solar • Sustainability • Energy • Design B-Corporation Best for the World 2018 Ho

Re: [RE-wrenches] rapid shutdown units for obscure inverter

2019-05-30 Thread Dave Tedeyan
em to not work at all. It held the string voltage down even when it should not have. The only way to get the string voltage back up was to physically disconnect the PV from the inverter. So we had to pull the rapid shutdown and will need to find another solution. Cheers, Dave *Dave Tedeyan, PE* S

Re: [RE-wrenches] rapid shutdown units for obscure inverter

2019-05-30 Thread Dave Tedeyan
I may have spoken too soon on this. It turns out that the LSOB system just does not work with PV charge controllers. The Princeton Power Systems DRI-10 inverter has charge controllers built in, which is why the system was not working. Cheers, Dave *Dave Tedeyan, PE* Senior Engineer | Taitem

Re: [RE-wrenches] Low OC Voltage

2019-06-13 Thread Dave Tedeyan
amera when the system is functioning can often show if 1/3 the module is not working or if there are some bad cells in the module. Cheers, Dave *Dave Tedeyan, PE* Senior Engineer | Taitem Engineering, PC 110 South Albany Street | Ithaca, NY 14850 o. *607.277.1118 x121* f. 607.277.2119 www.taite

Re: [RE-wrenches] Residential tracker options

2019-06-13 Thread Dave Tedeyan
Chris, We have used AER for trackers. We've had good success with them. https://www.allearthrenewables.com/product/allearth-solar-trackers Cheers, Dave *Dave Tedeyan, PE* Senior Engineer | Taitem Engineering, PC 110 South Albany Street | Ithaca, NY 14850 o. *607.277.1118 x121* f. 607.277

Re: [RE-wrenches] Low OC Voltage

2019-06-18 Thread Dave Tedeyan
modules for second hand use that otherwise would have ended up in the dump this way. Obviously though it wont be like new anymore. Cheers, Dave *Dave Tedeyan, PE* Senior Engineer | Taitem Engineering, PC 110 South Albany Street | Ithaca, NY 14850 o. *607.277.1118 x121* f. 607.277.2119 www.taitem.com

[RE-wrenches] Sunpower Ensemble

2019-06-25 Thread Dave Tedeyan
MI's will need to be upgraded. Can anyone confirm this? -Will Sunpower AC modules be compatible? If anyone out there has any of this info, that would be much appreciated! Cheers, Dave *Dave Tedeyan, PE* Senior Engineer | Taitem Engineering, PC 110 South Albany Street | Ithaca,

[RE-wrenches] Damaged in shipping

2019-07-01 Thread Dave Tedeyan
... but I am still not sure if it is right to charge the customer for all this back and forth when my actions have not resulted in a fixed and usable inverter. I'd appreciate anyone's thoughts and feedback on this sort of situation. Cheers, Dave *Dave Tedeyan, PE* Senior Enginee

Re: [RE-wrenches] Damaged in shipping

2019-07-02 Thread Dave Tedeyan
ly, I know that they are good people, who are also well connected in the area, so keeping a good relationship with them is certainly important. Cheers, Dave *Dave Tedeyan, PE* Senior Engineer | Taitem Engineering, PC 110 South Albany Street | Ithaca, NY 14850 o. *607.277.1118 x121* f. 607.277.2119

Re: [RE-wrenches] Consolidating meters

2019-07-08 Thread Dave Tedeyan
over when the power gets cut off.) They also had a set list of approved meters that can be used for submetering. We were planning on using eGauges, but ended up needing to put in an approved glass meter as well. Cheers, Dave *Dave Tedeyan, PE* Senior Engineer | Taitem Engineering, PC 110 South

Re: [RE-wrenches] SMA phantom arc faults

2019-09-03 Thread Dave Tedeyan
.. Cheers, Dave *Dave Tedeyan, PE* Senior Engineer | Taitem Engineering, PC 110 South Albany Street | Ithaca, NY 14850 o. *607.277.1118 x121* f. 607.277.2119 www.taitem.com Solar • Sustainability • Energy • Design B-Corporation Best for the World 2018 Honoree On Mon, Sep 2, 2019 at 12:03 PM Je

Re: [RE-wrenches] SMA phantom arc faults

2019-09-03 Thread Dave Tedeyan
wer dealer and you are a Sunpower dealer yourself. If the original system was from a Sunpower dealer, you can also have the customer call Sunpower directly. Cheers, Dave *Dave Tedeyan, PE* Senior Engineer | Taitem Engineering, PC 110 South Albany Street | Ithaca, NY 14850 o. *607.277.111

Re: [RE-wrenches] SMA phantom arc faults

2019-09-15 Thread Dave Tedeyan
quote me I triple the price. >> 1/3 up front and the rest when it is done. ABB is really slow with payment. >> I think they sold their inverter business? Sunpower is a great panel but >> they have had some bad runs. Probably why there are so many new/used panels >> on the secon

[RE-wrenches] Running a grid tied system when the grid is down

2019-09-20 Thread Dave Tedeyan
d of setup before. Thanks much! -Dave *Dave Tedeyan, PE* Senior Engineer | Taitem Engineering, PC 110 South Albany Street | Ithaca, NY 14850 o. *607.277.1118 x121* f. 607.277.2119 www.taitem.com Solar • Sustainability • Energy • Design B-Corporation Best for the World 20

Re: [RE-wrenches] Running a grid tied system when the grid is down

2019-09-20 Thread Dave Tedeyan
troller to initiate RSD. So this way it will continue to work with the grid down. Cheers, Dave *Dave Tedeyan, PE* Senior Engineer | Taitem Engineering, PC 110 South Albany Street | Ithaca, NY 14850 o. *607.277.1118 x121* f. 607.277.2119 www.taitem.com Solar • Sustainability • Energy • Design B-Corpor

Re: [RE-wrenches] Running a grid tied system when the grid is down

2019-09-20 Thread Dave Tedeyan
g for in this particular case. Although I am still curious if others have retrofitted other systems with something like I was initially talking about for an inverter that does not have a SPS. I think that at least in this market a low end 3rd party solution could gain a lot of traction. *Dave Tedeya

[RE-wrenches] Eversource utility in CT

2019-09-26 Thread Dave Tedeyan
the road)? This is a fairly simple roof mounted system, <25kw. Cheers, Dave *Dave Tedeyan, PE* Senior Engineer | Taitem Engineering, PC 110 South Albany Street | Ithaca, NY 14850 o. *607.277.1118 x121* f. 607.277.2119 www.taitem.com Solar • Sustainability • Energy • Design B-Corporation Best

[RE-wrenches] SPR-5200 inverter parts

2019-10-14 Thread Dave Tedeyan
inverter. Has anyone experienced this, and would a replacement board fix the issue? And would anyone have anything like that available? And if not, can anyone even get a grounded inverter these days? Sunpower tells me to get a SB6000US, but I cannot even find one of those. Thanks, Dave *Dave Tedeyan

[RE-wrenches] trickle charger for 4 12V batteries

2019-10-14 Thread Dave Tedeyan
? And is it best to get 4 separate 12V chargers, one 48V charger, or a single 12V charger and put them all in parallel? Or am I just overthinking this? Cheers, Dave *Dave Tedeyan, PE* Senior Engineer | Taitem Engineering, PC 110 South Albany Street | Ithaca, NY 14850 o. *607.277.1118 x121* f

Re: [RE-wrenches] SolarReady Service Panel vs adding Supply Side connection?

2019-10-24 Thread Dave Tedeyan
something in 2017 code makes this all not possible, as we are still on 2014 in NY. See 705.12(D)(2)(c) Cheers, Dave *Dave Tedeyan, PE* Senior Engineer | Taitem Engineering, PC 110 South Albany Street | Ithaca, NY 14850 o. *607.277.1118 x121* f. 607.277.2119 www.taitem.com Solar • Sustainability

Re: [RE-wrenches] non-sensor based tracker controller

2019-12-02 Thread Dave Tedeyan
Hey Mac, AER (All Earth Renewables) trackers are a dual axis tracker that uses GPS to follow the sun. We've had good luck with them. Cheers, Dave *Dave Tedeyan, PE* Senior Engineer | Taitem Engineering, PC 110 South Albany Street | Ithaca, NY 14850 o. *607.277.1118 x121* f. 607.277

[RE-wrenches] Xantrex SW 4048 grid tie mystery

2019-12-20 Thread Dave Tedeyan
e multiple N-G bonds could be causing these issues. Does anyone have any ideas? Cheers, Dave *Dave Tedeyan, PE* Senior Engineer | Taitem Engineering, PC 110 South Albany Street | Ithaca, NY 14850 o. *607.277.1118 x121* f. 607.277.2119 www.taitem.com Solar • Sustainability • Energy • Design C

Re: [RE-wrenches] Xantrex SW 4048 grid tie mystery

2019-12-20 Thread Dave Tedeyan
Dave, Sorry, misspeak on my part. It is DC negatives and grounds that are tied together. No neutrals in the DC box. Cheers, Dave *Dave Tedeyan, PE* Senior Engineer | Taitem Engineering, PC 110 South Albany Street | Ithaca, NY 14850 o. *607.277.1118 x121* f. 607.277.2119 www.taitem.com Solar

Re: [RE-wrenches] Xantrex SW 4048 grid tie mystery

2019-12-21 Thread Dave Tedeyan
. Can you tell me a little more about what operation this would confirm? The system is not AC coupled. I'll report back with what I learn. Cheers, Dave *Dave Tedeyan, PE* Senior Engineer | Taitem Engineering, PC 110 South Albany Street | Ithaca, NY 14850 o. *607.277.1118 x121* f. 607.277

Re: [RE-wrenches] Xantrex SW 4048 grid tie mystery

2019-12-24 Thread Dave Tedeyan
to begin with and it was not until many hours later that the issues with powering the backed up loads started appearing. Cheers, Dave *Dave Tedeyan, PE* Senior Engineer | Taitem Engineering, PC 110 South Albany Street | Ithaca, NY 14850 o. *607.277.1118 x121* f. 607.277.2119 www.taitem.com

Re: [RE-wrenches] Xantrex SW 4048 grid tie mystery

2019-12-25 Thread Dave Tedeyan
grid connection does not seem to work. Or maybe it would not waste too much energy to use the bulk charge timer initiate a bulk charge every evening after it has been selling all day? Cheers, Dave *Dave Tedeyan, PE* Senior Engineer | Taitem Engineering, PC 110 South Albany Street | Ithaca, NY 14

Re: [RE-wrenches] Inverter Output Circuit OCPD Meltdown

2020-01-21 Thread Dave Tedeyan
eaker in there to fail. Another thing I've seen burn marks on a breaker like that just due to loose connection (is what it appeared to be, anyway) arcing over time. Good luck, Dave *Dave Tedeyan, PE* Senior Engineer | Taitem Engineering, PC 110 South Albany Street | Ithaca, NY 14850 o. *60

Re: [RE-wrenches] Old & new Enphase communication issues

2020-03-10 Thread Dave Tedeyan
Since Enphase stopped making the old M215's, they have been sending out M215's that look like IQ microinverters, with an adapter. These supposedly work with the old Envoy. I am not sure if they are only available as warranty replacents, or if you can purchase them new though. Cheers, Dave On Tue,

[RE-wrenches] Mate3 not saving data

2020-03-26 Thread Dave Tedeyan
mware with the SD card. But there are never any logfiles on there. Any suggestions? Thanks! -Dave *Dave Tedeyan, PE* Senior Engineer | Taitem Engineering, PC 110 South Albany Street | Ithaca, NY 14850 o. *607.277.1118 x121* f. 607.277.2119 www.taitem.com Solar • Sustainability • Energy • Design

[RE-wrenches] Outback EQ not holding voltage

2020-04-28 Thread Dave Tedeyan
with this before and have any suggestions on how they fixed it? This system is 3-4 years old, and the issue only started in the past year or so. Cheers, Dave *Dave Tedeyan, PE* Senior Engineer | Taitem Engineering, PC 110 South Albany Street | Ithaca, NY 14850 o. *607.277.1118 x121* f. 607.277

Re: [RE-wrenches] Outback EQ not holding voltage

2020-04-28 Thread Dave Tedeyan
every EQ cycle, it just happens for most of them. I also received another suggestion that the battery bank has a couple bad cells which will lead to higher temps and so with the temperature compensation the bank is just not getting to a high enough voltage. Cheers, Dave *Dave Tedeyan, PE* Senior

Re: [RE-wrenches] Outback EQ not holding voltage

2020-04-28 Thread Dave Tedeyan
el battery strings all have the same length of premade cable, so current should be balanced (unless there is a dead cell or two in there...). Cheers, Dave *Dave Tedeyan, PE* Senior Engineer | Taitem Engineering, PC 110 South Albany Street | Ithaca, NY 14850 o. *607.277.1118 x121* f. 607.277.2119 www.

Re: [RE-wrenches] Outback EQ not holding voltage

2020-04-30 Thread Dave Tedeyan
to 61.6V it hovers around 61.6 and 61.5. Lots of good info and ideas here, thanks all. -Dave *Dave Tedeyan, PE* Senior Engineer | Taitem Engineering, PC 110 South Albany Street | Ithaca, NY 14850 o. *607.277.1118 x121* f. 607.277.2119 www.taitem.com Solar • Sustainability • Energy • Design

Re: [RE-wrenches] Rapid Shutdown Compliance

2020-04-30 Thread Dave Tedeyan
about? It seems that this would solve many of the issues associated with MLPE, but still be able to have the benefits. Cheers, Dave *Dave Tedeyan, PE* Senior Engineer | Taitem Engineering, PC 110 South Albany Street | Ithaca, NY 14850 o. *607.277.1118 x121* f. 607.277.2119 www.taitem.com Solar

[RE-wrenches] Skybox

2020-05-03 Thread Dave Tedeyan
same niche. Are those even available for purchase yet? If so, does anyone have experience with these? Cheers, Dave *Dave Tedeyan, PE* Senior Engineer | Taitem Engineering, PC 110 South Albany Street | Ithaca, NY 14850 o. *607.277.1118 x121* f. 607.277.2119 www.taitem.com Solar • Sustaina

Re: [RE-wrenches] Skybox

2020-05-06 Thread Dave Tedeyan
way more conservative as to what loads are allowed to be backed up. Also, is there an inverter bypass built into the BOS enclosure, or do you need to wire up a separate one in case of inverter failure. Cheers, Dave *Dave Tedeyan, PE* Senior Engineer | Taitem Engineering, PC 110 South Albany Street

[RE-wrenches] Princeton Power UL Listing

2020-06-09 Thread Dave Tedeyan
press release from Princeton Power stating that the DRI-10 inverter has received its UL listing. But does anyone out there actually have the certificate that they would be willing to share? Thanks! -Dave *Dave Tedeyan, PE* Senior Engineer | Taitem Engineering, PC 110 South Albany Street | Ithaca, NY

Re: [RE-wrenches] Oversized meter enclosure for line side connection recommendation

2020-06-18 Thread Dave Tedeyan
Make sure that your utility allows for this. NYSEG in NY gets very upset if you put anything in a meter enclosure other than the meter. Cheers, Dave On Thu, Jun 18, 2020, 10:00 AM Kristopher Schmid wrote: > If you are going to replace the meter socket, using a 200 amp Milbank and > a set of Milb

[RE-wrenches] SB6000U Derating Mode

2015-10-21 Thread Dave Tedeyan
alternative is to just get a whole new inverter. Cheers, Dave *--* *Dave Tedeyan* *Project Engineer* *Taitem Engineering, PC* 109 S. Albany Street, Ithaca, NY 14850 Voice: (607) 277-1118 x121 www.taitem.com ___ List sponsored by Redwood Alliance List

Re: [RE-wrenches] SB6000U Derating Mode

2015-10-23 Thread Dave Tedeyan
Thanks guys for the recommendations. -Dave *--* *Dave Tedeyan* *Project Engineer* *Taitem Engineering, PC* 109 S. Albany Street, Ithaca, NY 14850 Voice: (607) 277-1118 x121 www.taitem.com On Wed, Oct 21, 2015 at 6:38 PM, Jason Szumlanski < ja...@floridasolardesigngroup.com> wrote

Re: [RE-wrenches] Sunnyboy 7700 TL

2015-11-12 Thread Dave Tedeyan
Slightly different issue, but I have recently had multiple SB-TL screens not work correctly on arrival. The knock feature was not working and the backlight would not turn on. Called SMA (or Sunpower) and they are going to send us new screens. Cheers, Dave *--* *Dave Tedeyan* *Project Engineer

Re: [RE-wrenches] Temporary Roof Anchors

2016-01-08 Thread Dave Tedeyan
the shingles when we are done. On a related note, does anyone have a good product to use on a trapezoidal (agricultural) metal roof? Currently we tie ropes to large trees and/or structural members on the opposite side of the roof. Cheers, Dave *--* *Dave Tedeyan* *Project Engineer* *Ta

Re: [RE-wrenches] Temporary Roof Anchors

2016-01-08 Thread Dave Tedeyan
If the customer is very particular, we'll replace the shingle. But most of the time we just put in an aluminum flashing under the shingle. -Dave *--* *Dave Tedeyan* *Project Engineer* *Taitem Engineering, PC* 109 S. Albany Street, Ithaca, NY 14850 Voice: (607) 277-1118 x121 www.taitem.co

Re: [RE-wrenches] Rooftop disconnect for multi tracker TLs

2016-01-22 Thread Dave Tedeyan
Solar BOS makes some good disconnects. 4 pole disconnect: F2SK32-1-4XP. Less Expensive than Midnite Solar, but you have to buy directly from Solar BOS and the lead times can be longer. Cheers, Dave *--* *Dave Tedeyan* *Project Engineer* *Taitem Engineering, PC* 109 S. Albany Street, Ithaca

Re: [RE-wrenches] Optimal 200 or 225 Amp Square D MSP All-in-One meter for CT Clamps

2016-02-17 Thread Dave Tedeyan
It is not Square D, but a Milbank U5168-XTL-200 would do the trick. Cheers, Dave *--* *Dave Tedeyan* *Project Engineer* *Taitem Engineering, PC* 109 S. Albany Street, Ithaca, NY 14850 Voice: (607) 277-1118 x121 www.taitem.com On Wed, Feb 17, 2016 at 3:31 PM, Patrick A. Shortell wrote

Re: [RE-wrenches] AFCI trip on metal roof

2016-03-24 Thread Dave Tedeyan
Recently we have had the AFCI trip in a couple SB-TL-22 inverters. Restarted the inverter, the fault was not still present. It has not tripped in the month since at either site. Maybe an issue with the inverter? Only time will tell. Cheers, Dave *--* *Dave Tedeyan* *Project Engineer* *Taitem

[RE-wrenches] Metal Battery Box

2016-05-31 Thread Dave Tedeyan
? Thanks, Dave *--* *Dave Tedeyan* *Project Engineer* *Taitem Engineering, PC* 109 S. Albany Street, Ithaca, NY 14850 Voice: (607) 277-1118 x121 www.taitem.com ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org

Re: [RE-wrenches] Metal Battery Box

2016-06-02 Thread Dave Tedeyan
to go with metal, I would plan to use an equipment ground sized for the 175A breaker the is on the battery cables... Cheers, Dave *--* *Dave Tedeyan* *Project Engineer* *Taitem Engineering, PC* 109 S. Albany Street, Ithaca, NY 14850 Voice: (607) 277-1118 x121 www.taitem.com On Wed, Jun 1, 2016

Re: [RE-wrenches] Buried Conductors

2016-06-24 Thread Dave Tedeyan
ove ground conductor length is <5' you can go with the 30 degree C ambient temperature. Cheers, Dave *--* *Dave Tedeyan* *Project Engineer* *Taitem Engineering, PC* 109 S. Albany Street, Ithaca, NY 14850 Voice: (607) 277-1118 x121 www.taitem.com On Thu, Jun 23, 2016 at 4:41 PM, Peter Pa

Re: [RE-wrenches] Dependable kWh meters

2016-08-22 Thread Dave Tedeyan
here, so I would assume that they would be pretty good. Cheers, Dave *--* *Dave Tedeyan* *Project Engineer* *Taitem Engineering, PC* 109 S. Albany Street, Ithaca, NY 14850 Voice: (607) 277-1118 x121 www.taitem.com On Sun, Aug 21, 2016 at 5:33 PM, wrote: > i have bought from these folks

[RE-wrenches] SMA Arc-Fault

2016-11-10 Thread Dave Tedeyan
his can be caused by the generator? Has anyone run into a situation like this or something similar? Thanks for your help, Dave *--* *Dave Tedeyan* *Project Engineer* *Taitem Engineering, PC* 109 S. Albany Street, Ithaca, NY 14850 Voice: (607) 277-1118 x121 www.

Re: [RE-wrenches] SMA Arc-Fault

2016-11-10 Thread Dave Tedeyan
Daryl, That is what I thought at first. Very rare, but I suppose not impossible that I would have two inverters with bad arc fault detectors. But since we are still getting arc faults after replacing the inverters, I am thinking that it must be something else. Cheers, Dave *--* *Dave Tedeyan

Re: [RE-wrenches] SMA Arc-Fault

2016-11-11 Thread Dave Tedeyan
things you mentioned, although there may be a well pump. They also do have a large water storage tank for heating, but they say that they have not needed to use it yet this year. Then there is also the generator... Thanks for your recommendations. -Dave *--* *Dave Tedeyan* *Project Engineer

Re: [RE-wrenches] SMA Arc-Fault

2016-11-13 Thread Dave Tedeyan
test for this? eGague unit maybe? Cheers, Dave *--* *Dave Tedeyan* *Project Engineer* *Taitem Engineering, PC* 109 S. Albany Street, Ithaca, NY 14850 Voice: (607) 277-1118 x121 www.taitem.com On Fri, Nov 11, 2016 at 10:15 AM, Drake < drake.chamber...@redwoodalliance.org> wrote: > E

Re: [RE-wrenches] SMA Arc-Fault

2016-11-18 Thread Dave Tedeyan
*--* *Dave Tedeyan* *Project Engineer* *Taitem Engineering, PC* 109 S. Albany Street, Ithaca, NY 14850 Voice: (607) 277-1118 x121 www.taitem.com On Tue, Nov 15, 2016 at 10:40 AM, August Goers wrote: > Dave, > > > > It is particularly interesting that you have two inverters with

Re: [RE-wrenches] sma -40 monitoring and tech support

2016-12-15 Thread Dave Tedeyan
ebsite so that we can check it before we all waste hours on the phone with tech support and on site tracking down issues that simply cannot be fixed by us. Cheers, Dave *--* *Dave Tedeyan* *Project Engineer* *Taitem Engineering, PC* 109 S. Albany Street, Ithaca, NY 14850 Voice: (607) 277-1118 x121

[RE-wrenches] Voltage settings on PVP-4800 inverter

2017-06-22 Thread Dave Tedeyan
e inverter closer to the meter. Cheers, Dave *--* *Dave Tedeyan* *Project Engineer* *Taitem Engineering, PC* 10 Verizon Lane, Lansing, NY 14882 Voice: (607) 930-3481 x6 www.taitem.com ___ List sponsored by Redwood Alliance List Address: RE-wrenches@l

Re: [RE-wrenches] Outback warranty issues

2017-06-28 Thread Dave Tedeyan
Jay, I just called them about an hour ago about a FP2 system with a failed inverter. They said they'd have the new control board sent out today, hopefully they actually will. Cheers, Dave *--* *Dave Tedeyan* *Project Engineer* *Taitem Engineering, PC* 10 Verizon Lane, Lansing, NY 14882

Re: [RE-wrenches] Outback warranty issues

2017-06-28 Thread Dave Tedeyan
This one in particular is a warranty repair. They did say that if it was not warranty that I would be better off getting it through a distributor. We've used Ameresco in the past. -Dave *--* *Dave Tedeyan* *Project Engineer* *Taitem Engineering, PC* 10 Verizon Lane, Lansing, NY 14882

Re: [RE-wrenches] AFCI problems with SMA RSB

2017-10-02 Thread Dave Tedeyan
source of this figured out. I had talked to both Sunpower and SMA at the time of this issue, and neither was able to give much help. Cheers, Dave *--* *Dave Tedeyan* *Project Engineer* *Taitem Engineering, PC* 10 Verizon Lane, Lansing, NY 14882 Voice: (607) 930-3481 x6 www.taitem.com On S

Re: [RE-wrenches] sizing up equipment ground per NEC 690.45

2017-10-17 Thread Dave Tedeyan
*--* *Dave Tedeyan* *Project Engineer* *Taitem Engineering, PC* 10 Verizon Lane, Lansing, NY 14882 Voice: (607) 930-3481 x6 www.taitem.com On Mon, Oct 16, 2017 at 4:54 PM, August Goers wrote: > Hi Wrenches, > > Occasionally, we need to up-size the inverter output circuit conductor > s

Re: [RE-wrenches] SolarBridge microinverter troubleshooting and path ahead for stranded customers

2020-07-29 Thread Dave Tedeyan
x27;t used this specific one before, but I did order one today :) Cheers, Dave *Dave Tedeyan, PE* Senior Engineer | Taitem Engineering, PC 110 South Albany Street | Ithaca, NY 14850 o. *607.277.1118 x121* f. 607.277.2119 www.taitem.com Solar • Sustainability • Energy • Design Certified B-Corpor

Re: [RE-wrenches] SolarBridge microinverter troubleshooting and path ahead for stranded customers

2020-07-31 Thread Dave Tedeyan
ler than the rest. > > *Al Frishman* > EvolvedSolar > (917) 699-6641 > > On Jul 29, 2020, at 8:57 PM, Dave Tedeyan wrote: > > Scott, > The best way to find a faulty MI (at least one that is not working at all) > would be to scan the array with an IR camera. When done proper

[RE-wrenches] unfused disconnect before service disconnect

2020-10-29 Thread Dave Tedeyan
rvice point even though it comes first? Or is this not something that is allowed? We are on NEC 2017 here in NY.. . Thanks! -Dave *Dave Tedeyan, PE* Senior Engineer | Taitem Engineering, PC 110 South Albany Street | Ithaca, NY 14850 o. *607.277.1118 x121* f. 607.277.2119 www.taitem.com

Re: [RE-wrenches] unfused disconnect before service disconnect

2020-10-29 Thread Dave Tedeyan
ot; is the first point of overcurrent protection for the service. What I am thinking of is similar to the disconnect allowed on the line side of the meter (230.82 (3)), although this one is on the load side of the meter. Cheers, Dave *Dave Tedeyan, PE* Senior Engineer | Taitem Engineering, PC 110 So

[RE-wrenches] Sunpower monitoring site

2020-11-11 Thread Dave Tedeyan
oring site, but that one seems to be almost as slow, and give only basic system information. I am curious if others are having success monitoring their Sunpower systems, or if people are having similar issues. Cheers, Dave *Dave Tedeyan, PE* Senior Engineer | Taitem Engineering, PC 110 South A

Re: [RE-wrenches] Enphase intermittent breaker trippjng

2020-11-18 Thread Dave Tedeyan
Jason, Bright sunny days, disconnect on the west side of house, maybe in the sun? 43.56A * 1.25 for continuous duty = 54.45A. If these disconnects are also baking in the sun, maybe the extra ambient heat is enough to push it over the edge? Just a thought. Cheers, Dave *Dave Tedeyan, PE* Senior

[RE-wrenches] Conext SW4048 not charging from generator

2020-12-15 Thread Dave Tedeyan
generator from Harbor Freight. I have not laid my own eyes on it yet, but will be there in the next day or two. Just wondering if anyone has experienced these symptoms and have a good idea of what to look for first. Thanks! -Dave *Dave Tedeyan, PE* Senior Engineer | Taitem Engineering, PC 110

Re: [RE-wrenches] Conext SW4048 not charging from generator

2020-12-15 Thread Dave Tedeyan
do you know if the Conext will log an error if the relays have actually been damaged? I am hoping that there will be something in the error logs that will help identify whether there is an inverter issue now, or whether the issue lies with the generator input. Thanks! -Dave *Dave Tedeyan, PE* Sen

Re: [RE-wrenches] Conext SW4048 not charging from generator

2020-12-16 Thread Dave Tedeyan
around 52Hz, when loaded. After, we got it to stay around 56Hz. Fortunately, the homeowner is open to getting a better generator. Thanks for the tips! *Dave Tedeyan, PE* Senior Engineer | Taitem Engineering, PC 110 South Albany Street | Ithaca, NY 14850 o. *607.277.1118 x121* f. 607.277.2119

Re: [RE-wrenches] 600vdc A or B switch

2021-02-22 Thread Dave Tedeyan
It's big and expensive, but you can do a SQD DTU361. At least that part number should get you on the right track. You are looking for a double pole double throw switch, correct? Cheers, Dave On Mon, Feb 22, 2021, 4:59 PM Dave Angelini Offgrid Solar < offgridso...@sti.net> wrote: > Anyone know of

Re: [RE-wrenches] 600vdc A or B switch

2021-02-22 Thread Dave Tedeyan
t;we go where powerlines don't" > http://members.sti.net/offgridsolar/ <http://members.sti.net/offgridsolar/> > e-mail offgridso...@sti.net > text 209 813 0060* > > On Mon, 22 Feb 2021 18:52:14 -0500, Dave Tedeyan > wrote: > > It's big and expensive, b

Re: [RE-wrenches] fronius country set up

2021-03-01 Thread Dave Tedeyan
There is also a menu (I don't have the code handy now, but Fronius tech support should be able to tell you) where you can specifically adjust the individual operating windows - voltage and frequency trips and trip times. Cheers, Dave *Dave Tedeyan, PE* Senior Engineer | Taitem Engineerin

Re: [RE-wrenches] Enphase IQ Envoy Distance for Monitoring

2021-03-01 Thread Dave Tedeyan
put the ENH202 in the middle of someone's house and generally aim it in the right direction and there would be great signal 500' away even through some trees. The TP link one needs a much better line of sight. Cheers, Dave *Dave Tedeyan, PE* Senior Engineer | Taitem Engineering, PC 110 So

Re: [RE-wrenches] Small, non-Tesla GTBB system design

2021-03-03 Thread Dave Tedeyan
, and also if there is a battery failure at some point they can still run as a grid tied system. Cheers, Dave *Dave Tedeyan, PE* Senior Engineer | Taitem Engineering, PC 110 South Albany Street | Ithaca, NY 14850 o. *607.277.1118 x121* f. 607.277.2119 www.taitem.com Solar • Sustainability • Energy

Re: [RE-wrenches] Enphase IQ7A 3 phase limitations

2021-03-03 Thread Dave Tedeyan
I've never really trusted PVWatts on this. I just did a quick test using my location in the northeast, with all the standard values and then just changing the DC to AC ratio. It's telling me that a ratio of 1.5 is almost exactly the same as a ratio of 1, and that around 1.3 is best. You actually lo

Re: [RE-wrenches] Enphase IQ7A 3 phase limitations

2021-03-03 Thread Dave Tedeyan
Then just as a follow up, I looked at the SMA-41 datasheet. This shows that it runs at it's highest efficiency when the output power / rated power is about 0.4 to 0.6, and the only real loss in efficiency comes when you are running at about 0.1 and below. On Wed, Mar 3, 2021, 8:35 PM

Re: [RE-wrenches] Positive grounded inverters for SunPower modules

2021-03-19 Thread Dave Tedeyan
permail/re-wrenches-re-wrenches.org > > List rules & etiquette: > http://www.re-wrenches.org/etiquette.htm > > Check out or update participant bios: > http://www.members.re-wrenches.org > > -- *Dave Tedeyan, PE* [image: Sungineer Solar] 1653 Slaterville Road, Ithaca, NY

[RE-wrenches] Charging multiple battery banks from one array

2021-04-16 Thread Dave Tedeyan
allow all the solar to independently charge each battery? Is there another product out there that people would recommend for this? Thanks for the help! Cheers, Dave -- *Dave Tedeyan, PE* [image: Sungineer Solar] 1653 Slaterville Road, Ithaca, NY 14850 Cell: 607-288-2898 www.sungineersolar.com

Re: [RE-wrenches] seeking 3ph battery based/backed inverters and experiences

2021-04-21 Thread Dave Tedeyan
dfx.com > <http://www.solarandwindfx.com> ~ E-mail: ch...@solarandwindfx.com > * > > > Thomas Jefferson, the author of our great Constitution, once said, > "democracy" will cease to exist when you take away from those who are > willing to work and give to th

Re: [RE-wrenches] Trend away from roof flashings???

2021-04-23 Thread Dave Tedeyan
> List sponsored by Redwood Alliance > > Pay optional member dues here: http://re-wrenches.org > > List Address: RE-wrenches@lists.re-wrenches.org > > Change listserver email address & settings: > http://lists.re-wrenches.org/options.cgi/re-wrenches

[RE-wrenches] Generator and AC coupling on a Sol-Ark

2021-05-03 Thread Dave Tedeyan
will need something rated for just over 30A. This seems like a better way to allow the generator to run at any time it is needed, especially if it is a gloomy, snowy, winter day. Cheers, Dave -- *Dave Tedeyan, PE* [image: Sungineer Solar] 1653 Slaterville Road, Ithaca, NY 14850 Cell: 60

Re: [RE-wrenches] Generator and AC coupling on a Sol-Ark

2021-05-04 Thread Dave Tedeyan
. The 240 V output of the generator circuit provides the signal. >>> >>> At 10:02 AM 5/4/2021, you wrote: >>> >>> Get a contactor with a 240 VAC coil. Connect the coil wire wires to the >>> 240 V output circuit of the generator, so when the gene

Re: [RE-wrenches] Generator and AC coupling on a Sol-Ark

2021-05-07 Thread Dave Tedeyan
://members.sti.net/offgridsolar/> >> e-mail offgridso...@sti.net >> text 209 813 0060* >> >> On Tue, 4 May 2021 19:24:13 -0400, Dave Tedeyan >> wrote: >> >> I suppose the question here is - which is the worse failure mode? >> A. Solar turning of

Re: [RE-wrenches] DC transfer switch

2021-05-08 Thread Dave Tedeyan
Hi Dave, You did get the Square D part right. See the Schneider website, which shows that it is 600V DC and does have an off in the middle. https://www.se.com/us/en/product/DTU361/safety-switch%2C-double-throw%2C-non-fusible%2C-30a%2C-600-vac-vdc%2C-3-poles%2C-30-hp%2C-nema-1/ Cheers, Dave On S

Re: [RE-wrenches] Breakers weakening?

2021-05-08 Thread Dave Tedeyan
Kirk, Could there be a loose wire connection to the breaker? That could cause it to heat up an trip sooner than it otherwise would. Cheers, Dave On Sat, May 8, 2021, 2:13 PM Kirk Herander, VSE wrote: > I have a system where the SE1 inverter fried internally. The 60A AC > output breaker tripp

Re: [RE-wrenches] Generator and AC coupling on a Sol-Ark

2021-05-11 Thread Dave Tedeyan
__ > List sponsored by Redwood Alliance > > Pay optional member dues here: http://re-wrenches.org > > List Address: RE-wrenches@lists.re-wrenches.org > > Change listserver email address & settings: > http://lists.re-wrenches.org/options.cgi/re-