Jason,
Bright sunny days, disconnect on the west side of house, maybe in the sun?
43.56A * 1.25 for continuous duty = 54.45A. If these disconnects are also
baking in the sun, maybe the extra ambient heat is enough to push it over
the edge? Just a thought.
Cheers,
Dave
*Dave Tedeyan, PE*
Senior Engineer | Taitem Engineering, PC

110 South Albany Street | Ithaca, NY 14850
o. *607.277.1118 x121*  f. 607.277.2119
www.taitem.com

Solar • Sustainability • Energy • Design
Certified B-Corporation since 2013


On Wed, Nov 18, 2020 at 3:41 PM Jay <jay.pe...@gmail.com> wrote:

> Hi Jason
>
> Any chance for some photos?
>
> Jay
>
> On Nov 18, 2020, at 12:18 PM, Jason Szumlanski <
> ja...@floridasolardesigngroup.com> wrote:
>
> 
> The plot thickens on the fuse blowing issue. Again, we tore the Enphase IQ
> system apart looking for any reason for the fuse to keep blowing. We
> reconfirmed torque on all line side conductors to the service (supply side
> interconnection using Polaris taps).
>
> Low and behold, I get a second client with the exact same issue yesterday.
> The circumstances are eerily alike. Both disconnects are located on the
> west side of the house and have 36 IQ7+ microinverters on an IQ
> Combiner, requiring 60A fuses on the 60A fusible disconnect. The combined
> inverter output rating is 43.56A. The interconnections are identical with
> #6 THHN 90ºC conductors and Polaris taps. Both disconnects have conductors
> on the right-hand side line-side terminal that are discolored (the copper
> is silvery, the insulation is not burned). The fuses blow at peak current
> around 1:30 pm, only on bright and sunny days.
>
> I'm starting to suspect a faulty fusible disconnect switch. Maybe the
> blades are not making proper contact with the line side terminals.
>
> For the client who is having regular/frequent fuses blowing I plan to
> replace the disconnect with a heavy-duty version or possibly get a 100A
> disconnect with fuse reducers. I'm not sure which option would yield a
> better test. I might also switch brands.
>
> Currently, we are using GE TG3222R. The fuses are Bussman FRN-R Time
> Delay. I have to believe a heavy-duty switch would be less susceptible to
> this, but maybe a higher rated one would be a better option. I'm not a fan
> of fuse reducers, however.
>
> Jason Szumlanski
> Florida Solar Design Group
>
>
> On Sun, Aug 30, 2020 at 5:54 PM Jason Szumlanski <
> ja...@floridasolardesigngroup.com> wrote:
>
>> The tripping breaker occurred at random times, even at night. No
>> weather-related correlation.
>>
>> I have more research to do to see when this fuse issue is happening, but
>> previous visits showed no water ingress. I'm not sure about temperature.
>>
>>
>>
>>
>> On Thu, Aug 27, 2020 at 8:51 PM Jay <jay.pe...@gmail.com> wrote:
>>
>>> Hi Jason
>>>
>>> One thought I have about the blowing fuse is to check it with a IR tool.
>>>
>>> I suspect a poor connection of the fuse to holder which during higher
>>> air temp is causing it to fail.
>>> I’m assuming that the correct amp size and slow blow fuse Is installed
>>> and that the wire connections are done correctly. But again an IR tool
>>> during peak heat would be  a good test.
>>>
>>> About the enphase fix, wow what a head scratcher. But given that it’s
>>> fixed it means that it’s not a short, but enough amps going through over
>>> enough time to trip it. I wonder if a magnetic hydraulic vs thermal breaker
>>> ( CBI  vs CH etc) would have worked?
>>>
>>> Is that breaker box ever in the sun?  Is there any Correlation between
>>>  high ambient temperatures and tripping?
>>>
>>> It sure would keep me up at night too
>>>
>>> Jay
>>>
>>>
>>> On Aug 27, 2020, at 4:29 PM, Jason Szumlanski <
>>> ja...@floridasolardesigngroup.com> wrote:
>>>
>>> 
>>> So the resolution to this is in... But I still have no idea what was
>>> wrong.
>>>
>>> The string of 10 offending microinverters was split into 5 and 5. We had
>>> a spare breaker in the IQ Combiner so it was relatively easy to run another
>>> branch circuit. It has been over two months with no recurrence. So the
>>> issue seems to be resolved, but again, no idea why.
>>>
>>> So here we go again... On another system we have a similar problem now.
>>> In this case it is supply side interconnected with a fusible disconnect.
>>> The same fuse (same line) keeps blowing every few to several weeks. We
>>> can't find any home run wiring issues or issues with terminator caps. There
>>> are no apparent faults in the AC Combiner. We have no idea why this is
>>> happening. But in this system, just the fuse blows, not one of the
>>> individual branch circuit breakers.
>>>
>>> This is getting very frustrating. And this is way more serious because
>>> fuses and service calls are expensive and I can't isolate the issue to one
>>> branch circuit. I don't even know where to start. Leaving each circuit
>>> disconnected for several weeks to prove a negative is an untenable
>>> suggestion to make to a client. But I don't see any other good options.
>>>
>>> Jason Szumlanski
>>>
>>>
>>>
>>>
>>>
>>>
>>>
>>>
>>>
>>>
>>>
>>> On Tue, Jun 9, 2020, 3:42 PM Jason Szumlanski <
>>> ja...@floridasolardesigngroup.com> wrote:
>>>
>>>> Yes, we double-checked that. I have seen that happen before and it's
>>>> one of my early diagnostic steps for something like this.
>>>>
>>>>
>>>>
>>>>
>>>> On Tue, Jun 9, 2020 at 9:18 AM Mac Lewis <maclew...@gmail.com> wrote:
>>>>
>>>>> Hi Jason,
>>>>>
>>>>> Are you certain that the branch circuits aren't crisscrossed
>>>>> somewhere, meaning that an L1 branch 1, isn't connected to an L2 branch 2?
>>>>> That could explain two different breakers tripping.
>>>>>
>>>>> Good luck
>>>>>
>>>>>
>>>>> On Wed, Jun 3, 2020 at 1:07 PM Jason Szumlanski <
>>>>> ja...@floridasolardesigngroup.com> wrote:
>>>>>
>>>>>> Undoubtedly, the termination caps are the second thing we check after
>>>>>> the rooftop junction box(es). These are prone to installation errors, 
>>>>>> even
>>>>>> when the right parts are used. And given the cost, I've thought very long
>>>>>> and hard about abandoning them altogether and terminating strings in 
>>>>>> small
>>>>>> j-boxes with watertight fittings. But in this case, there was no evidence
>>>>>> of improper installation (we replaced them) and it was not correlated to
>>>>>> rain events.
>>>>>>
>>>>>> We are well equipped with bare Q-cable and field wireables that we
>>>>>> could use for troubleshooting to bypass certain sections, but the
>>>>>> intermittent nature of the problem and unpredictable timeframe between
>>>>>> faults is very frustrating. While this is a rare occurrence, it is
>>>>>> definitely a "con" to consider when comparing string vs. microinverters
>>>>>> that I had not strongly considered in the past. I'm intent on getting to
>>>>>> the bottom of this in order to learn what to look for in the future and 
>>>>>> how
>>>>>> to approach diagnoses of Enphase branch circuit faults.
>>>>>>
>>>>>> Jason
>>>>>>
>>>>>>
>>>>>>
>>>>>>
>>>>>>
>>>>>> On Wed, Jun 3, 2020 at 2:31 PM Amos Post <
>>>>>> integrityenergy...@gmail.com> wrote:
>>>>>>
>>>>>>> I was just at a site last week where the Enphase branch circuit
>>>>>>> breaker, outside utility disconnect breaker, and feed breaker in the 
>>>>>>> main
>>>>>>> panel all tripped simultaneously, and it happened about 1 hour before I
>>>>>>> showed up onsite.  The customer said it had happened 1 other time last 
>>>>>>> fall
>>>>>>> but that time it was just the 1 branch circuit in the Enphase combiner
>>>>>>> panel.  Interestingly the customer mentioned that he had just washed off
>>>>>>> the panels, also about 1 hour before I got there.  I went on the roof 
>>>>>>> and
>>>>>>> found that the installing contractor had not put on the Enphase 
>>>>>>> termination
>>>>>>> caps.  1 string was wire-nutted with regular wire nuts and sitting on 
>>>>>>> the
>>>>>>> roof, and the roof was damp right there. This was a fairly flat roof.  
>>>>>>> The
>>>>>>> other micro trunk cable was just cut with no protection at all, tied to 
>>>>>>> the
>>>>>>> rail…
>>>>>>>
>>>>>>>
>>>>>>> <IE LOGO 150x78.jpg>
>>>>>>>
>>>>>>>
>>>>>>>        Amos Post
>>>>>>>    Integrity Energy
>>>>>>>   W 802.763.7023
>>>>>>>    C 802.291.2188
>>>>>>>     ienergyVT.com
>>>>>>> <https://mailtrack.io/trace/link/3d62f76a530747b19a4154eb2e2b0d2548eee0a0?url=http%3A%2F%2Fwww.ienergyvt.com&userId=1613865&signature=6df658aa959a645e>
>>>>>>>         Facebook
>>>>>>> <https://mailtrack.io/trace/link/d6455a016d2384afbd80a78dab5594aee31be9f3?url=https%3A%2F%2Fwww.facebook.com%2Fintegrityenergyllp%3Fref%3Dhl&userId=1613865&signature=8d22e279508a21c8>
>>>>>>>
>>>>>>> On Jun 3, 2020, at 2:05 PM, Jason Szumlanski <
>>>>>>> ja...@floridasolardesigngroup.com> wrote:
>>>>>>>
>>>>>>> The breaker in the main panel IS tripping simultaneously with one of
>>>>>>> the branch circuit breakers each time.
>>>>>>>
>>>>>>>
>>>>>>>
>>>>>>>
>>>>>>>
>>>>>>>
>>>>>>> On Wed, Jun 3, 2020 at 12:43 PM Jay <jay.pe...@gmail.com> wrote:
>>>>>>>
>>>>>>>> A question that keeps nagging me is why do these breakers trip and
>>>>>>>> not the breaker in the main panel?
>>>>>>>> Presuming there is a 40 amp in the main
>>>>>>>>
>>>>>>>> I would have thought that given all the times the breakers have
>>>>>>>> tripped at some point that one would have tripped and I can’t 
>>>>>>>> understand
>>>>>>>> why not?
>>>>>>>>
>>>>>>>> Jay
>>>>>>>>
>>>>>>>> On Jun 3, 2020, at 8:27 AM, Jerry Shafer <jerrysgarag...@gmail.com>
>>>>>>>> wrote:
>>>>>>>>
>>>>>>>> 
>>>>>>>> Wrenches
>>>>>>>> Looking g at the bigger breaker tripping at the same time is very
>>>>>>>> likely do to response time of the breaker nothing more. As l suggested 
>>>>>>>> in a
>>>>>>>> previous message. Use a non bridged breaker to see if it is one or both
>>>>>>>> legs that trip. Also an eguage will help to see what if anything leads 
>>>>>>>> up
>>>>>>>> to the failure and when.
>>>>>>>> Jerry
>>>>>>>> Jerry
>>>>>>>>
>>>>>>>> On Wed, Jun 3, 2020, 7:58 AM Jason Szumlanski <
>>>>>>>> ja...@floridasolardesigngroup.com> wrote:
>>>>>>>>
>>>>>>>>> I wonder about that. Of course, it could be the "inverter output
>>>>>>>>> circuit" having a fault in the wiring still (an intermittent issue
>>>>>>>>> somewhere within the IQ cable or home run wiring). But internal to the
>>>>>>>>> microinverter, is it possible that a fault could still occur at 
>>>>>>>>> night? I
>>>>>>>>> had a suggestion from another wrench that there are film capacitors 
>>>>>>>>> on the
>>>>>>>>> AC output side, but are these isolated when there is no DC input? It 
>>>>>>>>> seems
>>>>>>>>> unlikely that this would be an issue, but I have seen microinverters
>>>>>>>>> reporting a couple of watts at night (in Enlighten). I'm not sure how 
>>>>>>>>> real
>>>>>>>>> that is.
>>>>>>>>>
>>>>>>>>> The overriding question I have is what kind of fault would cause
>>>>>>>>> BOTH a branch circuit and the main solar breaker to trip 
>>>>>>>>> simultaneously?
>>>>>>>>> That seems odd to me. If any normal load branch circuit has a fault, 
>>>>>>>>> you
>>>>>>>>> don't often see premises main breakers tripping, or even feeder 
>>>>>>>>> circuit
>>>>>>>>> breakers.
>>>>>>>>>
>>>>>>>>> I got to thinking that maybe there is some kind of issue between
>>>>>>>>> the BR220 and CH240 breakers not playing nicely together. But I would 
>>>>>>>>> think
>>>>>>>>> this would be a well-known issue because I'm sure there are tons of CH
>>>>>>>>> feeder breakers in the wild with BR branch circuits downstream.
>>>>>>>>>
>>>>>>>>>
>>>>>>>>>
>>>>>>>>> On Tue, Jun 2, 2020 at 9:25 AM <
>>>>>>>>> drake.chamber...@redwoodalliance.org> wrote:
>>>>>>>>>
>>>>>>>>>> If it trips at night, we know it is not the output from the
>>>>>>>>>> inverters causing the tripping. The current must be coming from the 
>>>>>>>>>> grid.
>>>>>>>>>> ---
>>>>>>>>>>
>>>>>>>>>>
>>>>>>>>>>
>>>>>>>>>> On 2020-06-01 12:05, Jason Szumlanski wrote:
>>>>>>>>>>
>>>>>>>>>>
>>>>>>>>>> It's not weather. It's at all times of the day and night, and I
>>>>>>>>>> confirmed that there is no correlation to rain or high winds. That 
>>>>>>>>>> was my
>>>>>>>>>> first suspicion.
>>>>>>>>>>
>>>>>>>>>>
>>>>>>>>>> On Mon, Jun 1, 2020 at 10:27 AM Ray <r...@solarray.com> wrote:
>>>>>>>>>>
>>>>>>>>>> Is it at all weather related?  Rain, or high humidity?  High
>>>>>>>>>> temperatures?  Do you have any indication what time of day it trips 
>>>>>>>>>> off at?
>>>>>>>>>>
>>>>>>>>>> Ray Walters
>>>>>>>>>> Remote Solar
>>>>>>>>>> 303 505-8760
>>>>>>>>>>
>>>>>>>>>> On 6/1/20 10:23 AM, Jason Szumlanski wrote:
>>>>>>>>>>
>>>>>>>>>> Well, that didn't resolve it. The main breaker and a branch
>>>>>>>>>> circuit breaker tripped again a few days ago. It was the same branch 
>>>>>>>>>> this
>>>>>>>>>> time.
>>>>>>>>>>
>>>>>>>>>> As my next diagnostic step I swapped two circuits (on which
>>>>>>>>>> breaker they are landed). If history is a guide, it will work for 
>>>>>>>>>> about two
>>>>>>>>>> weeks and then trip again.
>>>>>>>>>>
>>>>>>>>>> I'm dumbfounded. I really don't want to have to tear this whole
>>>>>>>>>> system apart. At this point, if I have to remove all the modules, I 
>>>>>>>>>> feel
>>>>>>>>>> that I need to replace all of the trunk cable which is an expensive
>>>>>>>>>> proposition. I really don't know what else to do at this point.
>>>>>>>>>>
>>>>>>>>>> Jason
>>>>>>>>>>
>>>>>>>>>>
>>>>>>>>>> On Mon, May 25, 2020, 10:43 AM Jason Szumlanski <
>>>>>>>>>> ja...@floridasolardesigngroup.com> wrote:
>>>>>>>>>>
>>>>>>>>>> I strongly suspect the CH240 combined breaker was compromised (we
>>>>>>>>>> will see). Since it happened that two different strings tripped, I 
>>>>>>>>>> doubt I
>>>>>>>>>> have two microinverters with internal faults. It has to be the 
>>>>>>>>>> combined
>>>>>>>>>> breaker. I was just surprised that branch circuit breakers were 
>>>>>>>>>> tripping
>>>>>>>>>> simultaneously with the combined output breaker.
>>>>>>>>>>
>>>>>>>>>> Of all the supply side connected systems I have installed, I have
>>>>>>>>>> never seen a combined output fusible disconnect fuse blow, but I 
>>>>>>>>>> have seen
>>>>>>>>>> many combined output breakers tripped. I was worried early on that I 
>>>>>>>>>> would
>>>>>>>>>> be replacing fuses constantly, but that has not been an issue 
>>>>>>>>>> whatsoever.
>>>>>>>>>>
>>>>>>>>>>
>>>>>>>>>>
>>>>>>>>>>
>>>>>>>>>>
>>>>>>>>>> On Thu, May 21, 2020 at 11:15 AM <scot.a...@solarcentex.com>
>>>>>>>>>> wrote:
>>>>>>>>>>
>>>>>>>>>> Actually, we had a IQ7 string loaded up to its max panel size and
>>>>>>>>>> max string length and in the spring on cool, clear day, it tripped 
>>>>>>>>>> the
>>>>>>>>>> string's associated breaker in the Enphase combiner.
>>>>>>>>>>
>>>>>>>>>>
>>>>>>>>>> We reset but of course that breaker was impaired and it tripped
>>>>>>>>>> again. We replaced and never had an issue going forward. We suspect 
>>>>>>>>>> the
>>>>>>>>>> breaker was less than perfect from the start as we've add equally 
>>>>>>>>>> nice days
>>>>>>>>>> since.
>>>>>>>>>>
>>>>>>>>>>
>>>>>>>>>> This almost reminds me of loading up Outback FM80. It says 4,000
>>>>>>>>>> watts but in reality, 3,600 is the max when amps spike. I will be 
>>>>>>>>>> extra
>>>>>>>>>> careful going forward on IQ7 string length when going to the max
>>>>>>>>>> published...
>>>>>>>>>>
>>>>>>>>>>
>>>>>>>>>> My story.
>>>>>>>>>>
>>>>>>>>>>
>>>>>>>>>> Scot
>>>>>>>>>>
>>>>>>>>>>
>>>>>>>>>> *From:* RE-wrenches <re-wrenches-boun...@lists.re-wrenches.org> *On
>>>>>>>>>> Behalf Of *Jason Szumlanski
>>>>>>>>>> *Sent:* Thursday, May 21, 2020 8:57 AM
>>>>>>>>>> *To:* RE-wrenches <re-wrenches@lists.re-wrenches.org>
>>>>>>>>>> *Subject:* [RE-wrenches] Enphase intermittent breaker trippjng
>>>>>>>>>>
>>>>>>>>>>
>>>>>>>>>> I'm trying to resolve an intermittent frustrating problem with
>>>>>>>>>> and Enphase IQ system. There are three AC Branch circuits of 9
>>>>>>>>>> microinverters each coming into an Enphase AC combiner.
>>>>>>>>>>
>>>>>>>>>>
>>>>>>>>>> What has been happening is one of the BR220 branch circuit
>>>>>>>>>> breakers and the combine CH240 breaker in the main backfed load 
>>>>>>>>>> center have
>>>>>>>>>> been tripping simultaneously. It has happened about four times in 
>>>>>>>>>> the last
>>>>>>>>>> 6 months. It was always the same branch circuit breaker, so we kept
>>>>>>>>>> investigating that string, checking the junction box, trunk cable, 
>>>>>>>>>> and cap,
>>>>>>>>>> etc. Finally we swapped out the BR220 breaker.
>>>>>>>>>>
>>>>>>>>>>
>>>>>>>>>> Fast forward 4 weeks, and we got another call. This time a
>>>>>>>>>> different branch circuit breaker and the main breaker tripped
>>>>>>>>>> simultaneously. We checked that branch circuit and could not find any
>>>>>>>>>> fault. It seems unlikely that two branch circuit breakers would be 
>>>>>>>>>> faulty,
>>>>>>>>>> so we have now switched out the CH240 main breaker in hopes that it 
>>>>>>>>>> is the
>>>>>>>>>> culprit.
>>>>>>>>>>
>>>>>>>>>>
>>>>>>>>>> I'm not totally confident in this resolution and I have my
>>>>>>>>>> fingers crossed. If that doesn't work, does anyone have any 
>>>>>>>>>> suggestions on
>>>>>>>>>> another diagnostic step? These intermittent problems are a major 
>>>>>>>>>> hassle.
>>>>>>>>>> One thought I had was to switch to a supply side interconnection 
>>>>>>>>>> with a
>>>>>>>>>> fusible disconnect. Maybe the intermittent fault would blow one of 
>>>>>>>>>> the two
>>>>>>>>>> line fuses so at least I could narrow it down to which line the 
>>>>>>>>>> fault is on
>>>>>>>>>> if there is in fact a fault.
>>>>>>>>>>
>>>>>>>>>>
>>>>>>>>>> I have experienced two other tripping breaker issues with Enphase
>>>>>>>>>> systems in the past. Neither of them were systems I installed. One 
>>>>>>>>>> turned
>>>>>>>>>> out to be branch circuits that were not properly paired up and 
>>>>>>>>>> landed on
>>>>>>>>>> different breakers. Another time we had an inverter with an internal 
>>>>>>>>>> fault
>>>>>>>>>> which eventually"blew up" with a loud popping noise and smoke 
>>>>>>>>>> billowing out
>>>>>>>>>> of it. That happened after resetting a trip breaker multiple times. 
>>>>>>>>>> This
>>>>>>>>>> case seems to be unrelated to those issues. I'm perplexed.
>>>>>>>>>>
>>>>>>>>>>
>>>>>>>>>> Jason Szumlanski
>>>>>>>>>>
>>>>>>>>>> Florida Solar Design Group
>>>>>>>>>>
>>>>>>>>>>
>>>>>>>>>> _______________________________________________
>>>>>>>>>>
>>>>>>>>>>
>>>>> <IE LOGO 150x78.jpg>
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>>
>>> List Address: RE-wrenches@lists.re-wrenches.org
>>>
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>> <https://mailtrack.io/trace/link/a801e11047bc1010037cfdbe055bd092d1a4f46c?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=05066884a48f1bfe>
>>>
>>> List-Archive:
>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>> <https://mailtrack.io/trace/link/3d05f25829ab04d841703b4ca92c987450b2ae03?url=http%3A%2F%2Flists.re-wrenches.org%2Fpipermail%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=fc0244766d9eeb43>
>>>
>>> List rules & etiquette:
>>> www.re-wrenches.org/etiquette.htm
>>> <https://mailtrack.io/trace/link/5f04781657fcaa5a49591b7a56acb717e508af4c?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=16aaa91e76397ba6>
>>>
>>> Check out or update participant bios:
>>> www.members.re-wrenches.org
>>> <https://mailtrack.io/trace/link/97ebe2c605c060f20eaee7d9963e71520c8d2ceb?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=6aecb4c1db8de13f>
>>>
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>>
>>> List Address: RE-wrenches@lists.re-wrenches.org
>>>
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>> <https://mailtrack.io/trace/link/705e025611710906a83f10daaa516a558c04e151?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=0c22c05a885185fb>
>>>
>>> List-Archive:
>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>> <https://mailtrack.io/trace/link/a7227ae7a26262025d10f2e9a9c9629b876e7115?url=http%3A%2F%2Flists.re-wrenches.org%2Fpipermail%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=ce2abedc2f74f364>
>>>
>>> List rules & etiquette:
>>> www.re-wrenches.org/etiquette.htm
>>> <https://mailtrack.io/trace/link/f55ae01ea290b7240fd7e8bee597be67495770e5?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=e1483c1346923a63>
>>>
>>> Check out or update participant bios:
>>> www.members.re-wrenches.org
>>> <https://mailtrack.io/trace/link/5268f9a24fc1fed0f4a7ce823fa3c56679cfae16?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=89d19125692e15d4>
>>>
>>> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to