Lloyd, I see what you are saying. Although in 250.24, it seems that they are expecting this first disconnect to have overcurrent protection and be the service disconnecting means. So what if the first disconnect does not have overcurrent protection? I am assuming the "service disconnect" is the first point of overcurrent protection for the service. What I am thinking of is similar to the disconnect allowed on the line side of the meter (230.82 (3)), although this one is on the load side of the meter. Cheers, Dave
*Dave Tedeyan, PE* Senior Engineer | Taitem Engineering, PC 110 South Albany Street | Ithaca, NY 14850 o. *607.277.1118 x121* f. 607.277.2119 www.taitem.com Solar • Sustainability • Energy • Design Certified B-Corporation since 2013 On Thu, Oct 29, 2020 at 12:03 PM Lloyd Hoffstatter < ll...@sunstruckconsulting.com> wrote: > Dave, > Looking at 2014, NEC 250.24(B) FPN and exhibits tends to imply bonding at > first means of disconnect. This also minimizes potential ground loops. > Best regards, > Lloyd Hoffstatter > Sunstruck Consulting > > Get Outlook for iOS <https://aka.ms/o0ukef> > ------------------------------ > *From:* RE-wrenches <re-wrenches-boun...@lists.re-wrenches.org> on behalf > of Dave Tedeyan <dtede...@taitem.com> > *Sent:* Thursday, October 29, 2020 9:56:47 AM > *To:* RE-wrenches <re-wrenches@lists.re-wrenches.org> > *Subject:* [RE-wrenches] unfused disconnect before service disconnect > > I'm looking to the hive mind here to see if others can weigh in on an > issue I am having with an inspector. Grid tied PV system, with a line side > tap in an automatic transfer switch. There is an outdoor utility required > system disconnect right next to the transfer switch. But there was not > enough physical space to get something that was service rated with > overcurrent protection. So we installed a QO200TR, which is a tiny switch > that looks like a circuit breaker, is rated at 60A, but does not actually > have overcurrent protection. Then just inside the basement is the service > disconnect with the neutral ground bond, etc. The inspector is telling me > to bond the neutral and ground in the outdoor unfused disconnect, and > remove it in the disconnect in the basement. > > I am having trouble finding a code reference. Does anyone know of one > showing that the unfused disconnect is not the service point even though it > comes first? Or is this not something that is allowed? We are on NEC 2017 > here in NY.. > . > Thanks! > -Dave > > *Dave Tedeyan, PE* > Senior Engineer | Taitem Engineering, PC > > 110 South Albany Street | Ithaca, NY 14850 > o. *607.277.1118 x121* f. 607.277.2119 > www.taitem.com > > Solar • Sustainability • Energy • Design > Certified B-Corporation since 2013 > _______________________________________________ > List sponsored by Redwood Alliance > > List Address: RE-wrenches@lists.re-wrenches.org > > Change listserver email address & settings: > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org > > There are two list archives for searching. When one doesn't work, try the > other: > https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/ > http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org > > List rules & etiquette: > http://www.re-wrenches.org/etiquette.htm > > Check out or update participant bios: > http://www.members.re-wrenches.org > >
_______________________________________________ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org There are two list archives for searching. When one doesn't work, try the other: https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/ http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: http://www.re-wrenches.org/etiquette.htm Check out or update participant bios: http://www.members.re-wrenches.org