CEP Certified Solar Professional (PVIP) Florida State Certified Solar Contractor CVC56956 Florida Certified Electrical Contractor EC13013208 On Tue, Apr 23, 2024 at 5:47 PM Dave Angelini Offgrid Solar via RE-wrenches wrote: Not being helpful but I walk away from these. It will come back to you.

Re: [RE-wrenches] XW Pro Firmware 2.04 melting devices

2024-04-25 Thread Dave Angelini Offgrid Solar via RE-wrenches
Good advice Michael! I had one that the grid code got set by FW and reverting did not help. Had to start fresh. I certainly would try the revert as it is so much easier. There just is too much grid firmware being changed and it does not need to be done offgrid. I beg people and Schneider,

Re: [RE-wrenches] XW Pro Firmware 2.04 melting devices

2024-04-25 Thread Dave Angelini Offgrid Solar via RE-wrenches
To be fare, Schneider does tell you to follow the commissioning guide. It should be in the firmware though and should be a warning. It is only an issue with older XWP BTW. Let us know what you end up doing Kevin please. Dave Angelini Offgrid Solar "we go where powerlines don't" [1]https://

Re: [RE-wrenches] Discover Xanbus SOC jumpy

2024-05-03 Thread Dave Angelini Offgrid Solar via RE-wrenches
Which model? Do you see the same dips in voltage? Probably yes. Are all the batts the same firmware? The AES dashboard can be useful for finding a differing module. No I have not seen this and only have had one bad battery that was replaced by AES. Yes check all wiring. Good Luck! Dave Angelin

Re: [RE-wrenches] Discover AES explosion!

2024-05-03 Thread Dave Angelini Offgrid Solar via RE-wrenches
Never heard of one with LFP. The cobalt and Magnesium Lions are definitely out there. Was this a 6650 model Michael? Going to be fun times doing a failure analysis on this one. Dave Angelini Offgrid Solar "we go where powerlines don't" [1]https://offgridsolar1.com/ [2] [1] e-mail offgridso.

Re: [RE-wrenches] Discover AES explosion!

2024-05-03 Thread Dave Angelini Offgrid Solar via RE-wrenches
The 6650 definitely meets all the UL's, ETLs, and UN's. Probably the first one to do this and since Michael said that it is a first for Discover, the jury is out until an FA is complete. Good points by you Larry, but not valid for many thousands of Discover AES 6650s. Dave Angelini Offgrid S

Re: [RE-wrenches] Discover Xanbus SOC jumpy

2024-05-03 Thread Dave Angelini Offgrid Solar via RE-wrenches
Kent, Battery monitor is internal to 6650 battery. No bat mon! Probably as you said the xanbus comms need a look as Mac said. Dave Angelini Offgrid Solar "we go where powerlines don't" [1]https://offgridsolar1.com/ [2] [1] e-mail offgridso...@sti.net text 209 813 0060 On 2024-05-03 10:24

Re: [RE-wrenches] Discover Xanbus SOC jumpy

2024-05-03 Thread Dave Angelini Offgrid Solar via RE-wrenches
You probably checked historical events and analysis below. Dave Angelini Offgrid Solar "we go where powerlines don't" [1]https://offgridsolar1.com/ [2] [1] e-mail offgridso...@sti.net text 209 813 0060 On 2024-05-03 10:30 am, Dave Angelini Offgrid Solar via RE-wrenches

Re: [RE-wrenches] Fortress Avalon

2024-05-14 Thread Dave Angelini Offgrid Solar via RE-wrenches
Huge mistake to me to use high voltage battery. I am biased for offgrid. Dave Angelini Offgrid Solar "we go where powerlines don't" [1]https://offgridsolar1.com/ [2] [1] e-mail offgridso...@sti.net text 209 813 0060 On 2024-05-14 5:28 pm, Mac Lewis via RE-wrenches wrote: Hello Wrenches,

Re: [RE-wrenches] Fortress Avalon

2024-05-15 Thread Dave Angelini Offgrid Solar via RE-wrenches
Hey Darryl, I got involved with the Schneider Home all in one (same thing as Fortress Avalon) Before that I was involved with another Schneider HV all in one long before Solark. Omnia failed to get to market. I get the hee bee jeebies with that kind of voltage offgrid. The numerous various fa

Re: [RE-wrenches] Optics

2024-05-19 Thread Dave Angelini Offgrid Solar via RE-wrenches
On November 8, 2023, the Company's Board of Directors approved a plan to stop production and operations of residential renewable energy products, which include our OutBack and Mojave brands. Management determined that residential renewable energy products no longer fit with the company's core s

Re: [RE-wrenches] Optics

2024-05-19 Thread Dave Angelini Offgrid Solar via RE-wrenches
Easier to read but still not a good sign! When I worked at HP in the 80's they struggled with keeping old equipment alive. It was terribly expensive and they just stopped after 5 years and let the secondary market do repairs. Even that was expensive and finally just stopped keeping any inven

Re: [RE-wrenches] Outback:

2024-05-20 Thread Dave Angelini Offgrid Solar via RE-wrenches
Interesting that Commerce, TX is 20 miles from Sulphur Springs, TX which is the home of Signature Solar. https://www.outbackpower.com/resources/ ... rt-request [4] Shows: 404 Page Not Found Component not found [5] The moderators (not Outback employees) on the forum have an interesting conspir

Re: [RE-wrenches] Optics

2024-05-21 Thread Dave Angelini Offgrid Solar via RE-wrenches
Anyone who fixes Outback's inability to run closed loop would be great. I think I have seen Outback claim it was coming soon for 5 years now. Hopefully they can get Optics up soon for my 3 clients. Dave Angelini Offgrid Solar "we go where powerlines don't" [8]https://offgridsolar1.com/ [9]

Re: [RE-wrenches] Optics

2024-05-21 Thread Dave Angelini Offgrid Solar via RE-wrenches
am, Todd Cory via RE-wrenches wrote: "OPTICS RE Back Online [1] * Report [2] * Quote [3] Post [1] by Marshall Neipert [4] » 20 May 2024 20:32 Enersys has fixed the issue and Optics RE is back online." Except it is not for me. Todd On Tuesday, May 21, 2024 7:22am, "Dave Angelini Of

Re: [RE-wrenches] I know you've all said, "I told you so..." SolarEdge...

2024-05-24 Thread Dave Angelini Offgrid Solar via RE-wrenches
Well to me the final, final straw is their stock price losing 2/3 its value in a year. I tell all of my clients if you ever have to do roof solar, you should use a central inverter and not ever put electronics on a roof. Bad enough to put solar panels up there! Dave Angelini Offgrid Solar "w

Re: [RE-wrenches] Outback Tech Support

2024-05-24 Thread Dave Angelini Offgrid Solar via RE-wrenches
Marshall Neipert [3]Forum MemberPosts: 11 [4]Joined: Mon May 20, 2024 10:07 amMy RE system: President of Outback Power https://www.linkedin.com/in/neipertContact: Contact Marshall Neipert [5] You should ask him Drake! He is on the forum and responding to some emails. Here is in a link that he i

Re: [RE-wrenches] Outback Tech Support

2024-05-24 Thread Dave Angelini Offgrid Solar via RE-wrenches
Jay, maybe the price was right? Obvious the old parent corporation wanted into commercial solar. As for EG4 maybe the old lawyer shark saying about eat or be eaten. It was about 5 years back that Schneider sold all commercial solar and it helped their stock. Crossing fingers! Happy hour soon!

Re: [RE-wrenches] Water system with Grundfos SQFlex

2024-05-26 Thread Dave Angelini Offgrid Solar via RE-wrenches
Hey Brad, Sometimes shooting is best if you tell more on what you have done so far like using the SQF shooting guide, especially on a holiday weekend😉 Assume there is a CU200 controller and pump is in ground still, must be with 100ft head, sorry No high amps? It runs, How old? --Dave Dave An

Re: [RE-wrenches] Discover AES exposion

2024-05-28 Thread Dave Angelini Offgrid Solar via RE-wrenches
Hey Michael, I heard that it was a pretty small shed, can you comment on that please. Good luck on the trouble shooting. Dave Angelini Offgrid Solar "we go where powerlines don't" [1]https://offgridsolar1.com/ [2] [1] e-mail offgridso...@sti.net text 209 813 0060 On 2024-05-27 8:40 pm, M

Re: [RE-wrenches] Simpliphi Phi 3.8 48V Case Color

2024-05-29 Thread Dave Angelini Offgrid Solar via RE-wrenches
All I can add is get the closed loop version with electronics that can interface. It is a huge improvement over open loop. Dave Angelini Offgrid Solar "we go where powerlines don't" [1]https://offgridsolar1.com/ [2] [1] e-mail offgridso...@sti.net text 209 813 0060 On 2024-05-29 9:10 am, D

Re: [RE-wrenches] How many times can a rafter have a lag screw put in and out before it is no longer structurally sound? Some roofs getting their 3rd set of new shingles

2024-05-30 Thread Dave Angelini Offgrid Solar via RE-wrenches
Scott, For liability you might want a before and after inspection by a really top inspector that you trust. I would also ask your insurance for guidance. My insurance is always telling me that going out of business is the typical last straw for roofers. Build a solar pergola😉 Dave Angelini

Re: [RE-wrenches] Sol-Ark Support

2024-06-05 Thread Dave Angelini Offgrid Solar via RE-wrenches
Optics was down again last weekend and I read this comment below from the Outback forum. Day 11….without communication with our Sol Ark 15k inverter….Thanks Sol-Ark Solar * Quote [4] Post [5] Mon Jun 03, 2024 4:07 pm Who would have known? A conspiracy theorist that is right??? So i

Re: [RE-wrenches] Two Outback Radian 8048 fails in same week..what is likely wrong in 7+ year inverters?

2024-06-10 Thread Dave Angelini Offgrid Solar via RE-wrenches
High temperatures are a major cause of electronic equipment failures, contributing to more than 50% of them. A rule of thumb is that for every 10°C increase in temperature, the failure rate of electronic components will double and their life will be reduced by half. This rule is based on the Ar

Re: [RE-wrenches] Xantrex XW6048 HOT!

2024-06-13 Thread Dave Angelini Offgrid Solar via RE-wrenches
killing electronics and the need of cooling down your way. Good Luck! Dave Angelini Offgrid Solar "we go where powerlines don't" [1]https://offgridsolar1.com/ [2] [1] e-mail offgridso...@sti.net text 209 813 0060 On 2024-06-13 8:26 am, Dave Angelini Offgrid Solar via RE-

Re: [RE-wrenches] Xantrex XW6048 HOT!

2024-06-13 Thread Dave Angelini Offgrid Solar via RE-wrenches
Disco 250A breaker on bad XW and remove its xanbus RJ45. Assume the bad one is not the master? Dave Angelini Offgrid Solar "we go where powerlines don't" [1]https://offgridsolar1.com/ [2] [1] e-mail offgridso...@sti.net text 209 813 0060 On 2024-06-13 8:01 am, Jason Szumlanski via RE-wrenc

Re: [RE-wrenches] Xantrex XW6048 HOT!

2024-06-13 Thread Dave Angelini Offgrid Solar via RE-wrenches
Yes worrisome. The fault log will show possible causes. The troubleshooting guide will tell you too look for black chunks of mosfet transistors in the right bay of XW down low. Really rare, but in a hot environment 10 years is pretty amazing. All of the docs are on the Schneider site under XW

Re: [RE-wrenches] Dual battery bank switch for 48 VDC system

2024-06-15 Thread Dave Angelini Offgrid Solar via RE-wrenches
Good Luck ! I look every year and there are never any rated this high. A few knock-off cheap ones but??? I have used the Blue Seas and one other with this app. If you are careful about switching under big loads/EQV's it will last. If this is an insured home, you have to disclose this or be

Re: [RE-wrenches] Outback app

2024-06-17 Thread Dave Angelini Offgrid Solar via RE-wrenches
Is this referring to the Android or iOS app? They appear to be dead horses. Optics is functional via a web browser. Dave Angelini Offgrid Solar "we go where powerlines don't" [1]https://offgridsolar1.com/ [2] [1] e-mail offgridso...@sti.net text 209 813 0060 On 2024-06-17 2:49 pm, Jay via R

[RE-wrenches] Looking for Powerewall installer for central California

2024-06-26 Thread Dave Angelini Offgrid Solar via RE-wrenches
Any wrenches installing the powerwall 3 in central Cali ? https://www.tesla.com/support/energy/powerwall/learn/what-expect-powerwall-3 Dave Angelini Offgrid Solar "we go where powerlines don't" [1]https://offgridsolar1.com/ [2] [1] e-mail offgridso...@sti.net text 209 813 0060 Links: ---

Re: [RE-wrenches] Fortress LFP batteries and Outback charge controller

2024-06-30 Thread Dave Angelini Offgrid Solar via RE-wrenches
You and the client lose the ability to monitor it all in one place do you not? Dave Angelini Offgrid Solar "we go where powerlines don't" [1]https://offgridsolar1.com/ [2] [1] e-mail offgridso...@sti.net text 209 813 0060 On 2024-06-29 4:48 pm, Kirk Herander via RE-wrenches wrote: All,

Re: [RE-wrenches] Ideas and help please. Solar Edge nightmare

2024-07-10 Thread Dave Angelini Offgrid Solar via RE-wrenches
You are talking about the LG RESU10 H right? Dave Angelini Offgrid Solar "we go where powerlines don't" [1]https://offgridsolar1.com/ [2] [1] e-mail offgridso...@sti.net text 209 813 0060 On 2024-07-10 3:20 pm, Peter Giroux via RE-wrenches wrote: Hi my fellow wrenchers, need some help w

Re: [RE-wrenches] AES RACK MOUNT

2024-07-17 Thread Dave Angelini Offgrid Solar via RE-wrenches
Awesome reliability on the AES 6650's we use with XW. Super easy installation. The cons on the new racks are that they are more work to install compared to the 6650. Two ways to install with Schneider though. Discover has said they will automate with the internet the install soon. I would not

Re: [RE-wrenches] Another Mate 3 programming issues

2024-07-19 Thread Dave Angelini Offgrid Solar via RE-wrenches
MX60 was not networked which was the reason I stopped using them and went to Xantrex around 2005. Not surprised that you could not change MX60 settings on mate. Long time ago... Dave Angelini Offgrid Solar "we go where powerlines don't" [2]https://offgridsolar1.com/ [3] [2] e-mail offgrid

Re: [RE-wrenches] Mate 3 firmware updates

2024-07-19 Thread Dave Angelini Offgrid Solar via RE-wrenches
https://www.youtube.com/results?search_query=outback+mate3s Dave Angelini Offgrid Solar "we go where powerlines don't" [1]https://offgridsolar1.com/ [2] [1] e-mail offgridso...@sti.net text 209 813 0060 On 2024-07-19 4:18 pm, Jim Gowdy via RE-wrenches wrote: I'm somewhat new to the solar i

Re: [RE-wrenches] KiloVault Issues

2024-07-30 Thread Dave Angelini Offgrid Solar via RE-wrenches
Another one bites the dust ! From Google. As of March 2024, KiloVault, a solar energy storage company, is no longer in business. "we go where powerlines don't" [2]https://offgridsolar1.com/ [3] [2] e-mail offgridso...@sti.net text 209 813 0060 On 2024-07-30 10:55 am, Chris Daum via RE-w

Re: [RE-wrenches] Sunpower connectors

2024-08-01 Thread Dave Angelini Offgrid Solar via RE-wrenches
As of July 19,2024 some say that SunPower's announcement to stop new leases, installations, and shipments may indicate the end of the company as an operating business. SunPower's stock has also dropped nearly 93% in the last 12 months Ouch, fair to say the writing has been on the wall or the W

Re: [RE-wrenches] discover lithium warranty issues.

2024-08-15 Thread Dave Angelini Offgrid Solar via RE-wrenches
What is a POP Jay? I assume the customer did not fill out the warranty info when new? Big mistake on something with a 10 year warranty. With all of the used junk on ebay/Amazon why would you not be difficult? Dave Angelini Offgrid Solar "we go where powerlines don't" [1]https://offgridsolar

Re: [RE-wrenches] discover lithium warranty issues.

2024-08-15 Thread Dave Angelini Offgrid Solar via RE-wrenches
Being from Manufacturing I just disagree that warranty should pass on to a different owner. (Unless in writing) Too much chance for failure with a new owner. We do want these folks to stay in business right? Batteries are hard enough in residential when doing everything correct. Dave Angelin

Re: [RE-wrenches] Portable systems

2024-08-17 Thread Dave Angelini Offgrid Solar via RE-wrenches
Some of these even have the 240 receptacle to plug into a 30A home dryer receptacle for hurricane connection. Get the HV solar mppt built-in option and a some panels and you are set for the 30% tax credit. Might not need a wrench someday 😉 Dave Angelini Offgrid Solar "we go where powerlines do

Re: [RE-wrenches] OB Radian / FM60 grid tie mystery

2024-08-18 Thread Dave Angelini Offgrid Solar via RE-wrenches
You are all the Outaback wrenches but with Schneider before you reset the defaults, you should just do a complete DC power down. Just in case it is a stuck bit in config. Dave Angelini Offgrid Solar "we go where powerlines don't" [2]https://offgridsolar1.com/ [3] [2] e-mail offgridso...@s

Re: [RE-wrenches] discover lithium warranty issues.

2024-08-19 Thread Dave Angelini Offgrid Solar via RE-wrenches
the right to be annoyed when a high-priced, properly-set-up, top tier product with a 10-year warranty fails in under three years and the case ends up in a warranty exception loophole with no joy. I'll get over it though. Luke Christy 719-588-3044 On Aug 15, 2024, at 12:08 PM, Dave Angeli

Re: [RE-wrenches] Fortress Shutdown?

2024-08-27 Thread Dave Angelini Offgrid Solar via RE-wrenches
When I have had someone lose an SPD (I assume it was on DC buss) there is often latent damage (shows up later) to many of the devices. In a Hi Rel mode, it is recommended to replace it all. Most offgrid is not that critical but try telling that to someone with rotten food. The freezers and re

Re: [RE-wrenches] Fortress Shutdown?

2024-08-27 Thread Dave Angelini Offgrid Solar via RE-wrenches
t the surge would make it past the Classic without damage, but then damage the Fortress BMS in an otherwise imperceptible manner. That is our current best theory at the moment though. I added an SPD on the 48 v buss, before this latest total shutdown. Ray Walters On 8/27/2024 2:35 PM,

Re: [RE-wrenches] Powerwall 3

2024-09-10 Thread Dave Angelini Offgrid Solar via RE-wrenches
I hear 3 still can't use a generator from youtube. Pretty cool other than that. Dave Angelini Offgrid Solar "we go where powerlines don't" [1]https://offgridsolar1.com/ [2] [1] e-mail offgridso...@sti.net text 209 813 0060 On 2024-09-10 4:37 pm, Jason Szumlanski via RE-wrenches wrote: Ce

Re: [RE-wrenches] XWPro and SCP

2024-11-11 Thread Dave Angelini Offgrid Solar via RE-wrenches
Is this a new (not installed) or existing XW pro? Dave Angelini Offgrid Solar "we go where powerlines don't" [1]https://offgridsolar1.com/ [2] [1] e-mail offgridso...@sti.net text 209 813 0060 On 2024-11-11 2:22 pm, jay via RE-wrenches wrote: I know this has been discussed before but I co

Re: [RE-wrenches] XWPro and SCP

2024-11-11 Thread Dave Angelini Offgrid Solar via RE-wrenches
As long as you use the default grid config this is fine and as long as you do not need the advanced modes for LFP. If you need to change to IEEE , (offgrid) you need the gateway. Dave Angelini Offgrid Solar "we go where powerlines don't" [2]https://offgridsolar1.com/ [3] [2] e-mail of

Re: [RE-wrenches] OB Charging/Comms Issues

2024-11-08 Thread Dave Angelini Offgrid Solar via RE-wrenches
Sounds like a basic generator issue. Use another gen for test ! Dave Angelini Offgrid Solar "we go where powerlines don't" [1]https://offgridsolar1.com/ [2] [1] e-mail offgridso...@sti.net text 209 813 0060 On 2024-11-08 12:42 pm, Chris Sparadeo via RE-wrenches wrote: Hey wrenchers, I ha

Re: [RE-wrenches] favortie micro inverters?

2024-09-24 Thread Dave Angelini Offgrid Solar via RE-wrenches
I am with Chris except I might put them on a barn roof ! Never a residence and never Offgrid ! Dave Angelini Offgrid Solar "we go where powerlines don't" [3]https://offgridsolar1.com/ [4] [3] e-mail offgridso...@sti.net text 209 813 0060 On 2024-09-24 10:16 am, Chris Schaefer via RE-wrench

Re: [RE-wrenches] Frozen LPF batteries - damaged or salvageable?

2024-11-24 Thread Dave Angelini Offgrid Solar via RE-wrenches
Hey Kevin, Think the op and storage Temps are mixed up? Even so, pretty cold, even for electronics 😉 Bill in advance on this one ! The all in one's are hard to warm up to but... Good Luck! Dave Angelini Offgrid Solar "we go where powerlines don't" [1]https://offgridsolar1.com/ [2] [1] e-ma

Re: [RE-wrenches] Panel installation in snow country 0.02

2024-12-09 Thread Dave Angelini Offgrid Solar via RE-wrenches
Agree and I only turn on the vertical axis for snow season. For Offgrid the vertical axis is really not needed except for snow in my opinion. Cheers! Dave Angelini Offgrid Solar "we go where powerlines don't" [5]https://offgridsolar1.com/ [6] [5] e-mail offgridso...@sti.net text 209 813 0

Re: [RE-wrenches] Who makes this racking?

2025-02-10 Thread Dave Angelini Offgrid Solar via RE-wrenches
Wattsun HZLA or fixed mount. Not enough resolution to see... Dave Angelini Offgrid Solar "we go where powerlines don't" [1]https://offgridsolar1.com/ [2] [1] e-mail offgridso...@sti.net text 209 813 0060 On 2025-02-04 10:12 am, Michael Morningstar via RE-wrenches wrote: I've been looking f

[RE-wrenches] Silent mode

2024-12-16 Thread Dave Angelini Offgrid Solar via RE-wrenches
Heard that boB Gudgel passed! Rest in peace old friend! Will raise one tonight ! Dave Angelini Offgrid Solar "we go where powerlines don't" [1]https://offgridsolar1.com/ [2] [1] e-mail offgridso...@sti.net text 209 813 0060 Links: -- [1] http://members.sti.net/offgridsolar/ [2] http

Re: [RE-wrenches] PowerWall 3 in an off-grid system?

2024-12-21 Thread Dave Angelini Offgrid Solar via RE-wrenches
No warranty is no warranty. Would love it if Elon would go offgrid. The model 3 is almost there. I did build an xw into a powerwall with bad electronics. It is still running. Dave Angelini Offgrid Solar "we go where powerlines don't" [1]https://offgridsolar1.com/ [2] [1] e-mail offgridso.

Re: [RE-wrenches] PG&E NEM3.0

2025-01-14 Thread Dave Angelini Offgrid Solar via RE-wrenches
Sure count me in ! I like to learn as much as possible of how not to be like California. Most everyone who has left there tells me this also. Northern Nevada is 11.7 cents per KWH and is looking at new transmission lines to be independent of the folks to the west. Avoiding the NEM3.0 is prett

Re: [RE-wrenches] Zero sell permitting

2025-02-11 Thread Dave Angelini Offgrid Solar via RE-wrenches
Insurance could be denied in a claim if you do not have a building permit or at least approval of AHJ. Dave Angelini Offgrid Solar "we go where powerlines don't" [1]https://offgridsolar1.com/ [2] [1] e-mail offgridso...@sti.net text 209 813 0060 On 2025-02-11 1:26 pm, Jay via RE-wrenches w

Re: [RE-wrenches] mini splits

2025-03-14 Thread Dave Angelini Offgrid Solar via RE-wrenches
I think the bottom line for me is super low startup surge and then fairly consistent power draw once desired temperature is reached. I feel this is much easier to plan for off-grid rather than repeated start/stop cycles. Jason Szumlanski And extremely quiet which is a main reason to be offgri

Re: [RE-wrenches] mini splits

2025-03-14 Thread Dave Angelini Offgrid Solar via RE-wrenches
It would depend on the size of the split 😉 It would also depend on the SEER rating and the climate you are in. I try to only use the best model in the brand for Offgrid. It cost more for a reason and can run longer into the evening before using the battery. The smaller 33 SEER units work well a

Re: [RE-wrenches] Inverter ratings exceeding 25kw fir battery backup

2025-02-17 Thread Dave Angelini Offgrid Solar via RE-wrenches
Why is there a need for more than 25KW for residential please? Just curious. In Nevada, 25KW is way into commercial. Dave Angelini Offgrid Solar "we go where powerlines don't" [1]https://offgridsolar1.com/ [2] [1] e-mail offgridso...@sti.net text 209 813 0060 On 2025-02-17 9:43 am, Tyrone

Re: [RE-wrenches] Inverter ratings exceeding 25kw fir battery backup

2025-02-18 Thread Dave Angelini Offgrid Solar via RE-wrenches
ntractor EC13013208 On Mon, Feb 17, 2025 at 12:58 PM Dave Angelini Offgrid Solar via RE-wrenches wrote: Why is there a need for more than 25KW for residential please? Just curious. In Nevada, 25KW is way into commercial. Dave Angelini Offgrid Solar "we go where powerlines don't"

Re: [RE-wrenches] Inverter ratings exceeding 25kw fir battery backup

2025-02-18 Thread Dave Angelini Offgrid Solar via RE-wrenches
On Tue, Feb 18, 2025 at 11:56 AM Dave Angelini Offgrid Solar via RE-wrenches wrote: Sure I get how important it is to electrically heat a pool in a power outage. 😉 Dave An,gelini Offgrid Solar "we go where powerlines don't" [1]https://offgridsolar1.com/ [2] [1] e-mail offgrid

Re: [RE-wrenches] RSS: Is it necessary?

2025-02-17 Thread Dave Angelini Offgrid Solar via RE-wrenches
Get the offgrid permit (PRETTY RARE) and then remove anything that makes the system less reliable. We use to be concerned with losing insurance offgrid but the cost is so high now that we (offgrid folks) often self insure. Do anything that can make it easier for a fire crew, if they stay. They

Re: [RE-wrenches] Popping Sounds From Roof

2025-03-07 Thread Dave Angelini Offgrid Solar via RE-wrenches
I would investigate the roof ! The only thing that should be on an offgrid dwelling is snow, rain, or bird doo! Dave Angelini Offgrid Solar "we go where powerlines don't" [1]https://offgridsolar1.com/ [2] [1] e-mail offgridso...@sti.net text 209 813 0060 On 2025-03-05 1:11 pm, Christopher

Re: [RE-wrenches] Backup Mode Indicator for Whole Home Battery?

2025-02-27 Thread Dave Angelini Offgrid Solar via RE-wrenches
There is already a single LED in most utility meters that tells you the grid is on. I have marked it with a sharpie for a client. I suppose you want something for clipping on to the Grid input that can give an alarm in the house. Amazon had something that I used once. Will try and look it up.

Re: [RE-wrenches] mini splits

2025-03-13 Thread Dave Angelini Offgrid Solar via RE-wrenches
I was a beta tester for Sanyo offgrid mini splits in 2008. Been using splits ever since. Costco sells DIY along with HVAC in Florida. Also EG4 has DIY. The best from Fugitsu and the like are 30 + SEER and need a pro to pull a vacuumed. I no longer do the installs unless it is in Hawaii or a real

Re: [RE-wrenches] No Mistake Conspiricy?

2025-02-19 Thread Dave Angelini Offgrid Solar via RE-wrenches
No comment other than there ought to be a place on the list where "in the weeds" type subjects can be discussed. Totally agree that if you do not want to see off topic comments the current policy is fine. Freedom of speech right! Dave Angelini Offgrid Solar "we go where powerlines don't" [1

Re: [RE-wrenches] Source for 600V Ethernet Cable

2025-02-25 Thread Dave Angelini Offgrid Solar via RE-wrenches
At least for the last 18 months no AEE ! Dave Angelini Offgrid Solar "we go where powerlines don't" [1]https://offgridsolar1.com/ [2] [1] e-mail offgridso...@sti.net text 209 813 0060 On 2025-02-25 11:12 am, Lou Russo via RE-wrenches wrote: Aloha All, Confirmed. AEE store website is down

Re: [RE-wrenches] Midnite AIO Generator Functionality

2025-05-12 Thread Dave Angelini Offgrid Solar via RE-wrenches
All sounds wrong to me. Call Midnite. Typically there is a AC bypass mechanical switch that allows the gen to bypass the inverter and power loads. Dave Angelini Offgrid Solar "we go where powerlines don't" [1]https://offgridsolar1.com/ [2] [1] e-mail offgridso...@sti.net text 209 813 0060

Re: [RE-wrenches] More Off-Grid Whole House RO

2025-05-09 Thread Dave Angelini Offgrid Solar via RE-wrenches
Definitely get a good test ! If you do go rainwater and have copper water pipes, you need to be very careful with LOW PH rainwater ! Might have to raise PH or lose copper piping with rain. Dave Angelini Offgrid Solar "we go where powerlines don't" [2]https://offgridsolar1.com/ [3] [2] e-ma

Re: [RE-wrenches] Midnite AIO Generator Functionality

2025-05-12 Thread Dave Angelini Offgrid Solar via RE-wrenches
ack on automatically. Jason Szumlanski Principal Solar Designer | Florida Solar Design Group NABCEP Certified Solar Professional (PVIP) Florida State Certified Solar Contractor CVC56956 Florida Certified Electrical Contractor EC13013208 On Mon, May 12, 2025 at 9:49 AM Dave Angelini Offgrid Solar v

Re: [RE-wrenches] Midnite AIO Generator Functionality

2025-05-13 Thread Dave Angelini Offgrid Solar via RE-wrenches
er does not close the relay and turn the inverter back on automatically. Jason Szumlanski Principal Solar Designer | Florida Solar Design Group NABCEP Certified Solar Professional (PVIP) Florida State Certified Solar Contractor CVC56956 Florida Certified Electrical Contractor EC13013208 On Mo

Re: [RE-wrenches] Midnite AIO Generator Functionality

2025-05-12 Thread Dave Angelini Offgrid Solar via RE-wrenches
All sounds wrong to me. Call Outback. Typically there is a AC bypass mechanical switch that allows the gen to bypass the inverter and power loads. Dave Angelini Offgrid Solar "we go where powerlines don't" [1]https://offgridsolar1.com/ [2] [1] e-mail offgridso...@sti.net text 209 813 0060

Re: [RE-wrenches] Midnite AIO Generator Functionality

2025-05-13 Thread Dave Angelini Offgrid Solar via RE-wrenches
Certified Solar Contractor CVC56956 Florida Certified Electrical Contractor EC13013208 On Mon, May 12, 2025 at 9:49 AM Dave Angelini Offgrid Solar via RE-wrenches wrote: All sounds wrong to me. Call Midnite. Typically there is a AC bypass mechanical switch that allows the gen to bypass

Re: [RE-wrenches] LFP Inter-Battery Communication

2025-05-17 Thread Dave Angelini Offgrid Solar via RE-wrenches
Good info Maverick on the 3 hours. From Discover rack batts (5) & Schneider The closed loop charge voltage is around mid to high 55V, the current will only decrease once the target charge voltage is reached. You can see the target charge voltage on both lynk II and Schneider side. This will

Re: [RE-wrenches] LFP Inter-Battery Communication

2025-05-17 Thread Dave Angelini Offgrid Solar via RE-wrenches
Discover has been showing cell level since the beginning of LFP via lynk, Dashboard, and spread sheets. Much nicer now with Lynk2. Dave Angelini Offgrid Solar "we go where powerlines don't" [2]https://offgridsolar1.com/ [3] [2] e-mail offgridso...@sti.net text 209 813 0060 On 2025-05-17 8:

Re: [RE-wrenches] Context XW+ Random Factory Defaults

2025-05-31 Thread Dave Angelini Offgrid Solar via RE-wrenches
Monday thru Friday. They may tell you that XW+ is not a good match with LFP unless the user knows what they are doing. XW pro was made to close loop and communicate with the bms. Since there were no faults logged it sounds like the battery cut out before the XW LBCO, which is wrong as you know

Re: [RE-wrenches] Context XW+ Random Factory Defaults

2025-05-31 Thread Dave Angelini Offgrid Solar via RE-wrenches
Screens were from cloud but should be similar on SCP. Device numbers must be different! Dave Angelini Offgrid Solar "we go where powerlines don't" [1]https://offgridsolar1.com/ [2] [1] e-mail offgridso...@sti.net text 209 813 0060 On 2025-05-31 9:56 am, Dave Angelini Offgrid Solar

Re: [RE-wrenches] EG4 Mini Split

2025-06-19 Thread Dave Angelini Offgrid Solar via RE-wrenches
The EG4 is not a bad split. Reason my client wanted it was a redundant cooling back-up if his battery/inverter/solar went down. Definitely run AC to it from the main system. Getting close to the solstice and solar can power this well into the evening😎 Dave Angelini Offgrid Solar "we go where

Re: [RE-wrenches] EG4 Mini Split

2025-06-19 Thread Dave Angelini Offgrid Solar via RE-wrenches
Not doing rapid shutdown because the panels are not on a roof, ever! Dave Angelini Offgrid Solar "we go where powerlines don't" [1]https://offgridsolar1.com/ [2] [1] e-mail offgridso...@sti.net text 209 813 0060 On 2025-06-19 3:15 am, Jason Szumlanski via RE-wrenches wrote: I'm getting req

Re: [RE-wrenches] Solar thermal covering

2025-06-18 Thread Dave Angelini Offgrid Solar via RE-wrenches
Perfectly said August! Dave Angelini Offgrid Solar "we go where powerlines don't" [3]https://offgridsolar1.com/ [4] [3] e-mail offgridso...@sti.net text 209 813 0060 On 2025-06-18 2:24 pm, August Goers via RE-wrenches wrote: I have a soft spot for solar hot water, but alas it is obsolete i

Re: [RE-wrenches] Solar thermal covering

2025-06-17 Thread Dave Angelini Offgrid Solar via RE-wrenches
At that age, abandon system and use gas! I sure would not want to do this at 70, let alone 80. Keep it simple or you will be the one in the crosshair! Dave Angelini Offgrid Solar "we go where powerlines don't" [1]https://offgridsolar1.com/ [2] [1] e-mail offgridso...@sti.net text 209 813

Re: [RE-wrenches] Solar thermal covering

2025-06-16 Thread Dave Angelini Offgrid Solar via RE-wrenches
Ground mount collector with plywood over the panels you do not want to use. Dave Angelini Offgrid Solar "we go where powerlines don't" [1]https://offgridsolar1.com/ [2] [1] e-mail offgridso...@sti.net text 209 813 0060 On 2025-06-15 7:47 pm, Jerry Shafer via RE-wrenches wrote: Wrenches,

Re: [RE-wrenches] charging a 2017 Chevy Volt off-grid

2025-06-23 Thread Dave Angelini Offgrid Solar via RE-wrenches
Check the outlet with an ammeter and a hair dryer. You need a load! Make sure the current is correct and not a neutral issue of the inverter or wiring. I have a hair dryer that I know the current on. I also use this in split phase to make sure the 2 legs add to the correct current. Test that

Re: [RE-wrenches] Permitting problem

2025-06-25 Thread Dave Angelini Offgrid Solar via RE-wrenches
Nice install in the link! "However for this project I am being denied a permit with this reason: By not using one of SnapNRack's suggested support structures I am "altering" the "racking kit." I am told if I provide a structural analysis a permit will be approved." What is snapnracks suppo

Re: [RE-wrenches] BMS as OCOD

2025-07-15 Thread Dave Angelini Offgrid Solar via RE-wrenches
I agree as long as you have a long history with the battery/BMS. Since all of this is so new or constantly changing I would add a class T as it has a minor chance of being a failure item. When I was testing this for Schneider, even they added the T fuse for insurance as no-one had tested the

Re: [RE-wrenches] Pairing OB with Lithium

2025-06-29 Thread Dave Angelini Offgrid Solar via RE-wrenches
Are they using optics or are you and want to monitor? Do they need State of charge from the BMS into their system to monitor? Dave Angelini Offgrid Solar "we go where powerlines don't" [3]https://offgridsolar1.com/ [4] [3] e-mail offgridso...@sti.net text 209 813 0060 On 2025-06-28 8:04 p

Re: [RE-wrenches] Speaking of Outback

2025-06-29 Thread Dave Angelini Offgrid Solar via RE-wrenches
Hey Jay, Last post on the forum was June 19th. Optics worked for me on a client last week. I do not expect good things from what I read... The X feed on the old twitter for Outback power systems is https://x.com/OpticsRE I' ve heard all the Signature solar stuff, nothing new. A search from

Re: [RE-wrenches] Different LFP Batteries in Parallel

2025-07-14 Thread Dave Angelini Offgrid Solar via RE-wrenches
Does the client know that they can't blame you for doing something that has chances of being a bad choice? Can the client keep track of two different Soc and be responsible about it? I would also look into how a home insurance policy would react to a claim. Dave Angelini Offgrid Solar "we

Re: [RE-wrenches] Battery RSD

2025-07-29 Thread Dave Angelini Offgrid Solar via RE-wrenches
I know very little about Solark and happy about it. In the old days, Midnite and Schneider had a 10 dollar switch that would shut down the inverter from outside. When I had to use this it was great as I could just remove it after the bozo, I mean inspector left. If he really wants a knife swit

Re: [RE-wrenches] Battery RSD

2025-07-29 Thread Dave Angelini Offgrid Solar via RE-wrenches
Things like this do happen sometimes. I do not have time for these and know it will not do much good most of the time. Do what the inspector (bozo) wants and fix it after he is gone. Dave Angelini Offgrid Solar "we go where powerlines don't" [6]https://offgridsolar1.com/ [7] [6] e-mail off

<    1   2