Re: [RE-wrenches] Panel installation in snow country 0.02

2024-12-08 Thread Garrison via RE-wrenches
Hi Howie,I have found one scenario where heat tape can help with snow on solar.As we know, solar panels warm up in the sun and melt snow even when ambient temperatures are below freezing. The water from this melting snow drips off the array and slush/snow can slide off the panels.On a cold day, in

Re: [RE-wrenches] SolarEdge Battery question

2024-09-30 Thread Garrison via RE-wrenches
Hi Jason,On a recent install 2 of 3 new batteries had a low SOE and failed the self test. This made sense as part of the self test is discharging the battery, which you wouldn’t want to do if the batteries are depleted. Anyway, the low SOE batteries also had trouble “associating” with the inverter

Re: [RE-wrenches] Snapnrack end caps

2023-07-05 Thread Garrison via RE-wrenches
/contraction is popping them off. Best, Garrison Riegel Celestar Solar LLC > On Jul 5, 2023, at 3:51 PM, Drake Chamberlin via RE-wrenches > wrote: > >  > Hello All, > > We have had a lot of end caps fall off Snapnrack Ultra Rail. Kevin at S&R was > wondering if

Re: [RE-wrenches] Truss finder

2023-04-17 Thread Garrison via RE-wrenches
be barely covered by the "flashing". Best, Garrison Riegel Licensed Electrician NABCEP Certified PV Installation Professional™ (c) 773-515-5168 (e) garri...@celestarsolar.com On Sun, Apr 16, 2023 at 10:13 AM Kristopher Schmid via RE-wrenches < re-wrenches@lists.re-wrenches.org>

Re: [RE-wrenches] Utility transformer limitations

2022-12-25 Thread Garrison via RE-wrenches
recent situation where a 40kW DC system had exceeded a utility transformer by only 2kW AC, so a simple redesign avoided an $8k invoice from the utility. The utility was not transparent about this option at first and only made it clear after some persistence.Good luck,Garrison RiegelCelestar SolarOn

Re: [RE-wrenches] Has anyone ever had one of his customers get a note from SolarEdge like this one?

2022-08-15 Thread Garrison via RE-wrenches
not your fault. I hope they change their attitude, but I’m not confident people at the top understand how bad support has become. The focus seems to be on marketing new products. Best, Garrison Riegel Celestar Solar (c) 773-515-5168 (e) garri...@celestarsolar.com > On Aug 15, 2022, at 10

Re: [RE-wrenches] Removing paint from solar modules

2022-04-15 Thread Garrison via RE-wrenches
Hi Mac, I second the isopropyl alcohol (diluted), a soft cloth, and razor blade if needed. Magic erasers would probably work too, but I believe they are made from very hard microscopic crystals. Good luck. Garrison Riegel Celestar Solar LLC > On Apr 15, 2022, at 9:45 AM, Dana Orzel via

Re: [RE-wrenches] Imax disturbance Error

2022-01-09 Thread Garrison
! Garrison Riegel Celestar Solar > On Jan 9, 2022, at 11:55 AM, Marco Mangelsdorf wrote: > > Hey Mac, > > It’s been my experience over the years that the Imax failure is fatal. > > marco > >> On Sunday, January 9, 2022, Mac Lewis wrote: >> Hello Wrenches, >>

Re: [RE-wrenches] Design Software?

2020-10-19 Thread Garrison
on a bar napkin would produce a better single line diagram :). Best, Garrison > On Oct 19, 2020, at 2:24 PM, Philip Lawes Insoltech > wrote: > >  > Aurora > > > > > Philip N Lawes > 172 Wave St. > Laguna Beach, Ca. 92651 > Office: 949-497-63

Re: [RE-wrenches] Commercial three phase inverter @208V

2020-09-18 Thread Garrison
ength, equipment location, etc. Best, Garrison Riegel On Fri, Sep 18, 2020 at 5:31 PM August Goers wrote: > We have a similar size system in the works and a designer recommended > Dongan transformers: https://dongan.com/product/ > > I have not sourced them or worked with them yet, but the

Re: [RE-wrenches] Contract permit packets

2020-02-05 Thread Garrison
I will also vouch for Jeff and team at Planet Plan Sets. I started using them for overflow but they are becoming a primary resource for grid tie, battery, and commercial plan sets. Highly recommend. Garrison Riegel Rethink Electric > On Feb 5, 2020, at 1:44 PM, jay wrote: > > H

Re: [RE-wrenches] Curved solar mounting

2019-02-08 Thread Garrison
Have you looked at the Lumos system? They are not cheap, but look nice, and would work well in this application. The rail has integrated wire management. https://lumossolar.com/ Sunny regards, Garrison Riegel Rethink Electric On Thu, Feb 7, 2019 at 8:06 AM Jason Szumlanski <

Re: [RE-wrenches] Neutral sizing

2018-09-22 Thread Garrison
phase inverters these days do not require a neutral at all, so if the AHJ will not accept downsizing it may be worth changing inverters. Garrison > On Sep 22, 2018, at 6:07 PM, Glenn Burt wrote: > > Here is the code reference explaining this conductor size disparity from 20

Re: [RE-wrenches] Tapping Parallel Conductors

2018-08-22 Thread Garrison
system then what’s the threshold? Thanks for any and all thoughts on this. Garrison > On Aug 21, 2018, at 11:02 AM, August Goers wrote: > > Hi Garrison, > > This is a new one for me - normally we always balance everything when dealing > with paralleled conductors. NEC 310

Re: [RE-wrenches] Tapping Parallel Conductors

2018-08-21 Thread Garrison
each set of three. Plans are stamped by an EE. I had been working under the assumption that if tapping parallel sets all conductors must be tapped. Any issues with not tapping all sets? Thanks, Garrison Riegel Rethink Electric 630-998-3629 ___ List

[RE-wrenches] Square D Recall

2018-04-19 Thread Garrison
-recalls-square-d-safety-switches-due-to-electrical-shock-hazard Be careful out there! Garrison Riegel Rethink Electric___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings:

Re: [RE-wrenches] PV ratings

2017-02-21 Thread Garrison Riegel
d.com/2015/2015-scorecard.php I haven't seen a performance comparison in a few years. You can find the Photon module yield tests up until 2014 online, but even those were limited to sometimes one model from a manufacturer which did not necessarily represent the available technology. Gar

Re: [RE-wrenches] Solar World Wind Damage

2017-01-16 Thread Garrison Riegel
also now listed to UL 2703, which could be a benefit over a custom solution. https://www.pvracking.com/ground-mounting-systems/overview/ Garrison Garrison Riegel PV Manager | Solar Service Inc<http://www.solarserviceinc.com/> [p] 847-677-0950 | garri...@solarserviceinc.com<mai

Re: [RE-wrenches] Solar World Wind Damage

2017-01-13 Thread Garrison Riegel
also now listed to UL 2703, which is helpful. https://www.pvracking.com/ground-mounting-systems/overview/ Garrison Garrison Riegel PV Manager | Solar Service Inc<http://www.solarserviceinc.com/> [p] 847-677-0950 | garri...@solarserviceinc.com<mailto:garri...@solarserviceinc.com

[RE-wrenches] Awning Mount Racking

2016-09-27 Thread Garrison Riegel
, Garrison Riegel PV Manager | Solar Service Inc<http://www.solarserviceinc.com/> [p] 847-677-0950 | garri...@solarserviceinc.com<mailto:garri...@solarserviceinc.com> NABCEP Certified PV Installation Professional™ ___ List sponsored by Redw

Re: [RE-wrenches] SMA Tripower

2016-09-01 Thread Garrison Riegel
low us to round down and the AHJ deems it acceptable. Just another gray area in the Code that keeps life exciting! Think I need to get out more... Garrison From: RE-wrenches on behalf of Rebekah Hren Sent: Thursday, September 1, 2016 9:31:23 AM To: RE-wrenc

Re: [RE-wrenches] SMA Tripower

2016-09-01 Thread Garrison Riegel
Hi Brian, Can we not invoke Art. 220.5(B) Fractions of an Ampere to round down to a 30A OCPD in this case? I suppose that .1 could be pretty significant when combining many of these inverters. Garrison Riegel Solar Service Inc On Aug 31, 2016, at 11:24 PM, Brian Mehalic mailto:br

Re: [RE-wrenches] Roof harness

2016-06-01 Thread Garrison Riegel
. Thanks, Garrison Riegel Solar Service Inc. From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Dan Fink Sent: Monday, May 30, 2016 2:04 PM To: RE-wrenches Subject: Re: [RE-wrenches] Roof harness The back dorsal D-ring is the ONLY place fall-arrest equipment should

Re: [RE-wrenches] supply side connection

2016-05-16 Thread Garrison Riegel
Hi Jay, I've used the Milbank K4977 taps for a few supply side connections in Milbank meter sockets. They make for a fast and clean connection. I would highly recommend them as long the utility will allow it. Best, Garrison Garrison Riegel Solar Service Inc -Original Me

Re: [RE-wrenches] 480 single phase delta

2016-04-29 Thread Garrison Riegel
The newer Tripower STP3 can be configured for delta, but the 12000-24000 cannot. A step up transformer sounds like the way to go. Best, Garrison Garrison Riegel Solar Service Inc From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of jerrysgarage01 Sent

Re: [RE-wrenches] Rooftop disconnect for multi tracker TLs

2016-01-26 Thread Garrison Riegel
I would have recommended SolarBOS here as well, but as of Jan 1 2016 they require a minimum 20 piece order. They also have not yet set up a distributor for smaller orders…seems like an oversight. Plan accordingly. Garrison Riegel PV Operations Manager | Solar Service Inc<h

Re: [RE-wrenches] Can anyone identify this mounting system and module

2015-10-22 Thread Garrison Riegel
It looks like the Westinghouse AC module system. Pretty sure these are no longer available. Garrison Riegel PV Operations Manager | <http://www.solarserviceinc.com/> Solar Service Inc [p] 847-677-0950 | <mailto:garri...@solarserviceinc.com> garri...@solarserviceinc.co

Re: [RE-wrenches] Racking for Steep Roofs

2015-10-16 Thread Garrison Riegel
Thanks Allan. I’ll see if I can get those values from IronRidge or UniRac. If not Pro Solar or SnapNrack look like they both could work well. Thanks again all. Garrison From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Allan Sindelar Sent: Thursday

Re: [RE-wrenches] Racking for Steep Roofs

2015-10-15 Thread Garrison Riegel
. Mid clamps should hold no problem. They suggested getting an engineer to stamp a custom bolted end clamp solution and we should be good. I’ve been looking for a good excuse to try Snap n Rack… Thanks, Garrison From: RE-wrenches [mailto:re-wrenches-boun...@lists.re

[RE-wrenches] Racking for Steep Roofs

2015-10-14 Thread Garrison Riegel
according to their design tools and manuals. Any advice would be much appreciated. Thanks, Garrison Garrison Riegel PV Operations Manager | <http://www.solarserviceinc.com/> Solar Service Inc [p] 847-677-0950 | <mailto:garri...@solarserviceinc.com> garri...@solarse

Re: [RE-wrenches] Serviceable equipment on a roof

2015-08-13 Thread Garrison Riegel
not apply. Permanent anchors also sound like a good, although expensive solution. Garrison Garrison Riegel PV Operations Manager | <http://www.solarserviceinc.com/> Solar Service Inc [p] 847-677-0950 | <mailto:garri...@solarserviceinc.com> garri...@solarserviceinc.co

Re: [RE-wrenches] Genasun

2015-06-24 Thread Garrison Riegel
Looks like a good fit for either a SunPower or Kyocera. Although with SunPower you might be paying as much for the single module as you did for the cart... Garrison Riegel PV Operations Manager | Solar Service Inc [p] 847-677-0950 | garri...@solarserviceinc.com NABCEP Certified PV Installation

Re: [RE-wrenches] Integrating with Lightning Protection

2015-06-05 Thread Garrison Riegel
approach, which sounds like the safest design especially when this “separation distance” can be maintained. Thanks all for the replies. Much appreciated. Garrison From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Glenn Burt Sent: Thursday, June

[RE-wrenches] Integrating with Lightning Protection

2015-06-04 Thread Garrison Riegel
bond these systems on the roof? Opinions on a 2009 Wrenches thread varied, but I've heard it from a few sources that these should be bonded directly. Wondering if there is a general consensus at this point? Or strong opinions one way or the other? Thanks for your thoughts. Garrison R

Re: [RE-wrenches] Copper bar current capacity?

2015-04-29 Thread Garrison Riegel
Hi Larry, It sounds like the Copper Development Association would agree. Take a look at this table on DC copper bus bar ampacities: http://www.copper.org/applications/electrical/busbar/busbar_ampacities.html Best, Garrison Riegel PV Operations Manager | Solar Service Inc [p] 847-677-0950

Re: [RE-wrenches] Fall Protection Equipment

2015-01-19 Thread Garrison Riegel
, Garrison Garrison Riegel PV Operations Manager | <http://www.solarserviceinc.com/> Solar Service Inc [p] 847-677-0950 | <mailto:garri...@solarserviceinc.com> garri...@solarserviceinc.com NABCEP Certified PV Installation Professional™ From: RE-wrenches [mailto:re-w

[RE-wrenches] Preventing 24/7 Transformer Losses

2014-11-14 Thread Garrison Riegel
g might be referring to? What are folks doing to mitigate these losses? Some kind of DC actuated switch on the utility side of the transformer maybe? Anything else to keep in mind when specifying a PV specific transformer? Thank you for your thoughts. Garrison Garrison Riege

Re: [RE-wrenches] Mounting height

2014-10-22 Thread Garrison Riegel
that would be the minimum. Garrison Garrison Riegel Project Manager | <http://www.solarserviceinc.com/> Solar Service Inc [p] 847-677-0950 | <mailto:garri...@solarserviceinc.com> garri...@solarserviceinc.com NABCEP Certified PV Installation Professional™ From:

Re: [RE-wrenches] Fall Protection Recommendations?

2014-10-07 Thread Garrison Riegel
l for lower slopes. Also check out their HitchClip. It is an excellent anchor for shingled, pitched roofs. http://www.guardianfall.com/performance-safety-products/anchor-points/reside ntial-anchor-points/hitchclip Garrison Riegel Project Manager | <http://www.solarserviceinc.com/> So

Re: [RE-wrenches] Conflict between solar PV and Zigbee-based home automation??

2014-07-29 Thread Garrison Riegel
Maybe the tech folks at SolarEdge could provide some advice. They use ZigBee to communicate wirelessly with their inverters, and it has worked flawlessly in my experience. Garrison Riegel Project Manager | <http://www.solarserviceinc.com/> Solar Service Inc [p] 847-67

Re: [RE-wrenches] Three Inverters, One Disconnect?

2014-04-05 Thread Garrison Riegel
Got it, thanks Bill. Single phase breakers for the inverters, 3-pole switch for the disconnect it will be. Thanks, Garrison From: Bill Brooks [mailto:billbroo...@yahoo.com] Sent: Friday, April 04, 2014 6:05 PM To: 'Garrison Riegel'; 'RE-wrenches' Subject: RE:

Re: [RE-wrenches] Three Inverters, One Disconnect?

2014-04-04 Thread Garrison Riegel
said, they do often listen to logic and reason if you can get through to the right people. Do you have an opinion on using a single 3-pole unfused switch as an AC disconnect for 3 single phase inverters? Good, bad, or ugly? Thanks, Garrison From: Bill Brooks [mailto:billbroo

Re: [RE-wrenches] Three Inverters, One Disconnect?

2014-04-04 Thread Garrison Riegel
thought each inverter required a dedicated breaker as per 705.12(D)(1). Thoughts? Thanks, Garrison From: d...@energysolarnow.com [mailto:d...@energysolarnow.com] Sent: Thursday, April 03, 2014 1:55 PM To: re-wrenches@lists.re-wrenches.org; Garrison Riegel Subject: RE: [RE-wrenches

[RE-wrenches] Three Inverters, One Disconnect?

2014-04-02 Thread Garrison Riegel
] AC disconnect before landing at each 1-pole 20A breaker in the main panel? It would be great to avoid an inverter subpanel and 3-pole breaker in the MDP if possible. Thanks for your thoughts. Garrison Garrison Riegel Project Manager | <http://www.solarserviceinc.com/> Solar Servi

Re: [RE-wrenches] Solar Carport on a Parking Ramp

2014-02-06 Thread Garrison Riegel
tell you it will likely not pass structural when installed on top of a parking garage without significant structural reinforcement. Good luck! Garrison Riegel PV Operations Manager | <http://www.solarserviceinc.com/> Solar Service Inc [p] 847-677-0950 | <mailto:garri...@solar

Re: [RE-wrenches] Fronius Installer Support Sucks- but who else?

2013-10-18 Thread Garrison Riegel
of this, in some cases it can actually restore imbalance since many buildings with 240 delta have few if any loads on the high leg. Contrary to their manual, Power-One also claims their smaller PVI inverters are compatible with 240 high-leg delta. Garrison Garrison Riegel Project

Re: [RE-wrenches] Fronius Installer Support Sucks- but who else?

2013-10-16 Thread Garrison Riegel
more than four units require a hardwire to the Cluster Controller. I was definitely hoping for Bluetooth. It worked well with the SunnyBoys. Hopefully they will add this to the TriPowers in the future. Garrison Riegel Project Manager | <http://www.solarserviceinc.com/> Solar Service

Re: [RE-wrenches] transformerless inverters and conductor colors // PV Wire

2013-09-27 Thread Garrison Riegel
t it is listed to UL 4703. http://ulstandardsinfonet.ul.com/outscope/outscope.asp?fn=4703.html Cheers, Garrison Garrison Riegel Project Manager | <http://www.solarserviceinc.com/> Solar Service Inc [p] 847-677-0950 | <mailto:garri...@solarserviceinc.com> garri...@solarser

Re: [RE-wrenches] Flat Roof PV Attachments with Tapered Insulation

2013-09-11 Thread Garrison Riegel
hop make them for us. Windsafe spec: http://www.schletter.us/support/Windsafe_Product_Sheet.pdf Stanchions on page 9: http://www.schletter.us/support/I43%20Component_OV.pdf Best Garrison Riegel Project Manager | <http://www.solarserviceinc.com/> Solar Service Inc [p] 847

Re: [RE-wrenches] double-insulated PV wire

2013-08-30 Thread Garrison Riegel
ire for a pretty decent price. www.pv-cables.com may also be a good resource for you. Garrison From: re-wrenches-boun...@lists.re-wrenches.org [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Marco Mangelsdorf Sent: Friday, August 30, 2013 1:59 PM To: 'RE-wrenches&#x

Re: [RE-wrenches] Combining Enphase M190 and M215 on same circuit

2013-05-20 Thread Garrison Riegel
Hi Jason, We have paralleled M190 with M215 and have had no comm issues.yet. Enphase gave their blessing as well. Garrison Riegel Project Manager | <http://www.solarserviceinc.com/> Solar Service Inc [p] 847-677-0950 | <mailto:garri...@solarserviceinc.com> garri...@solarse

Re: [RE-wrenches] Modules approved for horizontal mounting

2013-04-22 Thread Garrison Riegel
White efflorescence, or glass disease, is also mentioned in a number of installation manuals as a reason not to install modules horizontally. Sounds pretty serious. Garrison Garrison Riegel Project Manager | <http://www.solarserviceinc.com/> Solar Service Inc [p] 847-67

Re: [RE-wrenches] Fuse sizing in battery circuits

2013-04-17 Thread Garrison Riegel
on to the water main, but I suppose you could simply install a rod, bond it to the water main, and use #6 copper for the DC GEC. Thanks, Garrison -Original Message- From: re-wrenches-boun...@lists.re-wrenches.org [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Ray Walters

Re: [RE-wrenches] Fuse sizing in battery circuits

2013-04-16 Thread Garrison Riegel
) through (E). So if the GE is a water main wouldn't the GEC "need" to be 4/0, if the battery cables were 4/0? Not saying it makes sense, especially if the water main is 3/4", but this has always made me wonder. Thoughts? Garrison Riegel Project Manager | Solar Service Inc [p]

Re: [RE-wrenches] Conductor Sizing for Supply Side Connection

2013-03-01 Thread Garrison Reigel
Good point Ross. The panel is marked as a 200A with no indication that the bus has a higher rating, so I've assumed 200A. I considered downsizing the MB, but it's an discontinued panel, and filled to capacity so not exactly ideal. Thanks, Garrison ___

Re: [RE-wrenches] Conductor Sizing for Supply Side Connection

2013-02-28 Thread Garrison Riegel
Great point Dave. It crossed my mind that it was technically possible, but figured since I would be removing loads off the main panel it was highly unlikely. Thanks for the code reference. I'll go load side, and be prepared for some discussion. Thanks, Garrison From: re-wre

Re: [RE-wrenches] Conductor Sizing for Supply Side Connection

2013-02-28 Thread Garrison Riegel
less than 30A, but based on this conversation I plan to go with a 60A and try to convince the AHJ that it will be code compliant in their future! Thanks, Garrison From: re-wrenches-boun...@lists.re-wrenches.org [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Allan Sin

Re: [RE-wrenches] Conductor Sizing for Supply Side Connection

2013-02-28 Thread Garrison Riegel
CPD at the main panel. Your explanation makes more sense, but I wonder why then they don't list the AC input breaker size as 60A max. If you have few backup loads, and are not on the 2011 NEC, a 40A could theoretically be fine? Thanks all for your thoughts, much appreciated. Garr

Re: [RE-wrenches] Conductor Sizing for Supply Side Connection

2013-02-27 Thread Garrison Riegel
NEC would allow this as a load side connection, so maybe I should spend my energy trying to convince them to let us follow the current Code instead. Thanks much, Garrison From: re-wrenches-boun...@lists.re-wrenches.org [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of August

[RE-wrenches] Conductor Sizing for Supply Side Connection

2013-02-27 Thread Garrison Riegel
rely for a residential supply side connection? Thanks in advance, Garrison 847-677-0950 Solar Service Inc. ___ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Change email address & settings: h

Re: [RE-wrenches] Snow guards for pitched roof arrays?

2013-02-08 Thread Garrison Riegel
Have you considered installing a flashing like the EcoFasten GF-1, lagging the L-foot to the rafter, and then spanning the L-feet with some AL angle? We use flashings similarly for supporting conduit on roofs, which works very well. Garrison Solar Service Inc 847-677-0950 From: re

Re: [RE-wrenches] getting PV modules up to the roof

2013-02-07 Thread Garrison Riegel
ut is OSHA compliant, can lift multiple modules at once, and saves wear and tear on the crew. The only real issue is upfront cost, but this is cheap when compared to the long term cost of a workman’s comp claim. My 2¢ Garrison Solar Service Inc 847-677-0950 From: re-wre

Re: [RE-wrenches] high insolation value and inverter undersizing

2013-01-28 Thread Garrison Riegel
orientation. Garrison Riegel Solar Service Inc [p] 847-677-0950 <http://www.solarserviceinc.com/> www.solarserviceinc.com NABCEP Certified Solar PV and Thermal Installer™ From: re-wrenches-boun...@lists.re-wrenches.org [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Beh

Re: [RE-wrenches] Protecting/Cleaning un-connected MC Connectors

2012-11-26 Thread Garrison Riegel
he surface. Some parts cleaners can cause damage, and may void the module warranty if you have to replace the connector. Garrison Riegel Project Manager Solar Service Inc [p] 847-677-0950 <http://www.solarserviceinc.com/> www.solarserviceinc.com NABCEP Certified Sola

Re: [RE-wrenches] AET Rayport array #1

2012-08-23 Thread Garrison Riegel
would recommend either a slip sheet under the trays or you use the AET ballast pad to protect the roof membrane. Good luck! Garrison Garrison Riegel Project Manager Solar Service Inc [p] 847-677-0950 [f] 847-647-9360 www.solarserviceinc.com <http://www.solarserviceinc.

Re: [RE-wrenches] S5! question

2012-08-20 Thread Garrison Riegel
Agreed, standard S-5! with L-foot and rail allows for the easiest install and most flexibility. We also stagger the clamps as much as possible to hit as many seams as possible. Also, make sure the pans are installed correctly as they will be the weakest link. Garrison Garrison Riegel

Re: [RE-wrenches] Booster pump

2012-08-20 Thread Garrison Riegel
n the circulators. Garrison Garrison Riegel Project Manager Solar Service Inc [p] 847-677-0950 [f] 847-647-9360 www.solarserviceinc.com <http://www.solarserviceinc.com/> NABCEP Certified Solar PV and Thermal InstallerT _ From: re-wrenches-boun...@lists.re-w

Re: [RE-wrenches] DC GEC Sizing Issue - Water Main GE

2012-07-25 Thread Garrison Riegel
e are many different configuration possibilities and the Code cannot be rewritten for each one. Thanks again, Garrison Garrison Riegel Project Manager Solar Service Inc [p] 847-677-0950 [f] 847-647-9360 www.solarserviceinc.com NABCEP Certified Solar PV and Thermal InstallerT -Origin

Re: [RE-wrenches] DC GEC Sizing Issue - Water Main GE

2012-07-23 Thread Garrison Riegel
metal conduit. That said they have been known to allow certain exceptions if it meets the latest NEC cycle (and they are in a good mood). Thank you again for your time and knowledge. It is much appreciated. Garrison Garrison Riegel Project Manager Solar Service Inc [p] 847-677-0950 [f] 847-647-

[RE-wrenches] DC GEC Sizing Issue - Water Main GE

2012-07-20 Thread Garrison Riegel
llest size allowed)? Thank you in advance, Garrison Garrison Riegel Project Manager Solar Service Inc [p] 847-677-0950 www.solarserviceinc.com <http://www.solarserviceinc.com/> NABCEP Certified Solar PV and Thermal InstallerT

Re: [RE-wrenches] L feet no flashing in shingle roof

2012-07-03 Thread Garrison Riegel
K RSS (self tapping structural screw). The combination works great and does not require a pilot hole. RSS: http://www.grkfasteners.com/en/RSS_1_2_information.htm GF1 http://ecofastensolar.com/pdf/GF1%20Cutsheets.pdf Best, Garrison Riegel Project Manager Solar Service Inc [p] 84

Re: [RE-wrenches] poly tape

2012-05-25 Thread Garrison Riegel
Another one to check out is EternaBond Double Stick. We get it in 2" wide rolls which fit most L-Feet perfectly. http://www.bigrocksupply.com/store/Search.aspx?searchTerms=eternabond%20doub le&submit=true&type=AND Garrison Riegel Solar Service Inc [p] 847-677-0950 www.solars