Thanks for the reference Brian and the link Jarmo.  Thanks also Glenn for the 
NEC reference, which is consistent with Dehn saying that PV systems on roofs 
should be bonded to lightning protection systems if the required “separation 
distance” cannot be maintained.  If this separation distance is not maintained 
then “flashover” could jump from the LPS to the array possibly resulting in 
fire.  This separation distance is based on a number of site specific factors 
and is not necessarily easy to determine unfortunately.  It looks like the 
distance will be just over 3’ for the project I’m working on…assuming I did my 
calculations correctly.        

 

Interestingly Dehn says that on buildings with metal roofs there is no way to 
maintain the necessary separation distance and therefore the PV array needs to 
be directly connected to the external LPS in all cases.

 

Ray, I like your approach, which sounds like the safest design especially when 
this “separation distance” can be maintained. 

 

Thanks all for the replies.  Much appreciated.

 

Garrison       

 

From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf 
Of Glenn Burt
Sent: Thursday, June 04, 2015 3:46 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Integrating with Lightning Protection

 

Have you looked at NFPA 780-2011, standard for the installation of lightning 
protection systems as mentioned in 250.106?

I recently read somewhere else that any conductive material in contact with or 
in the vicinity of a LPS has a negative effect on the designed efficiency of 
the LPS, but have not investigated further.

Sincerely,
Glenn Burt
Sent from my 'smart' phone so please excuse grammar and typos.

  _____  

From:  <mailto:garri...@solarserviceinc.com> Garrison Riegel
Sent: ‎6/‎4/‎2015 14:03
To:  <mailto:re-wrenches@lists.re-wrenches.org> 'RE-wrenches'
Subject: [RE-wrenches]  Integrating with Lightning Protection

Wrenches,

 

Does anyone have any best practice recommendations (or books, articles, etc) 
for integrating a roof mounted PV system with a lightning protection system?  
Bare #6 copper and a split bolt to the braided copper connecting air terminals? 
 At both ends of the array?

 

Or should we not bond these systems on the roof?  Opinions on a 2009 Wrenches 
thread varied, but I’ve heard it from a few sources that these should be bonded 
directly.  Wondering if there is a general consensus at this point?  Or strong 
opinions one way or the other?

 

Thanks for your thoughts.

 

Garrison Riegel

PV Operations Manager |  <http://www.solarserviceinc.com/> Solar Service Inc

[p] 847-677-0950 |  <mailto:garri...@solarserviceinc.com> 
garri...@solarserviceinc.com

 

NABCEP Certified PV Installation Professional™

 

 

_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to