Hello Wrenches,
In my area we end up installing a lot of systems on 240V 3Ph high leg services. To allow for more inverter options (like TL that require a neutral) it seems like using a transformer would a good idea, but it is hard to justify the losses under load and especially 24/7 losses required to keep the core magnetized. In a recent post on this same subject by Greg Smith from SMA he wrote, "If you specify a transformer specifically for solar PV designs then the losses are negligible." The transformer tech people at the manufacturers I spoken with have no idea what this means. I emailed Greg for clarification but have not yet had a reply. On a recent project that needed a 30KVA transformer the 24/7 losses were 200-300W depending on manufacturer, which is not negligible, and in my area would require about 2kW of PV to offset. Does anyone know what Greg might be referring to? What are folks doing to mitigate these losses? Some kind of DC actuated switch on the utility side of the transformer maybe? Anything else to keep in mind when specifying a PV specific transformer? Thank you for your thoughts. Garrison Garrison Riegel Project Manager | <http://www.solarserviceinc.com/> Solar Service Inc [p] 847-677-0950 | <mailto:garri...@solarserviceinc.com> garri...@solarserviceinc.com NABCEP Certified PV Installation ProfessionalT
_______________________________________________ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org