Wrenches,
On an upcoming job we have a Xantrex XW4548 interconnecting with a 200A service, and I'd very much appreciate some advice if y'all are willing. Since the inverter output OCPD is required to be 60A we are looking at a supply side connection, and I have two questions: 1. Before the point of interconnection the inverter output circuit will first pass through the XW Power Distribution Panel and inverter bypass, which is essentially a 60A breaker. The service disconnect for the supply side connection will also be fused at 60A. Does the 120% rule apply to the conductor between these two OCPDs? Or since this is a supply side connection in accordance with 690.64(A), 690.64(B)(2) will not apply? [this AHJ is on the 2008 NEC] 2. Can anyone recommend a reliable insulation piercing tap connector? Or would you recommend something else entirely for a residential supply side connection? Thanks in advance, Garrison 847-677-0950 Solar Service Inc.
_______________________________________________ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Change email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org